Default How do you know a new circuit breaker is protecting the circuit properly?

I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,199
Default How do you know a new circuit breaker is protecting the circuit properly?


BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


Other than shorting both legs of the 220 line and creating an
impressive spark, you just assume, as the rest of us, that the breaker
works, and chances are that it will.

What is the current draw on your new oven at full load?

  #3   Report Post  
Posted to alt.home.repair
CJT CJT is offline
external usenet poster
 
Posts: 1,155
Default How do you know a new circuit breaker is protecting the circuitproperly?

BobH wrote:

I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?

Put a 30 amp load on the circuit?

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default How do you know a new circuit breaker is protecting the circuit properly?

The breaker is there to protect the wiring, not the appliance. And there's
no need to check them.

--
Steve Barker



"BobH" wrote in message
ups.com...
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 561
Default How do you know a new circuit breaker is protecting the circuit properly?


BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


There is no need to change the breaker to match the load, as long as
all the associated wiring is rated for 50A.

Dave



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 458
Default How do you know a new circuit breaker is protecting the circuit properly?

BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one?
In other words, if I install a new breaker, how do I know it will
trip if the load exceeds 30 amps?


You pretty much have to trust to their design and Quality operations, but
.... if it has UL, CSA, EU or other comparable safety markings (which are
required in order to sell them), you can pretty much assume they'll do the
job they're designed for.

Do NOT short the leads to "test" a breaker! You may or may not have a
functionally, to-spec breaker after that! Just in case the idea sounded
good to you g.

Pop`



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 222
Default How do you know a new circuit breaker is protecting the circuit properly?

Good and sound advise POP!!

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,185
Default How do you know a new circuit breaker is protecting the circuitproperly?

Pop` wrote:

Well, actually, there is. In fact, many local codes would require a change
in this case. 48 amps thru a 50 amp breaker into an appliance that is rated
for 30A would indeed be a fire hazard at the appliance itself or wherever
the extra current is going to.


Given that "standard" range circuits are 50A, I would expect that any
UL/CSA listed range will be safe to plug into such a circuit.

It may actually have a smaller fuse (or a thin wire designed to act as
one) in the appliance itself--this is what many kitchen appliances do,
and why they can have such tiny cords and still plug into 20A receptacles.

Chris
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 663
Default How do you know a new circuit breaker is protecting the circuit properly?

On 1 Dec 2006 09:31:58 -0800, "BobH" wrote:

I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


Will the plug go in a 50A recpt? If it does then I see no reason to
change it.

You would only have to change the breaker if you changed the outlet.

I think most receptacles are keyed somehow to keep you from using an
incorrect appliance.

You can plug a 15A device in a 20 Amp recpt, but you can not plug a
20A plug into a 15A recpt.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 259
Default How do you know a new circuit breaker is protecting the circuit properly?


Do NOT short the leads to "test" a breaker! You may or may not have a
functionally, to-spec breaker after that! Just in case the idea sounded
good to you g.

Pop`


Does that mean anytime a breaker opens it is thereafter suspect and
should be inspected by an electrician? If so, I have not been leading
a safe life. -- H

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default How do you know a new circuit breaker is protecting the circuit properly?

ACTUALLY, not.

The breaker is there to protect the wiring, not the appliance. And there's
no need to check them.

--
Steve Barker

There is no need to change the breaker to match the load, as long as
all the associated wiring is rated for 50A.

Dave


--

"Pop`" wrote in message
news:ir_bh.20$Wq.14@trnddc08...

Well, actually, there is. In fact, many local codes would require a
change in this case. 48 amps thru a 50 amp breaker into an appliance that
is rated for 30A would indeed be a fire hazard at the appliance itself or
wherever the extra current is going to.

Calls to the local code enforcement are quick, short, and the best way to
be sure of what the codes say, and logic and common sense says to use the
right sized breaker.



  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 317
Default How do you know a new circuit breaker is protecting the circuit properly?

I'd like to see a 20a plug. They're so few and far between, they might as
well obsolete them.

--
Steve Barker



"Terry" wrote in message
...
On 1 Dec 2006 09:31:58 -0800, "BobH" wrote:

I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


Will the plug go in a 50A recpt? If it does then I see no reason to
change it.

You would only have to change the breaker if you changed the outlet.

I think most receptacles are keyed somehow to keep you from using an
incorrect appliance.

You can plug a 15A device in a 20 Amp recpt, but you can not plug a
20A plug into a 15A recpt.



  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default How do you know a new circuit breaker is protecting the circuit properly?


Do NOT short the leads to "test" a breaker! You may or may not have a
functionally, to-spec breaker after that! Just in case the idea sounded
good to you g.

Pop`


I disagreee with the idea shorting a breaker either intentially or
accidently can damage a breaker......

I used to fix office macxhines at Westinghouse Beaver, a plant that
produced circuit breakers of all sizes.

spent a LOT of time there and made friends, at one point they offered
me a job, no interview necessary. just drop application with gorgeous
secretary, give notice to current employer start in 2 weeks. it was a
fascinating place.

they cycled breakers thru hundreds of dead shorts and other hard tests.
then tore them aart to see what failed.

some dead shorts arent a problem for a breaker, its part of normal
operation.

just like turning on a lamp is.........

given all this i would not makew a habit of it..........

but dangerous to the breaker thats like saying slamming on the brakes
of a car make it less likely to stop the next time

  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default How do you know a new circuit breaker is protecting the circuit properly?


Do NOT short the leads to "test" a breaker! You may or may not have a
functionally, to-spec breaker after that! Just in case the idea sounded
good to you g.

Pop`


I disagreee with the idea shorting a breaker either intentially or
accidently can damage a breaker......

I used to fix office macxhines at Westinghouse Beaver, a plant that
produced circuit breakers of all sizes.

spent a LOT of time there and made friends, at one point they offered
me a job, no interview necessary. just drop application with gorgeous
secretary, give notice to current employer start in 2 weeks. it was a
fascinating place.

they cycled breakers thru hundreds of dead shorts and other hard tests.
then tore them aart to see what failed.

some dead shorts arent a problem for a breaker, its part of normal
operation.

just like turning on a lamp is.........

given all this i would not makew a habit of it..........

but dangerous to the breaker thats like saying slamming on the brakes
of a car make it less likely to stop the next time



  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default How do you know a new circuit breaker is protecting the circuit properly?

Right. You're not testing fuses.
I assume your worked at Beaver, PA. Right? I used to know Donald C.
Burnham in Mt. Lebanon.


yeah beaver a nice place wonderful workers. cafeteria was great!

I decided to not take the job, but it was a very close decision. kinda
far from home and a family member was ill at the time. Great
oppportunity at the time

I made a good decision within 3 years everyone with less than 20 years
was let go. part of the general Westinghouse fiancial mess from its
fiancial services division they lost a fortune. I worked in lots of
westinghouse plants east pittsburgh the mother plant, Large pa, some
fiancial offices others serviced the nuclear division I never got
cleared for that.

Sad what happened to westinghouse, today I service the blairsville
plant that makes nuclear fuel rods..........

I pass the beaver plant often, its owner has changed the parking lot
largely empty

some of the last automated equiptement was awesome watching it run.

they had robots delivering stuff.

I fixed opffice machines now all obsolete

  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 81
Default How do you know a new circuit breaker is protecting the circuit properly?


BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


Connect it to a load that exceeds 30 amps.

  #19   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 674
Default How do you know a new circuit breaker is protecting the circuit properly?


"Steve Barker LT" wrote in message
...
I'd like to see a 20a plug. They're so few and far between, they might as
well obsolete them.

--
Steve Barker



"Terry" wrote in message
...
On 1 Dec 2006 09:31:58 -0800, "BobH" wrote:

I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here
about testing a bad circuit breaker, but how do you test a good one? In
other words, if I install a new breaker, how do I know it will trip if
the load exceeds 30 amps?


Will the plug go in a 50A recpt? If it does then I see no reason to
change it.

You would only have to change the breaker if you changed the outlet.

I think most receptacles are keyed somehow to keep you from using an
incorrect appliance.

You can plug a 15A device in a 20 Amp recpt, but you can not plug a
20A plug into a 15A recpt.



Some heaters and lots of airconditioners use 20 amp plugs. They are sold in
our local hardware stores.

Don Young


  #20   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,981
Default How do you know a new circuit breaker is protecting the circuitproperly?

Steve Barker LT wrote:

ACTUALLY, not.

The breaker is there to protect the wiring, not the appliance. And there's
no need to check them.


The breaker protects the wiring and the appliance (some exceptions, like
motor circuits). What do you think protects the appliance from faults
and failures? For instance Pop's 48A failure in a 30A appliance.

--
bud--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short in Circuit or Circuit breaker? Greg Home Repair 13 January 29th 06 06:45 PM
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? C5Ya Home Repair 10 August 26th 05 07:34 PM
Circuit breaker tester maps to wrong breaker!! Joe Doe Home Repair 7 November 30th 04 01:47 AM
circuit is off, circuit breaker is on Massi Home Repair 1 July 4th 04 11:31 PM
circuit breaker Smerby Home Repair 3 March 6th 04 04:51 AM


All times are GMT +1. The time now is 02:20 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"