UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

It's that time of year when one's thoughts turn to the smoothe running of ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm all
over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips, I've treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info seemed to
sugest that the pump needed to be on maximum. I've been running it like that for
a few days and things do seem to have improved regards balance of heat even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70 and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know if the
UPS 15-50 is powerful enough or not.

Cheers

Cliff
  #2   Report Post  
BillR
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

Moonshine wrote:
It's that time of year when one's thoughts turn to the smoothe
running of ones CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert
opinion on the suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've
always been concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel
warm all over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips,
I've treated myself to an IR themometer to do some proper
investigation.

As I say at the moment I won't go into all the figures, but the info
seemed to sugest that the pump needed to be on maximum. I've been
running it like that for a few days and things do seem to have
improved regards balance of heat even running all the LSV's open
until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80
degrees C at the input to the radiators, the boilier is cutting out
when the ouput has reached this temp. The max input to closesest rad
to pump is around 70 and the lowest is around 65. And the Boiler is
still short cycling.

So before I try and rectify anything balancing like crazy I want to
know if the UPS 15-50 is powerful enough or not.

I don't know this pump, what head rating is it?
I had similar situation for many years inc boiler kettling at times.
When I changed the pump for the second time I went for a beefer pump with a
6m head.
It runs a lot quieter on its medium setting and the system works much better
too.


  #3   Report Post  
IMM
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system


"Moonshine" wrote in message
...
It's that time of year when one's thoughts turn to the smoothe running of

ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion

on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always

been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm

all
over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips, I've

treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info

seemed to
sugest that the pump needed to be on maximum. I've been running it like

that for
a few days and things do seem to have improved regards balance of heat

even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C

at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70

and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know

if the
UPS 15-50 is powerful enough or not.


Cliff,

If this is microbore then a more powerful pumps appears the answer. Unless
there is sludge in the system blocking pipes. Did it ever work properly?
The boiler appears to be getting up to temp, so that appears to be working
fine.

Microbore requires generally a larger pump than a 15-50. A 15-50 generally
was not used on a house that large. Go for the next size up. and then do
your tests.



---
--

Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.548 / Virus Database: 341 - Release Date: 05/12/2003


  #4   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 9 Dec 2003 15:14:59 -0000, "BillR" wrote:

Moonshine wrote:
It's that time of year when one's thoughts turn to the smoothe
running of ones CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert
opinion on the suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've
always been concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel
warm all over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips,
I've treated myself to an IR themometer to do some proper
investigation.

As I say at the moment I won't go into all the figures, but the info
seemed to sugest that the pump needed to be on maximum. I've been
running it like that for a few days and things do seem to have
improved regards balance of heat even running all the LSV's open
until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80
degrees C at the input to the radiators, the boilier is cutting out
when the ouput has reached this temp. The max input to closesest rad
to pump is around 70 and the lowest is around 65. And the Boiler is
still short cycling.

So before I try and rectify anything balancing like crazy I want to
know if the UPS 15-50 is powerful enough or not.

I don't know this pump, what head rating is it?
I had similar situation for many years inc boiler kettling at times.
When I changed the pump for the second time I went for a beefer pump with a
6m head.
It runs a lot quieter on its medium setting and the system works much better
too.

Hi Bill

The 15-50 is rated at 5m head.

The annoying thing is I'm sure I fitted this myself soon after moving to the
house because the existing (non Grundfos) pump was very noisy. I no longer have
it to check what the rating was, but I'll pop round a neighbours and see what
theirs is.

Is a 15-60 going to be sufficient of an improvement?

I did flush out and Fernox the system a couple of years ago, but I don't know
how good a job that would have been rated as.

Cliff
  #5   Report Post  
Andy Hall
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 10:11:27 GMT, Moonshine
wrote:

It's that time of year when one's thoughts turn to the smoothe running of ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm all
over, and the boiler does a lot of 1-2 minute cycling.


This means hat either the boiler thermostat has a problem or that the
heat is not being delivered from it rapidly enough. The latter can
be because of poor circulation or because the boiler is oversized/burn
rate set too high for the installation or both.



Turning to this group again over the last week or so for some tips, I've treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info seemed to
sugest that the pump needed to be on maximum. I've been running it like that for
a few days and things do seem to have improved regards balance of heat even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70 and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know if the
UPS 15-50 is powerful enough or not.


This does all point to poor circulation as at least one of the
factors.

Is the system using microbore pipe (e.g. 8mm)? This may present a
higher system resistance and require a higher pump head.

Have you checked for sludging?


If you have TRVs especially, a better pump option could well be the
Grundfos Alpha. There is a 15-60 model of this which has a 6m max
head as opposed to the 5m of the UPS 15-50. It also adapts its
output to match the resistance requirements.

However, before doing a pump swap, I would check for why the
circulation is poor.




Cheers

Cliff


..andy

To email, substitute .nospam with .gl


  #6   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 16:39:37 +0000, Andy Hall wrote:

On Tue, 09 Dec 2003 10:11:27 GMT, Moonshine
wrote:

It's that time of year when one's thoughts turn to the smoothe running of ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm all
over, and the boiler does a lot of 1-2 minute cycling.


This means hat either the boiler thermostat has a problem or that the
heat is not being delivered from it rapidly enough. The latter can
be because of poor circulation or because the boiler is oversized/burn
rate set too high for the installation or both.


The Boiler is a GlowWorm FuelSaver 55F with a rated output between 35k & 55k
Btu/h. Its anyones guess as to what it has been set to. The manual talks about
putting a suppied self adhesive label by the data plate to record setting but
guess what I can't see one :-)




Turning to this group again over the last week or so for some tips, I've treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info seemed to
sugest that the pump needed to be on maximum. I've been running it like that for
a few days and things do seem to have improved regards balance of heat even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70 and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know if the
UPS 15-50 is powerful enough or not.


This does all point to poor circulation as at least one of the
factors.

Is the system using microbore pipe (e.g. 8mm)? This may present a
higher system resistance and require a higher pump head.


Yes it is 8mm Microbore (I put it in the Subject line but should have also
included it in the body text too for clarity sorry)


Have you checked for sludging?

What is the best way of doing this (i.e. least messy )


If you have TRVs especially, a better pump option could well be the
Grundfos Alpha. There is a 15-60 model of this which has a 6m max
head as opposed to the 5m of the UPS 15-50. It also adapts its
output to match the resistance requirements.


No TRV's


However, before doing a pump swap, I would check for why the
circulation is poor.




Cheers

Cliff


.andy

To email, substitute .nospam with .gl


  #7   Report Post  
Colin M
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

Moonshine wrote in message . ..
It's that time of year when one's thoughts turn to the smoothe running of ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm all
over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips, I've treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info seemed to
sugest that the pump needed to be on maximum. I've been running it like that for
a few days and things do seem to have improved regards balance of heat even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70 and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know if the
UPS 15-50 is powerful enough or not.

Cheers

Cliff



Cliff, I had exactly the same problems with a 15mm system. The
temperature of the water at the rad inputs is a function of the boiler
thermostat setting as well as the flow rate. I strongly recommend
balancing the system per recent threads here and the faq.

Initially I cranked my pump up to max to achieve the correct drop
across the boiler, but once the system was balanced, reset it to the
mid position. I then replaced it with a 15-60 Alpha + pump simply
because this new unit has an electronically controlled pressure output
to take into account thermostat valve operation around the house.

I was surprised at how much effect on temperature stability and boiler
cycling the balancing had.

Colin M
  #8   Report Post  
Ed Sirett
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 10:11:27 +0000, Moonshine wrote:

It's that time of year when one's thoughts turn to the smoothe running of ones
CH system (sad isn't it!)

Before I go into all the details I'd just like to get some expert opinion on the
suitability of the the UPS 15-50 in my system.

The pump has been running for years on the medium setting, but I've always been
concious that the system didn't seem to be running right.

The radiators were not piping hot to the touch, the house didn't feel warm all
over, and the boiler does a lot of 1-2 minute cycling.

Turning to this group again over the last week or so for some tips, I've treated
myself to an IR themometer to do some proper investigation.

As I say at the moment I won't go into all the figures, but the info seemed to
sugest that the pump needed to be on maximum. I've been running it like that for
a few days and things do seem to have improved regards balance of heat even
running all the LSV's open until I'm sure what the state of play is.

My main concernes at the moment are I never see anywhere near 80 degrees C at
the input to the radiators, the boilier is cutting out when the ouput has
reached this temp. The max input to closesest rad to pump is around 70 and the
lowest is around 65. And the Boiler is still short cycling.

So before I try and rectify anything balancing like crazy I want to know if the
UPS 15-50 is powerful enough or not.


The next size up will fit withoput modification, also the maximum setting
is pretty much the required going rate on microbore systems.

Check that the boiler is delivering at 80+ C. Which is what you should get
when turned on all the way.

--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html


  #9   Report Post  
G&M
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

I'd second that - use a 6m head Grundfos Alpha. It is rather more expensive
but offers a continuously variable setting to match most applications plus
three fixed settings for special cases. And it's sooooooo quiet.


  #10   Report Post  
geoff
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

In message , BillR
writes
Moonshine wrote:
It's that time of year when one's thoughts turn to the smoothe
running of ones CH system (sad isn't it!)


So before I try and rectify anything balancing like crazy I want to
know if the UPS 15-50 is powerful enough or not.

I don't know this pump, what head rating is it?


5.1m static

I had similar situation for many years inc boiler kettling at times.
When I changed the pump for the second time I went for a beefer pump with a
6m head.
It runs a lot quieter on its medium setting and the system works much better
too.



--
geoff


  #11   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

I want to balance my CH system at some time over the next few months. What
is an IR thermometer, where did you get it and how much did it cost? I've
been looking out for balancing thermometers but not found any. I notice
the FAQ on the subject was written by someone who used thermometers he
bought from Maplin.

Dougie

  #12   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 22:07:49 +0000, Dougie Nisbet wrote:

I want to balance my CH system at some time over the next few months. What
is an IR thermometer, where did you get it and how much did it cost? I've
been looking out for balancing thermometers but not found any. I notice
the FAQ on the subject was written by someone who used thermometers he
bought from Maplin.

Dougie


Hi Dougie,

IR is InfraRed, it is a non-contact type thermometer that gets a virtually
instantaeous read-out.

The one I got was the one from CPC www.cpc.co.uk

If there is a problem with the link it is Part Number IN0229366

http://custom1.farnell.com/cpc/product.asp?catalog%5Fname=CPC+Catalogue&product%5 Fid=275626

Cost £30+VAT no postage.

Unfortunately I'm in the process of getting a replacement because the Laser
Pointer did not work :-(


  #13   Report Post  
Andy Hall
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 17:21:52 GMT, Moonshine
wrote:


The Boiler is a GlowWorm FuelSaver 55F with a rated output between 35k & 55k
Btu/h. Its anyones guess as to what it has been set to. The manual talks about
putting a suppied self adhesive label by the data plate to record setting but
guess what I can't see one :-)


It doesn't matter greatly - this is a 10-16kW range and I would be
surprised if it is oversized for a house of this size. If you had
said twice this figure then I would have suggested looking further.




Yes it is 8mm Microbore (I put it in the Subject line but should have also
included it in the body text too for clarity sorry)


Sorry, I missed it in the subject line.





Have you checked for sludging?

What is the best way of doing this (i.e. least messy )


Before doing this, another thing to check is the motorised valve(s).
It could be that this is stuck or blocked. Try taking off the head
and turning the cam manually. You can also try operating the manual
lever on the valve. Sometimes the gearing mechanism in the head fails.
Any problems in this area and the general flow to the CH can be poor.
The fix is to replace the valve, which is an easy enough job..


Next, I would go round and open all of the lockshield valves fully and
check behaviour again. It could be that this is problem. If it
isn't, and there is a sludge problem then you will need to open them
all anyway.

To check for sludging and to resolve:

Pick a radiator where it is easy to get some old towels underneath
plus some polythene. A downstairs relatively smaller one is probably
better since fine sludge particles are likely to have collected more
so in lower radiators. You then need some containers to go underneath
each end of the radiator. I bought cat litter trays from the
supermarket. They're cheap, the right height and will take a fair
amount of water. You do need to take some care because sludgy water
is an effective dye.

With the heating off, turn off both valves on said radiator and
carefully undo one of the union nuts to let the water drain into one
tray, then undo the other. If you do it slowly, you can control the
flow easily. Undo the vent as well.
Once the water has stopped trickling out, lift and tip it to one end
and see if sludge comes out. If there is a fair amount, then you
will have pretty dirty water and sludge before this anyway.

Fasten small plastic bags over the radiator tails and take the
radiator outside. Give it a flush through with a mains hose or
pressure washer. With the radiator still off the wall, carefully
open each radiator valve and check that you are getting a respectable
flow of water. There may well be further sludge in the pipes if
there are long horizontal runs, but there should be enough head of
water from the feed tank in the roof (this is open vented system,
yes?) to flush out the pipes.

It will be reasonably clear if sludge has been the problem by this
time. If it is, then you need to repeat the exercise at each
radiator. Finally, give the system a good flush through with clean
water from the roof tank.

By this time, either because you opened the lockshields, resolved a
problem with the motorised valve(s) or with sludge, you should be able
to get reasonable flow on the pump mid and high settings. Before
my heating refurbishment, I had a 15-50 pump on an 8mm system and it
was fine.

If you have done the cleaning exercise, I would then put in some
flushing/cleaning agent and run the system hot for a week. Then
drain and flush again.

Once you've done all of this, then an Alpha pump may help further.
If I had still got the old system I would have replaced my pump with
one. As it was, I have one in my new boiler which is controlled by it
to match the heat output. However, I do have an Alpha on my separate
workshop circuit and that works well. The run from the house to the
workshop is quite long and the pipe resistance higher than for a
circuit purely within the house, so the extra head is a help.

However, before splashing out for one of these, I would check for the
more obvious things that are limiting flow first.



If you have TRVs especially, a better pump option could well be the
Grundfos Alpha. There is a 15-60 model of this which has a 6m max
head as opposed to the 5m of the UPS 15-50. It also adapts its
output to match the resistance requirements.


No TRV's


However, before doing a pump swap, I would check for why the
circulation is poor.




Cheers

Cliff


.andy

To email, substitute .nospam with .gl


..andy

To email, substitute .nospam with .gl
  #14   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 00:57:14 +0000, Andy Hall wrote:

On Tue, 09 Dec 2003 17:21:52 GMT, Moonshine
wrote:


The Boiler is a GlowWorm FuelSaver 55F with a rated output between 35k & 55k
Btu/h. Its anyones guess as to what it has been set to. The manual talks about
putting a suppied self adhesive label by the data plate to record setting but
guess what I can't see one :-)


It doesn't matter greatly - this is a 10-16kW range and I would be
surprised if it is oversized for a house of this size. If you had
said twice this figure then I would have suggested looking further.




Yes it is 8mm Microbore (I put it in the Subject line but should have also
included it in the body text too for clarity sorry)


Sorry, I missed it in the subject line.





Have you checked for sludging?

What is the best way of doing this (i.e. least messy )


Before doing this, another thing to check is the motorised valve(s).
It could be that this is stuck or blocked. Try taking off the head
and turning the cam manually. You can also try operating the manual
lever on the valve. Sometimes the gearing mechanism in the head fails.
Any problems in this area and the general flow to the CH can be poor.
The fix is to replace the valve, which is an easy enough job..


OK this might be an interesting one,could be on to something. I've removed the
operating head off the only motorised value in the past now when it has been
making a bit of a noise to find the valve below stuck. With some gentle
persuasion with pliers I've managed to free the valve. How much should this
turn? It only moves probably less than 1/8 of a turn. What is the correct
proceedure for putting the head back on? Does the motor/spring need to be under
tension? Is there a right and wrong way to turn the head when mating up to the
spindle?

It does not appear possible to just run the CH with the head removed as the
motor continues to turn and the cams cut the pump off on each revolution and
then come back on again, thinking out loud perhaps with the HW switch on it
won't do this.

As it is now the manual overide lever doesn't go under tension in either
direction.



Next, I would go round and open all of the lockshield valves fully and
check behaviour again. It could be that this is problem. If it
isn't, and there is a sludge problem then you will need to open them
all anyway.

To check for sludging and to resolve:

Pick a radiator where it is easy to get some old towels underneath
plus some polythene. A downstairs relatively smaller one is probably
better since fine sludge particles are likely to have collected more
so in lower radiators. You then need some containers to go underneath
each end of the radiator. I bought cat litter trays from the
supermarket. They're cheap, the right height and will take a fair
amount of water. You do need to take some care because sludgy water
is an effective dye.

With the heating off, turn off both valves on said radiator and
carefully undo one of the union nuts to let the water drain into one
tray, then undo the other. If you do it slowly, you can control the
flow easily. Undo the vent as well.
Once the water has stopped trickling out, lift and tip it to one end
and see if sludge comes out. If there is a fair amount, then you
will have pretty dirty water and sludge before this anyway.

Fasten small plastic bags over the radiator tails and take the
radiator outside. Give it a flush through with a mains hose or
pressure washer. With the radiator still off the wall, carefully
open each radiator valve and check that you are getting a respectable
flow of water. There may well be further sludge in the pipes if
there are long horizontal runs, but there should be enough head of
water from the feed tank in the roof (this is open vented system,
yes?) to flush out the pipes.

It will be reasonably clear if sludge has been the problem by this
time. If it is, then you need to repeat the exercise at each
radiator. Finally, give the system a good flush through with clean
water from the roof tank.

By this time, either because you opened the lockshields, resolved a
problem with the motorised valve(s) or with sludge, you should be able
to get reasonable flow on the pump mid and high settings. Before
my heating refurbishment, I had a 15-50 pump on an 8mm system and it
was fine.

If you have done the cleaning exercise, I would then put in some
flushing/cleaning agent and run the system hot for a week. Then
drain and flush again.

Once you've done all of this, then an Alpha pump may help further.
If I had still got the old system I would have replaced my pump with
one. As it was, I have one in my new boiler which is controlled by it
to match the heat output. However, I do have an Alpha on my separate
workshop circuit and that works well. The run from the house to the
workshop is quite long and the pipe resistance higher than for a
circuit purely within the house, so the extra head is a help.

However, before splashing out for one of these, I would check for the
more obvious things that are limiting flow first.



If you have TRVs especially, a better pump option could well be the
Grundfos Alpha. There is a 15-60 model of this which has a 6m max
head as opposed to the 5m of the UPS 15-50. It also adapts its
output to match the resistance requirements.


No TRV's


However, before doing a pump swap, I would check for why the
circulation is poor.




Cheers

Cliff

.andy

To email, substitute .nospam with .gl


.andy

To email, substitute .nospam with .gl


  #15   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Tue, 09 Dec 2003 22:24:15 +0000, Moonshine wrote:



Hi Dougie,

IR is InfraRed, it is a non-contact type thermometer that gets a virtually
instantaeous read-out.

The one I got was the one from CPC www.cpc.co.uk

If there is a problem with the link it is Part Number IN0229366

http://custom1.farnell.com/cpc/product.asp?catalog%5Fname=CPC+Catalogue&product%5 Fid=275626

Cost £30+VAT no postage.


Thanks for responding so quickly. They look very nice. This is gping to
sound dozy but, do you need two, or do you just 'scan' across the ends of
the rad to get the two flow/return readings?

Dougie



  #16   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 00:57:14 +0000, Andy Hall wrote:

[ ... ]



Fasten small plastic bags over the radiator tails and take the radiator
outside. Give it a flush through with a mains hose or pressure washer.


It's the "taking it outside" bit that I found so difficult when I
followed your advice for my system :-) Not so much a DIY job as a DIY and
have a friend handy with big biceps!

Dougie

  #17   Report Post  
Andy Hall
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 09:04:59 GMT, Moonshine
wrote:




OK this might be an interesting one,could be on to something. I've removed the
operating head off the only motorised value in the past now when it has been
making a bit of a noise to find the valve below stuck. With some gentle
persuasion with pliers I've managed to free the valve.


Hmm.. That's concerning. It can sometimes happen after the summer
if the heating has not been on. It shouldn't otherwise. You can
avoid the summer issue by turning the heating on briefly evey week or
so.

How much should this
turn? It only moves probably less than 1/8 of a turn.


I haven't looked at one for a few months, but I think it should move a
bit more than that. There are two main designs. One type has a
kind of cylindrical rotating paddle inside and is generally able to
rotate continuously. The other, which seems to be more common, has a
roughly spherical rubber component inside which is mounted
eccentrically. As this rotates it opens and closes against one port
or the other with a 3way valve and just against the port in a two way
valve. These tend to have restricted travel.


What is the correct
proceedure for putting the head back on? Does the motor/spring need to be under
tension? Is there a right and wrong way to turn the head when mating up to the
spindle?


There is basically a motor and gear train in the head and a big
spring. With power off the spring moves the actuator position to
one end of its travel. With power on, the motor runs the actuator to
the other end and then stalls (it's designed to do this). Basically
with the power off, you manually move the cam on the valve base so
that it will line up with the head as you locate it into place. It
should only go one way.



It does not appear possible to just run the CH with the head removed as the
motor continues to turn and the cams cut the pump off on each revolution and
then come back on again, thinking out loud perhaps with the HW switch on it
won't do this.

As it is now the manual overide lever doesn't go under tension in either
direction.


It sounds like the spring might have gone or possibly part of the gear
train has stripped because the valve base was stuck.

Normally, with the power off you should be able to slide the lever and
operate the valve, then latch the lever at the far end of the travel
in a notch in the case of the head. If you release it then it should
return under spring tension.

You probably would be able to fool the system by having the valve head
off of the base and creating a hot water demand, as you say, Then
operate the cam on the valve base to the CH position.

If it then works OK, I think that pretty much you will have diagnosed
a faulty head. They are easy to change, but note the wiring
connections.

Since you have been having valve sticking problems, I would replace
the valve base as well. You can buy the complete thing pretty
cheaply.




..andy

To email, substitute .nospam with .gl
  #18   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 09:37:14 +0000, Dougie Nisbet wrote:

On Tue, 09 Dec 2003 22:24:15 +0000, Moonshine wrote:



Hi Dougie,

IR is InfraRed, it is a non-contact type thermometer that gets a virtually
instantaeous read-out.

The one I got was the one from CPC www.cpc.co.uk

If there is a problem with the link it is Part Number IN0229366

http://custom1.farnell.com/cpc/product.asp?catalog%5Fname=CPC+Catalogue&product%5 Fid=275626

Cost £30+VAT no postage.


Thanks for responding so quickly. They look very nice. This is gping to
sound dozy but, do you need two, or do you just 'scan' across the ends of
the rad to get the two flow/return readings?

Dougie


No worries I asked the same question myself :-) No only one needed the reading
is that quick.
  #19   Report Post  
David Hearn
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system


"Dougie Nisbet" wrote in message
news
On Wed, 10 Dec 2003 00:57:14 +0000, Andy Hall wrote:

[ ... ]



Fasten small plastic bags over the radiator tails and take the radiator
outside. Give it a flush through with a mains hose or pressure

washer.

It's the "taking it outside" bit that I found so difficult when I
followed your advice for my system :-) Not so much a DIY job as a DIY and
have a friend handy with big biceps!


Yep, especially with our 9' double radiator. We actually needed 4 people to
move it, and that was with it drained (though sludgy). Even the smaller
1.2m doubles were quite heavy - I'd hate to have tried moving it with water
in!

D


  #20   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 10:04:15 +0000, Moonshine wrote:

On Wed, 10 Dec 2003 09:37:14 +0000, Dougie Nisbet wrote:

[quoted text muted]


No worries I asked the same question myself :-) No only one needed the reading
is that quick.


Nice. Ordering one right now!

Dougie



  #21   Report Post  
IMM
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system


"Andy Hall" wrote in message
news
On Wed, 10 Dec 2003 09:04:59 GMT, Moonshine
wrote:


OK this might be an interesting one,could be on to something. I've

removed the
operating head off the only motorised value in the past now when it has

been
making a bit of a noise to find the valve below stuck. With some gentle
persuasion with pliers I've managed to free the valve.


Hmm.. That's concerning. It can sometimes happen after the summer
if the heating has not been on. It shouldn't otherwise. You can
avoid the summer issue by turning the heating on briefly evey week or
so.


Using the correct inhibitor lubricates as well, reducing this sort of thing.




---
--

Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.548 / Virus Database: 341 - Release Date: 05/12/2003


  #22   Report Post  
Andy Hall
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 09:41:29 +0000, Dougie Nisbet
wrote:

On Wed, 10 Dec 2003 00:57:14 +0000, Andy Hall wrote:

[ ... ]



Fasten small plastic bags over the radiator tails and take the radiator
outside. Give it a flush through with a mains hose or pressure washer.


It's the "taking it outside" bit that I found so difficult when I
followed your advice for my system :-) Not so much a DIY job as a DIY and
have a friend handy with big biceps!

Dougie



Well.... you wouldn't want to pressure wash it in your living room,
would you ;-). That would remind me of the way that Mr Bean does
the decorating.



..andy

To email, substitute .nospam with .gl
  #23   Report Post  
Moonshine
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

On Wed, 10 Dec 2003 09:48:11 +0000, Andy Hall wrote:

On Wed, 10 Dec 2003 09:04:59 GMT, Moonshine
wrote:




OK this might be an interesting one,could be on to something. I've removed the
operating head off the only motorised value in the past now when it has been
making a bit of a noise to find the valve below stuck. With some gentle
persuasion with pliers I've managed to free the valve.


Hmm.. That's concerning. It can sometimes happen after the summer
if the heating has not been on. It shouldn't otherwise. You can
avoid the summer issue by turning the heating on briefly evey week or
so.

How much should this
turn? It only moves probably less than 1/8 of a turn.


I haven't looked at one for a few months, but I think it should move a
bit more than that. There are two main designs. One type has a
kind of cylindrical rotating paddle inside and is generally able to
rotate continuously. The other, which seems to be more common, has a
roughly spherical rubber component inside which is mounted
eccentrically. As this rotates it opens and closes against one port
or the other with a 3way valve and just against the port in a two way
valve. These tend to have restricted travel.


What is the correct
proceedure for putting the head back on? Does the motor/spring need to be under
tension? Is there a right and wrong way to turn the head when mating up to the
spindle?


There is basically a motor and gear train in the head and a big
spring. With power off the spring moves the actuator position to
one end of its travel. With power on, the motor runs the actuator to
the other end and then stalls (it's designed to do this). Basically
with the power off, you manually move the cam on the valve base so
that it will line up with the head as you locate it into place. It
should only go one way.



It does not appear possible to just run the CH with the head removed as the
motor continues to turn and the cams cut the pump off on each revolution and
then come back on again, thinking out loud perhaps with the HW switch on it
won't do this.

As it is now the manual overide lever doesn't go under tension in either
direction.


It sounds like the spring might have gone or possibly part of the gear
train has stripped because the valve base was stuck.

Normally, with the power off you should be able to slide the lever and
operate the valve, then latch the lever at the far end of the travel
in a notch in the case of the head. If you release it then it should
return under spring tension.

You probably would be able to fool the system by having the valve head
off of the base and creating a hot water demand, as you say, Then
operate the cam on the valve base to the CH position.

If it then works OK, I think that pretty much you will have diagnosed
a faulty head. They are easy to change, but note the wiring
connections.

Since you have been having valve sticking problems, I would replace
the valve base as well. You can buy the complete thing pretty
cheaply.




.andy

To email, substitute .nospam with .gl



OK I've checked with the neighbour and their's is the Grundfos UPS 15-50 too, so
my memory is obviously playing up and it was in the last house that I must have
changed it! So hopefully it has been properly spec'd for the job.

Also confirmed that their's is set on max speed, and I would imagine they
wouldn't have tinkered with it like me :-)

I've done some more research on the Valve and its a Honeywell V4073A Motorised
Mid-Position Valve. Which according to the spec sheet does only have between
10&15 degrees of spindle movement.

I haven't got my thermometer at the moment, but I could swear since giving the
spindle a good wiggle with pliers the rads "smell" hotter.

Would I be right in thinking that in a correctly spec'd and configured CH
system, the boiler should really be running pretty much continuosly if the room
stat is demanding heat?


  #24   Report Post  
Christian McArdle
 
Posts: n/a
Default Is Grundfos ups 15-50 man enough for 15 year old 4 bed detached 8mm Microbore CH system

Would I be right in thinking that in a correctly spec'd and configured
CH system, the boiler should really be running pretty much continuosly
if the room stat is demanding heat?


Only with a boiler with a modulating burner. A boiler with a fixed output
rate can't possibly be expected to be perfectly matched to the conditions
and outside temperature etc. every day of the heating system. Rather than
modulating down, such a boiler will cycle. However, provided it isn't too
overpowered and the pump is fast enough, the cycling should be reasonably
long in period. Not on for a minute and off for a minute.

Christian.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Closed system open system raditors Adam Topp UK diy 6 September 16th 03 06:14 PM
Radiators and CH system... Christian McArdle UK diy 4 September 2nd 03 04:10 PM
Please help - to microbore or not...? Rebecca UK diy 17 August 21st 03 04:05 PM
mains Hot water, and do I convert open heating to a closed heating system Ian Tracey UK diy 5 July 18th 03 09:55 AM


All times are GMT +1. The time now is 06:34 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"