Ive got a problem with a water heater at work. This is a natural gas
unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#2
![]() |
|||
|
|||
![]()
On Sat, 10 Jan 2004 18:12:43 -0800, Gunner wrote
(in message ): Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil My long distance guess: Bad gas solenoid. Second possibility, the contact in the controller that feeds the gas solenoid is burned. Hope this helps. Roger in Vegas Worlds Greatest Impulse Buyer |
#3
![]() |
|||
|
|||
![]()
My best guess from my chair and with a little hands on experience with
controlers that your problem is your flame sensor. If my memory serves me correctly you can take a 1.5 volt battery with a 15K ohm resistor in series and bypass the flame sensor . This will confirm the flame sensor function . I have seen some of these problems in the past caused by open inspection plates that allows drafts to blow the flame askew and by debris on the flame holder that slighly deflect the flame.... all worth looking at. good luck. "Gunner" wrote in message ... Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#4
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 02:12:43 GMT, the renowned Gunner
wrote: Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. That's my guess too, I don't think the flame rod could cause that kind of problem (but I'm coming at it from the other side..). Check the 24VAC at the controller- make sure it's in the right range and fairly steady as the gas valve is energized. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" Best regards, Spehro Pefhany -- "it's the network..." "The Journey is the reward" Info for manufacturers: http://www.trexon.com Embedded software/hardware/analog Info for designers: http://www.speff.com |
#5
![]() |
|||
|
|||
![]() Gunner wrote: Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. The blower unit worked OK, but did they actually hook it to a gas valve? Or, did they just hook a meter to the gas valve terminals? That might not be a good enough test. Assuming an AC gas solenoid, they probably use a triac (SSR) to drive the gas valve. These can have all manner of odd failure modes. You should hook a DVM to the solenoid leads, and see if the 24 V AC is going on and off. If so, it is the control. If a stady 24 V AC is going to the solenoid, then it is the solenoid valve that is bad. You can also connect the solenoid valve to 24 V AC and see if it holds steadily or clatters. Jon |
#6
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 03:13:07 GMT, Spehro Pefhany
wrote: On Sun, 11 Jan 2004 02:12:43 GMT, the renowned Gunner wrote: Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. That's my guess too, I don't think the flame rod could cause that kind of problem (but I'm coming at it from the other side..). Check the 24VAC at the controller- make sure it's in the right range and fairly steady as the gas valve is energized. 24vac is steady on input, but flakes out to the gas solenoid during the ignition sequence. I removed the coil from the solenoid from the circuit, thinking there was perhaps a short, ohmed it out, ok, refired the system and the 24vts still only fired for a second or so without the solenoid in the circuit. I would automaticly replace the controller, but the boss indicated it worked fine at the dealers so it should work fine yada yada yada... shrug. Gunner This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" Best regards, Spehro Pefhany "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#7
![]() |
|||
|
|||
![]()
On Sat, 10 Jan 2004 18:30:17 -0800, Roger Hull
wrote: On Sat, 10 Jan 2004 18:12:43 -0800, Gunner wrote (in message ): Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil My long distance guess: Bad gas solenoid. Second possibility, the contact in the controller that feeds the gas solenoid is burned. the controller is a sealed unit, containing what I believe are solid state switches. I was unable to feel even the slightest TICK when the ignition sequence would fire. Gunner Hope this helps. Roger in Vegas Worlds Greatest Impulse Buyer "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#8
![]() |
|||
|
|||
![]() "Gunner" wrote in message ... Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Turn off the gas, turn of the power, wire the solenoid directly to the transformer, turn on the power. Does the solenoid hold in? If not it's a bad transformer or solenoid. If it does your flame sensor is bad. My bet is a bad winding in the solenoid or transformer that shorts or opens under its own induced field. Loyd |
#9
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 01:05:22 -0500, "Blake Loyd"
wrote: "Gunner" wrote in message .. . Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Turn off the gas, turn of the power, wire the solenoid directly to the transformer, turn on the power. Does the solenoid hold in? If not it's a bad transformer or solenoid. If it does your flame sensor is bad. My bet is a bad winding in the solenoid or transformer that shorts or opens under its own induced field. Loyd Blink blink..ok....Ill try that. Ill also try that with the gas on at the appropriate time in the ignition cycle and see if the flame rod ever stablizes or has a rectification. I hate working with electrically operated natural gas devices that use a 1" gas line. Ive lost my eyebrows more than once... Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#10
![]() |
|||
|
|||
![]()
Hey Gunner,
I have a mid-efficiencey ( electronic control similar to yours) natural gas FAG in the crawl space in the new place here. So I can't, in my physical state, "get at it" like I could maybe 20 years back. Anyway, with-out suggesting mine had the identical problem, I can say that it was somewhat similar. My furnace guy said "Well, do you want to, spend $280 or just an hour service call?". Gee, guess what I picked?!? Anyway, he took out the flame sensor gadget, cleaned it off (it didn't look real dirty to me by the way) and it has run OK up to this point. So I'd try that if I were you. One other thought because I'm not sure what you meant. A test like this of a quick acting or short term electrical occurrence is easier to see with an analog VOM then one of the contemporary digital types. Take care. Good Luck. Brian Lawson, Bothwell, Ontario. ps.... At the 0 degree F temps here the past few days, my furnace is running about 20 minutes per hour in the day time. On and off about 4 times per hour for about 5 minutes each time. Don't know about night-time, and it's on a "set-back" anyway. hate to see the next gas bill. XXXXXXXXXXXXXXXXXXXXXXX On Sun, 11 Jan 2004 02:12:43 GMT, Gunner wrote: Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#11
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 06:24:36 GMT, Gunner
brought forth from the murky depths: I hate working with electrically operated natural gas devices that use a 1" gas line. Ive lost my eyebrows more than once... Silly wabbit. Try one of these next time, eh? http://www.harborfreight.com/cpi/cta...emnumber=46526 -- Vidi, Vici, Veni --- http://diversify.com Comprehensive Website Development |
#12
![]() |
|||
|
|||
![]() "Gunner" wrote in message ... On Sun, 11 Jan 2004 01:05:22 -0500, "Blake Loyd" wrote: "Gunner" wrote in message .. . Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Turn off the gas, turn of the power, wire the solenoid directly to the transformer, turn on the power. Does the solenoid hold in? If not it's a bad transformer or solenoid. If it does your flame sensor is bad. My bet is a bad winding in the solenoid or transformer that shorts or opens under its own induced field. Loyd Blink blink..ok....Ill try that. Ill also try that with the gas on at the appropriate time in the ignition cycle and see if the flame rod ever stablizes or has a rectification. I should have said the flame sensor circuit/system. Now, I am assuming that you haven't changed out the controller, because if you have and you have an external purge timer you just need to read the installation instructions regarding that situation. I am also assuming that the controller hasn't gotten wet as that could cause problems. That said, maybe this will be clearer. Turn off the gas. Turn off the power. Check the flame sensor wire to make sure it is not damaged and that it isn't touching anything to which it can ground out. If it appears ok then check the following. Mark the wires so you can reconnect them in the same manner as switching leads may cause the system to lock out. Disconnect the secondary of the transformer from everything. Disconnect the gas valve. Wire the transformer directly to the gas valve solenoid. Turn on the power. Does the gas valve open and stay open or does it chatter(open close open close open etc)? If it opens and stays open the transformer and valve are fine. If it chatters then one or the other is bad. Since you say the 24V is constant it is apparently the solenoid. If the transformer and gas valve solenoid are good then the problem lies in the flame detection system/circuit. Turn off the power. Rewire the transformer and gas valve as they were originally. Loosen and retighten the flame sensor mounting screw. See if that solves the problem(bad ground). If not, remove the flame sensor, disconnect it from the controller at the controller, attach meter to lead end disconnected from controller and base of sensor(ground), heat sensor with a propane torch to see if it produces the 0.8uA minimum through the lead. If it doesn't, disconnect the lead from the sensor and test the sensor again to see if it produces the 0.8uA minimum. If it does the lead is bad. If it doesn't the sensor is bad. If both check out as working properly and you are confident that the moving of the lead hasn't just happened to alleviate a ground in the lead, then the problem lies in the controller(unless you did alleviate a ground in the sensor lead). From your description of what's going on it sounds as if the problem lies in the solenoid circuit. It could be the solenoid or it could be the controller isn't holding in the solenoid circuit. Since it happens during the start-up I doubt it is the flame sensor. I guess is that it is the solenoid or the controller. Loyd |
#13
![]() |
|||
|
|||
![]()
In article , Blake Loyd says...
... remove the flame sensor, disconnect it from the controller at the controller, attach meter to lead end disconnected from controller and base of sensor(ground), heat sensor with a propane torch to see if it produces the 0.8uA minimum through the lead. If it doesn't, disconnect the lead from the sensor and test the sensor again to see if it produces the 0.8uA minimum. If it does the lead is bad. If it doesn't the sensor is bad. In this case, is the flame sensor a thermocouple? Jim ================================================== please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ================================================== |
#14
![]() |
|||
|
|||
![]()
On 11 Jan 2004 12:03:07 -0800, the renowned jim rozen
wrote: In article , Blake Loyd says... ... remove the flame sensor, disconnect it from the controller at the controller, attach meter to lead end disconnected from controller and base of sensor(ground), heat sensor with a propane torch to see if it produces the 0.8uA minimum through the lead. If it doesn't, disconnect the lead from the sensor and test the sensor again to see if it produces the 0.8uA minimum. If it does the lead is bad. If it doesn't the sensor is bad. In this case, is the flame sensor a thermocouple? These units use a rod sitting out in the open flame. They sense the rectifying action of a flame, which is very insensitive to soot contamination or other undesired side effects. Needless to say, a false positive flame detection would be a very serious matter. Flame out, gas valve stays open, ssssssssssssssssssssssssssss, mixing with air, seeping out, searching, until it finds *another* flame, anywhere. Best regards, Spehro Pefhany -- "it's the network..." "The Journey is the reward" Info for manufacturers: http://www.trexon.com Embedded software/hardware/analog Info for designers: http://www.speff.com |
#15
![]() |
|||
|
|||
![]() "Gunner" wrote in message ... Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" What's the gas pressure to the unit? I installed a new furnace a few years ago that wouldn't fire the main burner. Turned out the pressure was slightly higher than the valve could take. Old furnace worked fine for many years at the same pressure....Paul |
#16
![]() |
|||
|
|||
![]() "PJ" wrote in message ... "Gunner" wrote in message ... Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" What's the gas pressure to the unit? I installed a new furnace a few years ago that wouldn't fire the main burner. Turned out the pressure was slightly higher than the valve could take. Old furnace worked fine for many years at the same pressure....Paul Your question brings up other issues. I'd assumed it was a piece of equipment that was already in use. Is the equipment new? Had it been working and stopped? Had repairs been done to it recently and if so what? Your point about the gas pressure is a good one, especially if the equipment is new or the gas valve has been changed. Loyd |
#17
![]() |
|||
|
|||
![]()
On 11 Jan 2004 12:03:07 -0800, jim rozen
wrote: In article , Blake Loyd says... ... remove the flame sensor, disconnect it from the controller at the controller, attach meter to lead end disconnected from controller and base of sensor(ground), heat sensor with a propane torch to see if it produces the 0.8uA minimum through the lead. If it doesn't, disconnect the lead from the sensor and test the sensor again to see if it produces the 0.8uA minimum. If it does the lead is bad. If it doesn't the sensor is bad. In this case, is the flame sensor a thermocouple? Jim No..the flame rod is a device that puts 100 or so volts on the flame rod, which is exposed to the flame, and uses flame rectification to convert this to dc and then to ground. It senses the ground path Gunner ================================================= = please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ================================================= = "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#18
![]() |
|||
|
|||
![]()
In article , Gunner says...
...the flame rod is a device that puts 100 or so volts on the flame rod, which is exposed to the flame, and uses flame rectification to convert this to dc and then to ground. It senses the ground path Thanks, I've learned something today. I've never seen those, all the flame decectors I've been aware of are either thermocouples or CdS photocells. Also the SiC ignitor modules in our oven - which always seem to burn out at the *worst* time! Jim ================================================== please reply to: JRR(zero) at yktvmv (dot) vnet (dot) ibm (dot) com ================================================== |
#19
![]() |
|||
|
|||
![]()
In article , Blake Loyd says...
[about a Honeywell gas control...] ... remove the flame sensor, disconnect it from the controller at the controller, attach meter to lead end disconnected from controller and base of sensor(ground), heat sensor with a propane torch to see if it produces the 0.8uA minimum through the lead. On Sun, 11 Jan 2004 20:25:15 GMT, Spehro Pefhany wrote: [I think as a reply to the above, but I want to check if that is true or not...] These units use a rod sitting out in the open flame. They sense the rectifying action of a flame, which is very insensitive to soot contamination or other undesired side effects. I have a "Seahorse" heater with a Honeywell VR8204M control that uses one of those. I could never measure any self-generated output from it, and was under the impression that it rectified power supplied by the controller rather than sourcing its own thermopile current. Is that what you are saying here? Is there some way to test those with multimeter, maybe while they are connected to their controllers? My problem turned out to be that the pilot assembly, with the sensor rod and hot flag, had been bent out of position during manufacturing. If the heater had been off long enough for the gas in the burner lines to dissipate, then when the main gas valve re-opened it created a gust of air that turned off the pilot sensor before the burnable mixture could get to the pilot and ignite. It seems those "rectifying" sensors are a _lot_ faster to turn off than a thermopile would be! Moving the pilot assembly to its proper position let the sensor stay on long enough to ignite the main burner. Loren |
#20
![]() |
|||
|
|||
![]()
On 11 Jan 2004 14:18:08 -0800, the renowned jim rozen
wrote: In article , Gunner says... ...the flame rod is a device that puts 100 or so volts on the flame rod, which is exposed to the flame, and uses flame rectification to convert this to dc and then to ground. It senses the ground path Thanks, I've learned something today. I've never seen those, all the flame decectors I've been aware of are either thermocouples or CdS photocells. Some of the big industrial ones use a special electronic gas tube that is sensitive only to ultraviolet light. They are sunlight-blind even without a filter but respond to the UV given off by a flame. Also the SiC ignitor modules in our oven - which always seem to burn out at the *worst* time! Same thing with the hot-surface ignitor in our furnace. I should pick up a spare.. thanks for reminding me. Best regards, Spehro Pefhany -- "it's the network..." "The Journey is the reward" Info for manufacturers: http://www.trexon.com Embedded software/hardware/analog Info for designers: http://www.speff.com |
#21
![]() |
|||
|
|||
![]()
Gunner wrote in message . ..
Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" I ran into a simlar problem on our furnace. A friend suggested that I check the "flame sensor". In my unit it was a stainless steel rod that stuck into the flame. I removed it, it is on a little bracket, and cleaned it with denatured alcohol and when I reinstalled it the furnace worked fine. My friend said that after years of being stuck into a flame, the sensors get coated with a fine film of ash that insulates it. All I know is that a good cleaning solved my problems. Terry |
#22
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 16:10:20 -0500, "Blake Loyd"
wrote: "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" What's the gas pressure to the unit? I installed a new furnace a few years ago that wouldn't fire the main burner. Turned out the pressure was slightly higher than the valve could take. Old furnace worked fine for many years at the same pressure....Paul Your question brings up other issues. I'd assumed it was a piece of equipment that was already in use. Is the equipment new? Had it been working and stopped? Had repairs been done to it recently and if so what? Your point about the gas pressure is a good one, especially if the equipment is new or the gas valve has been changed. Loyd Existing installation, just getting flakier and flakier. I dont have any way to test the manifold pressure (gas), or the blower pressure, though the blower does have a shunt to increase or decrease blower pressure. Its never been moved as far as I can see. Gunner "Gun Control, the theory that a 110lb grandmother should fist fight a 250lb 19yr old criminal" |
#23
![]() |
|||
|
|||
![]() "Gunner" wrote in message ... Existing installation, just getting flakier and flakier. I dont have any way to test the manifold pressure (gas), or the blower pressure, though the blower does have a shunt to increase or decrease blower pressure. Its never been moved as far as I can see. Ok. You could take some clear plastic tubing and build a manometer. Or if push came to shove, put in a Schrader valve and use a tire gauge to get a rough reading. But the gas pressure probably isn't the problem since it is a preexisting system, unless the pressure regulator for the gas has gone bad. Another things to consider, since we can't see the setup, is the environment. Is it in a humid or dusty area? Humidity can cause spade connections to corrode, and if it is bad it can cause the burner to rust inside and the rust can block the gas flow.. Dust can get into burners and block the gas flow. It is a heater system to remove water from oil. Is the water vented outside or inside where the unit is? Is there any corrosive chemical used in the area? If so, connections may be corroding. Take a good look at the inside of the unit to see if it looks like water has been condensing in it. If so, the controller may have simply gone bad due to the water. Others have mentioned the flame sensor may be dirty. That could easily be the case especially if the flames have any yellow in them, the flames should burn blue. Yellow means incomplete combustion and sooting. Check the inside of the combustion chamber for sooting. Remove the flame sensor and wipe the sensor with a clean paper towel.. A little discoloration on the towel is normal but there shouldn't be black soot or at least very little. If cleaning the sensor solves the problem, inspect the inside of the burner to insure it is not blocked with foreign matter(dust, insect, rust,etc.), adjust the air inlet(s) on the burner(s) to eliminate any yellow flame. If the blower supplies the air for the burner, adjust the blower to eliminate any yellow flame. If the system is a very old one consider the gas line for a moment. Does it have a drip leg. If it has a drip leg at the unit, you might turn off the gas and remove the drip leg to insure that it isn't full. If for some reason oil or water has filled the drip leg it could be causing the flame to burn yellow and soot. But honestly, I've never seen a drip leg get that full. If it doesn't have a drip leg you might install one to prevent any oil or moisture from making it to the gas valve and burner. I take it the lines are iron pipe since you said they were 1". But since the unit has been there for some time any oil in the pipes that could migrate to the unit has probably already done so. Loyd |
#24
![]() |
|||
|
|||
![]()
On Sun, 11 Jan 2004 02:12:43 GMT, Gunner
wrote: Ive got a problem with a water heater at work. This is a natural gas unit used to boil water out of oil for reusing the oil Controller is a Honeywell S89F controller. Everything checks out normally..sorta Unit is powered up, gas on. 35 second prepurge cycle starts At this point, for 4 seconds the ignitor fires up, the gas solenoid is supposed to open, and then run for a few seconds to allow the flame sensor to stablizes (DC rectification through the flame) then run. If no flame, its supposed to recycle another 3 times then lock out if no burn is detected. My problem When the solenoid voltage for the gas valve comes on..it makes and breaks 3-4 times, or simply comes on then quits within a second. If the flame actually does fireup, it may trigger the solenoid on and off click click click for the 3-4 seconds, then shuts down sometimes it only clicks once. It may or may not go through the following 3 recycles. Ive checked the ground, cleaned all the grounding connections, double checked the ignitor via jumper and still I cant figure out whats causing it to not come on and stay on. Input voltage is constant, the 24vts to the controller is constant, etc etc. I put a DC milliamp meter in line with the flame sensor rod, but was unable to get any reading in the second or two that the flame actually did come on. Do I have a bad flame sensor or a bad controller? The flame sensor appears to be in the proper position from the burner face, and the flame sensor lug does appear to have 110vts on it, measured to ground. Any ideas? My gut instinct is a flaky controller, but the entire blower unit was removed and taken to the dealer where it did work properly, its alleged by the staff. This is the manual for the unit http://hbctechlit.honeywell.com/tech...0s/68-0066.pdf Gunner Well, you've gotten some good advice so far. Gunner. I read thru the responses to your posts. Seems as if folks have covered all the probable things. So I doubt I can offer much of value. However, a couple points stick out in my mind and cause me to go Hmmmm. You say entire blower unit was removed and sent off for a bench test and it supposedly worked there, on their test bench. AND You say it doesn't work on site. AND You describe the sequence of operation of the controller as being somewhat flakey on site. Sometimes multiple cycling of the solenoid, sometimes not. Sometimes does the 3 retries, sometimes not. The above bothers me. Makes me sorta curious. The thing about those controllers is that internally, they have digital circuitry. All digital circuits absolutely HATE differences in ground potential, any differences, between this point and that. Some are a little more tolerant than others, some less. In my experience, that particular series of Honeywell controllers is one of the top haters of any differences in ground potential anywhere within it's internals, or anything connected to it. Differences in ground potential which are minute, which would make no difference in electrical or electronic controls systems, can confuse and confound that line of Honeywell controllers. So I wonder to self. Hmmm. What is different between what you're calling the "blower assembly", which worked on a test bench. And what you're working with when you have everything put together on site, and now things aren't working. Did that "blower assembly" (I have no clear picture of exactly, precisely all the components you mean when you say that), as tested on the test bench include the very same transformer? The same solenoid valve? The same gas valve? Etc. Do you see what I'm getting at? What's different that's connected to that controller now, from what was connected to it when it was bench tested. First thing which jumps into my mind is that often when somebody says "blower assembly" ... that doesn't include the burner itself. May, or may not. ---- ALL---- grounds that system, anywhere in it, is supposed to have, MUST be solidly connected to that burner. You don't want even 2 ohms of difference between this leg of ground and that. Check the schematic. See all the points to be ground. Make absolutely sure that when testing from this point in ground to another, that your meter is as flatlined as possible. Personally, I'd make sure I wasn't measuring anything over one ohm anywhere. Less if I can make it happen. Next, I'd check connection from burner to cabinet. Now, sometimes folks rely on simple metal to metal contact between the pipes and other metal parts to establish that electrical connection to ground. And there is no separate ground wire bolted to burner, then bolted to the cabinet. This can work fine on a brand new unit. Can suck, and drive yah nuts trying to figure out the problem on an older unit. With age, joints and connections corrode. Resistance increases. Or ground path included a section of pipe, and somebody took it apart, and upon reassembly used some sealant on threads. And what used to be a good ground path is now not such a good one. I'd make sure. I'd add a damned good ground wire from burner to cabinet if there was not one. If there is, I'd investigate. Conductor intact? Both connections good, and solid and clean? Etc. I'd then double check. Power shut down. Do I measure zero ohms, or damned close to it, from grounded leg of transformer to cabinet? From gas valve grounded terminal to cabinet? Ground terminal(s) on controller to cabinet? Ground of ignitor to cabinet? Etc. That everything looks okay, doesn't hack it. Measure, verify. No more than 1 ohm, preferrably less. And I'd personally go for less. After verifying that. My next step would be to verify, beyond any doubt, that the cabinet is grounded to EARTH ground. One problem when dealing with digital circuits in particular arises here. In many installations, particularly older installations, cabinet ground was made by the electrician with him relying on a ground path running thru the conduit (if there is some) itself. In other words, he used the metal pipe as a ground path. This kinda, sorta works. Most times, most applications, works fine. At first. Problem is, the passage of time. All those conduit fittings that used to be tight, clean, nice metal to metal contact, after the passage of time often become not so tight, not so clean, etc. And if cabinet itself was grounded to earth ground via a path thru the conduit material itself, over the passge of years you might find there is significant resistance now built up (and thus potential, voltage, differences) between the cabinet and the actual earth ground of the building. As measured at the electrical service entry. Not a good thing. Couple volts aren't gonna hurt or even be noticeable to regular electrical devices. Some types of digital devices, and that Honeywell controller is one of em, aren't gonna like it much. BTW, do NOT consider a connection to AC common the same as a connection to ground. Period. I don't care that back at the breaker panel common may be hooked to the same ground bar as the ground wires. Do NOT consider a common wire as ground. Ground is ground. Common in normal operation carries current. Yah don't want the ground for that controller hooked to anything carrying current. Will confuse the devil out of it. The above ground related things, I'd be inclined to check, and double check first. Then I'd check whatever else is hooked to that controller one way or another, that did not accompany it to the shop for bench test. What else, that wasn't attached to it during bench test, might be shorting to ground, drawing too much current, etc. Sometimes a transformer will seem fine. Measure output voltage, she looks good. Hook her up to something that's drawing too much amperage, i.e. a relay or solenoid which does a big spike draw upon energizing, voltage droops. Sometimes very quickly then comes back to normal because relay coil dropped out and field collapsed. And what you hear is chatter. Often yah can't see that rapid fluctuation on many meters. But yah can usually hear it. Problem might be relay or solenoid coil is drawing more than it used to, particularly on energizing and making something move (inrush current), or windings are starting to fail and after a moment get too hot. Or sometimes it's the transformer. Age. Might say 40 watts on the label, but she can't handle half that any more. And particularly on inrush current draw, she starts putting out erratic, drooping voltage. Digital circuitry does not like this sort of thing. Just some thoughts. Best of luck. Bob |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Condensing/combi boiler vs. pipework question | UK diy | |||
Simple question regarding Ceiling tiles and sound? | UK diy | |||
Plumbing Question | UK diy | |||
OT - Norstar 3x8 phone system question | Metalworking | |||
chemistry question | Metalworking |