I have some questions related to the switches that can/should be used
for a fan/heater combination unit.

I want to install a Panasonic FV-11VH2 in my bathroom. The unit requires
a 20A circuit, which I assume is because of the heater. I will be
pulling a dedicated 20A circuit using 12-2 w/ground from the basement to
the attic for this unit, but I'm a tad confused about the switches.

On this page there are 2 switches that I am considering. One of them is
a humidity sensing switch (FS-100), the other is a 2 function toggle
switch (FSR-500).

http://www.dewstop.com/

I'm not sure which switch I want to use. Obviously if I use the FS-100
for the fan, I'll need a separate switch for the heater. If I decide to
forgo the humidity sensor, I'll use the FSR-500, assuming it's OK to use
based on my questions below.

Here are my questions:

Regarding the FS-100 Humidity Sensing switch:

The only rating I see for the FS-100 humidity sensing switch is "Maximum
Fan Load: 1/8th hp or 3 amps".

1 - Do I need to be concerned as to whether the switch is rated for 15A
or 20A?

2 - Since I will be using 12-2 w/ground for the 20A circuit, do I need
to run 12-2 to this switch also, regardless of it's rating?

Obviously this switch will only be used for the fan portion of the unit,
which would normally only require a 15A circuit, but I'm not sure how
the wiring rules deals with the switch and/or switch leg for a 20A
circuit. Note: this switch requires a neutral wire, so space in the box
may also be an issue, especially if I need to use 12g.

Regarding the FSR-500 2 function toggle switch:

The website says these 3 things:

- Compatible with ALL makers of Fans, Lights, Heaters
- Best for use with: a fan/light combination, a fan/heater
combination, or a 2-speed fan
- Maximum Total Load: 15 amps

1 - So, if the fan/heater unit itself requires a 20A circuit, am I
allowed to use a switch rated for 15A?

2 - Do the wires need to be 12g to the switch? (I'm pretty sure I know
that answer to but I just want to make sure.)

Thanks.




  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,377
Default Switch For Fan/Heater Unit On 20A Circuit

On 03/09/2014 01:29 PM, DerbyDad03 wrote:


snip

Regarding the FS-100 Humidity Sensing switch:

The only rating I see for the FS-100 humidity sensing switch is "Maximum
Fan Load: 1/8th hp or 3 amps".

1 - Do I need to be concerned as to whether the switch is rated for 15A
or 20A?

2 - Since I will be using 12-2 w/ground for the 20A circuit, do I need
to run 12-2 to this switch also, regardless of it's rating?


The wires going to the fan switch do not have tp be rated at 20 amps. 15
amp wiring is OK

Obviously this switch will only be used for the fan portion of the unit,
which would normally only require a 15A circuit, but I'm not sure how
the wiring rules deals with the switch and/or switch leg for a 20A
circuit. Note: this switch requires a neutral wire, so space in the box
may also be an issue, especially if I need to use 12g.

Regarding the FSR-500 2 function toggle switch:

The website says these 3 things:

- Compatible with ALL makers of Fans, Lights, Heaters
- Best for use with: a fan/light combination, a fan/heater
combination, or a 2-speed fan
- Maximum Total Load: 15 amps

1 - So, if the fan/heater unit itself requires a 20A circuit, am I
allowed to use a switch rated for 15A?


The heater will of course require a 20 amp switch or more. You'd never
want to use a 15 amp switch for a 15 amp load.

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Switch For Fan/Heater Unit On 20A Circuit

On Sunday, March 9, 2014 2:29:34 PM UTC-4, DerbyDad03 wrote:
I have some questions related to the switches that can/should be used

for a fan/heater combination unit.



I want to install a Panasonic FV-11VH2 in my bathroom. The unit requires

a 20A circuit, which I assume is because of the heater. I will be

pulling a dedicated 20A circuit using 12-2 w/ground from the basement to

the attic for this unit, but I'm a tad confused about the switches.



On this page there are 2 switches that I am considering. One of them is

a humidity sensing switch (FS-100), the other is a 2 function toggle

switch (FSR-500).



http://www.dewstop.com/



I'm not sure which switch I want to use. Obviously if I use the FS-100

for the fan, I'll need a separate switch for the heater. If I decide to

forgo the humidity sensor, I'll use the FSR-500, assuming it's OK to use

based on my questions below.



Here are my questions:



Regarding the FS-100 Humidity Sensing switch:



The only rating I see for the FS-100 humidity sensing switch is "Maximum

Fan Load: 1/8th hp or 3 amps".



1 - Do I need to be concerned as to whether the switch is rated for 15A

or 20A?



I would say no. The fan is within the switch rating. This is like
installing a ceiling fan control or light dimmer. There are millions
of light dimmers out there that are rated for say 700W max and
they are on 15A, 20A light circuits.




2 - Since I will be using 12-2 w/ground for the 20A circuit, do I need

to run 12-2 to this switch also, regardless of it's rating?


Yes. You kind of wind up doing that anyway no? They are
probably going in the same box, so what's left, some pig tails?




Obviously this switch will only be used for the fan portion of the unit,

which would normally only require a 15A circuit, but I'm not sure how

the wiring rules deals with the switch and/or switch leg for a 20A

circuit. Note: this switch requires a neutral wire, so space in the box

may also be an issue, especially if I need to use 12g.



Regarding the FSR-500 2 function toggle switch:



The website says these 3 things:



- Compatible with ALL makers of Fans, Lights, Heaters

- Best for use with: a fan/light combination, a fan/heater

combination, or a 2-speed fan

- Maximum Total Load: 15 amps



1 - So, if the fan/heater unit itself requires a 20A circuit, am I

allowed to use a switch rated for 15A?



No

And I wouldn't use that $18 switch. There should be similar
cheaper 20A switches available at HD, electric supply, etc.




2 - Do the wires need to be 12g to the switch? (I'm pretty sure I know

that answer to but I just want to make sure.)


Yes.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 460
Default Switch For Fan/Heater Unit On 20A Circuit

Derby,

Your unit draws more than 12 amps, so it needs 20amp wiring, fusing.
That's what needs to go to the switchbox from the main panel
.. The heater draws just under 12 amps. So the wiring to and switch for the
heater should be for 20 amps. Neither of the switches that you are looking
at can handle 20 amps. Any hardware store will have 20 amp switches in many
styles and colors.
Your fan draws 1/4 of an amp. It will happily work with the humidity
sensor switch. 12-2 is overkill for the fan but you've already got it so use
it.
So, in sum, use 12-2 throughout, get a 20 amp switch for the heater and
the snazzy FS-100 for the fan. Try to match the 20 amp switch style to the
FS-100. Get your wife's approval on the switch style, color, and
switchplate.

Dave M.



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8,582
Default Switch For Fan/Heater Unit On 20A Circuit

On Sun, 09 Mar 2014 13:37:30 -0500, philo* wrote:


Regarding the FSR-500 2 function toggle switch:

The website says these 3 things:

- Compatible with ALL makers of Fans, Lights, Heaters


I wonder if this is related to the problem. Switches are not meant to
be compatible with the makers of heaters. They can be compatible with
all makes of heaters. But not all models.

- Best for use with: a fan/light combination, a fan/heater
combination, or a 2-speed fan
- Maximum Total Load: 15 amps

1 - So, if the fan/heater unit itself requires a 20A circuit, am I
allowed to use a switch rated for 15A?


The heater will of course require a 20 amp switch or more. You'd never
want to use a 15 amp switch for a 15 amp load.


So since the OP is using a big heater, he can't use this switch. The
big heater is not one of the models it's compatible with, even if it
claims to be compatible with all makers.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Switch For Fan/Heater Unit On 20A Circuit

On Sunday, March 9, 2014 2:37:30 PM UTC-4, philo* wrote:
On 03/09/2014 01:29 PM, DerbyDad03 wrote:





snip



Regarding the FS-100 Humidity Sensing switch:




The only rating I see for the FS-100 humidity sensing switch is "Maximum


Fan Load: 1/8th hp or 3 amps".




1 - Do I need to be concerned as to whether the switch is rated for 15A


or 20A?




2 - Since I will be using 12-2 w/ground for the 20A circuit, do I need


to run 12-2 to this switch also, regardless of it's rating?






The wires going to the fan switch do not have tp be rated at 20 amps. 15

amp wiring is OK



I don't believe that is correct. There may be some exceptions
where a tap can use conductors that are less than that required
by the breaker, but I don't believe this is one of them. AFAIK,
if the breaker is 20A, then all the wiring connecting everything
needs to ge 12G.






Obviously this switch will only be used for the fan portion of the unit,


which would normally only require a 15A circuit, but I'm not sure how


the wiring rules deals with the switch and/or switch leg for a 20A


circuit. Note: this switch requires a neutral wire, so space in the box


may also be an issue, especially if I need to use 12g.




Regarding the FSR-500 2 function toggle switch:




The website says these 3 things:




- Compatible with ALL makers of Fans, Lights, Heaters


- Best for use with: a fan/light combination, a fan/heater


combination, or a 2-speed fan


- Maximum Total Load: 15 amps




1 - So, if the fan/heater unit itself requires a 20A circuit, am I


allowed to use a switch rated for 15A?




The heater will of course require a 20 amp switch or more. You'd never

want to use a 15 amp switch for a 15 amp load.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Switch For Fan/Heater Unit On 20A Circuit

On 3/9/2014 3:48 PM, David L. Martel wrote:
Derby,

Your unit draws more than 12 amps, so it needs 20amp wiring, fusing.
That's what needs to go to the switchbox from the main panel.


That is actually if the load is "continuous", which is over 3 hours. It
may be on that long. DD says the manufacturer wants a 20A circuit.

If you load a breaker over 80% and the load is on for over 3 hours the
breaker may trip. That is the only reason I know of for the 80% rule.

The heater draws just under 12 amps. So the wiring to and switch for the
heater should be for 20 amps.


The wiring has to be #12 because the circuit is #12.

The switch can be 15A. I would likely use a spec grade (better quality).

Neither of the switches that you are looking
at can handle 20 amps. Any hardware store will have 20 amp switches in many
styles and colors.
Your fan draws 1/4 of an amp. It will happily work with the humidity
sensor switch. 12-2 is overkill for the fan but you've already got it so use
it.


You need #12 because the circuit is #12.

I agree the humidity switch should be fine.

Dewstop - if the total load is 15A or less and Dewstop is rated 15A you
could use it. But it is expensive. Is it UL listed?

So, in sum, use 12-2 throughout, get a 20 amp switch for the heater and
the snazzy FS-100 for the fan. Try to match the 20 amp switch style to the
FS-100. Get your wife's approval on the switch style, color, and
switchplate.

Dave M.




  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,399
Default Switch For Fan/Heater Unit On 20A Circuit

On Monday, March 10, 2014 3:05:38 PM UTC-4, bud-- wrote:
On 3/9/2014 3:48 PM, David L. Martel wrote:

Derby,




Your unit draws more than 12 amps, so it needs 20amp wiring, fusing.


That's what needs to go to the switchbox from the main panel.




That is actually if the load is "continuous", which is over 3 hours. It

may be on that long. DD says the manufacturer wants a 20A circuit.



If you load a breaker over 80% and the load is on for over 3 hours the

breaker may trip. That is the only reason I know of for the 80% rule.



The heater draws just under 12 amps. So the wiring to and switch for the


heater should be for 20 amps.




The wiring has to be #12 because the circuit is #12.



The switch can be 15A. I would likely use a spec grade (better quality).



Neither of the switches that you are looking


at can handle 20 amps. Any hardware store will have 20 amp switches in many


styles and colors.


Your fan draws 1/4 of an amp. It will happily work with the humidity


sensor switch. 12-2 is overkill for the fan but you've already got it so use


it.




You need #12 because the circuit is #12.



I agree the humidity switch should be fine.



Dewstop - if the total load is 15A or less and Dewstop is rated 15A you

could use it. But it is expensive. Is it UL listed?



I don't see why the dewstop has to be rated at 15A. The fan draws less
that an amp. It's controlled by that electronic dewstop gizmo. That
would seem to me to be just like putting a ceiling fan controller or
a light dimmer that rated at 700W on any light circuit, be it 15A,
20A, etc. The light dimmer can't handle 15A, yet it's apparently
code compliant, no?
  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Switch For Fan/Heater Unit On 20A Circuit

wrote:
On Sun, 09 Mar 2014 14:29:34 -0400, DerbyDad03
wrote:

Panasonic FV-11VH2


I looked up the specs on this
"Combined Amps 12.2 "

A 15a switch will be fine since switches are selected based on the
load, not the circuit ampacity.
The switch that says "max 3a" is only good if you are switching the
fan. The heater would smoke it pretty quickly.

All of the wire in the wall needs to be sized to the over current
device (20a=12g copper). There are some exceptions but this is not
one.


Everything you have said is basically what I expected to hear.

I have a couple of other questions, based on the info in this document:

https://www.acwholesalers.com/hvac/p...FV-WCSW-sb.pdf

First "question" - I'm pretty sure I've got this right, please verify.

The first switch in the document - FV-WCCS1 - is what I am planning on
using for the fan. It's a Humidity Sensing switch rated for 15A.

The last switch in the document - FV-WCD01 - is what I am planning on using
for the heater. It's a count down timer switch rated for 20A.

That seems OK to me.

Second "question" - mostly just a curiosity.

I'm a bit confused by the switch directly above the FV-WCD01, specifically
FV-WCSW41. It contains 3 independent rocker switches, each rated for 15A,
but also says that the total switch amperage is 20A. It also says that it
is designed for the FV-11VHL2, which has a fan, heater and light. So does
that mean that if I wanted to, I could use a 15A switch for the heater in
my FV-11VH2, which is basically the same unit but without the light? In
other words, if I had 2 separate 15A switches, one for the fan and one for
the heater, that would be OK, right?

Thanks again for the help.
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 390
Default Switch For Fan/Heater Unit On 20A Circuit

On 3/10/2014 2:42 PM, wrote:
On Monday, March 10, 2014 3:05:38 PM UTC-4, bud-- wrote:
On 3/9/2014 3:48 PM, David L. Martel wrote:

Derby,

Your unit draws more than 12 amps, so it needs 20amp wiring, fusing.
That's what needs to go to the switchbox from the main panel.


That is actually if the load is "continuous", which is over 3 hours. It
may be on that long. DD says the manufacturer wants a 20A circuit.

If you load a breaker over 80% and the load is on for over 3 hours the
breaker may trip. That is the only reason I know of for the 80% rule.

The heater draws just under 12 amps. So the wiring to and switch for the
heater should be for 20 amps.


The wiring has to be #12 because the circuit is #12.

The switch can be 15A. I would likely use a spec grade (better quality).

Neither of the switches that you are looking
at can handle 20 amps. Any hardware store will have 20 amp switches in many
styles and colors.


Your fan draws 1/4 of an amp. It will happily work with the humidity
sensor switch. 12-2 is overkill for the fan but you've already got it so use


it.


You need #12 because the circuit is #12.

I agree the humidity switch should be fine.

Dewstop - if the total load is 15A or less and Dewstop is rated 15A you
could use it. But it is expensive. Is it UL listed?



I don't see why the dewstop has to be rated at 15A. The fan draws less
that an amp. It's controlled by that electronic dewstop gizmo. That
would seem to me to be just like putting a ceiling fan controller or
a light dimmer that rated at 700W on any light circuit, be it 15A,
20A, etc. The light dimmer can't handle 15A, yet it's apparently
code compliant, no?


If all you are handling is the fan you don't need 15A, which I said
above for the humidity sensor.

DD also talked about using a "2 function switch" which would presumably
switch the heater.


After looking again, price for the humidity sensor looks OK.

I like timers for bath fans, where you can run it for 5 minutes after
you leave (or whatever). The fan control has a timer too.



  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14,845
Default Switch For Fan/Heater Unit On 20A Circuit

bud-- wrote:
On 3/10/2014 2:42 PM, wrote:
On Monday, March 10, 2014 3:05:38 PM UTC-4, bud-- wrote:
On 3/9/2014 3:48 PM, David L. Martel wrote:

Derby,

Your unit draws more than 12 amps, so it needs 20amp wiring, fusing.
That's what needs to go to the switchbox from the main panel.

That is actually if the load is "continuous", which is over 3 hours. It
may be on that long. DD says the manufacturer wants a 20A circuit.

If you load a breaker over 80% and the load is on for over 3 hours the
breaker may trip. That is the only reason I know of for the 80% rule.

The heater draws just under 12 amps. So the wiring to and switch for the
heater should be for 20 amps.

The wiring has to be #12 because the circuit is #12.

The switch can be 15A. I would likely use a spec grade (better quality).

Neither of the switches that you are looking
at can handle 20 amps. Any hardware store will have 20 amp switches in many
styles and colors.

Your fan draws 1/4 of an amp. It will happily work with the humidity
sensor switch. 12-2 is overkill for the fan but you've already got it so use

it.

You need #12 because the circuit is #12.

I agree the humidity switch should be fine.

Dewstop - if the total load is 15A or less and Dewstop is rated 15A you
could use it. But it is expensive. Is it UL listed?



I don't see why the dewstop has to be rated at 15A. The fan draws less
that an amp. It's controlled by that electronic dewstop gizmo. That
would seem to me to be just like putting a ceiling fan controller or
a light dimmer that rated at 700W on any light circuit, be it 15A,
20A, etc. The light dimmer can't handle 15A, yet it's apparently
code compliant, no?


If all you are handling is the fan you don't need 15A, which I said above
for the humidity sensor.

DD also talked about using a "2 function switch" which would presumably switch the heater.


After looking again, price for the humidity sensor looks OK.

I like timers for bath fans, where you can run it for 5 minutes after you
leave (or whatever). The fan control has a timer too.


I ended up ordering a _real_ humidity sensor switch made by Leviton after
reading the reviews on the Dewstop FS-100. That's the actual switch that
Panasonic sells with their label.

Turns out the FS-100 is a non-adjustable _condensation_ sensing switch
which many people were not happy with. Seems that the FS-100 didn't come on
until the walls were dripping wet, especially depending on the placement of
the switch. Someone said it had to be really close to the shower and up
high to even activate.

The Leviton IPHS5-1LW got better reviews and seems like a better switch for
my needs. As long as I was buying Leviton, I also ordered the Leviton
LTB60-1LZ countdown timer. It's rated for 20A so it should work fine with
the heater.

I ran the wire to the attic last night. Now I need a deep 3 gang box and a
Leviton dimmer for the light. The current fan timer and light switch are in
2 separate switch boxes but I want to clean that up a bit. I'll need a deep
box because all of the switches are pretty big and there will be a bunch of
12g wire in the box. Luckily it's going in the wall where the main stack
runs so it's an extra deep wall. I could fit a switch box as deep as a
shoebox in there. Hey, that's an idea...I may just try that. ;-)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outside air conditioner unit blew circuit breaker, sparked ... Doug McLaren Home Repair 16 October 29th 09 02:08 PM
AC condensing unit + pressure switch JackpipE Home Repair 1 June 24th 08 02:02 PM
Furnace Comes On When Circuit Breaker Turned On To Central Unit nowforsale Home Repair 6 September 13th 06 04:12 AM
Comsumer unit RCD trips on non-RCD protected circuit activity ian UK diy 4 April 25th 06 08:59 PM
Consumer unit switch tripping despite RCD Dundonald UK diy 9 June 7th 05 09:50 AM


All times are GMT +1. The time now is 04:11 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"