Hello All,
I have been following the recent excellent threads and am now coming out of my confusion, I think. Our existing solid fuel boiler is not going to cope with the additional requirement of our extension and will be replaced by oil in the nearish future. This will allow some degree of control (yippee). My original plan was simple DHW stat and TRV's on all rads, but this , I now see, has difficulties in achieving 'boiler interlock' From pointers given by various recent posters I believe I want: 1) two CH zones, since I have identified that all our rooms fall into one of two distinct heating requirement patterns. 2) separate control of hot water. Now... someone (BillR, I think) mentioned the Honeywell CM67's. Having investigated, these look excellent, allowing each heating zone to be controlled to different temperature levels throughout six different periods of the day. I particularly like the look of the RF versions and, AIUI, by linking to an additional HC60NG to be used as the boiler/pump controller - as per honeywell installation guide - I could then have TRV's on all the radiators except those in the 2 rooms (1 room in each zone) where the CM67's are installed and this would provide the required 'boiler interlock'. I think I'm OK with this so far (?) Someone tell me if I'm not! Then I come to the DHW.... I cannot see an equivalent beast to the CM67 for DHW purposes.... I guess I can use a simple cylinder thermostat - although I don't necessarily want to have a tank full of hot water permanently. Even if I did, how do I get this stat to talk to the HC60NG that is controlling the boiler?? I am sure I am missing something very simple here but cannot put my finger on it. It may become clearer when I have the boiler installation information to hand but in the meantime, I'd really appreciate if some kind soul can enlighten me. Perhaps there is something to be said for the old anthracite boiler... a) light it once a year - DHW control is sorted b) switch on the pump when you want the CH c) twiddle with the TRV's d) switch the pump off at bedtime e) heat leak rad keeps the bathroom warm for the overnight tinkles and f) the heatloss from the boiler keeps it warm for breakfast! arhhh the simplicity! TIA Ian |
#2
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
My original plan was simple DHW stat and TRV's on all rads, but this ,
I now see, has difficulties in achieving 'boiler interlock' Not really. Interlock is easily achieved. Any argument is about whether it is worth achieving or not. The benefits of implementing the interlock depend largely on the attitudes of the occupier. If the occupier doesn't mind turn it off and on manually, then the interlock is not as effective in increasing efficiency as when they are not. I prefer a system I can just leave well alone, yet works efficiently. It is possible to have an all-TRV system, even subzoned for timing. You simply plumb as S-Plan, with a 3 channel programmer, or with separate programmers conveniently located. But rather than using the 2 port valve microswitches, you achieve interlock using a flow switch after the bypass, but before the heating zone valves. The output from the flow switch can be combined with the HWC zone valve microswitch to provide a boiler call for heat. Personally, I prefer to use a programmable room stat, as it allows different temperatures at different times of day. Having implemented it, it very effectively maintains temperature in all rooms, including those with TRVs, provided the system is reasonably balanced. The rooms with the programmable thermostats are those used most frequently (master bedroom and lounge). This provides very accurate temperature in those rooms (measured away from the radiator) and a handy nearby override mechanism. The only problem is the kitchen, which doesn't get to temperature. However, this isn't really a control issue, as the room is 5m x 2.5m, with 2 external solid walls, 3 large windows, 1 door, french doors and a single tiny radiator at one end suitable only for a little bathroom. I'm planning to put a fan convector (i.e. Myson Kickspace 800) in to resolve this. Unfortunately, there's no room for insulation, although the draught proofing could be seriously improved. I cannot see an equivalent beast to the CM67 for DHW purposes.... Do you mean an RF cylinder thermostat? I'm sure I've seen one somewhere. However, I prefer to use proper cable when possible. My experience with other RF stuff is that it isn't quite as reliable as a bit of twin and earth. OTOH, if running cable is very difficult, then they are tempting. When wiring this system up, you'll still need a normal programmer. The hot water side handles HWC timing. The heating side acts as a master controller for your heating zones. You normally set this side to either "OFF" or "24H" and allow the programmable thermostats to handle any timing. There is good reason for maintaining a separate programmer. Firstly, you can turn off the entire system simply, without traipsing round the house to all the room stats. Secondly, wayward teenagers wanting 30C in the middle of the night (and having a programmable stat in their room) can be defeated. It is best to leave on 24H, if possible, though, as the programmable thermostat can keep a reasonable overnight temperature, such as 12C, rather than turning off completely. However, if you go overboard in balancing up TRV radiators so as to starve the master room, this may not be as effective. Doing so just a little, though, helps maintain steady temperatures. Christian. |
#3
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Mon, 15 Dec 2003 16:23:12 +0000, Ian wrote:
Hello All, I have been following the recent excellent threads and am now coming out of my confusion, I think. Our existing solid fuel boiler is not going to cope with the additional requirement of our extension and will be replaced by oil in the nearish future. This will allow some degree of control (yippee). My original plan was simple DHW stat and TRV's on all rads, but this , I now see, has difficulties in achieving 'boiler interlock' From pointers given by various recent posters I believe I want: 1) two CH zones, since I have identified that all our rooms fall into one of two distinct heating requirement patterns. 2) separate control of hot water. Now... someone (BillR, I think) mentioned the Honeywell CM67's. Having investigated, these look excellent, allowing each heating zone to be controlled to different temperature levels throughout six different periods of the day. I particularly like the look of the RF versions and, AIUI, by linking to an additional HC60NG to be used as the boiler/pump controller - as per honeywell installation guide - I could then have TRV's on all the radiators except those in the 2 rooms (1 room in each zone) where the CM67's are installed and this would provide the required 'boiler interlock'. I think I'm OK with this so far (?) Someone tell me if I'm not! Then I come to the DHW.... I cannot see an equivalent beast to the CM67 for DHW purposes.... I guess I can use a simple cylinder thermostat - although I don't necessarily want to have a tank full of hot water permanently. Even if I did, how do I get this stat to talk to the HC60NG that is controlling the boiler?? I am sure I am missing something very simple here but cannot put my finger on it. It may become clearer when I have the boiler installation information to hand but in the meantime, I'd really appreciate if some kind soul can enlighten me. I think that a better and more convenient solution to this would be the Danfoss Randall TP75-RF (about to be replaced by TP7000-RF) for the heating zones and a WP75-RF for the hot water. This would give you completely independent time and temperature operation for each zone and the hot water. www.danfoss-randall.co.uk These have a common receiver type and you can get up to 3 channel receivers, although probably to order. www.controlscenter.co.uk should be able to or any heating supplier. You would sit the receiver at the boiler position and hook all the demand outputs to the switched input of the boiler and possibly the pump if the boiler doesn't have an overrun output for the pump. If the motorised zone valves need to be in a position remote from the boiler and you can get power there, then you could have additional single channel receivers if you wanted. The receivers are trained to the transmitted signal during installation and you can have multiple receivers listening to one transmitting programmer. Obviously this would cost a bit more to implement, but the trade off is against wiring convenience and time . Perhaps there is something to be said for the old anthracite boiler... a) light it once a year - DHW control is sorted b) switch on the pump when you want the CH c) twiddle with the TRV's d) switch the pump off at bedtime e) heat leak rad keeps the bathroom warm for the overnight tinkles and f) the heatloss from the boiler keeps it warm for breakfast! arhhh the simplicity! TIA Ian ..andy To email, substitute .nospam with .gl |
#4
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
Ian wrote: Then I come to the DHW.... I cannot see an equivalent beast to the CM67 for DHW purposes.... I guess I can use a simple cylinder thermostat - although I don't necessarily want to have a tank full of hot water permanently. Even if I did, how do I get this stat to talk to the HC60NG that is controlling the boiler?? I am sure I am missing something very simple here but cannot put my finger on it. It may become clearer when I have the boiler installation information to hand but in the meantime, I'd really appreciate if some kind soul can enlighten me. What you need is, in effect, an S-Plan-Plus [see http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for heating and one for hot water. Use a standard programmer and cyl stat to control the zone valve for the hot water - with 2 or 3 on/off periods per 24 hours, as desired - but always the same temperature unless you manually twiddle the cyl stat (which is probably acceptable). On the same standard programmer, set CH to permanently on and use its CH ON contact to feed the programmable room stats. The actual on/off periods (and different temperatures if desired) are then controlled by the room stats - which in turn control their respective zone valves. The volt-free contacts on all 3 zone valves are connected in parallel - with the output side controlling the boiler and pump. That way, the boiler and pump will run whenever one or more zones requires heat and will shut down when they are all satisfied - achieving the desired interlock. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#5
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In article ,
"Set Square" writes: What you need is, in effect, an S-Plan-Plus [see http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for heating and one for hot water. Use a standard programmer and cyl stat to control the zone valve for the hot water - with 2 or 3 on/off periods per 24 hours, as desired - but always the same temperature unless you manually twiddle the cyl stat (which is probably acceptable). On the same standard programmer, set CH to permanently on and use its CH ON contact to feed the programmable room stats. The actual on/off periods (and different temperatures if desired) are then controlled by the room stats - which in turn control their respective zone valves. The volt-free contacts on all 3 zone valves are connected in parallel - with the output side controlling the boiler and pump. That way, the boiler and pump will run whenever one or more zones requires heat and will shut down when they are all satisfied - achieving the desired interlock. You will need to allow for pump overrun with most boilers. The Honeywell schematic does not. -- Andrew Gabriel |
#6
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
Andrew Gabriel wrote: You will need to allow for pump overrun with most boilers. The Honeywell schematic does not. This is true. In fact, it's only a small change from the Honeywell diagram. The basic logic remains the same, but the output from the zone valves' volt-free contacts drives just the boiler rather than the boiler and pump in parallel. The pump is then connected to the boiler's pump control terminal - which is live whenever the boiler is firing plus whenever the boiler's pump over-run stat calls for circulation to continue. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#7
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Mon, 15 Dec 2003 17:11:27 -0000, "Set Square"
wrote: What you need is, in effect, an S-Plan-Plus [see http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for heating and one for hot water. Use a standard programmer and cyl stat to control the zone valve for the hot water - with 2 or 3 on/off periods per 24 hours, as desired - but always the same temperature unless you manually twiddle the cyl stat (which is probably acceptable). On the same standard programmer, set CH to permanently on and use its CH ON contact to feed the programmable room stats. The actual on/off periods (and different temperatures if desired) are then controlled by the room stats - which in turn control their respective zone valves. The volt-free contacts on all 3 zone valves are connected in parallel - with the output side controlling the boiler and pump. That way, the boiler and pump will run whenever one or more zones requires heat and will shut down when they are all satisfied - achieving the desired interlock. Very many thanks to all who responded. My missing link was the need to still have a normal programmer to handle the DHW - not realising that the programmable room stats do not replace the programmer. I now have a fairly large bulge appearing on my forehead! I don't really have a problem running cables everywhere since the whole place will be redecorated following the extension. I I've had a look at the Danfoss site and can see that that would meet the bill but have noted the comment from Christian concerning the potential reliability of the RF stats. Since one may be 20m from its receiver , I think it makes more sense to go the wire route. Is there anything to choose in reliability of the electronics or TRV's between various manufacturers? Thanks again all Ian |
#8
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Is there anything to choose in reliability of the electronics or
TRV's between various manufacturers? Electronics are normally reliable. I'd buy a room stat mainly on the basis of appearance, provided it had the required functionality. Brand in itself wouldn't matter to me, except in that a good brand is more likely to physically look better. TRVs should be from a reputable manufacturer and expect to replace every 7 years or so when they start to get a little slow. Cheap ones may fail in a couple of years. Christian. |
#9
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote:
On Mon, 15 Dec 2003 17:11:27 -0000, "Set Square" wrote: What you need is, in effect, an S-Plan-Plus [see http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for heating and one for hot water. Use a standard programmer and cyl stat to control the zone valve for the hot water - with 2 or 3 on/off periods per 24 hours, as desired - but always the same temperature unless you manually twiddle the cyl stat (which is probably acceptable). On the same standard programmer, set CH to permanently on and use its CH ON contact to feed the programmable room stats. The actual on/off periods (and different temperatures if desired) are then controlled by the room stats - which in turn control their respective zone valves. The volt-free contacts on all 3 zone valves are connected in parallel - with the output side controlling the boiler and pump. That way, the boiler and pump will run whenever one or more zones requires heat and will shut down when they are all satisfied - achieving the desired interlock. Very many thanks to all who responded. My missing link was the need to still have a normal programmer to handle the DHW - not realising that the programmable room stats do not replace the programmer. I now have a fairly large bulge appearing on my forehead! You don't.. You can have a programmable thermostat for the cylinder as I mentioned - either wired or wireless. If you do this plus programmable room controller(s), you don't need to have an additional programmer at the boiler at all. On the other hand if you are going for wired connection to the cylinder, you could cover that using a simple cylinder stat and a programmer at the boiler instead. I don't really have a problem running cables everywhere since the whole place will be redecorated following the extension. I I've had a look at the Danfoss site and can see that that would meet the bill but have noted the comment from Christian concerning the potential reliability of the RF stats. Since one may be 20m from its receiver , I think it makes more sense to go the wire route. They are pretty solid in fact. There are specific standards that they are required to meet and incorporate error detection to avoid errors due to interference problems. I would regard them as a convenience if wiring is awkward, because obviously they are more expensive as well. However, if you can wire easily then that makes more sense. Is there anything to choose in reliability of the electronics or TRV's between various manufacturers? I've used Danfoss and Honeywell controls and not had a problem with either. Similarly their TRVs. Since replacing a TRV typically involves a drain down if the problem is in the base, then I would avoid the cheap products and again go for Honeywell, Myson, Drayton, etc. Honeywell seem to be the most commonly available at the merchants. Thanks again all Ian ..andy To email, substitute .nospam with .gl |
#10
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
Andy Hall wrote: On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote: My missing link was the need to still have a normal programmer to handle the DHW - not realising that the programmable room stats do not replace the programmer. You don't.. You can have a programmable thermostat for the cylinder as I mentioned - either wired or wireless. If you do this plus programmable room controller(s), you don't need to have an additional programmer at the boiler at all. Whilst this is true, using a conventional programmer with its CH output connected to the programmable room stats has the advantage that the heating can be turned off from a single point (e.g. for the summer) without having to re-programme the stats. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#11
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Tue, 16 Dec 2003 16:40:30 -0000, "Set Square"
wrote: In an earlier contribution to this discussion, Andy Hall wrote: On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote: My missing link was the need to still have a normal programmer to handle the DHW - not realising that the programmable room stats do not replace the programmer. You don't.. You can have a programmable thermostat for the cylinder as I mentioned - either wired or wireless. If you do this plus programmable room controller(s), you don't need to have an additional programmer at the boiler at all. Whilst this is true, using a conventional programmer with its CH output connected to the programmable room stats has the advantage that the heating can be turned off from a single point (e.g. for the summer) without having to re-programme the stats. True, although a simple switch near the boiler connecting the switched outputs from the room programmers would achieve the same thing. ..andy To email, substitute .nospam with .gl |
#12
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
True, although a simple switch near the boiler connecting the
switched outputs from the room programmers would achieve the same thing. Better to supply the feed to the programmable room stats, rather than the switched returns. Then you only need a SP switch for the lot, instead of a pole per zone. Christian. |
#13
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Tue, 16 Dec 2003 17:32:02 -0000, "Christian McArdle"
wrote: True, although a simple switch near the boiler connecting the switched outputs from the room programmers would achieve the same thing. Better to supply the feed to the programmable room stats, rather than the switched returns. Then you only need a SP switch for the lot, instead of a pole per zone. Christian. No because they all come together at a common point at the boiler anyway, to form the switched live to fire it up. If you have two (or more) room programmers, you could bring their demand signals and connect them together, then go through the switch, bring in the HW demand and then into the boiler. This is an "or" function of the room programmers followed by an "and" created by the switch followed by an "or" with the HW. Boiler = ((Prog1 OR Prog2 OR ...... ProgN) AND Switch) OR DHW ..andy To email, substitute .nospam with .gl |
#14
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In article ,
"Set Square" writes: In an earlier contribution to this discussion, Andrew Gabriel wrote: You will need to allow for pump overrun with most boilers. The Honeywell schematic does not. This is true. In fact, it's only a small change from the Honeywell diagram. The basic logic remains the same, but the output from the zone valves' volt-free contacts drives just the boiler rather than the boiler and pump in parallel. The pump is then connected to the boiler's pump control terminal - which is live whenever the boiler is firing plus whenever the boiler's pump over-run stat calls for circulation to continue. That's not the problem. The problem is that when the last zone valve closes, there's no water circuit for the pump overrun. You have to make some provision for that. -- Andrew Gabriel |
#15
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
"Set Square" wrote in message ...
In an earlier contribution to this discussion, Andy Hall wrote: On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote: My missing link was the need to still have a normal programmer to handle the DHW - not realising that the programmable room stats do not replace the programmer. You don't.. You can have a programmable thermostat for the cylinder as I mentioned - either wired or wireless. If you do this plus programmable room controller(s), you don't need to have an additional programmer at the boiler at all. Whilst this is true, using a conventional programmer with its CH output connected to the programmable room stats has the advantage that the heating can be turned off from a single point (e.g. for the summer) without having to re-programme the stats. I installed a Honeywell CM67NG RF recently. It has an 'off' setting on the programmable thermostat part - which is not really off but a user-selectable frost-free setting which is 5 deg C out of the box, IIRC. Neil |
#16
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
If you have two (or more) room programmers, you could bring
their demand signals and connect them together, then go through the switch, bring in the HW demand and then into the boiler. You couldn't put the switch on the output of the programmers, as that would short the outputs of them together, causing the zone valves to open in unison, rather than being individually controlled. You could put the switch on the microswitch outputs of the 2 port zone valves. However, this would not be ideal, as if the boiler fires due to the HWC zone valve demanding heat, then the heating zone valves may already be open, causing unwanted heat in the radiators. You could always add relays. However, the standard (cheaper and simpler) method is the sequence: Programmer - Room Stat (programmable) - Zone Valve - Boiler (via microswitches) (or switch) Christian. |
#17
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
Andrew Gabriel wrote: In article , "Set Square" writes: In an earlier contribution to this discussion, Andrew Gabriel wrote: You will need to allow for pump overrun with most boilers. The Honeywell schematic does not. This is true. In fact, it's only a small change from the Honeywell diagram. The basic logic remains the same, but the output from the zone valves' volt-free contacts drives just the boiler rather than the boiler and pump in parallel. The pump is then connected to the boiler's pump control terminal - which is live whenever the boiler is firing plus whenever the boiler's pump over-run stat calls for circulation to continue. That's not the problem. The problem is that when the last zone valve closes, there's no water circuit for the pump overrun. You have to make some provision for that. Ah, I see! You're talking about the by-pass loop rather than the wiring. You are perfectly correct - the Honeywell schematic doesn't show a by-pass loop and ought to do so. My point is also valid. The Honeywell electrical diagram shows the boiler and pump feeds connected togther - so that the pump stops when the boiler demand is turned off. For a by-pass to work, the pump needs to be controlled by the boiler so that it can continue to run after the boiler has finished firing. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#18
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
Neil Jones wrote: "Set Square" wrote in message ... Whilst this is true, using a conventional programmer with its CH output connected to the programmable room stats has the advantage that the heating can be turned off from a single point (e.g. for the summer) without having to re-programme the stats. I installed a Honeywell CM67NG RF recently. It has an 'off' setting on the programmable thermostat part - which is not really off but a user-selectable frost-free setting which is 5 deg C out of the box, IIRC. Neil Sure - but the earlier discussion related to a system with 2 or more heating zones, each controlled by a programmable stat. So you would have to turn each of these off rather than doing it in just one place. Also, I'm not sure that with some programmable stats you can effectively turn it permanently off with disturbing the other settings. Maybe you can? -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#19
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 09:56:38 -0000, "Christian McArdle"
wrote: If you have two (or more) room programmers, you could bring their demand signals and connect them together, then go through the switch, bring in the HW demand and then into the boiler. You couldn't put the switch on the output of the programmers, as that would short the outputs of them together, causing the zone valves to open in unison, rather than being individually controlled. You could put the switch on the microswitch outputs of the 2 port zone valves. However, this would not be ideal, as if the boiler fires due to the HWC zone valve demanding heat, then the heating zone valves may already be open, causing unwanted heat in the radiators. Does your last sentence make sense ? If the heating zone valves are already open, then this can only be because one or both of their timers are on and one or both of their stats are demanding heat. In what way is heat in the radiators then "unwanted" ? Apart from that, yes, the outputs can only be commoned at the boiler after the zone valves, or independent zone control will not be achieved. -- I have a vitally important role serving as a bad example. Mail john rather than nospam... |
#20
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Does your last sentence make sense ? If the heating zone valves are
already open, then this can only be because one or both of their timers are on and one or both of their stats are demanding heat. In what way is heat in the radiators then "unwanted" ? It is unwanted because it happens despite you switching the central heating off. This switch should override the programmable thermostat. So, the idea is to provide a master switch to turn off the heating. If that master switch is after the zone valve microswitches, then the programmers may call for heat and turn on the zone valves. The switch only prevents the zone valves firing up the boiler. However, if the boiler fires up for DHW, then the valves are already open and will pass water. To work properly, you need to put the switch before the zone valves, so they aren't open unnecessarily. This is easiest done by switching the feed to the programmers, as doing so after the programmers requires relays, or a multi pole switch. Christian. |
#21
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 09:56:38 -0000, "Christian McArdle"
wrote: If you have two (or more) room programmers, you could bring their demand signals and connect them together, then go through the switch, bring in the HW demand and then into the boiler. You couldn't put the switch on the output of the programmers, as that would short the outputs of them together, causing the zone valves to open in unison, rather than being individually controlled. You could put the switch on the microswitch outputs of the 2 port zone valves. However, this would not be ideal, as if the boiler fires due to the HWC zone valve demanding heat, then the heating zone valves may already be open, causing unwanted heat in the radiators. You could always add relays. However, the standard (cheaper and simpler) method is the sequence: Programmer - Room Stat (programmable) - Zone Valve - Boiler (via microswitches) (or switch) Christian. I see what you're saying.... ..andy To email, substitute .nospam with .gl |
#22
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 10:54:24 -0000, "Christian McArdle"
wrote: Does your last sentence make sense ? If the heating zone valves are already open, then this can only be because one or both of their timers are on and one or both of their stats are demanding heat. In what way is heat in the radiators then "unwanted" ? It is unwanted because it happens despite you switching the central heating off. This switch should override the programmable thermostat. So, the idea is to provide a master switch to turn off the heating. If that master switch is after the zone valve microswitches, then the programmers may call for heat and turn on the zone valves. The switch only prevents the zone valves firing up the boiler. However, if the boiler fires up for DHW, then the valves are already open and will pass water. To work properly, you need to put the switch before the zone valves, so they aren't open unnecessarily. This is easiest done by switching the feed to the programmers, as doing so after the programmers requires relays, or a multi pole switch. I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. -- Do the impossible and your boss will add it to your duties. Mail john rather than nospam... |
#23
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
I think I missed the point about the master switch ;-) Sounds a bit like
overkill as the two zone programmers can be co-located anyway. Co-location is impossible. They are programmable room thermostats. They won't sense the right temperature if they are in the wrong room. I suppose you could use a multi-channel programmer and straight room stats. However, this would cause many disadvantages. Firstly, this system doesn't allow different temperatures at different times of day. Secondly, manual override (i.e. boost/advance) buttons will be in a dark cupboard under the sink with bottles of bleach in the way, rather than on a convenient well lit nearby wall. Christian. |
#24
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 13:00:05 -0000, "Christian McArdle"
wrote: I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. Co-location is impossible. They are programmable room thermostats. They won't sense the right temperature if they are in the wrong room. Oh do shut up ;-) I thought the OP had mentioned RF devices, so was presuming he was putting the sensors in suitable rooms, with the actual programmers nearer the (um, let's see) zone valves, I guess. They don't *have* to be next to one another, but it would be simpler if they were. -- A seminar on Time Travel will be held 2 weeks ago. Mail john rather than nospam... |
#25
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Christian McArdle wrote:
Does your last sentence make sense ? If the heating zone valves are already open, then this can only be because one or both of their timers are on and one or both of their stats are demanding heat. In what way is heat in the radiators then "unwanted" ? It is unwanted because it happens despite you switching the central heating off. This switch should override the programmable thermostat. So, the idea is to provide a master switch to turn off the heating. If that master switch is after the zone valve microswitches, then the programmers may call for heat and turn on the zone valves. The switch only prevents the zone valves firing up the boiler. However, if the boiler fires up for DHW, then the valves are already open and will pass water. To work properly, you need to put the switch before the zone valves, so they aren't open unnecessarily. This is easiest done by switching the feed to the programmers, as doing so after the programmers requires relays, or a multi pole switch. Have I missed somethinhg here? My three way time controller has buttons that switch off any of its three zones? Completely. No thermostats or valves are energized. So no pump and no boiler. Christian. |
#26
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Have I missed somethinhg here?
My three way time controller has buttons that switch off any of its three zones? The proposal is for programmable room thermostats and no overall programmer, just a switch to turn off the entire heating system (except HWC). Obviously, a 3 channel programmer with non-programmable stats is a different system, also with an easy way to totally turn off the heating. However, it doesn't allow a local button for override/boost and doesn't allow different temperatures at different times of day. Christian. |
#27
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
The proposal is for programmable room thermostats and no overall
programmer, just a switch to turn off the entire heating system (except HWC). P.S. I don't see the point of not having a programmer instead of a switch. You probably need one anyway for the hot water side, and a twin channel isn't much more than a single channel. I suppose some people would find it simpler to operate a switch, given that the timing function is unlikely to prove useful. Christian. |
#28
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Christian McArdle wrote:
Have I missed somethinhg here? My three way time controller has buttons that switch off any of its three zones? The proposal is for programmable room thermostats and no overall programmer, just a switch to turn off the entire heating system (except HWC). Obviously, a 3 channel programmer with non-programmable stats is a different system, also with an easy way to totally turn off the heating. However, it doesn't allow a local button for override/boost and doesn't allow different temperatures at different times of day. Fairy nuff. Sounds amusing enough. I am going to radically side with a single IMM comment, that circulation hot water through fan convectors does a fair job of heating without the fans on. If you are really picky, fit a motorized valve. I can;t answer for teh Kickspace, but my 'vectors had no balancing valves. These are manadatory to stop them hogging CH flow. If you have a motorsized valve per convector that may not be such a problem - since hey will hog till the romm warms up only. Christian. |
#29
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
If you are really picky, fit a motorized valve.
Well I was always going to install at least one valve, shared between the two. However, I'm leaning towards installing two now. The main objection to having two was aesthetic anyway. I can;t answer for teh Kickspace, but my 'vectors had no balancing valves. These are manadatory to stop them hogging CH flow. Well, I'd prefer a proper balanced system anyway even if fully valved. I was intending to install balancing valves if none were fitted. The technical specs don't mention it, but do say what flow rate you need through them to get full power, with the obvious implication that you should throttle them down to that if you want anything else on the system to work. Christian. |
#30
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 10:05:48 +0000, Set Square wrote:
In an earlier contribution to this discussion, Andrew Gabriel wrote: In article , "Set Square" writes: In an earlier contribution to this discussion, Andrew Gabriel wrote: You will need to allow for pump overrun with most boilers. The Honeywell schematic does not. This is true. In fact, it's only a small change from the Honeywell diagram. The basic logic remains the same, but the output from the zone valves' volt-free contacts drives just the boiler rather than the boiler and pump in parallel. The pump is then connected to the boiler's pump control terminal - which is live whenever the boiler is firing plus whenever the boiler's pump over-run stat calls for circulation to continue. That's not the problem. The problem is that when the last zone valve closes, there's no water circuit for the pump overrun. You have to make some provision for that. Ah, I see! You're talking about the by-pass loop rather than the wiring. You are perfectly correct - the Honeywell schematic doesn't show a by-pass loop and ought to do so. My point is also valid. The Honeywell electrical diagram shows the boiler and pump feeds connected togther - so that the pump stops when the boiler demand is turned off. For a by-pass to work, the pump needs to be controlled by the boiler so that it can continue to run after the boiler has finished firing. It all depends on the boiler. In my own home the bathroom towel warmer is the bypass. On other systems I have doen with S plan I have used a boiler that does not require (an external) bypass. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html |
#31
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 12:36:21 +0000, John Laird wrote:
On Wed, 17 Dec 2003 10:54:24 -0000, "Christian McArdle" wrote: Does your last sentence make sense ? If the heating zone valves are already open, then this can only be because one or both of their timers are on and one or both of their stats are demanding heat. In what way is heat in the radiators then "unwanted" ? It is unwanted because it happens despite you switching the central heating off. This switch should override the programmable thermostat. So, the idea is to provide a master switch to turn off the heating. If that master switch is after the zone valve microswitches, then the programmers may call for heat and turn on the zone valves. The switch only prevents the zone valves firing up the boiler. However, if the boiler fires up for DHW, then the valves are already open and will pass water. To work properly, you need to put the switch before the zone valves, so they aren't open unnecessarily. This is easiest done by switching the feed to the programmers, as doing so after the programmers requires relays, or a multi pole switch. I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. I over-hauled a large heating system last year. 4 Heating Zones and DHW. All this used a Keston C40 which has seperate temperature control for heating and HW. It is true that for a short while the boiler output is at a higher temperature whilst the tank is being reheated. However the extra heat in the radiators is not a particularly big problem and is further minimized by the fact that the water circuit for the DHW coil is very much lower than for the radiator zones. (Short run of 22mm pipe right off the 28mm main manifold). This means that very little water is inclined to go through the radiator for the 10 minutes (typically) whilst the tank is reheating. Another way would have been to use a large 28mm 3 port diverter valve with DHW priority which would kill the heating during DHW reheat. However experience shows that some people like to turn the heating & HW off if the go on away in winter and resent waiting the _entire_ cylinder reheat time say 25mins (170 litre, nominal 14kW coil) before the radiators _start_ to heat up. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html |
#32
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Wed, 17 Dec 2003 13:00:05 +0000, Christian McArdle wrote:
I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. Co-location is impossible. They are programmable room thermostats. They won't sense the right temperature if they are in the wrong room. I suppose you could use a multi-channel programmer and straight room stats. However, this would cause many disadvantages. Firstly, this system doesn't allow different temperatures at different times of day. Secondly, manual override (i.e. boost/advance) buttons will be in a dark cupboard under the sink with bottles of bleach in the way, rather than on a convenient well lit nearby wall. I agree the idea of a master switch is well useful for maintenance if nothing else. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html |
#33
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
Ed Sirett wrote:
On Wed, 17 Dec 2003 13:00:05 +0000, Christian McArdle wrote: I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. Co-location is impossible. They are programmable room thermostats. They won't sense the right temperature if they are in the wrong room. I suppose you could use a multi-channel programmer and straight room stats. However, this would cause many disadvantages. Firstly, this system doesn't allow different temperatures at different times of day. Secondly, manual override (i.e. boost/advance) buttons will be in a dark cupboard under the sink with bottles of bleach in the way, rather than on a convenient well lit nearby wall. I agree the idea of a master switch is well useful for maintenance if nothing else. I am pretty sure its mandatory - my whole heatng system is run off a big switched fused spur with its own neon and switch bang next door to the controller and very near the boiler. I thought you had to do this with all boilers extractor fans etc etc. |
#34
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
"Set Square" wrote in message ...
In an earlier contribution to this discussion, Neil Jones wrote: "Set Square" wrote in message ... Whilst this is true, using a conventional programmer with its CH output connected to the programmable room stats has the advantage that the heating can be turned off from a single point (e.g. for the summer) without having to re-programme the stats. I installed a Honeywell CM67NG RF recently. It has an 'off' setting on the programmable thermostat part - which is not really off but a user-selectable frost-free setting which is 5 deg C out of the box, IIRC. Neil Sure - but the earlier discussion related to a system with 2 or more heating zones, each controlled by a programmable stat. So you would have to turn each of these off rather than doing it in just one place. Also, I'm not sure that with some programmable stats you can effectively turn it permanently off with disturbing the other settings. Maybe you can? You can, because the programmable stat part is battery powered, whereas the receiver/controller part is wired into the boiler control system. If you power of the boiler it removes power from the receiver/controller (which actually decides to turn the boiler on/off) but the thermostat itself is still on. |
#35
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
I agree the idea of a master switch is well useful for maintenance
if nothing else. But then, that would be entirely different. The propsed switch only turns off the central heating side and certainly doesn't isolate anything. The boiler should remain powered. Obviously, some sort of DP isolation should be provided to the entire system, too. I've ended up with two DP isolators on mine. The boiler and cylinder are in the loft. The heating zone valves and programmer are in the understairs cupboard. I have a DP isolator in both locations, both of which isolate the entire system. Christian. |
#36
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
In an earlier contribution to this discussion,
The Natural Philosopher wrote: I am pretty sure its mandatory - my whole heatng system is run off a big switched fused spur with its own neon and switch bang next door to the controller and very near the boiler. I thought you had to do this with all boilers extractor fans etc etc. Yes, you need an isolating switch for the *whole* system - but that's not the point! This discussion is about turning off a multi-zoned heating system *without* also turning off the hot water. -- Cheers, Set Square ______ Please reply to newsgroup. Reply address is Black Hole! |
#37
|
|||
|
|||
Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question
On Thu, 18 Dec 2003 01:12:12 +0000, The Natural Philosopher wrote:
Ed Sirett wrote: On Wed, 17 Dec 2003 13:00:05 +0000, Christian McArdle wrote: I think I missed the point about the master switch ;-) Sounds a bit like overkill as the two zone programmers can be co-located anyway. Co-location is impossible. They are programmable room thermostats. They won't sense the right temperature if they are in the wrong room. I suppose you could use a multi-channel programmer and straight room stats. However, this would cause many disadvantages. Firstly, this system doesn't allow different temperatures at different times of day. Secondly, manual override (i.e. boost/advance) buttons will be in a dark cupboard under the sink with bottles of bleach in the way, rather than on a convenient well lit nearby wall. I agree the idea of a master switch is well useful for maintenance if nothing else. I am pretty sure its mandatory - my whole heatng system is run off a big switched fused spur with its own neon and switch bang next door to the controller and very near the boiler. I thought you had to do this with all boilers extractor fans etc etc. I am not suggesting that the programmer replaces proper DP isolation. I'm talking about, say, you want to diagnose the boiler, you are testing it out live but want to be sure you don't have a CH demand only a HW one. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Central Heating question | UK diy | |||
Central Heating - Controls | UK diy | |||
FAQ Question re. central heating | UK diy | |||
Further to my last post entitled 'Flushing and treating central heating question' | UK diy | |||
Flushing and treating Central Heating question | UK diy |