Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 55
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

Janitrol Model A36-15
Schemtaic here http://www.ceridium.com/schematic.html

The optional Emergency Heat Relay is installed, and the airhandler is wired
for slow speed.

What causes the electric heating elements in the unit to heat up and the
blower fan to come on when the 2 circuit breakers on the unit are flipped
on, with the thermostat set to Off?


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

nowforsale wrote:
Janitrol Model A36-15
Schemtaic here http://www.ceridium.com/schematic.html

The optional Emergency Heat Relay is installed, and the airhandler is wired
for slow speed.

What causes the electric heating elements in the unit to heat up and the
blower fan to come on when the 2 circuit breakers on the unit are flipped
on, with the thermostat set to Off?


Hi,
And it keeps running like that? Or I wownder if the thing is in test mode?
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 165
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

Either your heat sequencer is stuck or it is getting 24 volts from
somewhere. Check and see if you have 24 volts to the sequencer. If not,
tap on the sequencer with a screwdriver handle and see if it goes off.
Post the results and we can go from there. Good luck Larry

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 55
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

"lp13-30" wrote in message
...
Either your heat sequencer is stuck or it is getting 24 volts from
somewhere. Check and see if you have 24 volts to the sequencer. If not,
tap on the sequencer with a screwdriver handle and see if it goes off.
Post the results and we can go from there. Good luck Larry


Am not familiar with what the sequencer is or how to check to see if it is
getting 24 volts. Is the sequencer the thing with M1, M2, M3, M4, M5, and M6
on it?

Tried tapping on the 3 things now colored yellow in the schematic here
http://www.ceridium.com/schematic.html
(the Emergency Heat Relay, the Blower Time Delay Relay, and the other
thing),
to no avail, the furnace and blower sitll come on when the circuit breakers
are flipped on.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 55
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

the motor in this unit is 1/3 horsepower and the blower is wired for slow
speed, is there way to reduce the speed even more? maybe even have it to
where the speed could be adjusted in a variable fashion, like maybe hooking
up a light dimmer switch inline on the motor wiring?


Janitrol Model A36-15
Schemtaic here http://www.ceridium.com/schematic.html




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 55
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

"lp13-30" wrote in message
...
Either your heat sequencer is stuck or it is getting 24 volts from
somewhere. Check and see if you have 24 volts to the sequencer. If not,
tap on the sequencer with a screwdriver handle and see if it goes off.
Post the results and we can go from there. Good luck Larry


changed the sequencer with a new one but problem still exists

haven't yet checked to see if the sequencer is getting 24 volts; if it is
getting 24 volts, where would it be coming from?
isn't it supposed to get 24 volts from the 24 volt transformer?


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 165
Default Furnace Comes On When Circuit Breaker Turned On To Central Unit

The sequencer is nothing but a switch to turn the heat strips and blower
on when it gets 24 volts it. It is called a sequencer because it brings
the strips on one at a time (in sequence) rather than all at once,
mainly to keep lights from dimming etc, as itwould do if all came on at
once. Get a voltmeter and check between the white and common thermostat
wires at the air handler. Common should be blue. With the thermostat
off, there should be 0 volts. When he thermostat calls for heat, it
sends power from the red tstat wire to the white, putting 24 volts to
the sequencer, bringing the strips and blower on. If it is getting
24volts, disconnect the white at the thermostat and check again. If 0,
it is getting the voltage from the thermostat, if still 24, it is most
likely a short in the thermostat wires. Is this a heat pump, or just
electric heat? If it is, then it could also be shorted in the thermostat
wires going between the air handler and the ouside unit, or possibly a
bad defrost control board in the outside unit. Just go by the processs
of elimination til there is no 24 volts to the seq. Let me know what you
find. You in or near San Antonio? Larry

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
air conditioner circuit breaker trips Joseph Meehan Home Repair 18 May 11th 10 02:34 PM
Short in Circuit or Circuit breaker? Greg Home Repair 13 January 29th 06 06:45 PM
What Type Of Surge Protection House Circuit Breaker ? Robert11 Home Repair 9 August 4th 05 04:37 PM
Strange not-quite-240 high-voltage smoke problem... short? circuit breaker? Kent Monroe Home Repair 10 February 22nd 04 02:42 AM
Electric circuit breaker barry martin Home Repair 1 December 26th 03 04:41 AM


All times are GMT +1. The time now is 06:29 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"