Air compressor tripping 20 amp breaker
I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on
it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. |
#2
|
|||
|
|||
If this was working and it stopped I would suspect a bad check valve. If it is
new you will have to look at the nameplate FLA rating on the motor to see what you are dealing with. The number on the tank label is usually a fantasy. |
#3
|
|||
|
|||
Tom wrote:
I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Hi, There are breakers with different peak surge and trip delay rating, what kind of breaker do you have in there? Tony |
#4
|
|||
|
|||
Congratulations, your electrical system is working as it should.
Do any of you folks have any suggestions as to how I can cure this problem? Obviously, the compressor motor has a current surge problem on starting. You have several options: 1) Run it from a dedicated 30 amp circuit, new breaker, 10 ga wire, etc. 2) If it is a capacitor equipped motor, have a qualified shop check and/or replace the capacitor(s). 3) Replace the motor with one more suitable for the machine. 4) Rewire the system to run on 220 volts after ensuring that everything is OK otherwise. 5) Install a smaller motor pulley. That will reduce the starting current modestly, at the expense of slower output (no free lunch, ya know). One or more of the above ought to work. Good luck. Joe |
#5
|
|||
|
|||
Check motor startup peak amp draw with tank empty and as it trips the
breaker, You will be suprised. Then contact sears for maximum amp draw guidlines and remedies. |
#6
|
|||
|
|||
What does the manual say the circuit should be rated for?
-- Joseph E. Meehan 26 + 6 = 1 It's Irish Math "Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. |
#7
|
|||
|
|||
Tony,
It says on the Square D breaker 10KA 120/240V- "Tony Hwang" wrote in message news:IL7gd.44690$nl.25603@pd7tw3no... Tom wrote: I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Hi, There are breakers with different peak surge and trip delay rating, what kind of breaker do you have in there? Tony |
#8
|
|||
|
|||
"Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Make sure the unloader isnt clogged and the check valve is working correctly--when it shuts down, it should hiss for a couple seconds then stop. Otherwise it will be under too high of mechanical load on startup, not good as it will draw too much electrical current. -- SVL |
#9
|
|||
|
|||
If the machine starts OK with low tank pressure but trips a breaker with
some tank pressure (its low pressure limit), then it's almost certainly the check valve, AKA the unloading valve. These don't last forever, and they're really not expensive. If the motor is trying to turn the pump against existing tank pressure, almost any motor, even brand new, will draw excess current. |
#10
|
|||
|
|||
"Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. You do not mention the distance the circuit is. I assume you ran #12 copper? Have you checked the connections on the breaker and recpt. An motor can draw 6 times FLA on start up. With an air compressor with partical pressure the high current draw could be lasting longer than the breaker likes. Try changing breakers with another in the panel. If it still happens then check out the compressor. |
#11
|
|||
|
|||
Robert Barr wrote: If the machine starts OK with low tank pressure but trips a breaker with some tank pressure (its low pressure limit), then it's almost certainly the check valve, AKA the unloading valve. (Correction -- the unloading valve is an entirely different creature than the check valve.) |
#12
|
|||
|
|||
"Tom" wrote in message
newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Tom, does the compressor make a loud hissing noise after it shuts down at 150 psi? This would be the "un-loader" valve. The unloader allows the compressor to start with little of no pressure in the cylinders. This allows for a low starting amps until the compressor gets up to speed. If the unloader is not working, then the full system pressure is adding resistance to the starting load and may be too much for the breaker. john |
#13
|
|||
|
|||
John
When it shuts off there is no hissing noise. It's just quite. "John Beckman" wrote in message ... "Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Tom, does the compressor make a loud hissing noise after it shuts down at 150 psi? This would be the "un-loader" valve. The unloader allows the compressor to start with little of no pressure in the cylinders. This allows for a low starting amps until the compressor gets up to speed. If the unloader is not working, then the full system pressure is adding resistance to the starting load and may be too much for the breaker. john |
#14
|
|||
|
|||
"Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Check to see what the unit is rated at. Does it call for a 30 amp breaker? Also, you aren't running it with an extension cord are you? I had a neighbor that had trouble with his. Worked fine for years and it started tripping the breaker. He put a new breaker in - same thing. Bought a new capacitor and then eventually bought a new motor. I asked him what he was doing different and he said he was using it away from his shed and had it hooked to a 100 foot extension cord. Bingo. That was his problem. |
#15
|
|||
|
|||
The unloader valve should release the pressure from the output
line of the compressor as the compressor turns off. If you don't hear the air release, that valve is not doing its job. Bob "Tom" wrote in message news:Hebgd.17323$HA.14609@attbi_s01... John When it shuts off there is no hissing noise. It's just quite. "John Beckman" wrote in message ... "Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Tom, does the compressor make a loud hissing noise after it shuts down at 150 psi? This would be the "un-loader" valve. The unloader allows the compressor to start with little of no pressure in the cylinders. This allows for a low starting amps until the compressor gets up to speed. If the unloader is not working, then the full system pressure is adding resistance to the starting load and may be too much for the breaker. john |
#16
|
|||
|
|||
No I'm not using an extension cord. I go directly to a dedicated outlet from
the compressor. "Red Neckerson" wrote in message news:h7dgd.7581$8W6.2859@trnddc05... "Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. Check to see what the unit is rated at. Does it call for a 30 amp breaker? Also, you aren't running it with an extension cord are you? I had a neighbor that had trouble with his. Worked fine for years and it started tripping the breaker. He put a new breaker in - same thing. Bought a new capacitor and then eventually bought a new motor. I asked him what he was doing different and he said he was using it away from his shed and had it hooked to a 100 foot extension cord. Bingo. That was his problem. |
#17
|
|||
|
|||
I have a Sears 25 gallon/5HPhorizontal compressor as well and mine did the
same thing after about two years. It was on a 20A 110V breaker 5 feet from the panel on a dedicated outlet. I rewired the motor to 220v (simple jumpers and the schmetic is in the motor junction box) and put it on a 20A 220V breaker and has been fine since. When I was having the problem I checked the motor with a megger and checked the amperage of the load and the motor was fine but the startup current was around 22 amps. My guess is that this was due to the fact that it is a oil less compressor and is now wearing in a bit and has become hard starting. It has been fine on 220v and is drawing 8.5 amps on startup. "Tom" wrote in message newsk7gd.321434$MQ5.224771@attbi_s52... I have a Sears 25 gallon/4HP horizontal compressor. When I first turn it on it runs fine and shuts off at 150psi. The problem I have is when the pressure gets at the level where it automatically kicks on again it then pops the breaker off and I then have to reset the breaker before it will run again. I have a dedicated 20 amp circuit with 12/2WG using a Square D breaker and a 20 amp duplex receptacle for the compressor, and nothing else is on this circuit. Do any of you folks have any suggestions as to how I can cure this problem? Thanks for your help. |
#18
|
|||
|
|||
On Thu, 28 Oct 2004 21:02:05 GMT, "Red Neckerson"
wrote: Also, you aren't running it with an extension cord are you? I had a neighbor that had trouble with his. Worked fine for years and it started tripping the breaker. He put a new breaker in - same thing. Bought a new capacitor and then eventually bought a new motor. I asked him what he was doing different and he said he was using it away from his shed and had it hooked to a 100 foot extension cord. Bingo. That was his problem. That was exactly my problem too. There is a voltage drop if your extension cord is too long. That plus the start-up load trips the breaker. The solution 1. Use an extra long air hose instead. There won't be any air pressure drop and the tools will work at full power. 2. Open the air tank valve to release the pressure so that the start-up load isn't high enough to trip the breaker. This is still a poor solution because the breaker will still trip, though less often. |
#19
|
|||
|
|||
my god. . . there were only 2-3 guys that gave you the correct advice. it's 1
of 2 things, the unloader as they suggested is bad or if the check valve is not seating , air will be allowed to flow back into the cylinder thus giving the moter a much larger initial load at start up. Do these couple of checks: 1st start compressor and when it reaches it's cut off pressure and stops, loosen the fitting on the steel line going from cylinder to tank. loosen at the cylinder. you should be able to remove the fitting completely w/ out hearing any hissing. IF it hisses, check valve is bad. No hiss = bad unloader, located by your pressure sw. let me know what you find , but theres a 99.9 % chance iit's 1 of those 2 things. |
#20
|
|||
|
|||
are you serious ? ? ? and if it trips the 30 should he go up to . . .ohhh
maybe 60? Hell just go directly to the power co. feeder. and going to 220 isn't gonna do a damn thing either. if you go 220 then your F.L.A is 1/2 of F.L.A at 110. the moter is draw as much as it can to try and start. |
#21
|
|||
|
|||
Playintennis5274 wrote: my god. . . there were only 2-3 guys that gave you the correct advice. it's 1 of 2 things, the unloader as they suggested is bad or if the check valve is not seating , air will be allowed to flow back into the cylinder thus giving the moter a much larger initial load at start up. Do these couple of checks: 1st start compressor and when it reaches it's cut off pressure and stops, loosen the fitting on the steel line going from cylinder to tank. loosen at the cylinder. you should be able to remove the fitting completely w/ out hearing any hissing. IF it hisses, check valve is bad. No hiss = bad unloader, located by your pressure sw. let me know what you find , but theres a 99.9 % chance iit's 1 of those 2 things. If the check valve is shot (and unloader is OK), it will continue to hiss (constantly) until the compressor kicks back on. This is common. The compressor will try to cycle frequently to restore the pressure. Everything will seem fine while the compressor is running. Once it reaches pressure and shuts off (actuating the unloader), it will hiss constantly again, etcetera. |
#22
|
|||
|
|||
If the check valve is shot (and unloader is OK), it will continue to
hiss (constantly) until the compressor kicks back on. This is common. The compressor will try to cycle frequently to restore the pressure. Everything will seem fine while the compressor is running. Once it reaches pressure and shuts off (actuating the unloader), it will hiss constantly again, etcetera. Yup. I went out and played with my C/H today. If it shuts off on it's own (switch made) it hisses air. If I turn it off early from the disconnect it doesn't "unload" and it grunts when it restarts. (I didn't try that too many times). I vote for the unloader being bad too. Sorry about the check valve FUD. (Unless machine this predates unloaders). |
#23
|
|||
|
|||
|
#24
|
|||
|
|||
I was also thinking start up load. Sometimes the electrical switch has an
adjustment, so you can set the "turn on" pressure down a bit lower. Or you can make a pinhole leak right after the compressor, so that when the comp starts, it's under zero pressure. Needs a check valve after the pinhole leak. Best bet is to check the volts and amps at startup, and see if that tells you something useful. -- Christopher A. Young Learn more about Jesus www.lds.org www.mormons.com "PaPaPeng" wrote in message news On Thu, 28 Oct 2004 21:02:05 GMT, "Red Neckerson" wrote: Also, you aren't running it with an extension cord are you? I had a neighbor that had trouble with his. Worked fine for years and it started tripping the breaker. He put a new breaker in - same thing. Bought a new capacitor and then eventually bought a new motor. I asked him what he was doing different and he said he was using it away from his shed and had it hooked to a 100 foot extension cord. Bingo. That was his problem. That was exactly my problem too. There is a voltage drop if your extension cord is too long. That plus the start-up load trips the breaker. The solution 1. Use an extra long air hose instead. There won't be any air pressure drop and the tools will work at full power. 2. Open the air tank valve to release the pressure so that the start-up load isn't high enough to trip the breaker. This is still a poor solution because the breaker will still trip, though less often. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
circuit breaker popping once every 24 hrs | Home Repair | |||
Dryer flips main circuit breaker occasionally | Home Repair | |||
Strange not-quite-240 high-voltage smoke problem... short? circuit breaker? | Home Repair | |||
can a circuit re-enter the breaker box? | Home Repair | |||
breaker tripping | Home Repair |