Hi All,
I thought I'd start a new thread as I could do with an answer asap (to possibly get stuff moving) and I didn't want it to get lost on the end of a similar thread .. We had a letter the other day saying our meter was due for a change. I also read a post here suggesting running some extra tails to feed a garage supply? So, some questions come out of this .. 1) We currently have a dual rate meter (E7 or similar) with a clock / switch feeding a second CU running the storage rads. Will we get a new dual rate meter controlled by radio and if so how will they deal with the external switch for the E7? 2) While he is there doing the meter swap, would it be a 'good idea' to fit some sort of isolator / RCD ready for the pending feed to the garage. If I had the 'box' fitted nearby with a pair of suitable tails 'a dangling' would he / she be willing / able / allowed to hook it in for me? 3) If they take away the 'switch' part of the E7 service (can they do that?) I would be forced to add my own time-switches to each storage rad. Would they supply them to me foc? 4) The CU for the storage rads is a nice MK Sentry 9 way (7 modules and 1 x 2 wide incommer) steel unit with only 2 ways in use (was 3). Maybe I could replace that with a smaller unit and fit the garage 'box' beside it. I could even possibly use the 9 way unit down the garage as a split CU (Sw lights MCB, Lathe MCB, RCD, std ring Power MCB etc?) Am I likely to get bus bars / modules to suit this if I cut it down? Am I right that the SWA should to be 'protected' by an RCD (and that's where I would use a 100mA unit with a 30mA at the garage end? Is it likely I could fit the contents of a cheap plastic Clipsil garage CU into the MK box?) So I would end up with .. Main split CU for the house (with existing 30ma RCD / MCB's) Sub CU (no RCB etc for the storage rads / E7 cct) Garage 'd/p Switch protection box' (with single 100 mA RCD as switch) If anyone has any brands of module to hand I have a blank here for the Sentry and it measures .. The metal mounting rail is 35mm wide (*high* if you look at it from the front) 44mm from the front face of the rail to the inside face of the cu front cover (or module lip) 45mm high module (here it goes through the front panel) 18 mm wide module. What to do ... ? All the best .. you humble apprentice .. T i m |
#2
|
|||
|
|||
Garage supply and new meter?
"T i m" wrote
| 1) We currently have a dual rate meter (E7 or similar) with a clock / | switch feeding a second CU running the storage rads. Will we get a new | dual rate meter controlled by radio and if so how will they deal with | the external switch for the E7? Your existing meter may already be switched by radio for the rate change, and the timeswitch may only be controlling the off-peak CU, i.e. it's your responsibility to not run your storage heaters on peak rate electricity. If the timeswitch is controlling the rate change there will probably be a pair of lightweight wires back to the meter as well as the heavyweight meter tails to the CUs and the timeswitch will (should) be security sealed. If the timeswitch is not controlling the rate change then it will probably be a simple job to pull the old meter off the base and pop the new one on, i.e. the meter changer will not be doing any wiring at all. Owain |
#3
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 14:47:37 +0000, in uk.d-i-y T i m
strung together this: 1) We currently have a dual rate meter (E7 or similar) with a clock / switch feeding a second CU running the storage rads. Will we get a new dual rate meter controlled by radio and if so how will they deal with the external switch for the E7? Probably remove it and use the one built into the new meter. 2) While he is there doing the meter swap, would it be a 'good idea' to fit some sort of isolator / RCD ready for the pending feed to the garage. If I had the 'box' fitted nearby with a pair of suitable tails 'a dangling' would he / she be willing / able / allowed to hook it in for me? Most probably, but not a definite goer though. Depends who you get. 3) If they take away the 'switch' part of the E7 service (can they do that?) I would be forced to add my own time-switches to each storage rad. Would they supply them to me foc? Extremely doubtful. 4) The CU for the storage rads is a nice MK Sentry 9 way (7 modules and 1 x 2 wide incommer) steel unit with only 2 ways in use (was 3). Maybe I could replace that with a smaller unit and fit the garage 'box' beside it. I could even possibly use the 9 way unit down the garage as a split CU (Sw lights MCB, Lathe MCB, RCD, std ring Power MCB etc?) Am I likely to get bus bars / modules to suit this if I cut it down? Am I right that the SWA should to be 'protected' by an RCD (and that's where I would use a 100mA unit with a 30mA at the garage end? Is it likely I could fit the contents of a cheap plastic Clipsil garage CU into the MK box?) Possible, depends how much time and patience you've got. I personally would buy a new unit for the garage if you really want split load down there for the price difference. Get a standard CU with main switch, MCB's for 100mA circuits and RCBO's for 30mA circuits. So I would end up with .. Sorry, I've forgotten, what are your earthing arrangements? Are you TT, TN-C-S...? Main split CU for the house (with existing 30ma RCD / MCB's) Sub CU (no RCB etc for the storage rads / E7 cct) Garage 'd/p Switch protection box' (with single 100 mA RCD as switch) 18 mm wide module. That is 17.5mm actually! Measure more carefully next time ;-) -- SJW A.C.S. Ltd. |
#4
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 15:39:55 +0000, Owain wrote:
"T i m" wrote | 1) We currently have a dual rate meter (E7 or similar) with a clock / | switch feeding a second CU running the storage rads. Will we get a new | dual rate meter controlled by radio and if so how will they deal with | the external switch for the E7? Your existing meter may already be switched by radio for the rate change, and the timeswitch may only be controlling the off-peak CU, i.e. it's your responsibility to not run your storage heaters on peak rate electricity. If the timeswitch is controlling the rate change there will probably be a pair of lightweight wires back to the meter as well as the heavyweight meter tails to the CUs and the timeswitch will (should) be security sealed. If the timeswitch is not controlling the rate change then it will probably be a simple job to pull the old meter off the base and pop the new one on, i.e. the meter changer will not be doing any wiring at all. Owain When my meter was changed last yaer they fitted a digital meter,this meter has a small wire coming from the timeswitch (this was left alone,it also switches the storage heaters on/off) which controls which rate is being charged Martin Warby |
#5
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 15:39:55 -0000, "Owain"
wrote: "T i m" wrote | 1) We currently have a dual rate meter (E7 or similar) with a clock / | switch feeding a second CU running the storage rads. Will we get a new | dual rate meter controlled by radio and if so how will they deal with | the external switch for the E7? If the timeswitch is controlling the rate change there will probably be a pair of lightweight wires back to the meter as well as the heavyweight meter tails to the CUs and the timeswitch will (should) be security sealed. There *are* a pair of thinner (6A type size) wires between the meter and the Sangamo (as big as the meter) timeswitch (the live looks like it's fused). That in turn has a pair (or one live in and one out) that goes to the E7 CU? So, what are they likely to do meterwise under these circumstances Owain? It also happens that the clock is running 4 hours fast! All the best .. T i m |
#6
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 16:33:11 +0000, Martin Warby
wrote: On Sun, 14 Mar 2004 15:39:55 +0000, Owain wrote: "T i m" wrote | 1) We currently have a dual rate meter (E7 or similar) with a clock / | switch feeding a second CU running the storage rads. Will we get a new | dual rate meter controlled by radio and if so how will they deal with | the external switch for the E7? Your existing meter may already be switched by radio for the rate change, and the timeswitch may only be controlling the off-peak CU, i.e. it's your responsibility to not run your storage heaters on peak rate electricity. If the timeswitch is controlling the rate change there will probably be a pair of lightweight wires back to the meter as well as the heavyweight meter tails to the CUs and the timeswitch will (should) be security sealed. If the timeswitch is not controlling the rate change then it will probably be a simple job to pull the old meter off the base and pop the new one on, i.e. the meter changer will not be doing any wiring at all. Owain When my meter was changed last yaer they fitted a digital meter,this meter has a small wire coming from the timeswitch (this was left alone,it also switches the storage heaters on/off) which controls which rate is being charged Hi Martin, Ok let's hope they leave my timeswitch alone then .. ;-) All the best .. T i m |
#7
|
|||
|
|||
Garage supply and new meter?
|
#8
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 17:51:08 +0000, in uk.d-i-y T i m
strung together this: So the new meter will have 1 input and two outputs? I would have thought so, this is usually the case. Most probably, but not a definite goer though. Depends who you get. So plenty of tea and biscuits and the offer of a 'drink' ? Yep, always a good idea. 3) If they take away the 'switch' part of the E7 service (can they do that?) I would be forced to add my own time-switches to each storage rad. Would they supply them to me foc? Extremely doubtful. Ill take that reply as 'they won't take away your timed switching of your storage rads' ;-) They shouldn't do. But getting anything foc out of the REC was what I was referring to as being 'extremely doubtful'. Possible, depends how much time and patience you've got. Well, I've got more of that than I have money at the moment Lurch? ;-( That's sorted that out then. I personally would buy a new unit for the garage if you really want split load down there for the price difference. Get a standard CU with main switch, MCB's for 100mA circuits and RCBO's for 30mA circuits. Where has the 100mA RCD come in then? Also RCBO's are still about 25 quid more expensive than an MCB (aren't they?) and about the same price as the cheap garage CU? You mentioned in your OP. I was assuming it was because you had TT. I've got it! Buy a cheap garage RCD CU and strip it. Replace the contents with a single 100mA RCD and use it as the isolator to the garage at the house end. Put the parts stripped out of the cheapo garage CU in the nice metal MK unit down the garage! Electric Lego! So, who would make a 100mA RCD to go in a Clipsil CU (and where would I get it from cheap?) Could do that. Any din rail mounted RCD will mount in the Clipsal enclosure. Sorry, I've forgotten, what are your earthing arrangements? Are you TT, TN-C-S...? At the moment my (very old) supply provides the earth from the armour on the SWA from the supplier (plus other bonding to services etc). I haven't decided what to do down the garage yet but I can decide that nearer the time can't I ? (crudely, the 'difference' being the continuity of the house / garage earth + an earthing rod?) It also means the additional cost of a 100mA RCD and earth rod. 18 mm wide module. That is 17.5mm actually! Measure more carefully next time ;-) Not bad with a ruler tho eh ;-) Not bad, but not up to engineering standards! What about the other dimensions Lurch .. are these 10 yr old MK modules compatible with any new / current makes (assuming you can't still get MK ones or if you can they aren't much more expensive than 'cheaper' makes? Possibly compatible with something, I've got 2 big boxes full of MCB's etc... so I can usually find something to fit. Failing that, take one of the old MCB's round a few wholesalers and check what they've got and what will fit. Most importantly is the 'internal dimensions'. By that the din rail slot in relation to the front of the MCB and the alignment of the busbar connection. -- SJW A.C.S. Ltd. |
#10
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 18:38:47 +0000, in uk.d-i-y T i m
strung together this: I found the dimensions / spec for the current range of MK Sentry units .. http://tinyurl.com/2csu2 That looks the same size / format for my old blanking module? Possibly compatible with something, I've got 2 big boxes full of MCB's etc... so I can usually find something to fit. Failing that, take one of the old MCB's round a few wholesalers and check what they've got and what will fit. Most importantly is the 'internal dimensions'. By that the din rail slot in relation to the front of the MCB and the alignment of the busbar connection. So, I think you were suggesting previously I fit one of these .. http://www.tlc-direct.co.uk/Products/MK6180.html Only because of the mention of a 100mA RCD in your original post. Now I know what earth you've got, you don't need it. Can't check the busbar though. 61.70 +vat though! (I could fit that later though couldn't I) Instead of the incommer on my main CU then just stick a garage (RCD) CU or std switched CU with MCB's (lights) and 30mA RCBo's (power) in the garage. You've lost me there. Can I confirm .. the SWA to the garage HAS to be protected by a RCD or not? Not. -- SJW A.C.S. Ltd. |
#11
|
|||
|
|||
Garage supply and new meter?
Instead of the incommer on my main CU then just stick a garage (RCD)
CU or std switched CU with MCB's (lights) and 30mA RCBo's (power) in the garage. You've lost me there. Sri mate . What I was trying to say is that if I wanted to have the advantake of an RCD that protected the whole system (even those bits on the existing house CU that (as I believe was suggested here before) replace the incommer with a an 80A 100mA RCD. This would then protect the existing ccts only covered by MCB's like lights etc (noot needed but can't hurt). I would then take a (say) 32A MCB and use that through the SWA to feed the garage. The existing 30mA RCD on the house CU stays put. Then in the garage I could either .. 1) Fit a std Clipsal RCD CU (but may loose the lights in the garage if I get a nusiance trip in the garage) 2) Make up a small split CU with std incommer and MCB for garage lights and 30mA RCD / MCBs OR non split and RCBO's Can I confirm .. the SWA to the garage HAS to be protected by a RCD or not? Not. Thanks. Ok another Yes / No for ya. Do I have to have a double pole isolator at the house end of the garage SWA or would a house MCB or 30 mA d/p RCD or finally the std d/p incomer (or 100mA RCD if I get round to it) be sufficient? What I'm trying to achieve here is the best safest cover without nusiance trips from the garage taking the house out and at the best price? (Not that I've even blown a fuse or tripped the house RCD in the last 10 years on my unofficial semi permenant extension lead to garage solution ;-) (exept when I cranked the SIP up too high one day g) All the best .. T i m |
#12
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 19:16:59 +0000, in uk.d-i-y T i m
strung together this: Instead of the incommer on my main CU then just stick a garage (RCD) CU or std switched CU with MCB's (lights) and 30mA RCBo's (power) in the garage. You've lost me there. Sri mate . What I was trying to say is that if I wanted to have the advantake of an RCD that protected the whole system (even those bits on the existing house CU that (as I believe was suggested here before) replace the incommer with a an 80A 100mA RCD. This would then protect the existing ccts only covered by MCB's like lights etc (noot needed but can't hurt). I would then take a (say) 32A MCB and use that through the SWA to feed the garage. The existing 30mA RCD on the house CU stays put. Then in the garage I could either .. 1) Fit a std Clipsal RCD CU (but may loose the lights in the garage if I get a nusiance trip in the garage) 2) Make up a small split CU with std incommer and MCB for garage lights and 30mA RCD / MCBs OR non split and RCBO's Yep, with you know. The choice is yours, either way will work. Can I confirm .. the SWA to the garage HAS to be protected by a RCD or not? Not. Thanks. Ok another Yes / No for ya. Do I have to have a double pole isolator at the house end of the garage SWA or would a house MCB or 30 mA d/p RCD or finally the std d/p incomer (or 100mA RCD if I get round to it) be sufficient? It would require its own DP isolator. You could use a DP RCD, or a DP switch, or a DP switchfuse.. Again, the choice is yours. What I'm trying to achieve here is the best safest cover without nusiance trips from the garage taking the house out and at the best price? (Not that I've even blown a fuse or tripped the house RCD in the last 10 years on my unofficial semi permenant extension lead to garage solution ;-) (exept when I cranked the SIP up too high one day g) If you do as you mentioned earlier, fitting a new RCD to feed the garage by the meter, then it's totally seperate from the house and no chance of nuisance tripping in the house. -- SJW A.C.S. Ltd. |
#13
|
|||
|
|||
Garage supply and new meter?
|
#14
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 20:08:58 +0000, in uk.d-i-y T i m
strung together this: On Sun, 14 Mar 2004 19:36:02 GMT, (Lurch) wrote: Ok another Yes / No for ya. Do I have to have a double pole isolator at the house end of the garage SWA or would a house MCB or 30 mA d/p RCD or finally the std d/p incomer (or 100mA RCD if I get round to it) be sufficient? It would require its own DP isolator. You could use a DP RCD, or a DP switch, or a DP switchfuse.. Again, the choice is yours. Ok (and thanks again mate) you don't mention a DP MCB with inrt house CU in there? Do they make such a thing and would that work if I went that way (I'm trying to think how it would fit within the CU (having a neutral to switch as well ?) You can get DP MCB's in single or double module width but they have to go into either a SP+N CU or a heavily modified SP CU. Unless you have the former It's a lot easier to use a separate unit. -- SJW A.C.S. Ltd. |
#16
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 17:22:14 +0000, T i m wrote:
On Sun, 14 Mar 2004 16:33:11 +0000, Martin Warby wrote: On Sun, 14 Mar 2004 15:39:55 +0000, Owain wrote: "T i m" wrote | 1) We currently have a dual rate meter (E7 or similar) with a clock / | switch feeding a second CU running the storage rads. Will we get a | new dual rate meter controlled by radio and if so how will they deal | with the external switch for the E7? Your existing meter may already be switched by radio for the rate change, and the timeswitch may only be controlling the off-peak CU, i.e. it's your responsibility to not run your storage heaters on peak rate electricity. If the timeswitch is controlling the rate change there will probably be a pair of lightweight wires back to the meter as well as the heavyweight meter tails to the CUs and the timeswitch will (should) be security sealed. If the timeswitch is not controlling the rate change then it will probably be a simple job to pull the old meter off the base and pop the new one on, i.e. the meter changer will not be doing any wiring at all. Owain When my meter was changed last yaer they fitted a digital meter,this meter has a small wire coming from the timeswitch (this was left alone,it also switches the storage heaters on/off) which controls which rate is being charged Hi Martin, Ok let's hope they leave my timeswitch alone then .. ;-) All the best .. T i m this was with Hydro Electric,don't know if they do the same in other regions Martin Warby |
#17
|
|||
|
|||
Garage supply and new meter?
"T i m" wrote
| There *are* a pair of thinner (6A type size) wires between the | meter and the Sangamo (as big as the meter) timeswitch (the | live looks like it's fused). That in turn has a pair (or one | live in and one out) that goes to the E7 CU? The Sangamo needs a neutral from somewhere for the motor, so either the thin wires are L&N for the motor, or N for the motor (the motor getting its L from the meter tail) and a trigger back to the meter to change rate. Either way it shouldn't make much difference, if the timeswitch handles the rate change the meter changer should set it to the correct time and reseal it; if the new meter handles its own rate change it will do so and your timeswitch will continue to control the E7 CU - in which case you must ensure it is set to the correct time or the storage heaters will be charging up on peak rate electricity. The real point is that the meter changer probably won't need to do much if anything with rearranging tails etc so is unlikely to be willing/competent/insured to wire up your new garage supply. Owain |
#18
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 20:58:51 -0000, "Owain"
wrote: "T i m" wrote | There *are* a pair of thinner (6A type size) wires between the | meter and the Sangamo (as big as the meter) timeswitch (the | live looks like it's fused). That in turn has a pair (or one | live in and one out) that goes to the E7 CU? The Sangamo needs a neutral from somewhere for the motor, so either the thin wires are L&N for the motor, or N for the motor (the motor getting its L from the meter tail) and a trigger back to the meter to change rate. TYou could be spot on. I've just followed it all about and that's what it could all do. There are 3 thinish wires going into the timeswitch, a live via a fuse off the input live to the meter and the neutral straight to the netural co feed and another wire going into the meter directly from the timewsitch? Either way it shouldn't make much difference, if the timeswitch handles the rate change the meter changer should set it to the correct time and reseal it; Ok, so that's the 'easy' one .. ;-) if the new meter handles its own rate change it will do so and your timeswitch will continue to control the E7 CU - in which case you must ensure it is set to the correct time or the storage heaters will be charging up on peak rate electricity. Nice? I'd like to think that their kit would at least continue to do what it's always done? If *their* switch isn't synched to *their* time and I don't have any way of adjusting either? That means I might as well remove the E7 CU and get them to reconnect the tails back into the main supply. Then I can connect the storage rad radials to the main CU and fit timeswitced outlets at the storage rads? Then I can swap the tails over to my new garage feed isolator and use the (E7) CU down the garage ;-) The real point is that the meter changer probably won't need to do much if anything with rearranging tails etc so is unlikely to be willing/competent/insured to wire up your new garage supply. Oh ;-( The letter did suggest it would 'take around 20 mins' ? All the best again .. T i m |
#19
|
|||
|
|||
Garage supply and new meter?
Ok let's hope they leave my timeswitch alone then .. ;-)
If its *your* timeswitch they shouldn`t be touching it regardless. -- Please add "[newsgroup]" in the subject of any personal replies via email * old email address "btiruseless" abandoned due to worm-generated spam * --- My new email address has "ngspamtrap" & @btinternet.com in it ;-) --- |
#20
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 23:49:01 -0000, Colin Wilson
wrote: Ok let's hope they leave my timeswitch alone then .. ;-) If its *your* timeswitch they shouldn`t be touching it regardless. Sri Colin .. it's *their* timeswitch as such (it's supplied by them and on their board etc) but it was part of the install of E7 10 years or so ago and my house wiring was based around that? If a replacement device (they are due to change the meter .. their request / idea) and I had seen talk here of wireless switched meters and wondered if I was likely to get said and how that might affect my setup. Like when I wanted to add broadband internet access to my existing cable TV service. They said if I went 'digital' they would install it free but if I stayed analogue it would cost 25 quid. I asked if I would still get the 5 terrestrial channels fed through on the digital service and they said 'no' ? We paid the 25 and stayed analogue (so we can still watch / record any channel in any room at the same time?) All the best .. T i m |
#21
|
|||
|
|||
Garage supply and new meter?
On Sun, 14 Mar 2004 20:36:25 +0000, T i m wrote:
On Sun, 14 Mar 2004 20:21:15 GMT, (Lurch) wrote: Ok (and thanks again mate) you don't mention a DP MCB with inrt house CU in there? Do they make such a thing and would that work if I went that way (I'm trying to think how it would fit within the CU (having a neutral to switch as well ?) You can get DP MCB's in single or double module width but they have to go into either a SP CU or a heavily modified SP CU. Unless you have the former It's a lot easier to use a separate unit. Em, SP CU (Single Pole .. ?) I've just pulled a 'spare' MCB from the MK to try in the Clipsal unit at Dads tomorrow. I still might like to go for the swaparound (the MK Sentry currently on E7 duty and only 2/7ths used, as a split CU down the garage with the contents of the Clipsal etc). So, the MK MCB fits on the Clipsal rail and is exactly the same dimensions re fitting the CU lid, but, the electrical side of it wouldn't 'easily' mix. But, if I wanted to convert the 9 module MK Sentry into a split CU for the garage and used all Clipsal modules in it (to get some a cheap RCD) I should be able to sort the busbar side of it with a bit of imagination? Or not .. All the best .. T i m |
#22
|
|||
|
|||
Garage supply and new meter?
On Mon, 15 Mar 2004 21:15:08 +0000, in uk.d-i-y T i m
strung together this: So, the MK MCB fits on the Clipsal rail and is exactly the same dimensions re fitting the CU lid, but, the electrical side of it wouldn't 'easily' mix. But, if I wanted to convert the 9 module MK Sentry into a split CU for the garage and used all Clipsal modules in it (to get some a cheap RCD) I should be able to sort the busbar side of it with a bit of imagination? Or not .. You could buy a standard length of busbar, (Hager do it individually for a start, in 18 way lengths, cat. no. VACC10 IIRC), and cut it to size, as long as all the MCB's line up with the RCD. -- SJW A.C.S. Ltd. |
#23
|
|||
|
|||
Garage supply and new meter?
T i m wrote:
On Sun, 14 Mar 2004 23:49:01 -0000, Colin Wilson wrote: Ok let's hope they leave my timeswitch alone then .. ;-) If its *your* timeswitch they shouldn`t be touching it regardless. Sri Colin .. it's *their* timeswitch as such (it's supplied by them and on their board etc) but it was part of the install of E7 10 years or so ago and my house wiring was based around that? If a replacement device (they are due to change the meter .. their request / idea) and I had seen talk here of wireless switched meters and wondered if I was likely to get said and how that might affect my setup. Like when I wanted to add broadband internet access to my existing cable TV service. They said if I went 'digital' they would install it free but if I stayed analogue it would cost 25 quid. I asked if I would still get the 5 terrestrial channels fed through on the digital service and they said 'no' ? We paid the 25 and stayed analogue (so we can still watch / record any channel in any room at the same time?) They fuled you. With a digital cable box plugged in it won't stop you picking up the analogue channels that are also present on the cable, though you might need an analogue cable box also to convert them to UHF (usually they are VHF on CATV) |