Home |
Search |
Today's Posts |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
Hi All,
We are building a house with wet underfloor heating which goes back to 2 control units, which have all the wiring completed, only leaving 2 wires from each unit going back to the boiler (volt free). the boiler has now been installed (Worcester Greenstar 12/18) which I could not find any volt free connections, I spoke with Worcester bosch technical today and all they could tell me was that the boiler doesn`t have the appropriate connections, but could not tell me how I could resolve this problem. Anyone shed any light???. |
#2
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Fri, 02 Jan 2009 10:55:10 -0800, yekal_tytwr wrote:
Hi All, We are building a house with wet underfloor heating which goes back to 2 control units, which have all the wiring completed, only leaving 2 wires from each unit going back to the boiler (volt free). the boiler has now been installed (Worcester Greenstar 12/18) Is that an oil boiler? I don't recognise the model name as a gas one. ... which I could not find any volt free connections, I spoke with Worcester bosch technical today and all they could tell me was that the boiler doesn`t have the appropriate connections, but could not tell me how I could resolve this problem. Anyone shed any light???. Not sure what your UFH control units require. You say they want volt-free connections but not whether the connection is a signal from the boiler to the UFH controller or the other way. If the former maybe the UFH controller has its own mains power for its pump and just needs a contact closure to tell it to run the pump. In that case I'd be thinking along the lines of fitting a pipe thermostat to the boiler's flow pipe to tell the UFH when there's heat coming from the boiler. Alternatively if the volt-free connection is a signal /from/ the UFH controller /to/ the boiler from a set of contacts in the controller, then I'd think along the lines of connecting across the boiler's LS and LR terminals. I think you really need to scan and post the UFH instructions somewhere for us all to see (or point us to the mfr's docs online). -- John Stumbles -- http://yaph.co.uk A: Because it messes up the order in which people read text. Q: Why is top-posting a bad thing? |
#3
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Jan 2, 9:21*pm, YAPH wrote:
On Fri, 02 Jan 2009 10:55:10 -0800, yekal_tytwr wrote: Hi All, * *We are building a house with wet underfloor heating which goes back to 2 control units, which have all the wiring completed, only leaving 2 wires from each unit going back to the boiler *(volt free). the boiler has now been installed (Worcester Greenstar 12/18) Is that an oil boiler? I don't recognise the model name as a gas one. Yes this is an oil condensing boiler ... which I could not find any volt free connections, I spoke with Worcester bosch technical today and all they could tell me was that the boiler doesn`t have the appropriate connections, but could not tell me how I could resolve this problem. * *Anyone shed any light???. Not sure what your UFH control units require. You say they want volt-free connections but not whether the connection is a signal from the boiler to the UFH controller or the other way. If the former maybe the UFH controller has its own mains power for its pump and just needs a contact closure to tell it to run the pump. In that case I'd be thinking along the lines of fitting a pipe thermostat to the boiler's flow pipe to tell the UFH when there's heat coming from the boiler. Alternatively if the volt-free connection is a signal /from/ the UFH controller /to/ the boiler from a set of contacts in the controller, then I'd think along the lines of connecting across the boiler's LS and LR terminals. I think you really need to scan and post the UFH instructions somewhere for us all to see (or point us to the mfr's docs online). thanks for your reply , I can`t work out if it is possible to post the wiring diagrams on here, would you mind if I email them to you?. -- John Stumbles *-- *http://yaph.co.uk A: Because it messes up the order in which people read text. Q: Why is top-posting a bad thing? |
#4
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
Yekal wrote:
On Jan 2, 9:21 pm, YAPH wrote: On Fri, 02 Jan 2009 10:55:10 -0800, yekal_tytwr wrote: Hi All, We are building a house with wet underfloor heating which goes back to 2 control units, which have all the wiring completed, only leaving 2 wires from each unit going back to the boiler (volt free). the boiler has now been installed (Worcester Greenstar 12/18) Is that an oil boiler? I don't recognise the model name as a gas one. Yes this is an oil condensing boiler ... which I could not find any volt free connections, I spoke with Worcester bosch technical today and all they could tell me was that the boiler doesn`t have the appropriate connections, but could not tell me how I could resolve this problem. Anyone shed any light???. Not sure what your UFH control units require. You say they want volt-free connections but not whether the connection is a signal from the boiler to the UFH controller or the other way. If the former maybe the UFH controller has its own mains power for its pump and just needs a contact closure to tell it to run the pump. In that case I'd be thinking along the lines of fitting a pipe thermostat to the boiler's flow pipe to tell the UFH when there's heat coming from the boiler. Alternatively if the volt-free connection is a signal /from/ the UFH controller /to/ the boiler from a set of contacts in the controller, then I'd think along the lines of connecting across the boiler's LS and LR terminals. I think you really need to scan and post the UFH instructions somewhere for us all to see (or point us to the mfr's docs online). thanks for your reply , I can`t work out if it is possible to post the wiring diagrams on here, would you mind if I email them to you?. -- John Stumbles -- http://yaph.co.uk A: Because it messes up the order in which people read text. Q: Why is top-posting a bad thing? Scan - or photograph the picture[s] using a digital camera and upload them to www.tinypic.com, give a 'Tag' (or name) and then post the IMG Code for Forums & Message Boards link to the group. Example below (it works if you want to view the image): Note: leave out the [IMG] either side and post link thus: http://i44.tinypic.com/25gavxt.jpg - note the coloured and underlined text that indicates a valid link. Hope this helps Cash |
#5
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Jan 2, 11:07*pm, "Cash"
wrote: Yekal wrote: On Jan 2, 9:21 pm, YAPH wrote: On Fri, 02 Jan 2009 10:55:10 -0800, yekal_tytwr wrote: Hi All, We are building a house with wet underfloor heating which goes back to 2 control units, which have all the wiring completed, only leaving 2 wires from each unit going back to the boiler (volt free). the boiler has now been installed (Worcester Greenstar 12/18) Is that an oil boiler? I don't recognise the model name as a gas one. *Yes this is an oil condensing boiler ... which I could not find any volt free connections, I spoke with Worcester bosch technical today and all they could tell me was that the boiler doesn`t have the appropriate connections, but could not tell me how I could resolve this problem. Anyone shed any light???. Not sure what your UFH control units require. You say they want volt-free connections but not whether the connection is a signal from the boiler to the UFH controller or the other way. If the former maybe the UFH controller has its own mains power for its pump and just needs a contact closure to tell it to run the pump. In that case I'd be thinking along the lines of fitting a pipe thermostat to the boiler's flow pipe to tell the UFH when there's heat coming from the boiler. Alternatively if the volt-free connection is a signal /from/ the UFH controller /to/ the boiler from a set of contacts in the controller, then I'd think along the lines of connecting across the boiler's LS and LR terminals. I think you really need to scan and post the UFH instructions somewhere for us all to see (or point us to the mfr's docs online). thanks for your reply , I can`t work out if it is possible to post the wiring diagrams on here, would you *mind if I email them to you?. -- John Stumbles --http://yaph.co.uk A: Because it messes up the order in which people read text. Q: Why is top-posting a bad thing? Scan - or photograph the picture[s] using a digital camera and upload them towww.tinypic.com, give a 'Tag' (or name) and then post the IMG Code for Forums & Message Boards link to the group. *Example below (it works if you want to view the image): *Note: leave out the [IMG] either side and post link thus: http://i44.tinypic.com/25gavxt.jpg- note the coloured and underlined text that indicates a valid link. Hope this helps Cash- Hide quoted text - - Show quoted text - Thanks for all that, I will give it a go fingers crossed!! http://i40.tinypic.com/2eund40.jpg this one is the boiler wiring diagram http://i44.tinypic.com/303e4c7.jpg and this should be heating diagram this link has not gone blue as yours hopefully it will appear blue when I post, well here we go! |
#6
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Sat, 03 Jan 2009 11:31:12 -0800, Yekal wrote:
http://i40.tinypic.com/2eund40.jpg this one is the boiler wiring diagram http://i44.tinypic.com/303e4c7.jpg and this should be heating diagram OK the "boiler relay / volt-free" connection is a pair of contacts which close when the controller wants the boiler to run. It's "volt-free" because neither of the contacts is tied to anything of a set voltage, such as mains live. If you wire that pair of contacts to LR and LS (leaving NS not connected to anything) then the boiler will fire up when the controller wants it to. Assuming the boiler has a pump built-in then that wil run too, without you having to connect anything to the boiler's "pump relay / voltfree" contacts. -- John Stumbles -- http://yaph.co.uk Thank God I'm an atheist |
#7
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Jan 3, 9:00*pm, YAPH wrote:
On Sat, 03 Jan 2009 11:31:12 -0800, Yekal wrote: http://i40.tinypic.com/2eund40.jpg* * this one is the boiler wiring diagram http://i44.tinypic.com/303e4c7.jpg* * and this should be heating diagram OK the "boiler relay / volt-free" connection is a pair of contacts which close when the controller wants the boiler to run. It's "volt-free" because neither of the contacts is tied to anything of a set voltage, such as mains live. If you wire that pair of contacts to LR and LS (leaving NS not connected to anything) then the boiler will fire up when the controller wants it to. Assuming the boiler has a pump built-in then that wil run too, without you having to connect anything to the boiler's "pump relay / voltfree" contacts. -- John Stumbles *-- *http://yaph.co.uk Thank God I'm an atheist The boiler does have its own built in pump, and as per one of your previous posts the heating controls do have their own mains pump. If i understand this, I just need to connect the L & N from both the upstairs and downstairs heating controls to LR & LS of X2 on the boiler, (does it matter which wire goes to which connection?). Do you think I will be OK using the integral programmer? (which was purchased seperate and now fitted), or will I need to get an external one? as last time I spoke with Worcester they seem to think the integral one won`t work with underfloor heating. Cheers Yekal. |
#8
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Sat, 03 Jan 2009 14:20:18 -0800, Yekal wrote:
Do you think I will be OK using the integral programmer? (which was purchased seperate and now fitted), or will I need to get an external one? as last time I spoke with Worcester they seem to think the integral one won`t work with underfloor heating. I think you need to use a timer external to the boiler to control the heating. From what I saw of your UFH controllers it looks as if they either have or need to have their own time controls. If you just want the whole house heating on or off at the same times then you can use one timer. If you want zones controlled separately e.g. downstairs warm during day, warmer in evening, practically off at night; upstairs background during day, warm evening, cool night, warm morning; then I'd use separate programmable thermostats for the zones. Is the boiler a combi? If so you don't need a time control for hot water (unless the boiler has some sort of pre-heat or storage function which can be switched on & off). If it has, or if it's a conventional non-combi, then you'll need a time control for that. BTW a "programmer" is conventionally a device with independent timer controls for heating and HW in one box. -- John Stumbles -- http://yaph.co.uk I can't stand intolerance |
#9
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
YAPH wrote:
On Sat, 03 Jan 2009 14:20:18 -0800, Yekal wrote: Do you think I will be OK using the integral programmer? (which was purchased seperate and now fitted), or will I need to get an external one? as last time I spoke with Worcester they seem to think the integral one won`t work with underfloor heating. I think you need to use a timer external to the boiler to control the heating. From what I saw of your UFH controllers it looks as if they either have or need to have their own time controls. If you just want the whole house heating on or off at the same times then you can use one timer. If you want zones controlled separately e.g. downstairs warm during day, warmer in evening, practically off at night; upstairs background during day, warm evening, cool night, warm morning; then I'd use separate programmable thermostats for the zones. After calcuating the time constant for my floors, which are screed and wet UFH with not a huge margin over whats needed in temps like this, I decide to simply run the thing 24x7 on its own thermostatic circuit. The overshoot is much less. - about half a degree instead of a degree, and the heating isn't running as hard as it used to.. To be brutally honest, timing wet screeded UFH is almost a waste of time in the winter. Probably far better to simply hard wire it to a thermostat and a switch. Is the boiler a combi? If so you don't need a time control for hot water (unless the boiler has some sort of pre-heat or storage function which can be switched on & off). If it has, or if it's a conventional non-combi, then you'll need a time control for that. BTW a "programmer" is conventionally a device with independent timer controls for heating and HW in one box. |
#10
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
On Jan 6, 11:10*pm, The Natural Philosopher wrote:
YAPH wrote: On Sat, 03 Jan 2009 14:20:18 -0800, Yekal wrote: * Do you think I will be OK using the integral programmer? (which was purchased seperate and now fitted), or will I need to get an external one? as last time I spoke with Worcester they seem to think the integral one won`t work withunderfloorheating. I think you need to use a timer external to the boiler to control the heating. From what I saw of your UFH controllers it looks as if they either have or need to have their own time controls. If you just want the whole house heating on or off at the same times then you can use one timer. If you want zones controlled separately e.g. downstairs warm during day, warmer in evening, practically off at night; upstairs background during day, warm evening, cool night, warm morning; then I'd use separate programmable thermostats for the zones. After calcuating the time constant for my floors, which are screed andwetUFH with not a huge margin over whats needed in temps like this, I decide to simply run the thing 24x7 on its own thermostatic circuit. The overshoot is much less. - about half a degree instead of a degree, and the heating isn't running as hard as it used to.. To be brutally honest, timingwetscreeded UFH is almost a waste of time in the winter. Probably far better to simply hard wire it to a thermostat and a switch. Is the boiler a combi? If so you don't need a time control for hot water (unless the boiler has some sort of pre-heat or storage function which can be switched on & off). If it has, or if it's a conventional non-combi, then you'll need a time control for that. BTW a "programmer" is conventionally a device with independent timer controls for heating and HW in one box.- Hide quoted text - - Show quoted text -- Hide quoted text - - Show quoted text - Thanks everyone, got everything ready to go, but can`t get delivery of oil till next week, then I will know if it all works!. |
#11
Posted to uk.d-i-y
|
|||
|
|||
wet under floor heating/boiler
Yekal wrote:
On Jan 6, 11:10 pm, The Natural Philosopher wrote: YAPH wrote: On Sat, 03 Jan 2009 14:20:18 -0800, Yekal wrote: Do you think I will be OK using the integral programmer? (which was purchased seperate and now fitted), or will I need to get an external one? as last time I spoke with Worcester they seem to think the integral one won`t work withunderfloorheating. I think you need to use a timer external to the boiler to control the heating. From what I saw of your UFH controllers it looks as if they either have or need to have their own time controls. If you just want the whole house heating on or off at the same times then you can use one timer. If you want zones controlled separately e.g. downstairs warm during day, warmer in evening, practically off at night; upstairs background during day, warm evening, cool night, warm morning; then I'd use separate programmable thermostats for the zones. After calcuating the time constant for my floors, which are screed andwetUFH with not a huge margin over whats needed in temps like this, I decide to simply run the thing 24x7 on its own thermostatic circuit. The overshoot is much less. - about half a degree instead of a degree, and the heating isn't running as hard as it used to.. To be brutally honest, timingwetscreeded UFH is almost a waste of time in the winter. Probably far better to simply hard wire it to a thermostat and a switch. Is the boiler a combi? If so you don't need a time control for hot water (unless the boiler has some sort of pre-heat or storage function which can be switched on & off). If it has, or if it's a conventional non-combi, then you'll need a time control for that. BTW a "programmer" is conventionally a device with independent timer controls for heating and HW in one box.- Hide quoted text - - Show quoted text -- Hide quoted text - - Show quoted text - Thanks everyone, got everything ready to go, but can`t get delivery of oil till next week, then I will know if it all works!. You can tell if the boiler has been running here, by the 4 cats draped over the pipe runs in the corridor..never did install heating on the landing above..not needed. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
U.s. Gas Hot Water Heating Boiler | Home Repair | |||
Central heating boiler | UK diy | |||
Complicated central Heating; Back-Boiler and Combi-Boiler | UK diy | |||
Combi Boiler woes - first heating & no DHW, now DHW and no heating.... | UK diy | |||
Boiler, and heating question | Home Ownership |