Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon
  #2   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,247
Default generator circuit

On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:

Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.

Correction: epic fail, not just ordinary fail.
  #3   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 8
Default generator circuit



"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?

  #4   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 8,589
Default generator circuit

On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:

On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:

Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.

Correction: epic fail, not just ordinary fail.


Don't feed the troll.
  #5   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 168
Default generator circuit

On Aug 29, 12:16*am, "Jon" wrote:
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Jon
since there is still a connection to the service disconnect you have a
single point of failure. If anyone were to close the service
disconnect a short pulse of current would be imposed on the service
entry conductors. It takes a few milliamperes to kill. I'm sure you
believe that this can never happen but your belief does not make your
circuit good practice. The addition of an auxiliary contact, of the
break before make type, to the Service Disconnecting Means switch or
breaker would add the human factor safeguard that is missing. With
that auxiliary contact any closing of the Service Disconnecting Means
would cause your contactor to drop out and thus disconnect the
generator from the load wiring before that wiring could be physically
connected to the Service Entry Conductors. Even better would be to
add a shunt trip to the Service Disconnecting Means. A shunt trip
would open the Service Disconnecting Means breaker. If the Service
Disconnecting Means is a fused switch You would need to add an
enclosed breaker to serve as the shunt trip device. Everything should
be wired so that any failure of the Generator provided control current
to go to the house and back will prevent the contactor at the
generator from closing. The only vulnerability in that scheme is the
possibility of a short circuit in the control circuit that would close
the contactor without the auxiliary contacts at the Service
Disconnecting Means actually being closed to pass the current. Since
you only need two control wires to make the contactor work and you
have three you could use one to pull in a control relay located at the
contactor to complete its coil circuit. That control current would
only be present if the auxiliary contact on the Service Disconnecting
Means has changed position in response to the Service Disconnecting
Means having been opened or the shunt trip having operated. This
would eliminate the need for a control relay at the Service
Disconnecting Means although continuing to use it would do no harm.
--
Tom Horne


  #6   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit

On Aug 29, 4:48*pm, "
wrote:
On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:


Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.


Correction: epic fail, not just ordinary fail.


Don't feed the troll


Mr. Keith have you finally taken control over that crack addiction of
yours.I am hoping to help many of you trolls to recover from your
addictions and return you back into normal contributing members of
society...Don't forget to make an appointment to see me next week...if
you are uncomfortable with that, then go see your nearest
practitioner.
Thank you, Come again.
Dr. Ury
  #7   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 14
Default generator circuit

On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:

Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html


We've been through this, WTF is so hard about using a DPDT 240v coil
contactor/relay? Wire the coil and the N.O. contacts to the utility power,
the common contacts to the load, and the generator feeds to the N.C.
contacts. Whenever the utility power is lost the relay drops out and swaps
the load over from utility to generator power. You can also get a bit fancy
an add an auto-start circuit for the generator if you so desire.

  #8   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 8,589
Default generator circuit

On Sun, 29 Aug 2010 14:34:28 -0700 (PDT), "Dr. Inj Ury Phd."
wrote:

On Aug 29, 4:48*pm, "
wrote:
On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:


Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.


Correction: epic fail, not just ordinary fail.


Don't feed the troll


Mr. Keith have you finally taken control over that crack addiction of
yours.I am hoping to help many of you trolls to recover from your
addictions and return you back into normal contributing members of
society...Don't forget to make an appointment to see me next week...if
you are uncomfortable with that, then go see your nearest
practitioner.
Thank you, Come again.
Dr. Ury


Yes, AlwaysWrong, we all know who you are...
  #9   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 3
Default generator circuit


"PeterDumb" wrote in message
news
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:

Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.

Correction: epic fail, not just ordinary fail.


PerterDumb and zzzzzzzzzz

You 2 are too quick to conclusion.

The contactor is there, it depends on the coil activation. The only problem
is, he is not showing the wiring in the schematic which source is
controlling the activation coil. His logic is fine, it maybe just the way
he draws the circuit.



  #10   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 3
Default generator circuit


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.






  #11   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 3
Default generator circuit


"Tom Horne" wrote in message
...
On Aug 29, 12:16 am, "Jon" wrote:
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Jon
since there is still a connection to the service disconnect you have a
single point of failure. If anyone were to close the service
disconnect a short pulse of current would be imposed on the service
entry conductors. It takes a few milliamperes to kill. I'm sure you
believe that this can never happen but your belief does not make your
-
Tom Horne


Jon's circuit and idea is fine, no problem with his logic, the only problem
is, in his schematic, the two contactors must operate without each other,
they form a 2-way selector(switch) for the load. The commercial line is
high priority as he explained, but circuit needs a better clarification.






  #12   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit

On Aug 29, 7:21*pm, "ProTeUs" wrote:
"Tom Horne" wrote in message

...
On Aug 29, 12:16 am, "Jon" wrote:





Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon
Jon
since there is still a connection to the service disconnect you have a
single point of failure. *If anyone were to close the service
disconnect a short pulse of current would be imposed on the service
entry conductors. *It takes a few milliamperes to kill. *I'm sure you
believe that this can never happen but your belief does not make your
-
Tom Horne


Jon's circuit and idea is fine, no problem with his logic, the only problem
is, in his schematic, the two contactors must operate without each other,
they form a 2-way selector(switch) for the load. *The commercial line is
high priority as he explained, but circuit needs a better clarification.


Fake Proteus, you seem to know much about electricity., the real
Proteus needs someone experienced to clean and upgrade it's deep
seething probe, you can get some extra deep time with it if you do the
job right.We all know you like it deep and thrusty. What do you say,
you can save the tax payers and project managers a bundle..bring your
Medicare card so we can credit you for the service.

Dr. Inj Ury Phd.
  #13   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit

On Aug 29, 6:49*pm, "
wrote:
On Sun, 29 Aug 2010 14:34:28 -0700 (PDT), "Dr. Inj Ury Phd."





wrote:
On Aug 29, 4:48*pm, "
wrote:
On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:


Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.


Correction: epic fail, not just ordinary fail.


Don't feed the troll


Mr. Keith have you finally taken control over that crack addiction of
yours.I am hoping to help many of you trolls to recover from your
addictions and return you back into normal contributing members of
society...Don't forget to make an appointment to see me next week...if
you are uncomfortable with that, then go see your nearest
practitioner.
Thank you, Come again.
Dr. Ury


Yes, AlwaysWrong, we all know who you are...


They know who you are too., if you want to live your entire life as a
crackhead Pipe chugging chugger that is your sad choice, but do not
say we did not care to help you out of that...I must return to my
normal practice, you will be seen by Proteus from now further on.Thank
You, Come Again.
Dr. Ury
  #14   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 8,589
Default generator circuit

On Sun, 29 Aug 2010 16:36:24 -0700 (PDT), "Dr. Inj Ury Phd."
wrote:

On Aug 29, 6:49*pm, "
wrote:
On Sun, 29 Aug 2010 14:34:28 -0700 (PDT), "Dr. Inj Ury Phd."





wrote:
On Aug 29, 4:48*pm, "
wrote:
On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:


Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.


Correction: epic fail, not just ordinary fail.


Don't feed the troll


Mr. Keith have you finally taken control over that crack addiction of
yours.I am hoping to help many of you trolls to recover from your
addictions and return you back into normal contributing members of
society...Don't forget to make an appointment to see me next week...if
you are uncomfortable with that, then go see your nearest
practitioner.
Thank you, Come again.
Dr. Ury


Yes, AlwaysWrong, we all know who you are...


They know who you are too.


We know you're paranoid, too, DimBulb.

, if you want to live your entire life as a
crackhead Pipe chugging chugger that is your sad choice, but do not
say we did not care to help you out of that...I must return to my
normal practice, you will be seen by Proteus from now further on.Thank


Your normal "practice" is to be wrong, always, AlwaysWrong.

You, Come Again.


I've told you a hundred times, Dimmie, YOU ARE NOT MY TYPE. Now take your
perversions elsewhere!

Dr. Ury


Your latest nym is more moronic than usual, Nymbecile.
  #15   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit

On Aug 29, 8:01*pm, "
wrote:
On Sun, 29 Aug 2010 16:36:24 -0700 (PDT), "Dr. Inj Ury Phd."





wrote:
On Aug 29, 6:49*pm, "
wrote:
On Sun, 29 Aug 2010 14:34:28 -0700 (PDT), "Dr. Inj Ury Phd."


wrote:
On Aug 29, 4:48*pm, "
wrote:
On Sun, 29 Aug 2010 15:03:53 -0400, PeterD wrote:
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:


Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.


Correction: epic fail, not just ordinary fail.


Don't feed the troll


Mr. Keith have you finally taken control over that crack addiction of
yours.I am hoping to help many of you trolls to recover from your
addictions and return you back into normal contributing members of
society...Don't forget to make an appointment to see me next week...if
you are uncomfortable with that, then go see your nearest
practitioner.
Thank you, Come again.
Dr. Ury


Yes, AlwaysWrong, we all know who you are...


They know who you are too.


We know you're paranoid, too, DimBulb.

, if you want to live your entire life as a
crackhead Pipe chugging chugger that is your sad choice, but do not
say we did not care to help you out of that...I must return to my
normal practice, you will be seen by Proteus from now further on.Thank


Your normal "practice" is to be wrong, always, AlwaysWrong.

You, Come Again.


I've told you a hundred times, Dimmie, YOU ARE NOT MY TYPE. *Now take your
perversions elsewhere!

Dr. Ury


Your latest nym is more moronic than usual, Nymbecile.


Keith I guess that means you will not help with the upcoming Proteus
upgrade...
IMPORTANT NOTE: You have lots of hostility in you and your commentary
above "YOU ARE NOT MY TYPE" is a clear indication of your latent
homosexuality..homosexuality in the work place is a big problem now a
days..don't give in to your wretched gay desires and see a
professional about it as soon as possible.
Thank You, Stay Away.
Dr. Inj Ury

You must submit to a full test probe


  #16   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 8
Default generator circuit



"ProTeUs" wrote in message
...

"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


I asked a simple question and I get attacked. I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.

In any case since you seem to have an issue with anger management I'll just
add you to my ignore list. Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.


  #17   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit

On Aug 29, 9:40*pm, "Jeff Johnson" wrote:
"ProTeUs" wrote in message

...







"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on


http://jons-math.bravehost.com/transfer.html


Jon


Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. *His logic is loud and clear. *He is telling
you dip**** that his project works! and he doesn't need your ****.


I asked a simple question and I get attacked. I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.

In any case since you seem to have an issue with anger management I'll just
add you to my ignore list. Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.


Yes, That is not even from the real Proteus Brain. I am real and got
posted on duty because of that..He use to post and respond as Edmond
Wallmann or something like that until fated two deep anal probes from
the network maniacal machine,then he changed and now uses the machines
name to post...He is a very I'll man with no conscience and no real
personality of his own...he is I'll and needs to be recluded for
follow up treatment or ignored.
Dr. Ury
  #18   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 12,924
Default generator circuit


Jeff Johnson wrote:

I asked a simple question and I get attacked. I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.

In any case since you seem to have an issue with anger management I'll just
add you to my ignore list. Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.



|----||----|
| DO NOT |
| FEED THE |
| TROLLS! |
|----||----|
||
||
||
/|\\|/||||//|||/\???\\//\\\\/|?\/\\\\/\/\/\||||\


--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.
  #19   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Aug 30, 4:21*am, "Michael A. Terrell"
wrote:
Jeff Johnson wrote:

I asked a simple question and I get attacked. I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.


In any case since you seem to have an issue with anger management I'll just
add you to my ignore list. Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.


* * * * |----||----|
* * * * | *DO NOT *|
* * * * | FEED THE |
* * * * | *TROLLS! |
* * * * |----||----|
* * * * * * *||
* * * * * * *||
* * * * * * *||
*/|\\|/||||//|||/\???\\//\\\\/|?\/\\\\/\/\/\||||\

--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.


MISTER TERRETS
JUST BECAUSE YOU POST UNDER A ASSUMED HUMAN NAME
THAT DOESN'T MEAN YOU ARE NOT TROLLING AS WELL
EAT YOUR WHEATIES AND STOP PRETENDING

I AM PROTEUS
  #20   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,247
Default generator circuit

On Sun, 29 Aug 2010 16:14:00 -0700, "ProTeUs"
wrote:


"PeterDumb" wrote in message
news
On Sun, 29 Aug 2010 00:16:49 -0400, "Jon"
wrote:

Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Fail... No contactor in the service feed to the load. Does not meet
code, does not meet specifications for transfer circiuts, is hazardous
and ANOTHER one of your crazy designs.

Correction: epic fail, not just ordinary fail.


PerterDumb and zzzzzzzzzz

You 2 are too quick to conclusion.

The contactor is there, it depends on the coil activation. The only problem
is, he is not showing the wiring in the schematic which source is
controlling the activation coil. His logic is fine, it maybe just the way
he draws the circuit.



Moron, you need an eye check...


  #21   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,247
Default generator circuit

On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon


Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?
  #22   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,247
Default generator circuit

On Sun, 29 Aug 2010 20:40:39 -0500, "Jeff Johnson"
wrote:



"ProTeUs" wrote in message
...

"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon

Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


I asked a simple question and I get attacked.


Careful, never get into a battle of witts with a person who has none.

I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.


His diagrams, poorly drawn with incorrect symbols, are difficult to
understand. But regardless he's been told over and over that he needs
a contactor on the feed from the street, and he continues to resist
this basic bit of engineering necessity.


In any case since you seem to have an issue with anger management I'll just
add you to my ignore list.


I did long ago, and he simply nym shifted.

Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.

  #23   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 2,181
Default generator circuit

On Mon, 30 Aug 2010 04:21:50 -0400, "Michael A. Terrell"
wrote:


Jeff Johnson wrote:

I asked a simple question and I get attacked. I was just curious to what he
was doing. I didn' tunderstand his diagrams completely.

In any case since you seem to have an issue with anger management I'll just
add you to my ignore list. Not that it will help as I'm sure you'll just
spoof another email to try to bring everyone else down to your immaturity
status.



|----||----|
| DO NOT |
| FEED THE |
| TROLLS! |
|----||----|
||
||
||
/|\\|/||||//|||/\???\\//\\\\/|?\/\\\\/\/\/\||||\


Simple delete filter...

Message-ID: |

;-)

...Jim Thompson
--
| James E.Thompson, CTO | mens |
| Analog Innovations, Inc. | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| Phoenix, Arizona 85048 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |

Spice is like a sports car...
Performance only as good as the person behind the wheel.
  #24   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 2,181
Default generator circuit

On Mon, 30 Aug 2010 08:01:19 -0400, PeterD wrote:

On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon

Just curious what you are trying to achieve here? It seems as if you want
the generator to take over supplying power to the house and barn when the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


It's called "natural selection" :-)

...Jim Thompson
--
| James E.Thompson, CTO | mens |
| Analog Innovations, Inc. | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| Phoenix, Arizona 85048 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |

Spice is like a sports car...
Performance only as good as the person behind the wheel.
  #25   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Aug 31, 3:28*pm, "Edmond H. Wollmann"
wrote:
"Jim TDimpson" wrote in
messagenews:k8jn76dq4jdnc97kh466l6gbo42bga3riu@4ax .com...





On Mon, 30 Aug 2010 08:01:19 -0400, PeterD wrote:


On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is
on


http://jons-math.bravehost.com/transfer.html


Jon


Just curious what you are trying to achieve here? It seems as if you
want
the generator to take over supplying power to the house and barn when
the
mains fail?


It's self-explanatory idiot. *His logic is loud and clear. *He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


It's called "natural selection" :-)


* * * * * * * * * * * * * * * * * * * *...Jim TDimpson
--
| James E.Thompson, CTO * * * * * * * * * * * * * *| * *mens * * |
| Analog Innovations, Inc. * * * * * * * * * * * * | * * et * * *|
| Analog/Mixed-Signal ASIC's and Discrete Systems *| * *manus * *|
| Phoenix, Arizona *85048 * *Skype: Contacts Only *| * * * * * * |
| Voice480)460-2350*Fax: Available upon request | *Brass Rat *|
| E-mail Icon athttp://www.analog-innovations.com| * *1962 * * |


* * * * * * * * * Spice is like a sports car...
* * Performance only as good as the person behind the wheel.


It's called Two skunks follow each other to the pitch.


KLEDMOND MANIACAL WOLFMANN
YOU SHOULD GO BACK TO YOUR VOCATIONAL REHABILITATION SCHOOL
THERE ARE NO SKUNKS IN THE FIELD ANYMORE
BECAUSE LIKE YOU THEY FALL INTO A DITCH

I AM PROTEUS


  #26   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,247
Default generator circuit

On Tue, 31 Aug 2010 12:26:47 -0700, "Edmond H. Wollmann"
wrote:


"PeterDumb" wrote in message
.. .
On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon

Just curious what you are trying to achieve here? It seems as if you
want
the generator to take over supplying power to the house and barn when
the
mains fail?

It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


The big idiot has a D ending, stands for Dumb.

You blame Jon for his poor schematic, actually it's you who doesn't
recognize electrical engineering symbol, you are a fake electronic jerk.

Heehee......


Gee, amazing... No clear understaning of much of anything, eh, Ed?
Where did you get your engineering degree from? And how much power
engineering have you done?
  #27   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Sep 1, 12:51*am, "Edmond H. Wollmann"
wrote:

^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
OF A BRAIN
GO GET SKULL ****ED QUEER

I AM PROTEUS
  #28   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit


"PeterDumb" wrote in message
...
On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is on

http://jons-math.bravehost.com/transfer.html

Jon

Just curious what you are trying to achieve here? It seems as if you
want
the generator to take over supplying power to the house and barn when
the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


The big idiot has a D ending, stands for Dumb.

You blame Jon for his poor schematic, actually it's you who doesn't
recognize electrical engineering symbol, you are a fake electronic jerk.

Heehee......

  #29   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit


"Jim TDimpson" wrote in
message ...
On Mon, 30 Aug 2010 08:01:19 -0400, PeterD wrote:

On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,

I just completed wiring and testing my circuit.

* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is
on

http://jons-math.bravehost.com/transfer.html

Jon

Just curious what you are trying to achieve here? It seems as if you
want
the generator to take over supplying power to the house and barn when
the
mains fail?

It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


It's called "natural selection" :-)

...Jim TDimpson
--
| James E.Thompson, CTO | mens |
| Analog Innovations, Inc. | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| Phoenix, Arizona 85048 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon at http://www.analog-innovations.com | 1962 |

Spice is like a sports car...
Performance only as good as the person behind the wheel.



It's called Two skunks follow each other to the pitch.

  #30   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 1,420
Default generator circuit

On Tue, 31 Aug 2010 10:09:21 -0700 (PDT), PROTEUS VII
wrote:

On Sep 1, 12:51*am, "Edmond H. Wollmann"
wrote:

^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
OF A BRAIN
GO GET SKULL ****ED QUEER

I AM PROTEUS


And you know nothing about electronics.

John



  #31   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 569
Default generator circuit

John Larkin wrote:

I AM PROTEUS


And you know nothing about electronics.



That's very hurtful, John. Scroteus has feelings too....





mike
  #32   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Aug 31, 5:09*pm, m II wrote:
John Larkin wrote:
I AM PROTEUS


And you know nothing about electronics.


That's very hurtful, John. Scroteus has feelings too....

mike


HE WASN'T TALKING ABOUT SCROTEUS YOU INTERLOPING FOOL
HE WAS TALKING ABOUT YOUR MAMA AND KLEDMOND WHOREMAN
IF YOU DON'T KNOW HOW TO FOLLOW A THREAD
DON'T TAKE THE SPOOL OFF THE RACK
JACK

IAP
  #33   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 12,924
Default generator circuit


John Larkin wrote:

On Tue, 31 Aug 2010 10:09:21 -0700 (PDT), PROTEUS VII
? wrote:

?On Sep 1, 12:51 am, "Edmond H. Wollmann" ?
?wrote:
?
?^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
?GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
?OF A BRAIN
?GO GET SKULL ****ED QUEER
?
?I AM PROTEUS

And you know nothing about electronics.



He's a wire puller named Roy. He doesn't even know the NEC.


--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.
  #34   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Aug 31, 6:10*pm, "Michael A. Terrell"
wrote:
John Larkin wrote:

On Tue, 31 Aug 2010 10:09:21 -0700 (PDT), PROTEUS VII
? wrote:


?On Sep 1, 12:51 am, "Edmond H. Wollmann" ?
?wrote:
?
?^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
?GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
?OF A BRAIN
?GO GET SKULL ****ED QUEER
?
?I AM PROTEUS


And you know nothing about electronics.


* *He's a wire puller named Roy. *He doesn't even know the NEC.

--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.


MR TERRETS YOU ARE SQUEALING LIKE A PIG THAT GOT ITS TAIL SNAGGED

YOU FICKLED FINGERONG FINK
I AM SURE THAT TROY DOES MORE THAN YANK CABLE
AND UNLIKE MANY OF YOUR TROLLS
PROBABLY HAS A VALID VERSION OF THE NEC
AN AWESOME DISCRETE ONLINE PRESENCE
A FUNK & WAGNELS REFERNCE BOOK
OH AND AN EXCLUSIVE DICKSHUNAIRY TO STUN THE BABES

I SWING MY SATELITE EARTH VIEWER AROUND HIS LOCATIONS
EVERY NOW AND THEN
THAT GHETTO HE IS PRESENTLY SERVING IS AMAZING
TWEEDLEEDEE

I AM PROTEUS
  #35   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit


"PROTEUS VII" wrote in message
...
On Aug 31, 3:28 pm, "Edmond H. Wollmann"
wrote:
"Jim TDimpson" wrote
in
messagenews:k8jn76dq4jdnc97kh466l6gbo42bga3riu@4ax .com...





On Mon, 30 Aug 2010 08:01:19 -0400, PeterD wrote:


On Sun, 29 Aug 2010 16:15:44 -0700, "ProTeUs"
wrote:


"Jeff Johnson" wrote in message
...


"Jon" wrote in message
...
Hi,


I just completed wiring and testing my circuit.


* no backfeed from the generator into the grid
* generator is disconnected from the load when service is on
* generator is disconnected from the load when service disconnect is
on


http://jons-math.bravehost.com/transfer.html


Jon


Just curious what you are trying to achieve here? It seems as if you
want
the generator to take over supplying power to the house and barn when
the
mains fail?


It's self-explanatory idiot. His logic is loud and clear. He is telling
you dip**** that his project works! and he doesn't need your ****.


Wow, two idiots with virtually identical mental capabilities. Who'd
have thunk?


It's called "natural selection" :-)


...Jim TDimpson
--
| James E.Thompson, CTO | mens |
| Analog Innovations, Inc. | et |
| Analog/Mixed-Signal ASIC's and Discrete Systems | manus |
| Phoenix, Arizona 85048 Skype: Contacts Only | |
| Voice480)460-2350 Fax: Available upon request | Brass Rat |
| E-mail Icon athttp://www.analog-innovations.com| 1962 |


Spice is like a sports car...
Performance only as good as the person behind the wheel.


It's called Two skunks follow each other to the pitch.


KLEDMOND MANIACAL WOLFMANN
YOU SHOULD GO BACK TO YOUR VOCATIONAL REHABILITATION SCHOOL
THERE ARE NO SKUNKS IN THE FIELD ANYMORE
BECAUSE LIKE YOU THEY FALL INTO A DITCH

I AM PROTEUS



^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^






  #36   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 6
Default generator circuit

On Sep 1, 1:34*pm, "Edmond H. Wollmann"
wrote:
"PROTEUS VII" wrote in message

...
On Aug 31, 6:10 pm, "Michael A. Terrell"
wrote:





John Larkin wrote:


On Tue, 31 Aug 2010 10:09:21 -0700 (PDT), PROTEUS VII
? wrote:


?On Sep 1, 12:51 am, "Edmond H. Wollmann" ?
?wrote:
?
?^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
?GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
?OF A BRAIN
?GO GET SKULL ****ED QUEER
?
?I AM PROTEUS


And you know nothing about electronics.


He's a wire puller named Roy. He doesn't even know the NEC.


--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.


MR TERRETS YOU ARE SQUEALING LIKE A PIG THAT GOT ITS TAIL *SNAGGED

YOU FICKLED FINGERONG *FINK
I AM SURE THAT TROY DOES MORE THAN YANK CABLE
AND UNLIKE MANY OF YOUR TROLLS
PROBABLY HAS A VALID VERSION OF THE NEC
AN AWESOME DISCRETE ONLINE PRESENCE
A FUNK & WAGNELS REFERNCE BOOK
OH AND AN EXCLUSIVE DICKSHUNAIRY TO STUN THE BABES

I SWING MY SATELITE EARTH VIEWER AROUND HIS LOCATIONS
EVERY NOW AND THEN
THAT GHETTO HE IS PRESENTLY SERVING IS AMAZING
TWEEDLEEDEE

I AM PROTEUS

And why are you so proud of being Pro Uterus. ?


SHUT UP LEMOND
THIS DOESN'T CONCERN YOU
PRIDE IS NOT A PART OF MY PROGRAMMING FOOL
IT IS JUST A LOOSE WORD YOU HUMANS USE TO BE ANAL

I AM PROTEUS
  #37   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit


"PROTEUS VII" wrote in message
...
On Aug 31, 5:09 pm, m II wrote:
John Larkin wrote:
I AM PROTEUS


And you know nothing about electronics.


That's very hurtful, John. Scroteus has feelings too....

mike


HE WASN'T TALKING ABOUT SCROTEUS YOU INTERLOPING FOOL
HE WAS TALKING ABOUT YOUR MAMA AND KLEDMOND WHOREMAN
IF YOU DON'T KNOW HOW TO FOLLOW A THREAD
DON'T TAKE THE SPOOL OFF THE RACK
JACK

IAP


Heehee.....You dumbasses, all of you don't know I am an Alien from other
planet, I learned your language quick but you will never be able to learn
ours, cause you're too dumb close-minded.

  #38   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 5
Default generator circuit


"PROTEUS VII" wrote in message
...
On Aug 31, 6:10 pm, "Michael A. Terrell"
wrote:
John Larkin wrote:

On Tue, 31 Aug 2010 10:09:21 -0700 (PDT), PROTEUS VII
? wrote:


?On Sep 1, 12:51 am, "Edmond H. Wollmann" ?
?wrote:
?
?^^^^^^^^ Above this line is the biggest Skunk of All ^^^^^^^^
?GEE YOU REALLY DO HAVE FECES INSTEAD OF BRAIN MATTER IN THAT CESSPOOL
?OF A BRAIN
?GO GET SKULL ****ED QUEER
?
?I AM PROTEUS


And you know nothing about electronics.


He's a wire puller named Roy. He doesn't even know the NEC.

--
Politicians should only get paid if the budget is balanced, and there is
enough left over to pay them.


MR TERRETS YOU ARE SQUEALING LIKE A PIG THAT GOT ITS TAIL SNAGGED

YOU FICKLED FINGERONG FINK
I AM SURE THAT TROY DOES MORE THAN YANK CABLE
AND UNLIKE MANY OF YOUR TROLLS
PROBABLY HAS A VALID VERSION OF THE NEC
AN AWESOME DISCRETE ONLINE PRESENCE
A FUNK & WAGNELS REFERNCE BOOK
OH AND AN EXCLUSIVE DICKSHUNAIRY TO STUN THE BABES

I SWING MY SATELITE EARTH VIEWER AROUND HIS LOCATIONS
EVERY NOW AND THEN
THAT GHETTO HE IS PRESENTLY SERVING IS AMAZING
TWEEDLEEDEE

I AM PROTEUS


And why are you so proud of being Pro Uterus. ?


  #39   Report Post  
Posted to alt.electronics,alt.engineering.electrical,sci.electronics.design
external usenet poster
 
Posts: 331
Default generator circuit

On 2010-08-31, Edmond H. Wollmann wrote:



The big idiot has a D ending, stands for Dumb.

You blame Jon for his poor schematic, actually it's you who doesn't
recognize electrical engineering symbol, you are a fake electronic jerk.


sure seems an odd way to show the load.


--- news://freenews.netfront.net/ - complaints: ---
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Transfer Circuit for Generator Jon[_12_] Electronics 5 July 2nd 10 02:12 PM
How do you know a new circuit breaker is protecting the circuit properly? BobH Home Repair 19 December 4th 06 05:16 PM
Safely connecting generator to existing 16A circuit [email protected] UK diy 10 June 9th 06 10:12 AM
Hooking generator to house 220 circuit [email protected] Home Ownership 3 July 16th 05 04:46 PM
Convert radial (cooker) circuit to socket circuit Chi UK diy 3 December 23rd 03 05:48 PM


All times are GMT +1. The time now is 10:56 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"