Prompted by suggestions that a shop needs convenient power, I created a
(pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** in addition to GFCI CB's. |
#2
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Bill wrote:
Prompted by suggestions that a shop needs convenient power, I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Are you suggesting that you are going to take 120v off of a 240V home run for the outlets labeled BW and RW, and pass those runs down to the TS, DC, and compressor? If so, I would do things differently. 1) I'd just run the dedicated 240v circuits directly to the devices 2) I'd use 10/3 for the 240v circuits. You may not need it now, but the extra current capacity is there. The DC will probably never need that kind of capacity, but at some point, you may put something else there. 3) I'd run 2 120v branch circuits to the wall outlets. Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** in addition to GFCI CB's. I think you should not feel better about that. Pick one technique and don't rely on what makes you feel better. -- -Mike- |
#3
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Mike Marlow" wrote in message ... 2) I'd use 10/3 for the 240v circuits. You may not need it now, but the extra current capacity is there. The DC will probably never need that kind of capacity, but at some point, you may put something else there. Ah, I get it now. Use 10/3 NM cable, but still use a 20 Amp C-B (duh). No fuse necessary (to protect the equiptment). |
#4
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Bill" wrote:
"Mike Marlow" wrote in message ... 2) I'd use 10/3 for the 240v circuits. You may not need it now, but the extra current capacity is there. The DC will probably never need that kind of capacity, but at some point, you may put something else there. Ah, I get it now. Use 10/3 NM cable, but still use a 20 Amp C-B (duh). Or use a 30A breaker. No fuse necessary (to protect the equiptment). No fuse necessary anyway (to protect it from what?) |
#5
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Bill" wrote:
Prompted by suggestions that a shop needs convenient power, I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. In fact, all I seek is a simple nod. Sorry, you won't get that "simple nod" from me. Keep it simple. Rather than wiring your 120V outlets to opposite sides of the 240V circuits, keep them separate: run 120V circuits for your 120V outlets, and 240V circuits for your 240V outlets. It's easier to wire, gives you more flexibility in the placement of your 120V outlets, and -- most important -- doesn't limit your 240V circuits to the same 20A as your 120V circuits. Note that you need only two-conductor cable, not three, for the 240V circuits once you've put the 120V outlets on 120V circuits. You should install _at least_ twice as many 120V outlets as you think you need. I'm kicking myself for having installed only three 240V outlets in my 16x20 shop, but I do have enough 120V outlets (fourteen duplex receptacles). I have found it particularly useful to have a ceiling-mounted 120V outlet with a drop cord on a retractor. It worked so well in the shop that I put another one in the garage, plugged into the other half of the duplex receptacle that powers the garage door opener. The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Run a minimum of 10ga wire, maybe even 8ga, to your 240V outlets. Using 12ga wire unnecessarily constrains you to a future of small air compressors and table saws. If you ever upgrade to a more powerful compressor or saw, you'll have to rewire. Easier to just put in heavier wire at the outset. Thank you again to those of you who helped me to reach this point (of understanding)! Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** in addition to GFCI CB's. Why? There's no point at all in having both. |
#6
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Doug Miller" wrote in message ... The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Your point is well-taken. Unfortunatey, I'm not fully comitted on where the tools are going to be (I may decide I want the DC closer to the door to improve the sound-level). Dedicated 240v lines seems to maximize flexability, which seems appropriate. Thanks for making me think! Bill |
#7
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Bill" wrote:
Your point is well-taken. Unfortunatey, I'm not fully comitted on where the tools are going to be (I may decide I want the DC closer to the door to improve the sound-level). Dedicated 240v lines seems to maximize flexability, which seems appropriate. Thanks for making me think! If you have the option of locating the dust collector outside the shop and having only the ducts inside, that's something to consider. There are pluses and minuses either way. Having the DC outside the shop means less noise and dust inside the shop -- but more noise and dust outside. If you live in sufficiently rural area where the noise won't bother neighbors, think about putting the DC outdoors (protected from the weather, of course). |
#8
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Doug Miller wrote:
The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Wot? I could have all my tools on the same circuit EXCEPT the dust collector and air compressor, since they are the only ones that run at the same time as my other tools. -- Jack Obama Care...Freedom not Included! http://jbstein.com |
#9
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , Jack Stein wrote:
Doug Miller wrote: The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Wot? I could have all my tools on the same circuit EXCEPT the dust collector and air compressor, since they are the only ones that run at the same time as my other tools. You use pneumatic tools and the table saw at the same time? Yes, I understand the compressor could kick on even when it's not in use, but remember that "best practice" is to shut the compressor down and drain the water at the end of the day. If it cycles on, when not in use, once a day, then you have a pretty considerable air leak somewhere. |
#10
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On Jun 5, 9:45*am, (Doug Miller) wrote:
In article , Jack Stein wrote: I could have all my tools on the same circuit EXCEPT the dust collector and air compressor, since they are the only ones that run at the same time as my other tools. You use pneumatic tools and the table saw at the same time? Yes, I understand the compressor could kick on even when it's not in use, Or, you can dust the saw off with the airgun between cuts... or even, for heavy use, maybe direct a bolt-in air nozzle at the saw's teeth inside the table saw housing. A drill, saw, or router can benefit from airblast chip removal as well as from dust collection. If you want to be creative, consider air-powered clamps and vises, too. |
#11
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#13
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
zzzzzzzzzz wrote:
A compressor can come on at any time. Not really. It will only come on if the pressure drops below the cut in pressure. Quite predictable actually. Yes, I understand the compressor could kick on even when it's not in use, but remember that "best practice" is to shut the compressor down and drain the water at the end of the day. If it cycles on, when not in use, once a day, then you have a pretty considerable air leak somewhere. Are you saying that you never use your compressor in the same day as your saw? No, but his point is valid. The compressor is not going to come on just because it's sitting there. If you're not using it to drain down the pressure, it's not going to come on unless you have a leak. Best to fix the leak. -- -Mike- |
#14
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Doug Miller wrote:
In article , Jack Stein wrote: Doug Miller wrote: The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Wot? I could have all my tools on the same circuit EXCEPT the dust collector and air compressor, since they are the only ones that run at the same time as my other tools. You use pneumatic tools and the table saw at the same time? Not at the exact same time, but unlike other tools, the compressor doesn't stop running when you stop sanding, or drilling or whatever. Yes, I understand the compressor could kick on even when it's not in use, but remember that "best practice" is to shut the compressor down and drain the water at the end of the day. What happens with a compressor is it doesn't run until you use a bunch of air, then it runs until the tank pressure maxes out. You can be using other tools while it is running and you are not using an air tool. If it cycles on, when not in use, once a day, then you have a pretty considerable air leak somewhere. I have significant air leaks then, but not enough for me to bother with. One thing that also happens is if a tool drops the tank pressure to just above the start up level, the thing will start up later on it's own. Even if you have no leaks, some tools if left connected can have bleed through. At any rate, since the dust collector runs with all other tools, and the compressor starts up on it's own, sometimes when using other tools, it's good practice to have those two on their own circuit. -- Jack The Second Amendment is in place in case the politicians ignore the others. http://jbstein.com |
#15
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , Jack Stein wrote:
Doug Miller wrote: In article , Jack Stein wrote: Doug Miller wrote: The air compressor could be on the same circuit as either the table saw or the dust collector, since it's unlikely that you'd ever be using it at the same time as either of the others. Wot? I could have all my tools on the same circuit EXCEPT the dust collector and air compressor, since they are the only ones that run at the same time as my other tools. You use pneumatic tools and the table saw at the same time? Not at the exact same time, but unlike other tools, the compressor doesn't stop running when you stop sanding, or drilling or whatever. And you can't wait to start the table saw til the compressor stops? :-) Yes, I understand the compressor could kick on even when it's not in use, but remember that "best practice" is to shut the compressor down and drain the water at the end of the day. What happens with a compressor is it doesn't run until you use a bunch of air, then it runs until the tank pressure maxes out. You can be using other tools while it is running and you are not using an air tool. How often, though, do you really switch back and forth that quickly? If it cycles on, when not in use, once a day, then you have a pretty considerable air leak somewhere. I have significant air leaks then, but not enough for me to bother with. One thing that also happens is if a tool drops the tank pressure to just above the start up level, the thing will start up later on it's own. No, it won't, unless there's a leak somewhere. Even if you have no leaks, some tools if left connected can have bleed through. That's a leak. At any rate, since the dust collector runs with all other tools, and the compressor starts up on it's own, sometimes when using other tools, it's good practice to have those two on their own circuit. I agree that it's good practice. I don't agree that it's mandatory. And it certainly isn't a Code violation, as one person appeared to suggest. |
#16
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On Tue, 1 Jun 2010 05:44:49 -0400, "Bill"
wrote: Prompted by suggestions that a shop needs convenient power, I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** in addition to GFCI CB's. I'm going to agree with Doug and Mike both. Motor loads have some high start up currents and your asking for nuisance trips. Don't be stingy with the breakers and circuits. The retractable drop from the ceiling as recommended I've found really useful. Mike M |
#17
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On Jun 1, 5:44*am, "Bill" wrote:
Prompted by suggestions that a shop needs convenient power, *I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. *In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** *in addition to GFCI CB's. The top of my workbench overhangs the support frame by about 5 inches. I put a 120V duplex every 2.5 feet or so along the frame under the overhang, facing out into the shop. This keeps the top of the workbench clear of cords running from the back wall (as pictured in your "garage" sketch) when using sanders, heat guns, etc. I'm sure you already know that the lights should be on their own circuit so that no tools can take them out and plunge you into darkness. |
#18
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "DerbyDad03" wrote in message news:be4235af-adbc-4050-8fbe- The top of my workbench overhangs the support frame by about 5 inches. I put a 120V duplex every 2.5 feet or so along the frame under the overhang, facing out into the shop. This keeps the top of the workbench clear of cords running from the back wall (as pictured in your "garage" sketch) when using sanders, heat guns, etc. DD, This is a nice idea. Is the workbench powered using a male-male extension cord to the wall? Sorry if the answer is obvious. Bill |
#19
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On Jun 1, 8:11*pm, "Bill" wrote:
"DerbyDad03" wrote in message news:be4235af-adbc-4050-8fbe- The top of my workbench overhangs the support frame by about 5 inches. I put a 120V duplex every 2.5 feet or so along the frame under the overhang, facing out into the shop. This keeps the top of the workbench clear of cords running from the back wall (as pictured in your "garage" sketch) when using sanders, heat guns, etc. DD, This is a nice idea. *Is the workbench powered using a male-male extension cord to the wall? Sorry if the answer is obvious. Bill "Is the workbench powered using a male-male extension cord to the wall?" I was hoping nobody would ask that question! The workbench is a rather old structure (1950's?) that came with the house. It is basically framed with full-sized 2 x 4's (doubled up for the legs) and topped with 2 x 8's, upon which I added 1/4" hardboard to get a smooth yet replaceable work surface. The unit is just over 8' long and about 3' deep. It's a rather hefty unit. It is more or less "permanently" wired into the shop. There is a junction box attached to a back leg of the workbench with a run of 12/2 NM from a junction box in the ceiling. From the workbench junction box I ran more 12/2 along the frame and attached the outlets in surface mount boxes. I assume the junction box attached to the workbench is probably not code, but based on the weight of the workbench and it's location, it's not something that ever gets moved. If it needed to be moved, I would disconnect the wires in the ceiling box so no live wires would be exposed. What would be required to bring this up to code? Would a male-male be required? Would just a male pig-tail from the junction box to a receptacle be better? Or is it OK as is? |
#20
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article ,
DerbyDad03 wrote: On Jun 1, 8:11*pm, "Bill" wrote: "DerbyDad03" wrote in message news:be4235af-adbc-4050-8fbe- The top of my workbench overhangs the support frame by about 5 inches. I put a 120V duplex every 2.5 feet or so along the frame under the overhang, facing out into the shop. This keeps the top of the workbench clear of cords running from the back wall (as pictured in your "garage" sketch) when using sanders, heat guns, etc. DD, This is a nice idea. *Is the workbench powered using a male-male extension cord to the wall? Sorry if the answer is obvious. Bill "Is the workbench powered using a male-male extension cord to the wall?" I was hoping nobody would ask that question! The workbench is a rather old structure (1950's?) that came with the house. It is basically framed with full-sized 2 x 4's (doubled up for the legs) and topped with 2 x 8's, upon which I added 1/4" hardboard to get a smooth yet replaceable work surface. The unit is just over 8' long and about 3' deep. It's a rather hefty unit. It is more or less "permanently" wired into the shop. There is a junction box attached to a back leg of the workbench with a run of 12/2 NM from a junction box in the ceiling. From the workbench junction box I ran more 12/2 along the frame and attached the outlets in surface mount boxes. I assume the junction box attached to the workbench is probably not code, but based on the weight of the workbench and it's location, it's not something that ever gets moved. If it needed to be moved, I would disconnect the wires in the ceiling box so no live wires would be exposed. What would be required to bring this up to code? Would a male-male be required? Would just a male pig-tail from the junction box to a receptacle be better? Or is it OK as is? male-male is *illegal* in a lot of jurisdictions. Serious risk if the upstream (i.e. the wall outlet fed from utility power) end is plugged in and the other end is -not-. In most jurisdictions the outlets on the bench is perfectly legal (no different than a convenience outlet on a stove, say), with a simple drop cord to plug it into a wall outlet. I would probably consider using greenlee armored cable and a twist-lok connector. grin I'd use greenlee, or actual EMT conduit, for all the 'on bench' inter- connections. something -could- fly around and hit bare wiring (even NM) I don't believe in giving MURPHY a -chance- to muck with things. ![]() |
#21
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Bill wrote:
Prompted by suggestions that a shop needs convenient power, I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Bill BTW, I think I will feel better if I use 120v duplex outlets that are **GFCI protected** in addition to GFCI CB's. The last is just silly... I'd (more or less) agree w/ the other posters... Agree on separating the 120V on own circuits and moving up to 30A/10ga over 20A/12ga for at least a couple of the circuits (and if do any, might as well do all). Slight disagreement w/ at least one suggestion...30A @240V is enough for any reasonably efficient 5-horse single-phase motor and given that going to 30A outlets raises compatibility and cost significantly, I don't see any need/justification for more than that for anything other than a dedicated welder circuit or somesuch. Presuming, of course, that the distances are reasonable so that voltage drops are 5% or less and this is a typical home shop, not commercial or a behemoth thing... Agree that the "never enough" for 120V and the overhead are certainly also truisms as well as the admonition for lights to not be on work outlets. -- |
#22
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Never combine two motor loads on one circuit. The simultaneous starting
current will typically take out the breaker when you least want it to. Two motors on any breaker / circuit is a big no-no and will also not protect your equipment from any locked-rotor current. This is when the equipment jams or shorts out and the circuit breaker is sized wrong for that piece of equipment (big enough to carry the two motors), does not trip and your motor windings go up in smoke. Bigger repair bill and possible fire hazard. Proper motor protection circuits found in industry typically have two levels of protection, one for the large starting current and one for the typical loaded running current. Anything lasting longer than the two situations, at that current level, will trip out the breaker / circuit interupter. In home usage only one level of current protection is typically afforded with a simple breaker. Don't defeat it by combining two motor devices. The Electrical Inspector would advise against you doing this, if he catches it or you ask. "dpb" wrote in message ... Bill wrote: The last is just silly... I'd (more or less) agree w/ the other posters... Agree on separating the 120V on own circuits and moving up to 30A/10ga over 20A/12ga for at least a couple of the circuits (and if do any, might as well do all). Slight disagreement w/ at least one suggestion...30A @240V is enough for any reasonably efficient 5-horse single-phase motor and given that going to 30A outlets raises compatibility and cost significantly, I don't see any need/justification for more than that for anything other than a dedicated welder circuit or somesuch. Presuming, of course, that the distances are reasonable so that voltage drops are 5% or less and this is a typical home shop, not commercial or a behemoth thing... Agree that the "never enough" for 120V and the overhead are certainly also truisms as well as the admonition for lights to not be on work outlets. -- --- news://freenews.netfront.net/ - complaints: --- |
#23
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#24
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Doug Miller wrote:
In article , "Josepi" X-Complaints-to: . wrote: Never combine two motor loads on one circuit. Nonsense. .... What he said... ![]() -- |
#25
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
From your nonsense comments I see you must operate your compressor with a
manual on/off switch. Imagine you recommending a person operating a table saw to have it stall in the middle of a cut because they forgot to turn off the air compressor. You give dangerous advice here. I don't now what you kind of air compressor you operate but real compressors have a pressure sensor on the tank to keep the pressure within a range set by the operator. As far as overcurrent protection, you have no idea. Don't even try to convince me of anything in that regard. I was trying to display some common sense and adherance to most electrical safety codes. You could try reading yours. "Doug Miller" wrote in message ... In article , "Josepi" X-Complaints-to: . wrote: Never combine two motor loads on one circuit. Nonsense. The simultaneous starting current will typically take out the breaker when you least want it to. Only if you turn both of them on at the same moment -- a rather rare occurrence in a one-man home workshop, I'd say. Two motors on any breaker / circuit is a big no-no More nonsense. and will also not protect your equipment from any locked-rotor current. This is when the equipment jams or shorts out and the circuit breaker is sized wrong for that piece of equipment (big enough to carry the two motors), does not trip and your motor windings go up in smoke. Bigger repair bill and possible fire hazard. You have a serious misunderstanding of the purpose of overcurrent protective devices. Circuit breakers are there to protect the branch circuit wiring, *not* the loads that are plugged into the receptacles on that circuit. If a particular load needs some specific level of overcurrent protection, that is achieved by fusing that load. Proper motor protection circuits found in industry We're talking about a one-man home workshop here, not an industrial installation. typically have two levels of protection, one for the large starting current and one for the typical loaded running current. Anything lasting longer than the two situations, at that current level, will trip out the breaker / circuit interupter. One-man home workshop, remember? How often will two tools be operated simultaneously? In home usage only one level of current protection is typically afforded with a simple breaker. Don't defeat it by combining two motor devices. The Electrical Inspector would advise against you doing this, if he catches it or you ask. Nonsense. How often do you turn two motors on at the same time? How often do you *use* two motors at the same time (unless one of them is the dust collector)? There is _absolutely nothing wrong_ with the OP putting his table saw and air compressor on the same circuit, or his drill press and jointer. They will *never* be in use at the same time -- and even if they are, it's not likely to be a problem unless they're switched on simultaneously. Now you tell me how often that's going to happen. One-man home workshop, remember? --- news://freenews.netfront.net/ - complaints: --- |
#26
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Josepi" X-Complaints-to: . wrote:
From your nonsense comments I see you must operate your compressor with a manual on/off switch. Imagine you recommending a person operating a table saw to have it stall in the middle of a cut because they forgot to turn off the air compressor. You give dangerous advice here. OK, I'll give you that one. The rest of your post was complete nonsense. As far as overcurrent protection, you have no idea. Don't even try to convince me of anything in that regard. Point out exactly what errors you imagine I made in that regard. Hint: you are completely clueless if you think that branch circuit overcurrent protection has anything to do with protecting the loads that are plugged into that circuit. I was trying to display some common sense Had you actually managed to do so, it would have been its initial appearance in your posts. and adherance to most electrical safety codes. You could try reading yours. I'm quite familiar with mine; much more so, apparently, than you are with yours or any others. Here's a link to mine; perhaps you'd be good enough to point out where it prohibits putting two motors on the same circuit. http://nfpaweb3.gvpi.net/rrserver/br...NFPASTD/7008SB Perhaps you'd also be good enough to explain why the US NEC requires only two small-appliance circuits in a kitchen -- which, according to you, is enough for only two motors. Gosh, I must be in big trouble: blender, two mixers, coffee grinder, can opener... all that on only two circuits... Don't presume to lecture me on residential electrical installations. You have no idea. "Doug Miller" wrote in message ... In article , "Josepi" X-Complaints-to: . wrote: Never combine two motor loads on one circuit. Nonsense. The simultaneous starting current will typically take out the breaker when you least want it to. Only if you turn both of them on at the same moment -- a rather rare occurrence in a one-man home workshop, I'd say. Two motors on any breaker / circuit is a big no-no More nonsense. and will also not protect your equipment from any locked-rotor current. This is when the equipment jams or shorts out and the circuit breaker is sized wrong for that piece of equipment (big enough to carry the two motors), does not trip and your motor windings go up in smoke. Bigger repair bill and possible fire hazard. You have a serious misunderstanding of the purpose of overcurrent protective devices. Circuit breakers are there to protect the branch circuit wiring, *not* the loads that are plugged into the receptacles on that circuit. If a particular load needs some specific level of overcurrent protection, that is achieved by fusing that load. Proper motor protection circuits found in industry We're talking about a one-man home workshop here, not an industrial installation. typically have two levels of protection, one for the large starting current and one for the typical loaded running current. Anything lasting longer than the two situations, at that current level, will trip out the breaker / circuit interupter. One-man home workshop, remember? How often will two tools be operated simultaneously? In home usage only one level of current protection is typically afforded with a simple breaker. Don't defeat it by combining two motor devices. The Electrical Inspector would advise against you doing this, if he catches it or you ask. Nonsense. How often do you turn two motors on at the same time? How often do you *use* two motors at the same time (unless one of them is the dust collector)? There is _absolutely nothing wrong_ with the OP putting his table saw and air compressor on the same circuit, or his drill press and jointer. They will *never* be in use at the same time -- and even if they are, it's not likely to be a problem unless they're switched on simultaneously. Now you tell me how often that's going to happen. One-man home workshop, remember? --- news://freenews.netfront.net/ - complaints: --- |
#27
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#28
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On 6/1/2010 4:34 PM, Scott Lurndal wrote:
While I agree with you, just to play devil's advocate, I usually run my 2HP dust collector (240v) simultaneously with a 3HP tables saw, planer or bandsaw. That said, all my 240v tools are on dedicated circuits. As are mine. I do have the 240V shop heater (Dayton, ceiling mount) on the same 240 circuit as the shaper, simply because I don't use the shaper that often (and I ran out of slots in the subpanel). Compressors are a strange beast, since they may start at anytime the pressure switch hits some threshold (yet again, I've got mine on a dedicated 120v/20A breaker). I run mine on a 120v non-dedicated circuit that, being in a garage "shop" on residential property, is required by local code to be GFCI protected, but I've never had any trouble with the setup at all. The 20A circuit is shared with a small fan, some undercounter fluorescent lighting, battery charger, and the occasional shop vac. One of the good things about a dedicated circuit is that it's exempt from GFCI protection requirements in most locales where they are required in "garages" (which is most of them in the US). -- www.e-woodshop.net Last update: 4/15/2010 KarlC@ (the obvious) |
#29
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
All my 120v shop outlets are quad boxes, with the left outlets on a
separate breaker than the right ones. I run 12/3 to them and use a ganged breaker so you never have a half-live box. I've found a ceiling mounted 240v outlet to be *very* handy. It's not a locking outlet; if you trip over the cord you want it to just pull out. I have two sets of lights - the regular basement lights, and extra shop lights. One tripped breaker is not enough to plunge the shop into darkness. All my shop-specific circuits are off a shop-specific panel, which I can disconnect at the main panel for safety if needed. |
#30
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "DJ Delorie" wrote in message ... All my shop-specific circuits are off a shop-specific panel, which I can disconnect at the main panel for safety if needed. I bought a "shop specific" panel already. I've already considered that the lighting should be on separate circuits. I'm glad I bought a bigger panel than I thought I needed at the time (I bought the 24 pole one Lew advised). Thank all of you for helping me to learn more about these matters! I am surely not an expert and don't pretend to be one here. I have a couple of follow-up questions. 1. If having GFCI at the outlet and at the C'Breaker is redundant, then how come they now required GFCI at the outlet in bathrooms? Someone, I think a maintenance person, explained to me that having it at the outlet is more effective because it is closer to the source--and trips significantly faster/easier. Is this nonsense? 2. Consider running 30 Amps to the 240v outlets as has been suggested. A Grizzly G0690 TS is 15 Amps (240v) and Grizzly suggests that it should be on a 20 Amp circuilt. Does this imply it would be prudent to use a 20 Amp fuse near the connection to help protect the equiptment. Lew always said that the CBs are there to protect the lines and Not the equiptment. 3. It was suggested to run 2 120v branch circuits. Fine to run these off of one 14-3 cable? 4. Any problem with ripping down all of the drywall around the main panel for a while so I can "see everything"? I'm intending to install the subpanel adjacent to the main panel. I will of course turn off the main-breaker in the main panel before I do anything and I will keep in mind that the lines going into the main panel are still live. I think that the "worst" part of this whole operation may be drilling vertically up into the attic where there are already so many wires coming out of the main panel--and it's neer impossible to view from the attic because it is so close to the eave. I suspect I'll be "fishing" with a coathanger, stapling 8 feet along the attic framing and then going down into the wall. I think that my own standards are higher than those who have worked in the attic before...I've started wrapping plastic conduit around some of the small wires passing through. I hope I'm not the only one who has learning something from this thread. Thanks! Bill |
#31
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Bill" wrote:
Thank all of you for helping me to learn more about these matters! I am surely not an expert and don't pretend to be one here. I have a couple of follow-up questions. 1. If having GFCI at the outlet and at the C'Breaker is redundant, then how come they now required GFCI at the outlet in bathrooms? That's *not* required. At least not by the NEC. All the NEC requires is that the outlets "shall have ground-fault circuit interrupter protection". It does not specify where that protection is located. Someone, I think a maintenance person, explained to me that having it at the outlet is more effective because it is closer to the source--and trips significantly faster/easier. Is this nonsense? Yes, it is. Be careful taking wiring advice from this person. Even if the outlet is 100 meters from the breaker, the difference in trip speed due to the distance is on the order of half a microsecond. There is one legitimate reason for putting the protection at the outlet: it's easier to reset if it trips -- mostly because it's easier to find. 2. Consider running 30 Amps to the 240v outlets as has been suggested. A Grizzly G0690 TS is 15 Amps (240v) and Grizzly suggests that it should be on a 20 Amp circuilt. Does this imply it would be prudent to use a 20 Amp fuse near the connection to help protect the equiptment. Lew always said that the CBs are there to protect the lines and Not the equiptment. Lew is right. But what do you think you might need to protect the equipment from? Consider this: you use 0.5A light bulbs on a 15A circuit all the time and never worry about it. 3. It was suggested to run 2 120v branch circuits. Fine to run these off of one 14-3 cable? NO. You definitely want 12-3 with a 20A breaker for shop use. 4. Any problem with ripping down all of the drywall around the main panel for a while so I can "see everything"? Yes: you create a lot of unnecessary drywall repair work for yourself. All of the really important stuff to see is inside the main panel; what do you expect you might see behind the drywall besides a bunch of cables? I'm intending to install the subpanel adjacent to the main panel. I will of course turn off the main-breaker in the main panel before I do anything If the feed to the subpanel is coming from lugs in the main panel, then yes, you need to power off the main. If it's coming from a circuit breaker in the main panel -- which is a much better idea -- then there's really no need to power off the main as long as you don't put your fingers in places they don't belong. Make sure that the circuit breaker feeding the subpanel is off before you connect the feed to it, otherwise the shaft of your screwdriver becomes live, which could lead to unpleasant surprises. And let's be clear he I am NOT talking about the disconnect breaker in the subpanel; I'm talking about the breaker that you put in the main panel to connect the subpanel feed from. and I will keep in mind that the lines going into the main panel are still live. Always a good thing to remember. :-) |
#32
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() |
#33
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Doug Miller" wrote in message ... Doug Miller, Thank you for your reply. It is very informative and helpful! 4. Any problem with ripping down all of the drywall around the main panel for a while so I can "see everything"? Yes: you create a lot of unnecessary drywall repair work for yourself. Well, the drywall there is probably almost 40 years old and on it's second main panel. As long as I am replacing 3/4 of the drywall on 2 walls, maybe 3 before I'm finished, I may as well make the drywall near the main panel look Nice! : ) If the feed to the subpanel is coming from lugs in the main panel, then yes, you need to power off the main. If it's coming from a circuit breaker in the main panel -- which is a much better idea -- then there's really no need to power off the main as long as you don't put your fingers in places they don't belong. Make sure that the circuit breaker feeding the subpanel is off before you connect the feed to it, otherwise the shaft of your screwdriver becomes live, which could lead to unpleasant surprises. And let's be clear he I am NOT talking about the disconnect breaker in the subpanel; I'm talking about the breaker that you put in the main panel to connect the subpanel feed from. I'll tell ya Mr. Miller. There are folks here who don't believe I should be doing anything to any walls that have any live wires in them! I appreciate the precision with which you have described the operation above. It reminds me of an anecdote which I have found humorous since I heard it: There was a old blues singer, "Big Joe Williams" who frequented the barrelhouses and who I believe, besides for his music, was known for his temper, fighting, drinking and just being a "rough character". One day he decided he wanted to buy a gun. His friends escorted him to an purveyor of firearms (i.e. a gun store). They said to the store owner, "Mr. Williams here would like to buy a gun", meanwhile standing behind Joe Williams emphatically shaking their heads and mouthing "No, No, No!" I suspect that what you wrote may have caused a similar reaction from some readers. Maybe they'll speak up if I am correct. : ) I doubt that I'll be adding any CBs to any live panels anytime soon... Thank you again for your assistance. I'm hope to make meaningful progress during the next week. Bill |
#34
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , "Bill" wrote:
"Doug Miller" wrote in message ... Doug Miller, Thank you for your reply. It is very informative and helpful! 4. Any problem with ripping down all of the drywall around the main panel for a while so I can "see everything"? Yes: you create a lot of unnecessary drywall repair work for yourself. Well, the drywall there is probably almost 40 years old and on it's second main panel. As long as I am replacing 3/4 of the drywall on 2 walls, maybe 3 before I'm finished, I may as well make the drywall near the main panel look Nice! : ) Oh, well, as long as you're redoing most of the drywall anyway... If the feed to the subpanel is coming from lugs in the main panel, then yes, you need to power off the main. If it's coming from a circuit breaker in the main panel -- which is a much better idea -- then there's really no need to power off the main as long as you don't put your fingers in places they don't belong. Make sure that the circuit breaker feeding the subpanel is off before you connect the feed to it, otherwise the shaft of your screwdriver becomes live, which could lead to unpleasant surprises. And let's be clear he I am NOT talking about the disconnect breaker in the subpanel; I'm talking about the breaker that you put in the main panel to connect the subpanel feed from. I'll tell ya Mr. Miller. There are folks here who don't believe I should be doing anything to any walls that have any live wires in them! Wusses. g If you have to cut into a wall that you know, or suspect, has live wires inside it, use a utility knife. Not a saw. A utility knife won't extend through the drywall far enough to hit a wire, and even if it does the wire will simply move out of the way. I appreciate the precision with which you have described the operation above. It reminds me of an anecdote which I have found humorous since I heard it: There was a old blues singer, "Big Joe Williams" who frequented the barrelhouses and who I believe, besides for his music, was known for his temper, fighting, drinking and just being a "rough character". One day he decided he wanted to buy a gun. His friends escorted him to an purveyor of firearms (i.e. a gun store). They said to the store owner, "Mr. Williams here would like to buy a gun", meanwhile standing behind Joe Williams emphatically shaking their heads and mouthing "No, No, No!" :-) I suspect that what you wrote may have caused a similar reaction from some readers. Maybe they'll speak up if I am correct. : ) I doubt that I'll be adding any CBs to any live panels anytime soon... That's up to you. Certainly it's safer to kill the power to the panel first, but if you're careful about where you put your fingers it's only slightly safer. At SWMBO's insistence, I never work in live panels alone. And at *my* insistence, SWMBO never works in live panels at all. She knows what she's doing (degreed engineer). The issue is that she knows CPR, and I don't. Another rule of thumb is to keep one hand in your pocket or behind your back. If you're wearing rubber-soled shoes, it's nearly (but not completely) impossible to get a fatal shock if you have only one hand in the panel. The greatest danger in AC comes when the current passes across the heart: from hand to hand, or from hand to opposite foot. I've been stung a couple of times; that encourages a healthy respect for 120VAC, but it also helps to dispel exaggerated fears of it too. The last time, about five years ago, the back of my hand was against the panel chassis and I inadvertently brushed the tip of my index finger against a live busbar, so the grounding path was just the length of my finger plus half of my hand. I felt it up the the shoulder; half an hour later, I could still feel it in my elbow. It *hurts*. Make no mistake about that. But I'm still alive. Thank you again for your assistance. I'm hope to make meaningful progress during the next week. You're quite welcome, Bill. Keep asking questions -- it's the best way to learn. |
#35
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
Yes, some of this is nonsense. Having the GFCI at the receptical is more
convenience to reset and easier to see what happened if it trips. Breaker panel GFCIs have been brutally expensive in years past compared to receptical types. They are getting cheaper. Many bubble tubs are wired with a receptical type GFCI at the panel, labelled and then a circuit taken to the tub due to price differences. Tripping faster is nonsense. The GFCI senses differential current. OTOW it compares the hot leg current with the neutral current to see if they are the same. If there is a difference then there is current leaking to ground and a fault in the equipment. It does not protect the equipment from stalled currents or internal shorts unless it goes to the case. Mostly it protects the human by tripping out fast so the time the fault travels through your body is limited. Contrary to what some say they do not limit the actual current level amount. This does not matter where it is done. I am not in the UK despite what the OCD boy thinks. "Bill" wrote in message ... 1. If having GFCI at the outlet and at the C'Breaker is redundant, then how come they now required GFCI at the outlet in bathrooms? Someone, I think a maintenance person, explained to me that having it at the outlet is more effective because it is closer to the source--and trips significantly faster/easier. Is this nonsense? Bill --- news://freenews.netfront.net/ - complaints: --- |
#36
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
1. If having GFCI at the outlet and at the C'Breaker is redundant,
No, a panel GFCI and an outlet GFCI are redundant. You need *one* GFCI per circuit, extras won't help. You need *one* breaker per circuit. Breakers and GFCIs serve two different purposes. 2. Consider running 30 Amps to the 240v outlets as has been suggested. A Grizzly G0690 TS is 15 Amps (240v) and Grizzly suggests that it should be on a 20 Amp circuilt. Does this imply it would be prudent to use a 20 Amp fuse near the connection to help protect the equiptment. Lew always said that the CBs are there to protect the lines and Not the equiptment. If you use a 30 amp breaker, you have to have everything permanent on that circuit rated for 30 amps - wiring and outlet. That means your TS needs a 30 amp plug, although code does not require the TS to have wiring rated for 30 amps. If you *do* put a 20 amp rated tool on a 30 amp circuit, it would be prudent (but not required by code) to put additional protection on that's sized for the tool. 3. It was suggested to run 2 120v branch circuits. Fine to run these off of one 14-3 cable? I wouldn't use 14 gauge wire at all in a shop - that's limited to 15 amps, and many of my tools need 20 amp anyway, which means 12 gauge. As for putting two 120v outlets on a single 240v wire - check with your local code and find out what the rules are. Most likely, you'll at least need to use a ganged breaker to protect the branch properly. |
#37
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "DJ Delorie" wrote in message ... 1. If having GFCI at the outlet and at the C'Breaker is redundant, No, a panel GFCI and an outlet GFCI are redundant. You need *one* GFCI per circuit, extras won't help. You need *one* breaker per circuit. Breakers and GFCIs serve two different purposes. Yes. By panel GFCI, I meant a C-B with a built-in GFCI. I apologize for not being more careful in my writing. It is nice to know that having a GFCI at the panel suffices! 2. Consider running 30 Amps to the 240v outlets as has been suggested. A Grizzly G0690 TS is 15 Amps (240v) and Grizzly suggests that it should be on a 20 Amp circuilt. Does this imply it would be prudent to use a 20 Amp fuse near the connection to help protect the equiptment. Lew always said that the CBs are there to protect the lines and Not the equiptment. If you use a 30 amp breaker, you have to have everything permanent on that circuit rated for 30 amps - wiring and outlet. That means your TS needs a 30 amp plug, although code does not require the TS to have wiring rated for 30 amps. If you *do* put a 20 amp rated tool on a 30 amp circuit, it would be prudent (but not required by code) to put additional protection on that's sized for the tool. Thank you. I had been thinking about this ever since it came up. In my situation, I was thinking that the prudent thing to do, is to stick with the 20 Amp CBs, and consider installing heavier wire where I think I might like to have it someday. I learned "plenty" about 20, 30 and 50 amp 240v plugs and outlets a few months ago! 3. It was suggested to run 2 120v branch circuits. Fine to run these off of one 14-3 cable? I wouldn't use 14 gauge wire at all in a shop - that's limited to 15 amps, and many of my tools need 20 amp anyway, which means 12 gauge. As for putting two 120v outlets on a single 240v wire - check with your local code and find out what the rules are. Most likely, you'll at least need to use a ganged breaker to protect the branch properly. That's what I had in mind (ganged breaker). The reference to 14-3 was a momentary slip-up on my part. As I see it, and as someone else surely brought to my attention, is that the problem with such a circuit configuration is that it can be half-live and half-dead. Potentially confusing! Thank you for your help! Bill |
#38
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
In article , DJ Delorie wrote:
As for putting two 120v outlets on a single 240v wire - check with your local code and find out what the rules are. Most likely, you'll at least need to use a ganged breaker to protect the branch properly. Yes. That's required by Code now. It didn't use to be. |
#39
![]()
Posted to rec.woodworking
|
|||
|
|||
![]()
On Jun 1, 2:44*am, "Bill" wrote:
Prompted by suggestions that a shop needs convenient power, *I created a (pdf) SU view of my proposed outlet configuration (for one wall), and also a corresponding wiring model: http://web.newsguy.com/MySite/ Comments or suggestions welcome. *In fact, all I seek is a simple nod. Thank you again to those of you who helped me to reach this point (of understanding)! Bill, here is something from the Antifaq I hope it helps: 5.1 HOW DO I WIRE MY SHOP? As my friend Doug, the journeyman cabinetmaker, says: there's only four things you gotta know about being an electrician: S--- flows downhill, Payday is on Friday, It may be s--- to you but its bread and butter to them, and Every asshole is a potential customer. Oops! That was about plumbers. Forget it. Anyway, Doug is just jealous of plumbers 'cause they make more money than cabinetmakers, just like Tom. Actually, all the regulars and most of the newbies on the wreck are electrical experts. That's why any thread on wiring and electricity gets so many responses. Most of us work with electricity all the time. After all computers and power tools are electrical, and so's the TV we watch Norm on. If you want to change the plug on your tablesaw, you still need to know everything about wiring and amps and volts and watts and volt-amps and wire gauges and phases and power factors and impedance and resistance and plug configurations and panel sizes and capacitors and motors and switches and electrical codes. But that's OK, don't be afraid. You can trust any wiring and electrical advice from anybody on the wreck, apply it and be absolutely sure that it will meet code and be perfectly safe. No point in getting ripped off by electricians or consulting an inspector. Just ask away on the group and you can be sure of getting a whole lot of accurate and consistent responses, just like when you ask any math question of all the rocket scientists on the wreck. HTH Luigi |
#40
![]()
Posted to rec.woodworking
|
|||
|
|||
![]() "Luigi Zanasi" wrote in message news:9ca52b6c-e329-4a93-bc9a- Just ask away on the group and you can be sure of getting a whole lot of accurate and consistent responses, just like when you ask any math question of all the rocket scientists on the wreck. Luigi, Your concerns are well-taken. But I do not require a lot of consistent responses. I think if 3 different contractors showed up at my door, they would not be consistent. I do not even think they would try to understand my needs as well as the folks here do. I have earned a PhD in mathematics so I can field at least some of your math questions with some authority, just as some of the folks here have been able to field my questions about electricity with the same sort of authority. I think you are under-estimating the amount of intellect which is here. Why you choose to take this point of view I am uncertain. I think it is not so difficult to separate the wheat from the chaff. It is more difficult to navigate my attic--but I am working on that! : ) I wonder how many people learned something useful about GFCI today? I know I did--or at least, I think I did! Best, Bill |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Heating my shop. Two options both electric | Woodworking | |||
Heating my shop. Two options both electric | Woodworking | |||
Heating my shop. Two options both electric | Woodworking | |||
Heating my shop. Two options both electric | Woodworking | |||
Shop electric question | Woodworking |