On 3/6/2013 6:38 AM, HeyBub wrote:
The Daring Dufas wrote: On 3/5/2013 7:20 PM, Mikepier wrote: What about the outside disconnect? It is just simply a "pull-out" type disconnect, no fuses, just solid copper buss bars. I don't see any rating for it. How do I know it's rating? Or are all these type of disconnects just a standard rating? I personally don't like the pull out disconnects because they can corrode from mishandling and pranksters can make off with the pull out. I use the Square D dummy breaker in a rain proof box. It looks like a standard Square D QO breaker but with no over current protection and a real circuit breaker will actually snap-in in its place. ^_^ As for pranksters, my disconnect has a a padlock, the key to which is kept in the main circuit-breaker box (which also has a padlock). Trust no one. ^_^ TDD |
#42
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
The Daring Dufas wrote:
As for pranksters, my disconnect has a a padlock, the key to which is kept in the main circuit-breaker box (which also has a padlock). Trust no one. ^_^ I trust YOU -- To give what you believe to be the straight skinney on this newsgroup. Who know, if we ever met in person, I might even loan you a tool... |
#43
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/7/2013 7:27 AM, HeyBub wrote:
The Daring Dufas wrote: As for pranksters, my disconnect has a a padlock, the key to which is kept in the main circuit-breaker box (which also has a padlock). Trust no one. ^_^ I trust YOU -- To give what you believe to be the straight skinney on this newsgroup. Who know, if we ever met in person, I might even loan you a tool... I can appreciate that. I remember a famous man saying something to the effect, "Experience is a fool's best teacher." Believe me, I can admit to being a fool on more than one occasion but I survived it and learned from it. Years ago, I trained in martial arts and got knocked on my butt numerous times but I learned from it to the point that my instructors couldn't get through my coverup and I could block kicks and punches. Of course now, a couple of five year old kids could take me. ^_^ TDD |
#44
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Ok ,guys. Now something just came up . I know we are up to 51 posts
for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( 2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? |
#45
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
I'd leave the AC wire alone, and wire a power inlet. You'd be wise to make
some kind of transfer switch to make it idiot resistant. During a high stress power cut, it's easy enough to forget a step or two in the procedure. Christopher A. Young Learn more about Jesus www.lds.org .. "Mikepier" wrote in message ... I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? |
#46
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 8, 8:51*am, Mikepier wrote:
Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had *an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the *main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( *2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/ |
#47
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/8/2013 8:51 AM, Mikepier wrote:
Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. Hay bailing sounds great and of course he will never forget, be sick, not there and someone else needs to do it or whatever. What you described is simply hay bailing instead of using conventional common methods. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( 2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? |
#48
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 8, 9:09*am, "
wrote: On Mar 8, 8:51*am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had *an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the *main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( *2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? *Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? *If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/- Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. |
#49
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/8/2013 8:30 AM, Mikepier wrote:
On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( 2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/- Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...27-_-100151733 http://tinyurl.com/a9fqckb TDD |
#50
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 8, 10:01*am, The Daring Dufas the-daring-du...@stinky-
finger.net wrote: On 3/8/2013 8:30 AM, Mikepier wrote: On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had *an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the *main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( *2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? *Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? *If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...733&storeId=10.... http://tinyurl.com/a9fqckb TDD- Hide quoted text - - Show quoted text - So that double throw switch has to be put between the main panel and subpanel, (where the subpanel would have the essential circuits in them to run off generator) , right? |
#51
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/8/2013 9:31 AM, Mikepier wrote:
On Mar 8, 10:01 am, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 8:30 AM, Mikepier wrote: On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( 2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...733&storeId=10... http://tinyurl.com/a9fqckb TDD- Hide quoted text - - Show quoted text - So that double throw switch has to be put between the main panel and subpanel, (where the subpanel would have the essential circuits in them to run off generator) , right? Exactly. Sometimes there is a separate lighting panel which will have loads like wall outlets, furnace blower, kitchen, bathroom, etc with the heavy loads in an outdoor breaker box below the power meter and a large breaker feeding the indoor panel. Sometimes a separate panel with the heavy loads could be indoors next to the lighting panel. It depends on your setup but if there is only one main panel that is not the split variety (another variation) you can get a sub-panel which will use the same type breakers you have so you save money on breakers. I had my local inspector tell me it was OK the use the old panel as a junction box to splice your circuits for the sub-panel if the wires/cables were too short to move over to the sub panel. Don't forget the knock out blank inserts to fill in the openings for the removed breakers. ^_^ TDD |
#52
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 8, 12:08*pm, The Daring Dufas the-daring-du...@stinky-
finger.net wrote: On 3/8/2013 9:31 AM, Mikepier wrote: On Mar 8, 10:01 am, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 8:30 AM, Mikepier wrote: On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had *an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the *main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( *2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? *Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? *If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hidequoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...733&storeId=10... http://tinyurl.com/a9fqckb TDD- Hide quoted text - - Show quoted text - So that double throw switch has to be put between the main panel and subpanel, (where the subpanel would have the essential circuits in them to run off generator) , right? Exactly. Sometimes there is a separate lighting panel which will have loads like wall outlets, furnace blower, kitchen, bathroom, etc with the heavy loads in an outdoor breaker box below the power meter and a large breaker feeding the indoor panel. Sometimes a separate panel with the heavy loads could be indoors next to the lighting panel. It depends on your setup but if there is only one main panel that is not the split variety (another variation) you can get a sub-panel which will use the same type breakers you have so you save money on breakers. I had my local inspector tell me it was OK the use the old panel as a junction box to splice your circuits for the sub-panel if the wires/cables were too short to move over to the sub panel. Don't forget the knock out blank inserts to fill in the openings for the removed breakers. ^_^ TDD- Hide quoted text - - Show quoted text - Lets's go one step further. By any chance do they make double throw circuit breakerss? So if one wants to wire up just the essential circuits ( heat, light, etc), there would be 2 terminals on the individual breaker: one for normal power and one for generator. That way you just flip the breaker and it will switch to the generator side.without having to worry about shutting off the main. |
#53
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/8/2013 11:19 AM, Mikepier wrote:
On Mar 8, 12:08 pm, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 9:31 AM, Mikepier wrote: On Mar 8, 10:01 am, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 8:30 AM, Mikepier wrote: On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( 2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hidequoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...733&storeId=10... http://tinyurl.com/a9fqckb TDD- Hide quoted text - - Show quoted text - So that double throw switch has to be put between the main panel and subpanel, (where the subpanel would have the essential circuits in them to run off generator) , right? Exactly. Sometimes there is a separate lighting panel which will have loads like wall outlets, furnace blower, kitchen, bathroom, etc with the heavy loads in an outdoor breaker box below the power meter and a large breaker feeding the indoor panel. Sometimes a separate panel with the heavy loads could be indoors next to the lighting panel. It depends on your setup but if there is only one main panel that is not the split variety (another variation) you can get a sub-panel which will use the same type breakers you have so you save money on breakers. I had my local inspector tell me it was OK the use the old panel as a junction box to splice your circuits for the sub-panel if the wires/cables were too short to move over to the sub panel. Don't forget the knock out blank inserts to fill in the openings for the removed breakers. ^_^ TDD- Hide quoted text - - Show quoted text - Lets's go one step further. By any chance do they make double throw circuit breakerss? So if one wants to wire up just the essential circuits ( heat, light, etc), there would be 2 terminals on the individual breaker: one for normal power and one for generator. That way you just flip the breaker and it will switch to the generator side.without having to worry about shutting off the main. I'm sure someone manufactures a molded case high current switch like that but I haven seen one and I don't know of one that would have built in over-current protection. ^_^ TDD |
#54
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 8, 12:19*pm, Mikepier wrote:
On Mar 8, 12:08*pm, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 9:31 AM, Mikepier wrote: On Mar 8, 10:01 am, The Daring Dufas the-daring-du...@stinky- finger.net wrote: On 3/8/2013 8:30 AM, Mikepier wrote: On Mar 8, 9:09 am, " wrote: On Mar 8, 8:51 am, Mikepier wrote: Ok ,guys. Now something just came up . I know we are up to 51 posts for this thread already, and I was not sure whether to continue this one, or start a new one, but anyway: My friend had *an idea if he had gotten a generator one day, he can utilize the A/C disconnect panel outside to backfeed into the *main panel. Of course he would shut off the main breaker and pull the A/C disconnect when he did this. I can put an outdoor twistlock outlet next to the A/C disconnect panel, and put a short nipple between them an connect the wiring. But I cannot do this with the existing 10 guage wire since it is the old 10/2 stuff with a small ground on it. I would need to run an 8/3 with gnd ( *2 phases plus neutral). I know this is not the right way to backfeed a panel, but regardless, does it make sense now to run the 8/3 ? If you know it's not the right way, then why are you proposing to do it? *Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? *If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hidequotedtext - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. The interlock kit trader4 showed you is the least expensive "safe" way to do it but before that product was available I used a double throw safety switch and sub panel or put it between the lighting panel if it was separate from the a main panel with the heavy loads. Of course you run a separate line outdoors to your portable genset and depending on its capacity you will have to choose which loads to turn off/on as needed. ^_^ http://www.homedepot.com/p/t/1001517...733&storeId=10... http://tinyurl.com/a9fqckb TDD- Hide quoted text - - Show quoted text - So that double throw switch has to be put between the main panel and subpanel, (where the subpanel would have the essential circuits in them to run off generator) , right? Exactly. Sometimes there is a separate lighting panel which will have loads like wall outlets, furnace blower, kitchen, bathroom, etc with the heavy loads in an outdoor breaker box below the power meter and a large breaker feeding the indoor panel. Sometimes a separate panel with the heavy loads could be indoors next to the lighting panel. It depends on your setup but if there is only one main panel that is not the split variety (another variation) you can get a sub-panel which will use the same type breakers you have so you save money on breakers. I had my local inspector tell me it was OK the use the old panel as a junction box to splice your circuits for the sub-panel if the wires/cables were too short to move over to the sub panel. Don't forget the knock out blank inserts to fill in the openings for the removed breakers. ^_^ TDD- Hide quoted text - - Show quoted text - Lets's go one step further. By any chance do they make double throw circuit breakerss? So if one wants to wire up just the essential circuits ( heat, light, etc), there would be 2 terminals on the individual breaker: one for normal power and one for generator. That way you just flip the breaker and it will switch to the generator side.without having to worry about shutting off the main.- Hide quoted text - - Show quoted text - It would have to be not only a unique breaker, but also a unique panel to accept said breaker. It doesn't exist for some very good reasons. And if it did, what do you think that special panel and those special breakers would cost compared to the simple alternatives? |
#55
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
Mikepier wrote:
If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/- Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. Just an observation, but none of the devices offered on this website are UL approved. They claim to meet "all NEC requirements for optional standby systems (Article 702)," but that's easy to say. |
#56
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Mar 9, 9:19*am, "HeyBub" wrote:
Mikepier wrote: If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/-Hide quoted text - - Show quoted text - That is an excellent invention. I did not even know those interlocks existed. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. Just an observation, but none of the devices offered on this website are UL approved. They claim to meet "all NEC requirements for optional standby systems (Article 702)," but that's easy to say.- Hide quoted text - - Show quoted text - They go a bit further than that. They have the test reports that show that they have been tested for use as accessories with UL 67 listed panelboards. What exactly that means in regard to making them code compliant when put on a panel, I don't know. This issue is why I recommended going with an interlock from the actual panel manufacturer, if one is available. That way you know there is no issue. From some discussions I've seen online it looks like people are using the Interlockit product. How many of those are actually inspected, do some inspectors have issues with it, IDK. Given that it's just a piece of metal, has no direct involvement with the electricity, obviously does what it' intended to do, I'd have no problem using it from a safety standpoint. But it would be a bitch to buy it, install it and have it rejected. I guess best thing would be to take a print out of the info, including their test report, over to the inspector and ask before buying. Especially if you're in an area that tends to be tougher. |
#57
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/9/2013 8:19 AM, HeyBub wrote:
Mikepier wrote: If you know it's not the right way, then why are you proposing to do it? Why take an AC circuit that is 100% legal nd safe as it is and turn it into something to be used as a dangerous code violation? If he wants a generator connection, install an inlet outside and run it to a proper interlock device installed on the main panel. If the panel maker doesn't have one, then try: http://www.interlockkit.com/ That is an excellent invention. I did not even know those interlocks existed. They usually show up when threads get into connecting generators to the house panel. Last time was probably November. A little pricey at $150, but I'll definately consider it. The only issue is finding space in the main panel for an extra double pole breaker for the generator, but I can use some twins here and there on lighting circuits to to free it up. You can add a subpanel and move some of the loads to it. Panels will have a limitation on where you can install half-sized breakers. It may be in all positions, no positions, or anywhere in between. The label will tell you. Half-size/twin breakers (in general) can only be installed where the label says they can. Just an observation, but none of the devices offered on this website are UL approved. They claim to meet "all NEC requirements for optional standby systems (Article 702)," but that's easy to say. http://www.interlockkit.com/warranty01.htm "Tested for use with UL 67 Listed Panelboards Ref. Wyle Laboratories Test Report T52431-01 Wyle is a Nationally Recognized Testing Laboratory authorized by OSHA for UL standard 67 and recognized by all 50 US States" Depends on whether your AHJ recognizes Wylie. There is probably not a clean way to get these interlocks listed for other manufacturer's panelboards. But they are a mechanical device that does not have electrical ratings - likely they are OK. Ask the AHJ. Several manufacturers (including SquareD and Siemens) have a similar mechanical interlock for their panels. |
#59
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#60
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On 3/3/2013 7:22 PM, Mikepier wrote:
I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. a new unit will require less amps. 10 ga on a 30 is all you need for what he has. -- Steve Barker remove the "not" from my address to email |
#61
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sunday, March 3, 2013 at 7:22:54 PM UTC-6, Mikepier wrote:
I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. well you will just have to upgrade |
#62
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Tuesday, March 19, 2013 at 10:57:02 PM UTC-5, Steve Barker wrote:
On 3/3/2013 7:22 PM, Mikepier wrote: I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. a new unit will require less amps. 10 ga on a 30 is all you need for what he has. -- Steve Barker remove the "not" from my address to email |
#63
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sunday, March 3, 2013 at 7:22:54 PM UTC-6, Mikepier wrote:
I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. |
#64
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sunday, March 3, 2013 at 7:22:54 PM UTC-6, Mikepier wrote:
I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. |
#65
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Sunday, March 3, 2013 at 7:22:54 PM UTC-6, Mikepier wrote:
I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. |
#66
![]()
Posted to alt.home.repair
|
|||
|
|||
![]() |
#67
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
On Friday, May 27, 2016 at 8:50:41 PM UTC-4, wrote:
On Fri, 27 May 2016 17:38:19 -0700 (PDT), wrote: On Sunday, March 3, 2013 at 7:22:54 PM UTC-6, Mikepier wrote: I'm running new electric in a friends basement and so far uncovered a lot of bad wiring jobs, buried splice boxes, you name it. So now I noticed that the central A/C compressor is wired with 10 guage wire. I'm pretty sure its suppose to be 8 guage. And also the existing 10 guage wire is hooked up to a 40 A breaker, which of course is not right, its suppose to be a 30A breaker. So since everything is wide open now, I was wondering should I run new 8 guage wire to the A/C? The unit is a Lennox, I beleive a 3 ton unit, and the plate says "Min circuit ampacity 24.4 amps" and it also says " Max fuse or ckt bkr 40A". Even if the unit has been running fine all these years, I'm wondering what happens down the road if it needs to be replaced with a new unit that needs more amperage. the existing 10 guage wire will not be sufficient I'm thinking. well you will just have to upgrade Wrong, 10ga is plenty. There are different rules for motor loads IDK why this old thread had to be re-opened, the full thread with all the facts is here, but as you say, what's there is fine. The problem is that some people can't understand that motor load circuit breakers are sized differently and you can have a breaker that is larger than would be allowed for a lighting or water heater circuit that used the same size conductor. |
#68
![]()
Posted to alt.home.repair
|
|||
|
|||
![]()
lol so they come and arrest you for arguing with them? Where do you live? Afghanistan? China?
-- For full context, visit https://www.homeownershub.com/mainte...or-739437-.htm |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Air Compressor usage & size | Home Ownership | |||
Air compressor hose size | Home Repair | |||
What size air compressor | Home Repair | |||
Compressor size for HVLP | Woodworking | |||
compressor size | Woodworking |