OK I now I am a complete idiot but I just drilled through a mains cable. Big
flash then the RCD trip switch kicked in and put all the power in the house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that was
the case would the RCD/MCB kick in?

Thanks

PS Try to limit the comments on my stupidity and about how cheap pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


  #2   Report Post  
ARWadsworth
 
Posts: n/a
Default Drilling through mains cable!


"N" wrote in message
...
OK I now I am a complete idiot but I just drilled through a mains cable.

Big
flash then the RCD trip switch kicked in and put all the power in the

house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that was
the case would the RCD/MCB kick in?

Thanks

PS Try to limit the comments on my stupidity and about how cheap

pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


If you are that concerned then just turn the MCB off that powers this cable.
Use extension leads to power essential equipment e.g. fridge/freezer if it
is that circuit. The RCD or MCB should kick back in if there is a short but
if it was my house I would turn the power off to that circuit for one night.

--
Adam



PS We have all done it. The rules are to damage the CH cable on the coldest
night of the year, the lighting circuits just before nightfall and the ring
main just before a film you have wanted to watch for ages is due to start

  #3   Report Post  
enuff
 
Posts: n/a
Default Drilling through mains cable!


"ARWadsworth" wrote in message
...

"N" wrote in message
...
OK I now I am a complete idiot but I just drilled through a mains cable.

Big
flash then the RCD trip switch kicked in and put all the power in the

house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty

melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead

is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that

was
the case would the RCD/MCB kick in?

Thanks

PS Try to limit the comments on my stupidity and about how cheap

pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


If you are that concerned then just turn the MCB off that powers this

cable.
Use extension leads to power essential equipment e.g. fridge/freezer if it
is that circuit. The RCD or MCB should kick back in if there is a short

but
if it was my house I would turn the power off to that circuit for one

night.

--
Adam



PS We have all done it. The rules are to damage the CH cable on the

coldest
night of the year, the lighting circuits just before nightfall and the

ring
main just before a film you have wanted to watch for ages is due to start


Good advice


  #4   Report Post  
Andy Hall
 
Posts: n/a
Default Drilling through mains cable!

On Mon, 12 Jan 2004 19:26:26 -0000, "N"
wrote:

OK I now I am a complete idiot but I just drilled through a mains cable. Big
flash then the RCD trip switch kicked in and put all the power in the house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that was
the case would the RCD/MCB kick in?

Thanks

PS Try to limit the comments on my stupidity and about how cheap pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


Oh dear. You can get an RCD trip by connecting earth and neutral
together but since you had a flash then it is live and either neutral
or earth or both.

I don't think that it's a good idea to leave the cable powered,
especially since it is hidden away. This would be a fire risk.

Do you have any way to identify which circuit the cable is other than
poking a screwdriver into it? If you have a mains testing
screwdriver you could put the tip *near* the cable and you *may* get
an indication that it is live. Then you could selectively turn
breakers off until you find which it is.

If you can't do that, then you should turn the power off for safety I
think.

Regarding the other issue - flowers or a nice dinner, but not today.
:-)








..andy

To email, substitute .nospam with .gl
  #5   Report Post  
Soup
 
Posts: n/a
Default Drilling through mains cable!

N wrote:
OK I now I am a complete idiot but I just drilled through a mains
cable. Big flash then the RCD trip switch kicked in and put all the
power in the house out.

snip
Think the best one along these lines is that when a chap drilled
through the cable all the power got cut,he couldn't connect the
fact that with no power the mains drill would no longer work,
he then took the drill to bits to "fix" it couldn't put it back together
so had to buy a new drill., (was on Britain's worst DIYer).
--
Yours S. addy not usable (not that you would try it) ( )
Utinam logica falsa tuam philosophiam totam suffodiant! / \
www.killies.co.uk/forums/index.php




  #6   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!

Andy and others thanks for the replies.

I have tried to isolate by using a mains testing screwdriver but there are 4
or 5 mains cables running near each other so the screwdriver does not give a
clear answer.

I have noticed something odd in my consumer unit though, my MCBs are the
type that go to the mid way mark when they trip, you then have to push them
all the way down and all the way back up to reset. The one for my cooker is
just all loose and floppy although the cooker is still working, could this
be a knackered MCB but one that is still letting power through?


"Andy Hall" wrote in message
...
On Mon, 12 Jan 2004 19:26:26 -0000, "N"
wrote:

OK I now I am a complete idiot but I just drilled through a mains cable.

Big
flash then the RCD trip switch kicked in and put all the power in the

house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty

melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that

was
the case would the RCD/MCB kick in?

Thanks

PS Try to limit the comments on my stupidity and about how cheap

pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


Oh dear. You can get an RCD trip by connecting earth and neutral
together but since you had a flash then it is live and either neutral
or earth or both.

I don't think that it's a good idea to leave the cable powered,
especially since it is hidden away. This would be a fire risk.

Do you have any way to identify which circuit the cable is other than
poking a screwdriver into it? If you have a mains testing
screwdriver you could put the tip *near* the cable and you *may* get
an indication that it is live. Then you could selectively turn
breakers off until you find which it is.

If you can't do that, then you should turn the power off for safety I
think.

Regarding the other issue - flowers or a nice dinner, but not today.
:-)








.andy

To email, substitute .nospam with .gl



  #7   Report Post  
PoP
 
Posts: n/a
Default Drilling through mains cable!

On Mon, 12 Jan 2004 19:26:26 -0000, "N"
wrote:

PS Try to limit the comments on my stupidity and about how cheap pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!


Take heart from the fact that I did the same thing about 20 years ago
in a previous house. And we didn't have RCD's in them days.

It was a very useful lesson - subsequently I've always (without fail)
checked for cables buried in the wall and take special care if there
are sockets on the wall, or on the far side of the wall.

And I am always conscious if the drill appears to suddenly change in
terms of physical feedback which could suggest it has stopped drilling
brick and is now drilling something which isn't brick.

PoP

If you really must use the email address provided
with my newsreader please be aware that the email
is processed with spamcop. As a result your email
to me might be treated as spam!
  #8   Report Post  
Terry
 
Posts: n/a
Default Drilling through mains cable!


"Soup" wrote in message
...
N wrote:
OK I now I am a complete idiot but I just drilled through a mains
cable. Big flash then the RCD trip switch kicked in and put all the
power in the house out.

snip
Think the best one along these lines is that when a chap drilled
through the cable all the power got cut,he couldn't connect the
fact that with no power the mains drill would no longer work,
he then took the drill to bits to "fix" it couldn't put it back together
so had to buy a new drill., (was on Britain's worst DIYer).
--
Yours S. addy not usable (not that you would try it) ( )
Utinam logica falsa tuam philosophiam totam suffodiant! / \
www.killies.co.uk/forums/index.php


Oh boy done that twice in my life!
Once on that side of the Atlantic, in that instance it was fairly obvious
what we (I) had disrupted; the lights in all the bedrooms! So we removed the
fuse for that circuit and kept an eye on it until we went to bed.
We did toy with the idea of turning off 'everything' overnight but decided
against.
The second time was on this side of the Atantic where we (I) cleverly
drilled through a wooden floor joist at angle while completing this wood
framed house; and ..... fssst! Splat! Into 115/230 volt house wiring.
Fortunately everything was exposed and it only took about ten minutes to run
a new piece of cable; minus the time spent cursing myself!
Cheers. Terry.


  #9   Report Post  
The Natural Philosopher
 
Posts: n/a
Default Drilling through mains cable!

N wrote:

OK I now I am a complete idiot but I just drilled through a mains cable. Big
flash then the RCD trip switch kicked in and put all the power in the house
out. However, when I put the power back on everything works no circuit
trips? So I put an insulated screwdriver in the drill hole to check and
everything trips again, the end of the screwdriver also got pretty melted.
Reset trip switches and everything works fine.

I am having someone with a brain, unlike me, look at it tomorrow - an
electrician. But is it safe to leave the power on overnight - the lead is
below a floorboard but can not be accessed without a fair bit of work -
skirting off etc hence the wait for the man with a brain. I am concerned
that something may be smouldering away under my floorboards or if that was
the case would the RCD/MCB kick in?



I didn't do this, but had to fix an identivl situatin in a rented place
- I was pianting it an FLASH as you desribe. Emuslion pain in old screw
hole with plug...

The electrician who came (via a call to teh letting agency) simply
chased the wire out, and crimped on a new bit. We wrapped it all in
insulation tape and I plastered it back where it came from.

Yes, it was in the end that simple.


Thanks

PS Try to limit the comments on my stupidity and about how cheap pipe/cable
detectors are. my wife wants to kill me as it is - take pity on me!





  #10   Report Post  
Pet
 
Posts: n/a
Default Drilling through mains cable!

The Natural Philosopher wrote:

The electrician who came (via a call to teh letting agency) simply
chased the wire out, and crimped on a new bit. We wrapped it all in
insulation tape and I plastered it back where it came from.

Yes, it was in the end that simple.


from my experience of such circumstances, Damage to drill
bit/screw/driver is far vorse than cable damage.

With RCD cable damage is often nothing more than slight loss of sleve.

chase out onough wall to get a few turns of good insulation tape around
mising sheath then plaster back in. I'd be inclined to patch up existing
cable than cut out and crimp a new piece in.


--
http://gymratz.co.uk
The Worlds No1 Fitness & Gym Equipment/nutrition specialists.
http://www.water-rower.co.uk
The ultimate rowing simulator.


  #11   Report Post  
 
Posts: n/a
Default Drilling through mains cable!

In uk.d-i-y, Pet wrote:

chase out onough wall to get a few turns of good insulation tape around
mising sheath then plaster back in. I'd be inclined to patch up existing
cable than cut out and crimp a new piece in.

Oh, FFS! The original poster has had fault currents coursing through this
little stretch of the cable not once, but twice. The first time he's had
"a big flash"; the second time the fault current was enough to do damge to
the end of his tool (a screwdriver, before you ask). That amount of
energy released before his protective devices kicked in strongly suggests
a hefty live-to-neutral flow, rather than a benign neutral-earth short or
even a quickly-cleared live-to-earth. Assuming a modern installation, the
main lengths of the cables ought to be OK, as the protective devices are
specced to act quickly enough to limit the temperature rise in the
conductors to below PVC-melting/softening point. *BUT* at the point of
the short, the insulation and immediate conductors *will* be damaged,
and it's irresponsible not to cut out the cable in the immediate area of
the drilling and extend with a nice new bit.

With a bit of luck it might be possible to run a new length of cable to
the nearest fitting in one direction without too much disruption, and
make the join to the old cable in the other direction either by crimping
or in a new wallbox fitted with a blanking plate, to act as a permanent
reminder when next drilling, or maybe a wall-clock connection point ;-)
Failing that, replacing the run of cable between the two existing fittings
it serves makes for a decent job.

Patching up the injured cable with "a few turns of good insulating tape"
is an approach worthy only of the spur-wearing mob...

Stefek
  #12   Report Post  
Andy Hall
 
Posts: n/a
Default Drilling through mains cable!

On Tue, 13 Jan 2004 17:09:38 +0000, Pet wrote:

The Natural Philosopher wrote:

The electrician who came (via a call to teh letting agency) simply
chased the wire out, and crimped on a new bit. We wrapped it all in
insulation tape and I plastered it back where it came from.

Yes, it was in the end that simple.


from my experience of such circumstances, Damage to drill
bit/screw/driver is far vorse than cable damage.

With RCD cable damage is often nothing more than slight loss of sleve.

chase out onough wall to get a few turns of good insulation tape around
mising sheath then plaster back in. I'd be inclined to patch up existing
cable than cut out and crimp a new piece in.



This is a very dangerous idea.

The insulation is likely to be melted locally around the damage and
the conductors will not be at their original condition even if the
damage had only been slight. At best the continuity in the cable
is going to be unreliable, and at worst it is a fire risk.
Considering that the cable is also hidden and going to be hidden
behind decorations that will be inconvenient to replace.

Cutting in a piece of cable with crimps is a 5 minute job. Making
good the decorations will take longer.

It's silly bodging a job when it can be done properly and safely.


..andy

To email, substitute .nospam with .gl
  #13   Report Post  
Owain
 
Posts: n/a
Default Drilling through mains cable!

|Stefek Zaba wrote
| ... in a new wallbox fitted with a blanking plate, to act as a
| permanent reminder when next drilling, or maybe a wall-clock
| connection point ;-)

"We'd always wondered why the previous owners had a Smiths Selectric Sun-Ray
wired into the cooker circuit"

Owain


  #14   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!

Well It is all sorted now. Basically, there was enough slack in the cable to
cut out the damaged portion and fit a 30/40 Amp junction box to join the two
sides of the cable. It was the old feed for the cooker which now just feeds
3 sockets as we have a gas cooker.

I was suprised by this whole thing because I was drilling and screwing along
the joists as I have done to floorboards in the past. However, when the
board was lifted you could see that someone has previously cut a fair size
hole in the joist from its top i.e. u shaped and fed a few mains cables
through.

Is/was this normal practice? I always thought following the joists was quite
safe, I am begining to wonder if any of the other boards I have screwed down
over the years, about half the house, may have screws perilously close to
wiring. Although where possible I have always tried to look and work out the
routing of wiring piping etc. I just got carried away yesterday as it was
one of the last boards along the line of the joist.

What is/was normal practice?

Regards and thanks for the replies.


"Andy Hall" wrote in message
...
On Tue, 13 Jan 2004 17:09:38 +0000, Pet wrote:

The Natural Philosopher wrote:

The electrician who came (via a call to teh letting agency) simply
chased the wire out, and crimped on a new bit. We wrapped it all in
insulation tape and I plastered it back where it came from.

Yes, it was in the end that simple.


from my experience of such circumstances, Damage to drill
bit/screw/driver is far vorse than cable damage.

With RCD cable damage is often nothing more than slight loss of sleve.

chase out onough wall to get a few turns of good insulation tape around
mising sheath then plaster back in. I'd be inclined to patch up existing
cable than cut out and crimp a new piece in.



This is a very dangerous idea.

The insulation is likely to be melted locally around the damage and
the conductors will not be at their original condition even if the
damage had only been slight. At best the continuity in the cable
is going to be unreliable, and at worst it is a fire risk.
Considering that the cable is also hidden and going to be hidden
behind decorations that will be inconvenient to replace.

Cutting in a piece of cable with crimps is a 5 minute job. Making
good the decorations will take longer.

It's silly bodging a job when it can be done properly and safely.


.andy

To email, substitute .nospam with .gl



  #15   Report Post  
Andy Hall
 
Posts: n/a
Default Drilling through mains cable!

On Tue, 13 Jan 2004 23:18:33 -0000, "N"
wrote:

Well It is all sorted now. Basically, there was enough slack in the cable to
cut out the damaged portion and fit a 30/40 Amp junction box to join the two
sides of the cable. It was the old feed for the cooker which now just feeds
3 sockets as we have a gas cooker.


Do you mean a junction box with screw terminals? If so, they are not
supposed to be used in concealed places according to the Wiring
Regulations - there needs to be access for repair. I believe that
the theory is that screw terminals are considered to be liable to
coming loose over time. Hence the discussion about using crimps.
These are permitted for concealed joints.



I was suprised by this whole thing because I was drilling and screwing along
the joists as I have done to floorboards in the past. However, when the
board was lifted you could see that someone has previously cut a fair size
hole in the joist from its top i.e. u shaped and fed a few mains cables
through.

Is/was this normal practice? I always thought following the joists was quite
safe, I am begining to wonder if any of the other boards I have screwed down
over the years, about half the house, may have screws perilously close to
wiring. Although where possible I have always tried to look and work out the
routing of wiring piping etc. I just got carried away yesterday as it was
one of the last boards along the line of the joist.

What is/was normal practice?


Again the Wiring Regulations come into play. Cables are not
supposed to be installed in notches in joists. The requirement is
that they should be at least 50mm from either surface, so the
convention is to drill through the centre of the joist and thread the
cables. If there is a need to go nearer the surface, then the
cables must be covered with a substantial shield - typically a thick
steel plate which must then be earthed.

In any case, it is not a good idea to notch joists if at all possible
because it does weaken them.







Regards and thanks for the replies.


..andy

To email, substitute .nospam with .gl


  #16   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!


"Andy Hall" wrote in message
...
On Tue, 13 Jan 2004 23:18:33 -0000, "N"
wrote:

Well It is all sorted now. Basically, there was enough slack in the cable

to
cut out the damaged portion and fit a 30/40 Amp junction box to join the

two
sides of the cable. It was the old feed for the cooker which now just

feeds
3 sockets as we have a gas cooker.


Do you mean a junction box with screw terminals? If so, they are not
supposed to be used in concealed places according to the Wiring
Regulations - there needs to be access for repair. I believe that
the theory is that screw terminals are considered to be liable to
coming loose over time. Hence the discussion about using crimps.
These are permitted for concealed joints.



I was suprised by this whole thing because I was drilling and screwing

along
the joists as I have done to floorboards in the past. However, when the
board was lifted you could see that someone has previously cut a fair

size
hole in the joist from its top i.e. u shaped and fed a few mains cables
through.

Is/was this normal practice? I always thought following the joists was

quite
safe, I am begining to wonder if any of the other boards I have screwed

down
over the years, about half the house, may have screws perilously close to
wiring. Although where possible I have always tried to look and work out

the
routing of wiring piping etc. I just got carried away yesterday as it was
one of the last boards along the line of the joist.

What is/was normal practice?


Again the Wiring Regulations come into play. Cables are not
supposed to be installed in notches in joists. The requirement is
that they should be at least 50mm from either surface, so the
convention is to drill through the centre of the joist and thread the
cables. If there is a need to go nearer the surface, then the
cables must be covered with a substantial shield - typically a thick
steel plate which must then be earthed.

In any case, it is not a good idea to notch joists if at all possible
because it does weaken them.

Not sure about the screw terminals as an electrician did it not me.

The wiring for the house was done in the early 70's would cut joists have
been OK then?

The wiring was tested when the new consumer unit with RCD and MCB's was
fitted 3 years ago and found to be sound - until I trashed it yesterday!


  #17   Report Post  
Dave Plowman
 
Posts: n/a
Default Drilling through mains cable!

In article ,
N wrote:

Is/was this normal practice? I always thought following the joists was
quite safe, I am begining to wonder if any of the other boards I have
screwed down over the years, about half the house, may have screws
perilously close to wiring. Although where possible I have always tried
to look and work out the routing of wiring piping etc. I just got
carried away yesterday as it was one of the last boards along the line
of the joist.


What is/was normal practice?


It's possible in an older house they simply re-used a notch made for
either older cables or now redundant gas pipes etc. However, such a notch
would normally be in the middle of a floorboard so it may still be nailed
or screwed safely. If not, I'd put a steel strap across the notch *and*
mark the floorboard clearly with the position of the cable.

--
*Beauty is in the eye of the beer holder...

Dave Plowman London SW 12
RIP Acorn
  #18   Report Post  
Andy Hall
 
Posts: n/a
Default Drilling through mains cable!

On Tue, 13 Jan 2004 23:51:48 -0000, "N"
wrote:



Not sure about the screw terminals as an electrician did it not me.



The wiring for the house was done in the early 70's would cut joists have
been OK then?


I think it might have been. I've seen it in houses of that age.

Given what you've found, it's worth doing a check for buried cables in
future (but you knew that :-) )

Are you still in trouble, BTW?


The wiring was tested when the new consumer unit with RCD and MCB's was
fitted 3 years ago and found to be sound - until I trashed it yesterday!


..andy

To email, substitute .nospam with .gl
  #19   Report Post  
Chris Oates
 
Posts: n/a
Default Drilling through mains cable!


"N" wrote in message
...


Not sure about the screw terminals as an electrician did it not me.

thermal cycling can loosen screws

The wiring for the house was done in the early 70's would cut joists have
been OK then?

as mentioned - only if plated over

The wiring was tested


the wiring wasn't tested !

the circuits might have been tested for loop impedance
and insulation values but the wiring was certainly not
'tested' - i.e. search for buried junction boxes and
notched loits.

when the new consumer unit with RCD and MCB's was
fitted 3 years ago and found to be sound.


sound - only in the vaguest terms probably

- until I trashed it yesterday!

I can't believe you poked at it twice




  #20   Report Post  
 
Posts: n/a
Default Drilling through mains cable!

In uk.d-i-y, N wrote:
Well It is all sorted now. Basically, there was enough slack in the cable to
cut out the damaged portion and fit a 30/40 Amp junction box to join the two
sides of the cable. It was the old feed for the cooker which now just feeds
3 sockets as we have a gas cooker.

Super; hadn't realised it was in the floor rather than in the wall; that's
better for accessibility. Which is both a practical requirement (you did
replace the floorboard nails with screws when you put them back down,
didn't you? Makes lifting them next time *so* much easier; *and* gives you
another opportunity to put a screw right through the cable you only just
saw. Been there, done that, saw the flash, felt a total prat, still remember
it though it was just about 20 years ago!) - and (breathlessly recovering
back to the "both" where we started this sentence ;-) a requirement of the
Regs when using junction boxen. I claim that under a screwed-down floorboard
is accessible within the meaning of the Regs here, though I'll admit that
it rather depends on the floor covering - vinyl you can peel back to reveal
a nice hardboard with pipe and cable runs clearly labelled and access
hatches is one end of the spectrum, while gert big sheets of marine ply,
screed, and big-ass slate tiles would be quite the other ;-)

Is/was this normal practice? I always thought following the joists was quite
safe, I am begining to wonder if any of the other boards I have screwed down
over the years, about half the house, may have screws perilously close to
wiring. Although where possible I have always tried to look and work out the
routing of wiring piping etc. I just got carried away yesterday as it was
one of the last boards along the line of the joist.

Ah, you *have* been screwing the boards back - good man! Joist notching
*was* normal practice, judging by the couple of older houses I've lived
in and worked on, and comments in older installation guides. Except when
I didn't, I usually played safe by putting any screws to replace lifted
boards into, or pretty damn close to, the existing nail holes. These days
notching's frowned upon, both because it weakens the joist, and because it
makes it too unsportingly easy for Sod to guide your drill bit to them, as
you discovered ;-) The current On-Site Guide says it's OK for cable to go
*through* joists; holes a minimum of 5cm away from top and bottom surface,
and (for structural reasons) close neither to the centre nor the edges of
the span. It's also OK to run the cable in earthed steel conduit, which
provides good mechanical protection; the conduit can go in notches in
the top of joints, and again there's guidance on max depth of notches
(no more than 1/8th the depth of the joist) and position (away from
center of span, not right close up to edges either). As a third alternative,
it says you can try to provide "protection sufficient to prevent penetration
of the cable by nails, screws and the like", and immediately pooh-poohs its
own suggestion by saying that it's "difficult to meet" that requirement for
protection! Hunky steel plate (2-3mm thick or more) is sometimes fitted
over existing joist notches as a nod towards this "mechanical protection"
requirement, but by the time you've done the chiselling around the notch
to install and secure such plates, you could probably have rerun the
cable through holes deeper down the joists anyway.

Hope that helps, and glad to hear you got a proper job done on the
damaged bit of cable...

cheers, Stefek


  #21   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!

No I am out of trouble everything is working fine and the Mrs has forgiven
me and boy have I learnt a lesson!

"Andy Hall" wrote in message
...
On Tue, 13 Jan 2004 23:51:48 -0000, "N"
wrote:



Not sure about the screw terminals as an electrician did it not me.



The wiring for the house was done in the early 70's would cut joists have
been OK then?


I think it might have been. I've seen it in houses of that age.

Given what you've found, it's worth doing a check for buried cables in
future (but you knew that :-) )

Are you still in trouble, BTW?


The wiring was tested when the new consumer unit with RCD and MCB's was
fitted 3 years ago and found to be sound - until I trashed it yesterday!


.andy

To email, substitute .nospam with .gl



  #22   Report Post  
Chris Oates
 
Posts: n/a
Default Drilling through mains cable!


"N" wrote in message
...
Well It is all sorted now. Basically, there was enough slack in the cable

to
cut out the damaged portion and fit a 30/40 Amp junction box to join the

two
sides of the cable. It was the old feed for the cooker which now just

feeds
3 sockets as we have a gas cooker.


I still can't believe that after the initial flash you poked at it
with a screwdriver
A pal of mine drilled into an incoming main which
(unlike yours) was un-fused - he lost huge areas of skin
and had a long painful recovery - electricity is a killer
...not only for you as it can kill the person trying to save you,


Is/was this normal practice?

fatal assumption that anything is 'normal'



  #23   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!

Chris

Are you suggesting that buried junction boxes and notched loits are
routinely checked before fitting new consumer units?

I poked at it twice because in my panic to restore power the first time I
did not make a note of which MCB had tripped. I used thick rubber gloves and
an insulated elecrticians screw driver. I also knew the RCD would cut in
again - not a great idea I admit but I was happy with the precautions.

Regards

"Chris Oates" none wrote in message
...

"N" wrote in message
...


Not sure about the screw terminals as an electrician did it not me.

thermal cycling can loosen screws

The wiring for the house was done in the early 70's would cut joists

have
been OK then?

as mentioned - only if plated over

The wiring was tested


the wiring wasn't tested !

the circuits might have been tested for loop impedance
and insulation values but the wiring was certainly not
'tested' - i.e. search for buried junction boxes and
notched loits.

when the new consumer unit with RCD and MCB's was
fitted 3 years ago and found to be sound.


sound - only in the vaguest terms probably

- until I trashed it yesterday!

I can't believe you poked at it twice






  #24   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!

Good idea Thanks.

"Dave Plowman" wrote in message
...
In article ,
N wrote:

Is/was this normal practice? I always thought following the joists was
quite safe, I am begining to wonder if any of the other boards I have
screwed down over the years, about half the house, may have screws
perilously close to wiring. Although where possible I have always tried
to look and work out the routing of wiring piping etc. I just got
carried away yesterday as it was one of the last boards along the line
of the joist.


What is/was normal practice?


It's possible in an older house they simply re-used a notch made for
either older cables or now redundant gas pipes etc. However, such a notch
would normally be in the middle of a floorboard so it may still be nailed
or screwed safely. If not, I'd put a steel strap across the notch *and*
mark the floorboard clearly with the position of the cable.

--
*Beauty is in the eye of the beer holder...

Dave Plowman London SW 12
RIP Acorn



  #25   Report Post  
N
 
Posts: n/a
Default Drilling through mains cable!


"Chris Oates" none wrote in message
...

"N" wrote in message
...
Well It is all sorted now. Basically, there was enough slack in the

cable
to
cut out the damaged portion and fit a 30/40 Amp junction box to join the

two
sides of the cable. It was the old feed for the cooker which now just

feeds
3 sockets as we have a gas cooker.


I still can't believe that after the initial flash you poked at it
with a screwdriver
A pal of mine drilled into an incoming main which
(unlike yours) was un-fused - he lost huge areas of skin
and had a long painful recovery - electricity is a killer
..not only for you as it can kill the person trying to save you,


Is/was this normal practice?

fatal assumption that anything is 'normal'


I poked at it twice because in my panic to restore power the first time I
did not make a note of which MCB had tripped. I used thick rubber gloves and
an insulated elecrticians screw driver. I also knew the RCD would cut in
again - not a great idea I admit but I was happy with the precautions.





  #26   Report Post  
Chris Oates
 
Posts: n/a
Default Drilling through mains cable!


wrote in message
...
The current On-Site Guide says it's OK for cable to go
*through* joists; holes a minimum of 5cm away from top and bottom surface,
and (for structural reasons) close neither to the centre nor the edges of
the span.

and then Mr 'no brains' will drill a huge hole and feed all
his cables thro it rather than drill some small much safer ones




  #27   Report Post  
 
Posts: n/a
Default Drilling through mains cable!

In uk.d-i-y, Chris Oates none wrote:

and then Mr 'no brains' will drill a huge hole and feed all
his cables thro it rather than drill some small much safer ones

No legislating around stupidity (contrary to apparent beliefs of some
Govt departments). Mr No Brains isn't going to be referring to any poncy
On-Site Guide or other form of advice anyway...
  #28   Report Post  
Chris Oates
 
Posts: n/a
Default Drilling through mains cable!


"N" wrote in message
...
Chris

Are you suggesting that buried junction boxes and notched loits are
routinely checked before fitting new consumer units?


no they aren't - nobody would know where to start looking

the Regs are (maybe) a deterrent

all that's (maybe) done is an insulation test
which 'might' find a nail close to conductors
and a loop test to confirm that circuits reach the
consumer unit - a ring final test would be good.

I've seen testers walk around with hugely expensive
multifunction testers confirming everything good without ever
conducting basic tests like is a ring actually a ring

We were left with a sub circuit wired upside down
(live neutral swapped) by a power company !

Don't trust anyone



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mains failure generator switching tips? Chris Wilson UK diy 5 October 15th 03 12:12 AM
Fluorescent lights - heat rating of cable? David UK diy 8 September 2nd 03 09:00 PM
Cable - pricing up NorwichLad UK diy 3 July 25th 03 12:59 PM
Routeing Electrical FTE cable pickerel UK diy 3 July 24th 03 12:43 AM


All times are GMT +1. The time now is 07:35 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"