How do you know a new circuit breaker is protecting the circuit properly?
I am changing a 50-amp breaker to a 30-amp one to install an oven that
draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? |
#2
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
BobH wrote: I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Other than shorting both legs of the 220 line and creating an impressive spark, you just assume, as the rest of us, that the breaker works, and chances are that it will. What is the current draw on your new oven at full load? |
#3
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuitproperly?
BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Put a 30 amp load on the circuit? -- The e-mail address in our reply-to line is reversed in an attempt to minimize spam. Our true address is of the form . |
#4
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
The breaker is there to protect the wiring, not the appliance. And there's
no need to check them. -- Steve Barker "BobH" wrote in message ups.com... I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? |
#5
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
BobH wrote: I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? There is no need to change the breaker to match the load, as long as all the associated wiring is rated for 50A. Dave |
#6
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
BobH wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? You pretty much have to trust to their design and Quality operations, but .... if it has UL, CSA, EU or other comparable safety markings (which are required in order to sell them), you can pretty much assume they'll do the job they're designed for. Do NOT short the leads to "test" a breaker! You may or may not have a functionally, to-spec breaker after that! Just in case the idea sounded good to you g. Pop` |
#7
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
|
#8
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
Good and sound advise POP!!
|
#9
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuitproperly?
Pop` wrote:
Well, actually, there is. In fact, many local codes would require a change in this case. 48 amps thru a 50 amp breaker into an appliance that is rated for 30A would indeed be a fire hazard at the appliance itself or wherever the extra current is going to. Given that "standard" range circuits are 50A, I would expect that any UL/CSA listed range will be safe to plug into such a circuit. It may actually have a smaller fuse (or a thin wire designed to act as one) in the appliance itself--this is what many kitchen appliances do, and why they can have such tiny cords and still plug into 20A receptacles. Chris |
#10
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
On 1 Dec 2006 09:31:58 -0800, "BobH" wrote:
I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Will the plug go in a 50A recpt? If it does then I see no reason to change it. You would only have to change the breaker if you changed the outlet. I think most receptacles are keyed somehow to keep you from using an incorrect appliance. You can plug a 15A device in a 20 Amp recpt, but you can not plug a 20A plug into a 15A recpt. |
#11
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
Do NOT short the leads to "test" a breaker! You may or may not have a functionally, to-spec breaker after that! Just in case the idea sounded good to you g. Pop` Does that mean anytime a breaker opens it is thereafter suspect and should be inspected by an electrician? If so, I have not been leading a safe life. -- H |
#12
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
ACTUALLY, not.
The breaker is there to protect the wiring, not the appliance. And there's no need to check them. -- Steve Barker There is no need to change the breaker to match the load, as long as all the associated wiring is rated for 50A. Dave -- "Pop`" wrote in message news:ir_bh.20$Wq.14@trnddc08... Well, actually, there is. In fact, many local codes would require a change in this case. 48 amps thru a 50 amp breaker into an appliance that is rated for 30A would indeed be a fire hazard at the appliance itself or wherever the extra current is going to. Calls to the local code enforcement are quick, short, and the best way to be sure of what the codes say, and logic and common sense says to use the right sized breaker. |
#13
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
I'd like to see a 20a plug. They're so few and far between, they might as
well obsolete them. -- Steve Barker "Terry" wrote in message ... On 1 Dec 2006 09:31:58 -0800, "BobH" wrote: I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Will the plug go in a 50A recpt? If it does then I see no reason to change it. You would only have to change the breaker if you changed the outlet. I think most receptacles are keyed somehow to keep you from using an incorrect appliance. You can plug a 15A device in a 20 Amp recpt, but you can not plug a 20A plug into a 15A recpt. |
#14
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
Do NOT short the leads to "test" a breaker! You may or may not have a functionally, to-spec breaker after that! Just in case the idea sounded good to you g. Pop` I disagreee with the idea shorting a breaker either intentially or accidently can damage a breaker...... I used to fix office macxhines at Westinghouse Beaver, a plant that produced circuit breakers of all sizes. spent a LOT of time there and made friends, at one point they offered me a job, no interview necessary. just drop application with gorgeous secretary, give notice to current employer start in 2 weeks. it was a fascinating place. they cycled breakers thru hundreds of dead shorts and other hard tests. then tore them aart to see what failed. some dead shorts arent a problem for a breaker, its part of normal operation. just like turning on a lamp is......... given all this i would not makew a habit of it.......... but dangerous to the breaker thats like saying slamming on the brakes of a car make it less likely to stop the next time |
#15
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
Do NOT short the leads to "test" a breaker! You may or may not have a functionally, to-spec breaker after that! Just in case the idea sounded good to you g. Pop` I disagreee with the idea shorting a breaker either intentially or accidently can damage a breaker...... I used to fix office macxhines at Westinghouse Beaver, a plant that produced circuit breakers of all sizes. spent a LOT of time there and made friends, at one point they offered me a job, no interview necessary. just drop application with gorgeous secretary, give notice to current employer start in 2 weeks. it was a fascinating place. they cycled breakers thru hundreds of dead shorts and other hard tests. then tore them aart to see what failed. some dead shorts arent a problem for a breaker, its part of normal operation. just like turning on a lamp is......... given all this i would not makew a habit of it.......... but dangerous to the breaker thats like saying slamming on the brakes of a car make it less likely to stop the next time |
#16
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuitproperly?
|
#17
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
Right. You're not testing fuses.
I assume your worked at Beaver, PA. Right? I used to know Donald C. Burnham in Mt. Lebanon. yeah beaver a nice place wonderful workers. cafeteria was great! I decided to not take the job, but it was a very close decision. kinda far from home and a family member was ill at the time. Great oppportunity at the time I made a good decision within 3 years everyone with less than 20 years was let go. part of the general Westinghouse fiancial mess from its fiancial services division they lost a fortune. I worked in lots of westinghouse plants east pittsburgh the mother plant, Large pa, some fiancial offices others serviced the nuclear division I never got cleared for that. Sad what happened to westinghouse, today I service the blairsville plant that makes nuclear fuel rods.......... I pass the beaver plant often, its owner has changed the parking lot largely empty some of the last automated equiptement was awesome watching it run. they had robots delivering stuff. I fixed opffice machines now all obsolete |
#18
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
BobH wrote: I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Connect it to a load that exceeds 30 amps. |
#19
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuit properly?
"Steve Barker LT" wrote in message ... I'd like to see a 20a plug. They're so few and far between, they might as well obsolete them. -- Steve Barker "Terry" wrote in message ... On 1 Dec 2006 09:31:58 -0800, "BobH" wrote: I am changing a 50-amp breaker to a 30-amp one to install an oven that draws less current than the old one did. I have seen information here about testing a bad circuit breaker, but how do you test a good one? In other words, if I install a new breaker, how do I know it will trip if the load exceeds 30 amps? Will the plug go in a 50A recpt? If it does then I see no reason to change it. You would only have to change the breaker if you changed the outlet. I think most receptacles are keyed somehow to keep you from using an incorrect appliance. You can plug a 15A device in a 20 Amp recpt, but you can not plug a 20A plug into a 15A recpt. Some heaters and lots of airconditioners use 20 amp plugs. They are sold in our local hardware stores. Don Young |
#20
Posted to alt.home.repair
|
|||
|
|||
How do you know a new circuit breaker is protecting the circuitproperly?
Steve Barker LT wrote:
ACTUALLY, not. The breaker is there to protect the wiring, not the appliance. And there's no need to check them. The breaker protects the wiring and the appliance (some exceptions, like motor circuits). What do you think protects the appliance from faults and failures? For instance Pop's 48A failure in a 30A appliance. -- bud-- |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Short in Circuit or Circuit breaker? | Home Repair | |||
A/C Unit Keeps Tripping Circuit Breaker - How to test breaker before calling repair man? | Home Repair | |||
Circuit breaker tester maps to wrong breaker!! | Home Repair | |||
circuit is off, circuit breaker is on | Home Repair | |||
circuit breaker | Home Repair |