  #1   Report Post  
Posted to uk.d-i-y
Steve S
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.

I have a radial circuit, protected by a 16A MCB that is used for the
following:

CH (boiler, pump, valves, controller) via a FCU (3A)
Immersion heater, no FCU, just a switch

I would like to add a single socket to power a wireless repeater. This thing
requires a 13A socket for its wall-wart, and no other socket is within
reach. I would take it from the fused side of the FCU.
The current (no pun intended) 3A fuse would be fine.

Is such a thing permissible?

TIA,

Steve S
--



  #2   Report Post  
Posted to uk.d-i-y
Sparks
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.

"Steve S" wrote in message
k...
I have a radial circuit, protected by a 16A MCB that is used for the
following:

CH (boiler, pump, valves, controller) via a FCU (3A)
Immersion heater, no FCU, just a switch

I would like to add a single socket to power a wireless repeater. This
thing requires a 13A socket for its wall-wart, and no other socket is
within reach. I would take it from the fused side of the FCU.
The current (no pun intended) 3A fuse would be fine.

Is such a thing permissible?


I think so, but it would be better to connect to the input of the spur (Or
place a junction box on the cable between the spur and the consumer unit,
and connect to that), then you have a socket that wont blow a fuse if
something bigger was plugged in to it at a later date (and take out the
heating system!)

Sparks...


  #3   Report Post  
Posted to uk.d-i-y
Steve S
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.


"Sparks" wrote :

I think so, but it would be better to connect to the input of the spur (Or
place a junction box on the cable between the spur and the consumer unit,
and connect to that), then you have a socket that wont blow a fuse if
something bigger was plugged in to it at a later date (and take out the
heating system!)


Thanks for that. Good point about taking the heating out. The thing that
worries me about having a socket on the immersion heater/CH radial is the
mixed use aspect. Would someone coming later realise that they need to throw
the CH MCB to isolate that socket? Perhaps clear labelling at both socket
and in the CU might be sufficient?

Steve S


  #4   Report Post  
Posted to uk.d-i-y
jim_in_sussex
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.


Steve S wrote:
"Sparks" wrote :

I think so, but it would be better to connect to the input of the spur (Or
place a junction box on the cable between the spur and the consumer unit,
and connect to that), then you have a socket that wont blow a fuse if
something bigger was plugged in to it at a later date (and take out the
heating system!)


Thanks for that. Good point about taking the heating out. The thing that
worries me about having a socket on the immersion heater/CH radial is the
mixed use aspect. Would someone coming later realise that they need to throw
the CH MCB to isolate that socket? Perhaps clear labelling at both socket
and in the CU might be sufficient?


doubt very much that a 13A socket complies with regs for at least 2
reasons (1) circuit load - a 13A socket is normally assumed to require
a 20A spur or 32A ring that + your heating load & your circuit is
overloaded (2) under diversity you can't average down a heating load.

One option is to consider using 2 amp unswitched round pin sockets - eg
see www.tlc-direct.co.uk - stock item no MK K770. You'd need to feed
this through a 2A fused spur, but that might keep you within your
circuit maximum load & prevent any future misuse of the socket. You'd
have to find an adapter to go 13A to 2A or change the plug on your
router.

Even so it doesn't feel entirely satisfactory & personally I'd look
hard to see if it really couldn't be hooked into a 'proper' 32A ring.

HTH

  #5   Report Post  
Posted to uk.d-i-y
Steve S
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.


"jim_in_sussex" wrote:

doubt very much that a 13A socket complies with regs for at least 2
reasons (1) circuit load - a 13A socket is normally assumed to require
a 20A spur or 32A ring that + your heating load & your circuit is
overloaded (2) under diversity you can't average down a heating load.

One option is to consider using 2 amp unswitched round pin sockets - eg
see www.tlc-direct.co.uk - stock item no MK K770. You'd need to feed
this through a 2A fused spur, but that might keep you within your
circuit maximum load & prevent any future misuse of the socket. You'd
have to find an adapter to go 13A to 2A or change the plug on your
router.

Even so it doesn't feel entirely satisfactory & personally I'd look
hard to see if it really couldn't be hooked into a 'proper' 32A ring.


A 13A - 2A adapter sounds horrible. Looks like I'll have to find a
different solution.

Thanks anyway.

Steve S




  #6   Report Post  
Posted to uk.d-i-y
Mike Harrison
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.

On 13 Feb 2006 13:32:58 -0800, "jim_in_sussex" wrote:


Steve S wrote:
"Sparks" wrote :

I think so, but it would be better to connect to the input of the spur (Or
place a junction box on the cable between the spur and the consumer unit,
and connect to that), then you have a socket that wont blow a fuse if
something bigger was plugged in to it at a later date (and take out the
heating system!)


Thanks for that. Good point about taking the heating out. The thing that
worries me about having a socket on the immersion heater/CH radial is the
mixed use aspect. Would someone coming later realise that they need to throw
the CH MCB to isolate that socket? Perhaps clear labelling at both socket
and in the CU might be sufficient?


doubt very much that a 13A socket complies with regs for at least 2
reasons (1) circuit load - a 13A socket is normally assumed to require
a 20A spur or 32A ring that + your heating load & your circuit is
overloaded (2) under diversity you can't average down a heating load.

One option is to consider using 2 amp unswitched round pin sockets - eg
see www.tlc-direct.co.uk - stock item no MK K770. You'd need to feed
this through a 2A fused spur, but that might keep you within your
circuit maximum load & prevent any future misuse of the socket. You'd
have to find an adapter to go 13A to 2A or change the plug on your
router.

Even so it doesn't feel entirely satisfactory & personally I'd look
hard to see if it really couldn't be hooked into a 'proper' 32A ring.

HTH


How about putting a fused spur unit and the 13a socket in one of those double-unit back-boxes, so
the socket had its own fuse, say 2 or 5A, suitably labelled of course. Can't see why this wouldn't
be OK from the technical or safety point of view, don't know about what the regs say. This would
certainly better than some 2A-13A adapter arrangement being used on a plug-in wall-wart (I'm
assuming it's the type with an integral plug).

  #7   Report Post  
Posted to uk.d-i-y
jim_in_sussex
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.

not utterly horrible - somewhere there's probably one of those
multi-way travellers' adapters which will do this job.

or just change the plug on the router as it's surely not going to move
around much?

  #8   Report Post  
Posted to uk.d-i-y
Sparks
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.


"Steve S" wrote in message
k...

"jim_in_sussex" wrote:

doubt very much that a 13A socket complies with regs for at least 2
reasons (1) circuit load - a 13A socket is normally assumed to require
a 20A spur or 32A ring that + your heating load & your circuit is
overloaded (2) under diversity you can't average down a heating load.

One option is to consider using 2 amp unswitched round pin sockets - eg
see www.tlc-direct.co.uk - stock item no MK K770. You'd need to feed
this through a 2A fused spur, but that might keep you within your
circuit maximum load & prevent any future misuse of the socket. You'd
have to find an adapter to go 13A to 2A or change the plug on your
router.

Even so it doesn't feel entirely satisfactory & personally I'd look
hard to see if it really couldn't be hooked into a 'proper' 32A ring.


A 13A - 2A adapter sounds horrible. Looks like I'll have to find a
different solution.


Quite, I expect the repeaters plug is a wall wart, not a normal 13A plug.

You could make sure the cable is at least 2.5mm, then uprate the MCB to 20A,
then replace the switch on the immersion with a 13A FCU, then connect the
new socket as I suggested before - this would then be a pukka radial.

Assuming the cable is OK, then it isn't much work, and little cost.

Personally I would label the socket on the front with "Part of the CH
Circuit" or whatever
I have labelled all my hidden sockets with the circuit number (A3 for
example, means CU A, CCT 3) but to be honest, you would have to be a bit
incompetent to just turn off 1 circuit and assume it has isolated a
particular socket - I would always test it before touching anything unless
it is my house, and I know what is what!

Sparks...


  #9   Report Post  
Posted to uk.d-i-y
Mike the Unshavable
 
Posts: n/a
Default Electrical regs question - adding a socket to a fused spur.

"Steve S" writed in news:_A7If.19775$wl.5107
@text.news.blueyonder.co.uk:

"jim_in_sussex" wrote:

doubt very much that a 13A socket complies with regs for at least 2
reasons (1) circuit load - a 13A socket is normally assumed to require
a 20A spur or 32A ring that + your heating load & your circuit is
overloaded (2) under diversity you can't average down a heating load.

One option is to consider using 2 amp unswitched round pin sockets -

eg
see www.tlc-direct.co.uk - stock item no MK K770. You'd need to feed
this through a 2A fused spur, but that might keep you within your
circuit maximum load & prevent any future misuse of the socket. You'd
have to find an adapter to go 13A to 2A or change the plug on your
router.

Even so it doesn't feel entirely satisfactory & personally I'd look
hard to see if it really couldn't be hooked into a 'proper' 32A ring.


A 13A - 2A adapter sounds horrible. Looks like I'll have to find a
different solution.

Or a Europlug / Schuko socket perhaps, difficult to source in the UK,
plugs are easier to find though, ussuly on the end of a '8' plug for a
low power appliance.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Spur for boiler needed - Via junction box or socket? [email protected] UK diy 10 June 1st 05 08:42 AM
extra socket off fused spur - is this OK? Zikki Malambo UK diy 0 December 21st 04 02:06 PM
Adding Headphone socket to TV Michael Murray UK diy 29 September 10th 03 12:28 AM
New Electrical Regs PoP UK diy 22 September 1st 03 08:41 PM
Electrical Wiring Grouping Factors in IEE Regs pickerel UK diy 5 July 14th 03 01:26 AM


All times are GMT +1. The time now is 03:48 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"