  #1   Report Post  
Ian
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

Hello All,

I have been following the recent excellent threads and am now coming
out of my confusion, I think.
Our existing solid fuel boiler is not going to cope with the
additional requirement of our extension and will be replaced by oil in
the nearish future. This will allow some degree of control (yippee).
My original plan was simple DHW stat and TRV's on all rads, but this ,
I now see, has difficulties in achieving 'boiler interlock'

From pointers given by various recent posters I believe I want:
1) two CH zones, since I have identified that all our rooms fall into
one of two distinct heating requirement patterns.
2) separate control of hot water.

Now... someone (BillR, I think) mentioned the Honeywell CM67's. Having
investigated, these look excellent, allowing each heating zone to be
controlled to different temperature levels throughout six different
periods of the day. I particularly like the look of the RF versions
and, AIUI, by linking to an additional HC60NG to be used as the
boiler/pump controller - as per honeywell installation guide - I
could then have TRV's on all the radiators except those in the 2 rooms
(1 room in each zone) where the CM67's are installed and this would
provide the required 'boiler interlock'. I think I'm OK with this so
far (?) Someone tell me if I'm not!

Then I come to the DHW....
I cannot see an equivalent beast to the CM67 for DHW purposes....
I guess I can use a simple cylinder thermostat - although I don't
necessarily want to have a tank full of hot water permanently. Even if
I did, how do I get this stat to talk to the HC60NG that is
controlling the boiler?? I am sure I am missing something very simple
here but cannot put my finger on it.
It may become clearer when I have the boiler installation information
to hand but in the meantime, I'd really appreciate if some kind soul
can enlighten me.

Perhaps there is something to be said for the old anthracite boiler...
a) light it once a year - DHW control is sorted
b) switch on the pump when you want the CH
c) twiddle with the TRV's
d) switch the pump off at bedtime
e) heat leak rad keeps the bathroom warm for the overnight tinkles and
f) the heatloss from the boiler keeps it warm for breakfast!
arhhh the simplicity!

TIA
Ian


  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

My original plan was simple DHW stat and TRV's on all rads, but this ,
I now see, has difficulties in achieving 'boiler interlock'


Not really. Interlock is easily achieved. Any argument is about whether it
is worth achieving or not. The benefits of implementing the interlock depend
largely on the attitudes of the occupier. If the occupier doesn't mind turn
it off and on manually, then the interlock is not as effective in increasing
efficiency as when they are not. I prefer a system I can just leave well
alone, yet works efficiently.

It is possible to have an all-TRV system, even subzoned for timing. You
simply plumb as S-Plan, with a 3 channel programmer, or with separate
programmers conveniently located. But rather than using the 2 port valve
microswitches, you achieve interlock using a flow switch after the bypass,
but before the heating zone valves. The output from the flow switch can be
combined with the HWC zone valve microswitch to provide a boiler call for
heat.

Personally, I prefer to use a programmable room stat, as it allows different
temperatures at different times of day. Having implemented it, it very
effectively maintains temperature in all rooms, including those with TRVs,
provided the system is reasonably balanced. The rooms with the programmable
thermostats are those used most frequently (master bedroom and lounge). This
provides very accurate temperature in those rooms (measured away from the
radiator) and a handy nearby override mechanism.

The only problem is the kitchen, which doesn't get to temperature. However,
this isn't really a control issue, as the room is 5m x 2.5m, with 2 external
solid walls, 3 large windows, 1 door, french doors and a single tiny
radiator at one end suitable only for a little bathroom. I'm planning to put
a fan convector (i.e. Myson Kickspace 800) in to resolve this.
Unfortunately, there's no room for insulation, although the draught proofing
could be seriously improved.

I cannot see an equivalent beast to the CM67 for DHW purposes....


Do you mean an RF cylinder thermostat? I'm sure I've seen one somewhere.
However, I prefer to use proper cable when possible. My experience with
other RF stuff is that it isn't quite as reliable as a bit of twin and
earth. OTOH, if running cable is very difficult, then they are tempting.

When wiring this system up, you'll still need a normal programmer. The hot
water side handles HWC timing. The heating side acts as a master controller
for your heating zones. You normally set this side to either "OFF" or "24H"
and allow the programmable thermostats to handle any timing. There is good
reason for maintaining a separate programmer. Firstly, you can turn off the
entire system simply, without traipsing round the house to all the room
stats. Secondly, wayward teenagers wanting 30C in the middle of the night
(and having a programmable stat in their room) can be defeated. It is best
to leave on 24H, if possible, though, as the programmable thermostat can
keep a reasonable overnight temperature, such as 12C, rather than turning
off completely. However, if you go overboard in balancing up TRV radiators
so as to starve the master room, this may not be as effective. Doing so just
a little, though, helps maintain steady temperatures.

Christian.


  #3   Report Post  
Andy Hall
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

On Mon, 15 Dec 2003 16:23:12 +0000, Ian wrote:

Hello All,

I have been following the recent excellent threads and am now coming
out of my confusion, I think.
Our existing solid fuel boiler is not going to cope with the
additional requirement of our extension and will be replaced by oil in
the nearish future. This will allow some degree of control (yippee).
My original plan was simple DHW stat and TRV's on all rads, but this ,
I now see, has difficulties in achieving 'boiler interlock'

From pointers given by various recent posters I believe I want:
1) two CH zones, since I have identified that all our rooms fall into
one of two distinct heating requirement patterns.
2) separate control of hot water.

Now... someone (BillR, I think) mentioned the Honeywell CM67's. Having
investigated, these look excellent, allowing each heating zone to be
controlled to different temperature levels throughout six different
periods of the day. I particularly like the look of the RF versions
and, AIUI, by linking to an additional HC60NG to be used as the
boiler/pump controller - as per honeywell installation guide - I
could then have TRV's on all the radiators except those in the 2 rooms
(1 room in each zone) where the CM67's are installed and this would
provide the required 'boiler interlock'. I think I'm OK with this so
far (?) Someone tell me if I'm not!

Then I come to the DHW....
I cannot see an equivalent beast to the CM67 for DHW purposes....
I guess I can use a simple cylinder thermostat - although I don't
necessarily want to have a tank full of hot water permanently. Even if
I did, how do I get this stat to talk to the HC60NG that is
controlling the boiler?? I am sure I am missing something very simple
here but cannot put my finger on it.
It may become clearer when I have the boiler installation information
to hand but in the meantime, I'd really appreciate if some kind soul
can enlighten me.


I think that a better and more convenient solution to this would be
the Danfoss Randall TP75-RF (about to be replaced by TP7000-RF) for
the heating zones and a WP75-RF for the hot water. This would give
you completely independent time and temperature operation for each
zone and the hot water.

www.danfoss-randall.co.uk

These have a common receiver type and you can get up to 3 channel
receivers, although probably to order.

www.controlscenter.co.uk should be able to or any heating supplier.

You would sit the receiver at the boiler position and hook all the
demand outputs to the switched input of the boiler and possibly the
pump if the boiler doesn't have an overrun output for the pump.

If the motorised zone valves need to be in a position remote from the
boiler and you can get power there, then you could have additional
single channel receivers if you wanted. The receivers are trained to
the transmitted signal during installation and you can have multiple
receivers listening to one transmitting programmer.

Obviously this would cost a bit more to implement, but the trade off
is against wiring convenience and time .






Perhaps there is something to be said for the old anthracite boiler...
a) light it once a year - DHW control is sorted
b) switch on the pump when you want the CH
c) twiddle with the TRV's
d) switch the pump off at bedtime
e) heat leak rad keeps the bathroom warm for the overnight tinkles and
f) the heatloss from the boiler keeps it warm for breakfast!
arhhh the simplicity!

TIA
Ian


..andy

To email, substitute .nospam with .gl
  #4   Report Post  
Set Square
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In an earlier contribution to this discussion,
Ian wrote:


Then I come to the DHW....
I cannot see an equivalent beast to the CM67 for DHW purposes....
I guess I can use a simple cylinder thermostat - although I don't
necessarily want to have a tank full of hot water permanently. Even if
I did, how do I get this stat to talk to the HC60NG that is
controlling the boiler?? I am sure I am missing something very simple
here but cannot put my finger on it.
It may become clearer when I have the boiler installation information
to hand but in the meantime, I'd really appreciate if some kind soul
can enlighten me.


What you need is, in effect, an S-Plan-Plus [see
http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for
heating and one for hot water.

Use a standard programmer and cyl stat to control the zone valve for the hot
water - with 2 or 3 on/off periods per 24 hours, as desired - but always the
same temperature unless you manually twiddle the cyl stat (which is probably
acceptable). On the same standard programmer, set CH to permanently on and
use its CH ON contact to feed the programmable room stats. The actual on/off
periods (and different temperatures if desired) are then controlled by the
room stats - which in turn control their respective zone valves.

The volt-free contacts on all 3 zone valves are connected in parallel - with
the output side controlling the boiler and pump. That way, the boiler and
pump will run whenever one or more zones requires heat and will shut down
when they are all satisfied - achieving the desired interlock.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #5   Report Post  
Andrew Gabriel
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In article ,
"Set Square" writes:

What you need is, in effect, an S-Plan-Plus [see
http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for
heating and one for hot water.

Use a standard programmer and cyl stat to control the zone valve for the hot
water - with 2 or 3 on/off periods per 24 hours, as desired - but always the
same temperature unless you manually twiddle the cyl stat (which is probably
acceptable). On the same standard programmer, set CH to permanently on and
use its CH ON contact to feed the programmable room stats. The actual on/off
periods (and different temperatures if desired) are then controlled by the
room stats - which in turn control their respective zone valves.

The volt-free contacts on all 3 zone valves are connected in parallel - with
the output side controlling the boiler and pump. That way, the boiler and
pump will run whenever one or more zones requires heat and will shut down
when they are all satisfied - achieving the desired interlock.


You will need to allow for pump overrun with most boilers.
The Honeywell schematic does not.

--
Andrew Gabriel


  #6   Report Post  
Set Square
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In an earlier contribution to this discussion,
Andrew Gabriel wrote:

You will need to allow for pump overrun with most boilers.
The Honeywell schematic does not.



This is true. In fact, it's only a small change from the Honeywell diagram.
The basic logic remains the same, but the output from the zone valves'
volt-free contacts drives just the boiler rather than the boiler and pump in
parallel. The pump is then connected to the boiler's pump control terminal -
which is live whenever the boiler is firing plus whenever the boiler's pump
over-run stat calls for circulation to continue.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #7   Report Post  
Andrew Gabriel
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In article ,
"Set Square" writes:
In an earlier contribution to this discussion,
Andrew Gabriel wrote:

You will need to allow for pump overrun with most boilers.
The Honeywell schematic does not.



This is true. In fact, it's only a small change from the Honeywell diagram.
The basic logic remains the same, but the output from the zone valves'
volt-free contacts drives just the boiler rather than the boiler and pump in
parallel. The pump is then connected to the boiler's pump control terminal -
which is live whenever the boiler is firing plus whenever the boiler's pump
over-run stat calls for circulation to continue.


That's not the problem. The problem is that when the last zone valve
closes, there's no water circuit for the pump overrun. You have to
make some provision for that.

--
Andrew Gabriel
  #8   Report Post  
Set Square
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In an earlier contribution to this discussion,
Andrew Gabriel wrote:

In article ,
"Set Square" writes:
In an earlier contribution to this discussion,
Andrew Gabriel wrote:

You will need to allow for pump overrun with most boilers.
The Honeywell schematic does not.



This is true. In fact, it's only a small change from the Honeywell
diagram. The basic logic remains the same, but the output from the
zone valves' volt-free contacts drives just the boiler rather than
the boiler and pump in parallel. The pump is then connected to the
boiler's pump control terminal - which is live whenever the boiler
is firing plus whenever the boiler's pump over-run stat calls for
circulation to continue.


That's not the problem. The problem is that when the last zone valve
closes, there's no water circuit for the pump overrun. You have to
make some provision for that.


Ah, I see! You're talking about the by-pass loop rather than the wiring. You
are perfectly correct - the Honeywell schematic doesn't show a by-pass loop
and ought to do so.

My point is also valid. The Honeywell electrical diagram shows the boiler
and pump feeds connected togther - so that the pump stops when the boiler
demand is turned off. For a by-pass to work, the pump needs to be controlled
by the boiler so that it can continue to run after the boiler has finished
firing.

--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #9   Report Post  
Ian
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

On Mon, 15 Dec 2003 17:11:27 -0000, "Set Square"
wrote:

What you need is, in effect, an S-Plan-Plus [see
http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for
heating and one for hot water.

Use a standard programmer and cyl stat to control the zone valve for the hot
water - with 2 or 3 on/off periods per 24 hours, as desired - but always the
same temperature unless you manually twiddle the cyl stat (which is probably
acceptable). On the same standard programmer, set CH to permanently on and
use its CH ON contact to feed the programmable room stats. The actual on/off
periods (and different temperatures if desired) are then controlled by the
room stats - which in turn control their respective zone valves.

The volt-free contacts on all 3 zone valves are connected in parallel - with
the output side controlling the boiler and pump. That way, the boiler and
pump will run whenever one or more zones requires heat and will shut down
when they are all satisfied - achieving the desired interlock.


Very many thanks to all who responded.
My missing link was the need to still have a normal programmer to
handle the DHW - not realising that the programmable room stats do not
replace the programmer. I now have a fairly large bulge appearing on
my forehead!

I don't really have a problem running cables everywhere since the
whole place will be redecorated following the extension. I
I've had a look at the Danfoss site and can see that that would meet
the bill but have noted the comment from Christian concerning the
potential reliability of the RF stats. Since one may be 20m from its
receiver , I think it makes more sense to go the wire route.

Is there anything to choose in reliability of the electronics or TRV's
between various manufacturers?

Thanks again all

Ian

  #10   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

Is there anything to choose in reliability of the electronics or
TRV's between various manufacturers?


Electronics are normally reliable. I'd buy a room stat mainly on the basis
of appearance, provided it had the required functionality. Brand in itself
wouldn't matter to me, except in that a good brand is more likely to
physically look better.

TRVs should be from a reputable manufacturer and expect to replace every 7
years or so when they start to get a little slow. Cheap ones may fail in a
couple of years.

Christian.




  #11   Report Post  
Andy Hall
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote:

On Mon, 15 Dec 2003 17:11:27 -0000, "Set Square"
wrote:

What you need is, in effect, an S-Plan-Plus [see
http://content.honeywell.com/uk/homes/systems.htm] with 3 zones, 2 for
heating and one for hot water.

Use a standard programmer and cyl stat to control the zone valve for the hot
water - with 2 or 3 on/off periods per 24 hours, as desired - but always the
same temperature unless you manually twiddle the cyl stat (which is probably
acceptable). On the same standard programmer, set CH to permanently on and
use its CH ON contact to feed the programmable room stats. The actual on/off
periods (and different temperatures if desired) are then controlled by the
room stats - which in turn control their respective zone valves.

The volt-free contacts on all 3 zone valves are connected in parallel - with
the output side controlling the boiler and pump. That way, the boiler and
pump will run whenever one or more zones requires heat and will shut down
when they are all satisfied - achieving the desired interlock.


Very many thanks to all who responded.
My missing link was the need to still have a normal programmer to
handle the DHW - not realising that the programmable room stats do not
replace the programmer. I now have a fairly large bulge appearing on
my forehead!


You don't.. You can have a programmable thermostat for the cylinder
as I mentioned - either wired or wireless.

If you do this plus programmable room controller(s), you don't need to
have an additional programmer at the boiler at all.

On the other hand if you are going for wired connection to the
cylinder, you could cover that using a simple cylinder stat and a
programmer at the boiler instead.



I don't really have a problem running cables everywhere since the
whole place will be redecorated following the extension. I
I've had a look at the Danfoss site and can see that that would meet
the bill but have noted the comment from Christian concerning the
potential reliability of the RF stats. Since one may be 20m from its
receiver , I think it makes more sense to go the wire route.


They are pretty solid in fact. There are specific standards that they
are required to meet and incorporate error detection to avoid errors
due to interference problems.

I would regard them as a convenience if wiring is awkward, because
obviously they are more expensive as well. However, if you can wire
easily then that makes more sense.



Is there anything to choose in reliability of the electronics or TRV's
between various manufacturers?


I've used Danfoss and Honeywell controls and not had a problem with
either. Similarly their TRVs.

Since replacing a TRV typically involves a drain down if the problem
is in the base, then I would avoid the cheap products and again go for
Honeywell, Myson, Drayton, etc. Honeywell seem to be the most
commonly available at the merchants.




Thanks again all

Ian


..andy

To email, substitute .nospam with .gl
  #12   Report Post  
Set Square
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

In an earlier contribution to this discussion,
Andy Hall wrote:

On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote:
My missing link was the need to still have a normal programmer to
handle the DHW - not realising that the programmable room stats do
not replace the programmer.


You don't.. You can have a programmable thermostat for the cylinder
as I mentioned - either wired or wireless.

If you do this plus programmable room controller(s), you don't need to
have an additional programmer at the boiler at all.



Whilst this is true, using a conventional programmer with its CH output
connected to the programmable room stats has the advantage that the heating
can be turned off from a single point (e.g. for the summer) without having
to re-programme the stats.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is Black Hole!


  #13   Report Post  
Andy Hall
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

On Tue, 16 Dec 2003 16:40:30 -0000, "Set Square"
wrote:

In an earlier contribution to this discussion,
Andy Hall wrote:

On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote:
My missing link was the need to still have a normal programmer to
handle the DHW - not realising that the programmable room stats do
not replace the programmer.


You don't.. You can have a programmable thermostat for the cylinder
as I mentioned - either wired or wireless.

If you do this plus programmable room controller(s), you don't need to
have an additional programmer at the boiler at all.



Whilst this is true, using a conventional programmer with its CH output
connected to the programmable room stats has the advantage that the heating
can be turned off from a single point (e.g. for the summer) without having
to re-programme the stats.


True, although a simple switch near the boiler connecting the switched
outputs from the room programmers would achieve the same thing.

..andy

To email, substitute .nospam with .gl
  #14   Report Post  
Neil Jones
 
Posts: n/a
Default Central Heating Zoning controls (was Are room thermostats out of fashion?) longish question

"Set Square" wrote in message ...
In an earlier contribution to this discussion,
Andy Hall wrote:

On Tue, 16 Dec 2003 14:54:43 +0000, Ian wrote:
My missing link was the need to still have a normal programmer to
handle the DHW - not realising that the programmable room stats do
not replace the programmer.


You don't.. You can have a programmable thermostat for the cylinder
as I mentioned - either wired or wireless.

If you do this plus programmable room controller(s), you don't need to
have an additional programmer at the boiler at all.



Whilst this is true, using a conventional programmer with its CH output
connected to the programmable room stats has the advantage that the heating
can be turned off from a single point (e.g. for the summer) without having
to re-programme the stats.


I installed a Honeywell CM67NG RF recently. It has an 'off' setting on
the programmable thermostat part - which is not really off but a
user-selectable frost-free setting which is 5 deg C out of the box,
IIRC.

Neil
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Central Heating question Mike Hibbert UK diy 28 December 10th 03 03:52 PM
Central Heating - Controls IMM UK diy 12 September 2nd 03 04:14 PM
FAQ Question re. central heating Andy Hall UK diy 24 August 14th 03 02:31 PM
Further to my last post entitled 'Flushing and treating central heating question' David W.E. Roberts UK diy 0 July 29th 03 07:15 PM
Flushing and treating Central Heating question echo21 UK diy 4 July 27th 03 10:19 AM


All times are GMT +1. The time now is 02:15 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"