My elderly father has just bought a new AEG-Electrolux washer-drier. It
was delivered yesterday and I helped him get it installed and working.
While adjusting the feet with my hand between the casing and the
concrete floor I noticed a distinct tingling, until I disconnected the
machine from the mains. I thought that was odd, and wondered if the
earth connection was not quite right. But I was running late and keen
to get home, so didn't follow it up at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his
faculties aren't as acute as they were, he's a retired electrician so
fully aware of the difference between a mild and a more serious electric
shock. From his description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place
for maybe 30-40 years, so it might have a corroded earth connection -
something I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can
be plugged into somewhere else in the adjacent kitchen, which ought to
be ok. If the leak between live and the metal casing of the machine is
really large it ought to blow a fuse or two when properly earthed.

Appliances like washing machines are clearly designed to be used when
earthed properly, but I assume they must be designed to be reasonably
safe even when accidentally used without a proper earth connection. Does
anyone know if there are rules on how much current can be allowed to
leak from live to the metal casing?

Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if
one gets a detectable shock from it?


--
Clive Page
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default Electric shocks from new washing machine

On Nov 17, 9:38*pm, Clive Page wrote:
Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if
one gets a detectable shock from it?


If the earth is broken or high impedance, the mains filter will
create a low current (up to 1.5mA) leak to the machine's case.

The fault is thus with the lack of earthing since the
machine is probably class-1 ("Must Be Earthed").

Check the earth continuity for that final circuit, check MEB
is present & correct, check supplementary bonding etc. If
the area is prone to damp, solid floor, perhaps add RCD.

Also, use new hoses not any old original (they fail eventually :-)
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Electric shocks from new washing machine

on 17/11/2009, Clive Page supposed :
My elderly father has just bought a new AEG-Electrolux washer-drier. It was
delivered yesterday and I helped him get it installed and working. While
adjusting the feet with my hand between the casing and the concrete floor I
noticed a distinct tingling, until I disconnected the machine from the mains.
I thought that was odd, and wondered if the earth connection was not quite
right. But I was running late and keen to get home, so didn't follow it up
at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his faculties
aren't as acute as they were, he's a retired electrician so fully aware of
the difference between a mild and a more serious electric shock. From his
description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place for
maybe 30-40 years, so it might have a corroded earth connection - something
I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be ok.
If the leak between live and the metal casing of the machine is really large
it ought to blow a fuse or two when properly earthed.

Appliances like washing machines are clearly designed to be used when earthed
properly, but I assume they must be designed to be reasonably safe even when
accidentally used without a proper earth connection. Does anyone know if
there are rules on how much current can be allowed to leak from live to the
metal casing?

Also - even if it turns out to be badly earthed, is there a case to be made
that the machine is faulty and should be replaced by the shop if one gets a
detectable shock from it?


The shock could have been from a fault where by the ground is live and
the casing of the washer is properly earthed - just something to keep
in mind.

Now assuming the more likely shock from the case of the machine.
Machine these days are microprocessor controlled, so it will have a
filter on its mains input. The filter has some leakage to its earth
connection and if the machine lacks a proper earth, it would then be
possible to get a slight shock by touching the case and a ground.

Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 36
Default Electric shocks from new washing machine


"Clive Page" wrote in message
...
My elderly father has just bought a new AEG-Electrolux washer-drier. It
was delivered yesterday and I helped him get it installed and working.
While adjusting the feet with my hand between the casing and the concrete
floor I noticed a distinct tingling, until I disconnected the machine from
the mains. I thought that was odd, and wondered if the earth connection
was not quite right. But I was running late and keen to get home, so
didn't follow it up at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his
faculties aren't as acute as they were, he's a retired electrician so
fully aware of the difference between a mild and a more serious electric
shock. From his description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place for
maybe 30-40 years, so it might have a corroded earth connection -
something I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be ok.
If the leak between live and the metal casing of the machine is really
large it ought to blow a fuse or two when properly earthed.


The fault is with his socket and/or house wiring.


Appliances like washing machines are clearly designed to be used when
earthed properly, but I assume they must be designed to be reasonably safe
even when accidentally used without a proper earth connection. Does anyone
know if there are rules on how much current can be allowed to leak from
live to the metal casing?


You should not use the appliance without having the wiring fault in the
house
rectified. You could kill him by not acting.


Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if one
gets a detectable shock from it?


Why would a shop replace a new product because a person chose to use it with
faulty and/or unsafe
sockets and/or wiring in a house?



--
Clive Page



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 36
Default Electric shocks from new washing machine


"Harry Bloomfield" wrote in message
. uk...
on 17/11/2009, Clive Page supposed :
My elderly father has just bought a new AEG-Electrolux washer-drier. It
was delivered yesterday and I helped him get it installed and working.
While adjusting the feet with my hand between the casing and the concrete
floor I noticed a distinct tingling, until I disconnected the machine
from the mains. I thought that was odd, and wondered if the earth
connection was not quite right. But I was running late and keen to get
home, so didn't follow it up at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his
faculties aren't as acute as they were, he's a retired electrician so
fully aware of the difference between a mild and a more serious electric
shock. From his description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place
for maybe 30-40 years, so it might have a corroded earth connection -
something I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be
ok. If the leak between live and the metal casing of the machine is
really large it ought to blow a fuse or two when properly earthed.

Appliances like washing machines are clearly designed to be used when
earthed properly, but I assume they must be designed to be reasonably
safe even when accidentally used without a proper earth connection. Does
anyone know if there are rules on how much current can be allowed to leak
from live to the metal casing?

Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if one
gets a detectable shock from it?


The shock could have been from a fault where by the ground is live and the
casing of the washer is properly earthed - just something to keep in mind.

Now assuming the more likely shock from the case of the machine. Machine
these days are microprocessor controlled, so it will have a filter on its
mains input. The filter has some leakage to its earth connection and if
the machine lacks a proper earth, it would then be possible to get a
slight shock by touching the case and a ground.

Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.

--
Regards,
Harry (M1BYT) (L)



Good advice, i have seen this so many times with old and damaged wiring.
The best was someone who had a firework display using a washing machine
and also had incredible electric shocks reaching in to a chest freezer.
It is the socket and/or wiring in the house that is faulty. It seems stupid
to
ask about changing a product but leaving faulty wiring and/or sockets!
Buy a socket tester, then get it sorted before you see the person killed.
I saw one person who had a wiring fault after he touched both taps to
put water in a sink, he was dead as the current flowed up one arm and down
the other. Others I have seen with some nasty burns, one person even
jumped backwards and hit a worktop with a knife on it! Cuts and burns
are easier to treat - bringing someone back to life is a touch more
difficult.




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,040
Default Electric shocks from new washing machine

Roger wrote:


Good advice, i have seen this so many times


Doubtful. More words of "advice" from our resident ****.

--
Adrian C
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Electric shocks from new washing machine

on 17/11/2009, Adrian C supposed :
Roger wrote:


Good advice, i have seen this so many times


Doubtful. More words of "advice" from our resident ****.


Have you some less doubtful advice to offer, or do you just like to
hide behind a keyboard spouting drivel?

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,040
Default Electric shocks from new washing machine

Harry Bloomfield wrote:
on 17/11/2009, Adrian C supposed :
Roger wrote:


Good advice, i have seen this so many times


Doubtful. More words of "advice" from our resident ****.


Have you some less doubtful advice to offer, or do you just like to hide
behind a keyboard spouting drivel?


Roger, you've got yourself a friend!

--
Adrian C
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Electric shocks from new washing machine


"Roger" wrote in message
...

"Harry Bloomfield" wrote in message
. uk...
on 17/11/2009, Clive Page supposed :
My elderly father has just bought a new AEG-Electrolux washer-drier. It
was delivered yesterday and I helped him get it installed and working.
While adjusting the feet with my hand between the casing and the
concrete floor I noticed a distinct tingling, until I disconnected the
machine from the mains. I thought that was odd, and wondered if the
earth connection was not quite right. But I was running late and keen
to get home, so didn't follow it up at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his
faculties aren't as acute as they were, he's a retired electrician so
fully aware of the difference between a mild and a more serious electric
shock. From his description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place
for maybe 30-40 years, so it might have a corroded earth connection -
something I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can
be plugged into somewhere else in the adjacent kitchen, which ought to
be ok. If the leak between live and the metal casing of the machine is
really large it ought to blow a fuse or two when properly earthed.

Appliances like washing machines are clearly designed to be used when
earthed properly, but I assume they must be designed to be reasonably
safe even when accidentally used without a proper earth connection. Does
anyone know if there are rules on how much current can be allowed to
leak from live to the metal casing?

Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if
one gets a detectable shock from it?


The shock could have been from a fault where by the ground is live and
the casing of the washer is properly earthed - just something to keep in
mind.

Now assuming the more likely shock from the case of the machine. Machine
these days are microprocessor controlled, so it will have a filter on its
mains input. The filter has some leakage to its earth connection and if
the machine lacks a proper earth, it would then be possible to get a
slight shock by touching the case and a ground.

Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.

--
Regards,
Harry (M1BYT) (L)



Good advice, i have seen this so many times with old and damaged wiring.
The best was someone who had a firework display using a washing machine
and also had incredible electric shocks reaching in to a chest freezer.
It is the socket and/or wiring in the house that is faulty. It seems
stupid to
ask about changing a product but leaving faulty wiring and/or sockets!
Buy a socket tester, then get it sorted before you see the person killed.
I saw one person who had a wiring fault after he touched both taps to
put water in a sink, he was dead as the current flowed up one arm and down
the other. Others I have seen with some nasty burns, one person even
jumped backwards and hit a worktop with a knife on it! Cuts and burns
are easier to treat - bringing someone back to life is a touch more
difficult.

Paramedics see far less deaths and injury due to electrical faults than you
have!

I have seen some bad wiring faults in my time but they have caused no
deaths.

I did see a worktop with a knife on it last week. I forgot to inform the
emergency services as I was busy washing up at the time.

Roger



..


  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Electric shocks from new washing machine


"Harry Bloomfield" wrote in message
. uk...
on 17/11/2009, Clive Page supposed :
My elderly father has just bought a new AEG-Electrolux washer-drier. It
was delivered yesterday and I helped him get it installed and working.
While adjusting the feet with my hand between the casing and the concrete
floor I noticed a distinct tingling, until I disconnected the machine
from the mains. I thought that was odd, and wondered if the earth
connection was not quite right. But I was running late and keen to get
home, so didn't follow it up at the time, unfortunately.

This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. Although his
faculties aren't as acute as they were, he's a retired electrician so
fully aware of the difference between a mild and a more serious electric
shock. From his description over the phone, it sounded like the latter.

The machine is in a back porch, and the mains socket has been in place
for maybe 30-40 years, so it might have a corroded earth connection -
something I'll obviously follow up as soon as I can.

Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be
ok. If the leak between live and the metal casing of the machine is
really large it ought to blow a fuse or two when properly earthed.

Appliances like washing machines are clearly designed to be used when
earthed properly, but I assume they must be designed to be reasonably
safe even when accidentally used without a proper earth connection. Does
anyone know if there are rules on how much current can be allowed to leak
from live to the metal casing?

Also - even if it turns out to be badly earthed, is there a case to be
made that the machine is faulty and should be replaced by the shop if one
gets a detectable shock from it?


The shock could have been from a fault where by the ground is live and the
casing of the washer is properly earthed - just something to keep in mind.

Now assuming the more likely shock from the case of the machine. Machine
these days are microprocessor controlled, so it will have a filter on its
mains input. The filter has some leakage to its earth connection and if
the machine lacks a proper earth, it would then be possible to get a
slight shock by touching the case and a ground.





Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.



Indeed. Unplug the machine until the socket is tested.

Adam



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 229
Default Electric shocks from new washing machine

In message , Roger
writes
It is the socket and/or wiring in the house that is faulty. It seems stupid
to
ask about changing a product but leaving faulty wiring and/or sockets!
Buy a socket tester, then get it sorted before you see the person killed.
I saw one person who had a wiring fault after he touched both taps to
put water in a sink, he was dead as the current flowed up one arm and down
the other. Others I have seen with some nasty burns, one person even
jumped backwards and hit a worktop with a knife on it! Cuts and burns
are easier to treat - bringing someone back to life is a touch more
difficult.


Well as I said in my original posting, obviously I suspect the house
wiring and have told him to use it only when plugged into a different
socket until that one has been checked and fixed.

I was surprised about the leakage from mains to earth in the appliance,
but others suggested that modern appliances have a mains filter which
has that effect. Thanks - that's news to me, though maybe I should have
guessed.

I suppose one could think of the effects of that leakage as a useful
warning: if you plug the washing machine into a socket with a poor earth
the shocks you get warn you that something is wrong. The old one, now
defunct, didn't do that.


--
Clive Page
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,319
Default Electric shocks from new washing machine

ARWadsworth wrote:
"Roger" wrote in message

SNIP

Good advice, i have seen this so many times with old and damaged
wiring. The best was someone who had a firework display using a
washing machine and also had incredible electric shocks reaching in
to a chest freezer. It is the socket and/or wiring in the house that
is faulty. It seems stupid to
ask about changing a product but leaving faulty wiring and/or
sockets! Buy a socket tester, then get it sorted before you see the
person killed. I saw one person who had a wiring fault after he
touched both taps to put water in a sink, he was dead as the current
flowed up one arm
and down the other. Others I have seen with some nasty burns, one
person even jumped backwards and hit a worktop with a knife on it! Cuts
and burns are easier to treat - bringing someone back to life
is a touch more difficult.

Paramedics see far less deaths and injury due to electrical faults
than you have!


Just asked my paramedic daughter about that. In 4 years of frontline duty
she has attended just 2 cases of electric shock. One was a bloke who was
woken by a mains smoke alarm. To silence it, he stood on some metal kitchen
steps (barefoot) and used a pair of metal kitchen scissors to cut the cable.
He also managed to stab himself in the leg - twice - whilst falling off the
steps :-)

Thats a brain fault, not an electrical fault. The other one was faulty
wiring.


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk




  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Electric shocks from new washing machine


"The Medway Handyman" wrote in message
...
ARWadsworth wrote:
"Roger" wrote in message

SNIP

Good advice, i have seen this so many times with old and damaged
wiring. The best was someone who had a firework display using a
washing machine and also had incredible electric shocks reaching in
to a chest freezer. It is the socket and/or wiring in the house that
is faulty. It seems stupid to
ask about changing a product but leaving faulty wiring and/or
sockets! Buy a socket tester, then get it sorted before you see the
person killed. I saw one person who had a wiring fault after he
touched both taps to put water in a sink, he was dead as the current
flowed up one arm
and down the other. Others I have seen with some nasty burns, one
person even jumped backwards and hit a worktop with a knife on it! Cuts
and burns are easier to treat - bringing someone back to life
is a touch more difficult.

Paramedics see far less deaths and injury due to electrical faults
than you have!


Just asked my paramedic daughter about that. In 4 years of frontline duty
she has attended just 2 cases of electric shock. One was a bloke who was
woken by a mains smoke alarm. To silence it, he stood on some metal
kitchen steps (barefoot) and used a pair of metal kitchen scissors to cut
the cable. He also managed to stab himself in the leg - twice - whilst
falling off the steps :-)

Thats a brain fault, not an electrical fault. The other one was faulty
wiring.


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk



It might be a brainfault but it is bloody priceless:-)

Adam


  #14   Report Post  
Posted to uk.d-i-y
GMM GMM is offline
external usenet poster
 
Posts: 488
Default Electric shocks from new washing machine

On 17 Nov, 22:02, Harry Bloomfield
wrote:
on 17/11/2009, Clive Page supposed :





My elderly father has just bought a new AEG-Electrolux washer-drier. *It was
delivered yesterday and I helped him get it installed and working. While
adjusting the feet with my hand between the casing and the concrete floor I
noticed a distinct tingling, until I disconnected the machine from the mains.
*I thought that was odd, and wondered if the earth connection was not quite
right. *But I was running late and keen to get home, so didn't follow it up
at the time, unfortunately.


This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. *Although his faculties
aren't as acute as they were, he's a retired electrician so fully aware of
the difference between a mild and a more serious electric shock. *From his
description over the phone, it sounded like the latter.


The machine is in a back porch, and the mains socket has been in place for
maybe 30-40 years, so it might have a corroded earth connection - something
I'll obviously follow up as soon as I can.


Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be ok. *
If the leak between live and the metal casing of the machine is really large
it ought to blow a fuse or two when properly earthed.


Appliances like washing machines are clearly designed to be used when earthed
properly, but I assume they must be designed to be reasonably safe even when
accidentally used without a proper earth connection. Does anyone know if
there are rules on how much current can be allowed to leak from live to the
metal casing?


Also - even if it turns out to be badly earthed, is there a case to be made
that the machine is faulty and should be replaced by the shop if one gets a
detectable shock from it?


The shock could have been from a fault where by the ground is live and
the casing of the washer is properly earthed - just something to keep
in mind.

Now assuming the more likely shock from the case of the machine.
Machine these days are microprocessor controlled, so it will have a
filter on its mains input. The filter has some leakage to its earth
connection and if the machine lacks a proper earth, it would then be
possible to get a slight shock by touching the case and a ground.

Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.

--
Regards,
* * * * Harry (M1BYT) (L)http://www.ukradioamateur.co.uk


That's interesting: Never knew that before but wouldn't earth leakage
like that trip an RCD, ie take out any newly wired house? Or am I
misunderstanding something (which is always very likely!)
  #15   Report Post  
Posted to uk.d-i-y
GMM GMM is offline
external usenet poster
 
Posts: 488
Default Electric shocks from new washing machine

On 18 Nov, 11:10, "The Medway Handyman"
wrote:
ARWadsworth wrote:
"Roger" wrote in message


SNIP





Good advice, i have seen this so many times with old and damaged
wiring. The best was someone who had a firework display using a
washing machine and also had incredible electric shocks reaching in
to a chest freezer. It is the socket and/or wiring in the house that
is faulty. *It seems stupid to
ask about changing a product but leaving faulty wiring and/or
sockets! Buy a socket tester, then get it sorted before you see the
person killed. I saw one person who had a wiring fault after he
touched both taps to put water in a sink, he was dead as the current
flowed up one arm
and down the other. *Others I have seen with some nasty burns, one
person even jumped backwards and hit a worktop with a knife on it! Cuts
and burns are easier to treat - bringing someone back to life
is a touch more difficult.


Paramedics see far less deaths and injury due to electrical faults
than you have!


Just asked my paramedic daughter about that. *In 4 years of frontline duty
she has attended just 2 cases of electric shock. *One was a bloke who was
woken by a mains smoke alarm. *To silence it, he stood on some metal kitchen
steps (barefoot) and used a pair of metal kitchen scissors to cut the cable.
He also managed to stab himself in the leg - twice - whilst falling off the
steps :-)

Thats a brain fault, not an electrical fault. *The other one was faulty
wiring.

--
Dave - The Medway Handymanwww.medwayhandyman.co.uk


You never never have a video camera handy when you need one - He could
have become a youtube star......


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 895
Default Electric shocks from new washing machine

On Wed, 18 Nov 2009 09:18:51 -0800 (PST), GMM
wrote:

On 17 Nov, 22:02, Harry Bloomfield
wrote:
on 17/11/2009, Clive Page supposed :





My elderly father has just bought a new AEG-Electrolux washer-drier. *It was
delivered yesterday and I helped him get it installed and working. While
adjusting the feet with my hand between the casing and the concrete floor I
noticed a distinct tingling, until I disconnected the machine from the mains.
*I thought that was odd, and wondered if the earth connection was not quite
right. *But I was running late and keen to get home, so didn't follow it up
at the time, unfortunately.


This evening my father phoned me to say he got a distinct shock from the
metal barrel when unloading a new batch of clothes. *Although his faculties
aren't as acute as they were, he's a retired electrician so fully aware of
the difference between a mild and a more serious electric shock. *From his
description over the phone, it sounded like the latter.


The machine is in a back porch, and the mains socket has been in place for
maybe 30-40 years, so it might have a corroded earth connection - something
I'll obviously follow up as soon as I can.


Meanwhile I told him to try the machine on an extension lead so it can be
plugged into somewhere else in the adjacent kitchen, which ought to be ok. *
If the leak between live and the metal casing of the machine is really large
it ought to blow a fuse or two when properly earthed.


Appliances like washing machines are clearly designed to be used when earthed
properly, but I assume they must be designed to be reasonably safe even when
accidentally used without a proper earth connection. Does anyone know if
there are rules on how much current can be allowed to leak from live to the
metal casing?


Also - even if it turns out to be badly earthed, is there a case to be made
that the machine is faulty and should be replaced by the shop if one gets a
detectable shock from it?


The shock could have been from a fault where by the ground is live and
the casing of the washer is properly earthed - just something to keep
in mind.

Now assuming the more likely shock from the case of the machine.
Machine these days are microprocessor controlled, so it will have a
filter on its mains input. The filter has some leakage to its earth
connection and if the machine lacks a proper earth, it would then be
possible to get a slight shock by touching the case and a ground.

Most likely scenario is the the socket you have plugged the washer in,
lacks an effective earth. Attend to it as a matter of urgency.

--
Regards,
* * * * Harry (M1BYT) (L)http://www.ukradioamateur.co.uk


That's interesting: Never knew that before but wouldn't earth leakage
like that trip an RCD, ie take out any newly wired house? Or am I
misunderstanding something (which is always very likely!)



The original poster did say that the wiring had been in place for
30-40 years (you quoted the text, above). So it is quite likely that
no RCD was fitted.

  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Electric shocks from new washing machine

GMM explained :
That's interesting: Never knew that before but wouldn't earth leakage
like that trip an RCD, ie take out any newly wired house? Or am I
misunderstanding something (which is always very likely!)


The leakage has to be of a sufficient value, before the RCD will trip.
Filters, though of sufficient leakage to provide a mild shock, do not
provide enough leakage to trip the RCD. The exception is when a number
of the filters are used on the same circuit, where the leakage adds up
and can be enough to cause a trip, or cause nuisance tripping.

--
Regards,
Harry (M1BYT) (L)
http://www.ukradioamateur.co.uk


  #18   Report Post  
Posted to uk.d-i-y
GMM GMM is offline
external usenet poster
 
Posts: 488
Default Electric shocks from new washing machine

On 18 Nov, 17:30, Harry Bloomfield
wrote:
GMM explained :

That's interesting: *Never knew that before but wouldn't earth leakage
like that trip an RCD, ie take out any newly wired house? *Or am I
misunderstanding something (which is always very likely!)


The leakage has to be of a sufficient value, before the RCD will trip.
Filters, though of sufficient leakage to provide a mild shock, do not
provide enough leakage to trip the RCD. The exception is when a number
of the filters are used on the same circuit, where the leakage adds up
and can be enough to cause a trip, or cause nuisance tripping.

--
Regards,
* * * * Harry (M1BYT) (L)http://www.ukradioamateur.co.uk


Very interesting - it sounds like there's a bit of a tension between
the technologies here. Maybe I should stick with the old re-wireable
fusebox with a few nails in place of the fuse wires after all!
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Electric shocks from new washing machine

In article ,
The Medway Handyman wrote:
Just asked my paramedic daughter about that. In 4 years of frontline
duty she has attended just 2 cases of electric shock. One was a bloke
who was woken by a mains smoke alarm. To silence it, he stood on some
metal kitchen steps (barefoot) and used a pair of metal kitchen
scissors to cut the cable. He also managed to stab himself in the leg -
twice - whilst falling off the steps :-)


My long dead mother did something similar in the early stages of
Alzheimer's. She couldn't remember how to stop her electric alarm clock
from buzzing so cut the flex with scissors. Luckily only suffered a minor
burn. The alarm was on one of those pukka clock sockets which need a nut
removed before they can be unplugged.

--
*White with a hint of M42*

Dave Plowman London SW
To e-mail, change noise into sound.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric shocks-How long to wait before you call an electrician ARWadsworth UK diy 107 May 6th 09 12:24 PM
washing machine steve20 Home Repair 1 September 29th 06 04:05 PM
Electric shocks (was: 100V appliance on 110v power supply) TJ Hertz Electronics 19 June 3rd 05 11:22 PM
Electric shocks from computer case NickW UK diy 3 August 7th 04 10:03 AM
Washing machine not washing Carl Home Repair 2 March 6th 04 05:32 PM


All times are GMT +1. The time now is 06:31 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"