Hi everyone!
I have a Danfoss Controller (FP715) connected to a Honeywell 3 way valve via the Danfoss wiring box. I installed it a while back, but it is only now the days have become warmer that I had spotted a problem. If I, via the programmer, turn the central heating on, the rads get hot. If I turn the CH and hot water on, the rads get hot and the water is heated. Now that the warmer days are here, I only wanted the hot water heater, with no central heating. Unfortunately both the hot water and central heating are switched on! This isn't really what I wanted to happen! I have read, and re-read, the FAQ on 3 port valves, and can only assume that I have wired it incorreclty. Can anyone else who has a honeywell 3 port valve please confirm what colour cable I should have where? I have my hot feed to AB, my CH is port A, the HW is port B (is the OK)? (As I am writing this, I think the ports should be the other way round?) The connections for the wiring box a Green Earth Blue Neutral White CH Call for heat Grey HW off Orange HW on (via the cyl sat) Does this sound correct? From the FAQ (which makes me think I have the valve the wrong way round). Green/Yellow Safety Earth Brown Not used. Orange Go fully to 'B' when live. Grey Live when at 'AB' or 'B' White Go to 'AB' or 'B'. If I have the valve the wrong way round, can I just swap the Grey and white connections over? Many thanks for your help, and apologies for my ramblings! Matthew |
#3
|
|||
|
|||
Bolier Control Wiring Query
On Sun, 11 Apr 2004 11:00:13 GMT, (Lurch)
wrote: I have my hot feed to AB, my CH is port A, the HW is port B (is the OK)? (As I am writing this, I think the ports should be the other way round?) Nope, thats fine. The connections for the wiring box a Green Earth Blue Neutral White CH Call for heat Grey HW off Orange HW on (via the cyl sat) Does this sound correct? Yes. No. I think your wiring fault is elsewhere in the system, assuming it isn't a faulty component somewhere. You might want to read these. http://tinyurl.com/2dr9m http://tinyurl.com/26hzu Check the system through, with a test meter, for the correct voltages at the right places. Many thanks for that SJW. Thanks for the links. Looks like the plumbing is correct, perhaps I have a wiring fault elsewhere. Any ideas where to start? If I call for heating only, the CH side of the pipework get hot. If I call for both, both sets of pipework gets hot - if I lower the seting on the tank stat the HW side of the pipework cools down. If I call for HW only, both sides get hot, and adjusting the stat switches the pump off so both sides cool down! Does this help? Thanks again, Matthew |
#4
|
|||
|
|||
Bolier Control Wiring Query
In an earlier contribution to this discussion,
Matthew Humphreys wrote: On Sun, 11 Apr 2004 11:00:13 GMT, (Lurch) wrote: I have my hot feed to AB, my CH is port A, the HW is port B (is the OK)? (As I am writing this, I think the ports should be the other way round?) Nope, thats fine. The connections for the wiring box a Green Earth Blue Neutral White CH Call for heat Grey HW off Orange HW on (via the cyl sat) Does this sound correct? Yes. No. I think your wiring fault is elsewhere in the system, assuming it isn't a faulty component somewhere. You might want to read these. http://tinyurl.com/2dr9m http://tinyurl.com/26hzu Check the system through, with a test meter, for the correct voltages at the right places. Many thanks for that SJW. Thanks for the links. Looks like the plumbing is correct, perhaps I have a wiring fault elsewhere. Any ideas where to start? If I call for heating only, the CH side of the pipework get hot. If I call for both, both sets of pipework gets hot - if I lower the seting on the tank stat the HW side of the pipework cools down. If I call for HW only, both sides get hot, and adjusting the stat switches the pump off so both sides cool down! Does this help? Thanks again, Matthew Check the wiring in your junction box. When hot water only is switched on, pins 1 and 6 in the junction box should be live. When you turn the cylinder stat up to a high temperature, pin 8 should be live (and pin 7 not live). When you turn the cylstat down to a low temperature, pin 8 should cease to be live and pin 7 should become live instead. The boiler and pump (or just the boiler if the pump is connected via an over-run stat on the boiler) should be connected to pin 8 - so the boiler should fire when the cylstat is turned up. Check these things, and let us know the score. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#5
|
|||
|
|||
Bolier Control Wiring Query
On Sun, 11 Apr 2004 14:54:13 +0100, "Set Square"
wrote: Matthew Check the wiring in your junction box. When hot water only is switched on, pins 1 and 6 in the junction box should be live. When you turn the cylinder stat up to a high temperature, pin 8 should be live (and pin 7 not live). When you turn the cylstat down to a low temperature, pin 8 should cease to be live and pin 7 should become live instead. The boiler and pump (or just the boiler if the pump is connected via an over-run stat on the boiler) should be connected to pin 8 - so the boiler should fire when the cylstat is turned up. Check these things, and let us know the score. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! Thanks for the help - not bad support for an Easter Sunday! OK, If I ask for HW only, pins 6,7,8 and 9 of the Danfoss wiring box are live! This doesn't sound right! If I drop the stat temp, then 8 and 9 go off. The boiler is on pin 9, which in turn is linked to pin 8 (as per the installation sheet) - which seems OK. Pin 7 is the "HW off" from the stat, I think Hope this is starting to make sense to someone! |
#6
|
|||
|
|||
Bolier Control Wiring Query
In an earlier contribution to this discussion,
Matthew Humphreys wrote: On Sun, 11 Apr 2004 14:54:13 +0100, "Set Square" wrote: Matthew Check the wiring in your junction box. When hot water only is switched on, pins 1 and 6 in the junction box should be live. When you turn the cylinder stat up to a high temperature, pin 8 should be live (and pin 7 not live). When you turn the cylstat down to a low temperature, pin 8 should cease to be live and pin 7 should become live instead. The boiler and pump (or just the boiler if the pump is connected via an over-run stat on the boiler) should be connected to pin 8 - so the boiler should fire when the cylstat is turned up. Check these things, and let us know the score. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! Thanks for the help - not bad support for an Easter Sunday! OK, If I ask for HW only, pins 6,7,8 and 9 of the Danfoss wiring box are live! This doesn't sound right! If I drop the stat temp, then 8 and 9 go off. The boiler is on pin 9, which in turn is linked to pin 8 (as per the installation sheet) - which seems OK. Pin 7 is the "HW off" from the stat, I think Hope this is starting to make sense to someone! I was referring to the pin (connection) numbers in the 10-way junction box shown under Y-plan in http://content.honeywell.com/uk/homes/systems.htm It sounds like you have a different wiring scheme if the boiler is on 9! Do you have a reference to a diagram which covers your setup? [On the Honeywell diagram shown in my reference, 9 and 10 are not used!] That aside, if - as you say - 8 and 9 are live when calling for HW only, and the boiler is on 9, I'm at a loss to know why the boiler isn't coming on and heating the water. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#7
|
|||
|
|||
Bolier Control Wiring Query
On Sun, 11 Apr 2004 15:56:17 GMT, in uk.d-i-y
(Matthew Humphreys) strung together this: Check the wiring in your junction box. When hot water only is switched on, pins 1 and 6 in the junction box should be live. When you turn the cylinder stat up to a high temperature, pin 8 should be live (and pin 7 not live). When you turn the cylstat down to a low temperature, pin 8 should cease to be live and pin 7 should become live instead. The boiler and pump (or just the boiler if the pump is connected via an over-run stat on the boiler) should be connected to pin 8 - so the boiler should fire when the cylstat is turned up. Check these things, and let us know the score. Thanks for the help - not bad support for an Easter Sunday! OK, If I ask for HW only, pins 6,7,8 and 9 of the Danfoss wiring box are live! This doesn't sound right! I think from what you say pins 8+9 are the boiler and pump. If I drop the stat temp, then 8 and 9 go off. That sounds right. The boiler is on pin 9, which in turn is linked to pin 8 (as per the installation sheet) - which seems OK. Pin 7 is the "HW off" from the stat, I think Hope this is starting to make sense to someone! I think this might help. http://tinyurl.com/3fyca I'm assuming the wiring you have is as this diagram is, if it's different then what I said could be totally wrong. If I were you I would check the wiring at the clock, stat etc and ensure it is all right. -- SJW A.C.S. Ltd. |
#8
|
|||
|
|||
Bolier Control Wiring Query
In an earlier contribution to this discussion,
Matthew Humphreys wrote: Hi everyone! I have a Danfoss Controller (FP715) connected to a Honeywell 3 way valve via the Danfoss wiring box. I installed it a while back, but it is only now the days have become warmer that I had spotted a problem. If I, via the programmer, turn the central heating on, the rads get hot. If I turn the CH and hot water on, the rads get hot and the water is heated. Now that the warmer days are here, I only wanted the hot water heater, with no central heating. Unfortunately both the hot water and central heating are switched on! This isn't really what I wanted to happen! I have read, and re-read, the FAQ on 3 port valves, and can only assume that I have wired it incorreclty. Can anyone else who has a honeywell 3 port valve please confirm what colour cable I should have where? I have my hot feed to AB, my CH is port A, the HW is port B (is the OK)? (As I am writing this, I think the ports should be the other way round?) The connections for the wiring box a Green Earth Blue Neutral White CH Call for heat Grey HW off Orange HW on (via the cyl sat) Does this sound correct? From the FAQ (which makes me think I have the valve the wrong way round). Green/Yellow Safety Earth Brown Not used. Orange Go fully to 'B' when live. Grey Live when at 'AB' or 'B' White Go to 'AB' or 'B'. If I have the valve the wrong way round, can I just swap the Grey and white connections over? Many thanks for your help, and apologies for my ramblings! Matthew Make sure that the layout and wiring is as per the Y-plan details given in http://content.honeywell.com/uk/homes/systems.htm I think A is ok for heating and B for hot water - check the Honeywell references which someone else has given. If you *do* get them the wrong way round, you can't easily correct it with a simple wiring change. This is because - when installed correctly - the hot water wiring requires an ON *and* OFF signal from the programmer, and requires the cylinder stat to have change-over (as opposed to just on/off) contacts. If you swap this round, the heating would need a "not required" signal from the programmer, and the room stat would have to be the change-over sort. It also means that the valve actuator would be consuming power rather than sitting at its home position throughout the summer when only hot water is required. Under these circumstances, it is far better to turn the valve round - even though it means partially draining the system. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Central Heating : Wiring Query | UK diy | |||
Changing a room thermostat / wiring | UK diy | |||
Light Socket Wiring Query | UK diy | |||
Electrical wiring inspector? | UK diy | |||
Danfoss Control Box wiring - with one single 2 port valve | UK diy |