Default Let me belabor the 12 gauge - 14 guage discussion

Hi,

I recently asked whether it's OK an a 20amp dedicated circuit intended
for a heater/fan/n.light/light combination to run 14 gauge wire from
the switch to the fixture, except for the heater part. And of course,
the answer was "no" because you are not suppose to use 14 guage wire
on a 20 amp circuit.

But the wire in the fixture is 14 gauge! (Except for the heater part.
There are three 14 gauge and one 12 gauge pairs inside the fixture.)
How is that not breaking the code on the part of the manufacturer?

Thanks,

Aaron
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 109
Default Let me belabor the 12 gauge - 14 guage discussion


wrote in message
...
Hi,

I recently asked whether it's OK an a 20amp dedicated circuit intended
for a heater/fan/n.light/light combination to run 14 gauge wire from
the switch to the fixture, except for the heater part. And of course,
the answer was "no" because you are not suppose to use 14 guage wire
on a 20 amp circuit.

But the wire in the fixture is 14 gauge! (Except for the heater part.
There are three 14 gauge and one 12 gauge pairs inside the fixture.)
How is that not breaking the code on the part of the manufacturer?


Because you won't be adding more circuits inside the fixture!

With 14 gauge in your wiring (not inside a fixture) there is the chance that
someone will later add more 20 amp circuits because they see the 12 guage
wire and don't realize that there is any 14 gauge in your circuit.




  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 8
Default Let me belabor the 12 gauge - 14 guage discussion

Yes, but I was proposing is connecting the switch to the fixture (a 4'
run!) with 14 gauge wire. That would essentially make it an extension
of the fixture's own 14 guage. Why is that not legitimate. If the
answer is that "the code tries to be overprotective", I'll accept
that. But I want to make sense out of it.

Thanks.

Aaron
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 109
Default Let me belabor the 12 gauge - 14 guage discussion


wrote in message
...
Yes, but I was proposing is connecting the switch to the fixture (a 4'
run!) with 14 gauge wire. That would essentially make it an extension
of the fixture's own 14 guage. Why is that not legitimate. If the
answer is that "the code tries to be overprotective", I'll accept
that. But I want to make sense out of it.


Because the fixture will be at a junction box... Wiring could get added from
this box to a new circuit.


  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 350
Default Let me belabor the 12 gauge - 14 guage discussion

On Jun 3, 3:17*am, "Calab" wrote:
wrote in message

...

Yes, but I was proposing is connecting the switch to the fixture (a 4'
run!) with 14 gauge wire. That would essentially make it an extension
of the fixture's own 14 guage. Why is that not legitimate. If the
answer is that "the code tries to be overprotective", I'll accept
that. But I want to make sense out of it.


Because the fixture will be at a junction box... Wiring could get added from
this box to a new circuit.


The fixture's junction box is _inside_ the fixture. Are you suggesting
that someone might add a new circiut downstream from the fixture? That
would be far fetched.


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,563
Default Let me belabor the 12 gauge - 14 guage discussion


"Calab" wrote in message
news:Wd61k.2403$gc5.1343@pd7urf2no...

wrote in message
...
Yes, but I was proposing is connecting the switch to the fixture (a 4'
run!) with 14 gauge wire. That would essentially make it an extension
of the fixture's own 14 guage. Why is that not legitimate. If the
answer is that "the code tries to be overprotective", I'll accept
that. But I want to make sense out of it.


Because the fixture will be at a junction box... Wiring could get added
from this box to a new circuit.


The wiring in the fixture probably wasn't even #14, as the fixture
manufacturers use wires sizes only large enough for the loads on them, and
don't have a minimum trade size of #14. They are also governed by a
different code than the building wiring




  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,199
Default Let me belabor the 12 gauge - 14 guage discussion

On Jun 3, 6:40�am, "RBM" wrote:
"Calab" wrote in message

news:Wd61k.2403$gc5.1343@pd7urf2no...



wrote in message
...
Yes, but I was proposing is connecting the switch to the fixture (a 4'
run!) with 14 gauge wire. That would essentially make it an extension
of the fixture's own 14 guage. Why is that not legitimate. If the
answer is that "the code tries to be overprotective", I'll accept
that. But I want to make sense out of it.


Because the fixture will be at a junction box... Wiring could get added
from this box to a new circuit.


The wiring in the fixture probably wasn't even #14, as the fixture
manufacturers use wires sizes only large enough for the loads on them, and
don't have a minimum trade size of #14. They are also governed by a
different code than the building wiring



- Hide quoted text -

- Show quoted text -


I do admit its wierd, a great example you can plug a 4 0r even 16
gauge extension cord in a 20 amp outlet..........

and probbly have a nice fire........

have customers who try that

one in a mall put a groundung adapter in line oin a 16 gauge lamp cord
extension cord and plugged in their 18 amp seal press, appearance
before function or safety.

this in a mall.

I warned them, documented the hazard on my service slip and left.

6 months later they called again, having new problem.

they had responded to my safety issuem by stapling the lamp cord to a
carpeted wall

I fixed the machine left it heating, and went shopping for a air
conditioner extension cord which I gave them FREE.

came back removed light cord cut into pieces and tossed in trash.

the manager was MAD, We cant pay for the new cord.........

I told them its FREE, my contribution so the mall doesnt burn down or
someone get killed, espically a customer..... they could walk by the
area.

hey the paperwork for the fire reports will cost more than the
extension cord
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 280
Default Let me belabor the 12 gauge - 14 guage discussion

i use a 12 guage , but have heard that 10 guage and 14 guage shotguns
used to be popular , but not anymore.

----------------------------------------------------------------
http://www.minibite.com/america/malone.htm


  #11   Report Post  
Posted to alt.home.repair
Pat Pat is offline
external usenet poster
 
Posts: 657
Default Let me belabor the 12 gauge - 14 guage discussion

On Jun 3, 1:39*am, wrote:
Hi,

I recently asked whether it's OK an a 20amp dedicated circuit intended
for a heater/fan/n.light/light combination to run 14 gauge wire from
the switch to the fixture, except for the heater part. And of course,
the answer was "no" because you are not suppose to use 14 guage wire
on a 20 amp circuit.

But the wire in the fixture is 14 gauge! (Except for the heater part.
There are three 14 gauge and one 12 gauge pairs inside the fixture.)
How is that not breaking the code on the part of the manufacturer?

Thanks,

Aaron


If you want twisted logic, I'd bet it has more to do with distance.
The greater the load AND the longer the distance, the bigger wire you
need. The larger wire is needed on the feed to carry enough current
to the heater. If you ran the #14 the entire distance, it would be
undersized, considering the distance.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 330
Default Let me belabor the 12 gauge - 14 guage discussion


wrote in message
...
Hi,

I recently asked whether it's OK an a 20amp dedicated circuit intended
for a heater/fan/n.light/light combination to run 14 gauge wire from
the switch to the fixture, except for the heater part. And of course,
the answer was "no" because you are not suppose to use 14 guage wire
on a 20 amp circuit.

But the wire in the fixture is 14 gauge! (Except for the heater part.
There are three 14 gauge and one 12 gauge pairs inside the fixture.)
How is that not breaking the code on the part of the manufacturer?


1) that's the manufacturer's problem, not yours. If it's UL approved then
that's "gud enuf." There is little question that a hard fault across #14
wire will trip a 20 amp breaker so there really isn't much of a safety
concern. Light fixures often have #16 wire inside them. Most extension
cords are only #16.

2) In your PARTICULAR case, if you can you might want to run separate
circuits for the heater and for the lights. You can flip a coin to decide
whether to put the fan on the "light" side or the "heater" side. If the
heater is 10 amps or so, you can power it from #14 and #14 is already OK for
the lights and a small fan. If you use separate feeds in the same fixture
you have to make sure you connect the right neutral wire to the right cable.
Of course, the breaker for #14 circuits must be only 15 amps.


** Posted from http://www.teranews.com **
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 944
Default Let me belabor the 12 gauge - 14 guage discussion

On Tue, 03 Jun 2008 13:48:09 -0400, wrote:
On Tue, 3 Jun 2008 13:39:57 -0400, "John Gilmer"
wrote:



wrote in message
...
Hi,

I recently asked whether it's OK an a 20amp dedicated circuit intended
for a heater/fan/n.light/light combination to run 14 gauge wire from
the switch to the fixture, except for the heater part. And of course,
the answer was "no" because you are not suppose to use 14 guage wire
on a 20 amp circuit.

But the wire in the fixture is 14 gauge! (Except for the heater part.
There are three 14 gauge and one 12 gauge pairs inside the fixture.)
How is that not breaking the code on the part of the manufacturer?


1) that's the manufacturer's problem, not yours. If it's UL approved then
that's "gud enuf." There is little question that a hard fault across #14
wire will trip a 20 amp breaker so there really isn't much of a safety
concern. Light fixures often have #16 wire inside them. Most extension
cords are only #16.

2) In your PARTICULAR case, if you can you might want to run separate
circuits for the heater and for the lights. You can flip a coin to decide
whether to put the fan on the "light" side or the "heater" side. If the
heater is 10 amps or so, you can power it from #14 and #14 is already OK for
the lights and a small fan. If you use separate feeds in the same fixture
you have to make sure you connect the right neutral wire to the right cable.
Of course, the breaker for #14 circuits must be only 15 amps.


** Posted from
http://www.teranews.com **


Please note that the filiment wire in a perfectly safe and legal 100
watt incandescent light bulb is no where near 14 gauge!



Irrelevent. 100W incadecent lights aren't used to carry current to 2000W loads.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 664
Default Let me belabor the 12 gauge - 14 guage discussion

In article ,
bud-- wrote:

The NEC is available online.


If I recall correctly, NFPA charges A LOT to access the NEC on-line.

I'd rather pay the difference, whatever it might be, and get a hard
copy. Still, that, also, is too expensive considering I have no
PROFESSIONAL need to purchase such a reference.
--

JR


  #16   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 109
Default Let me belabor the 12 gauge - 14 guage discussion

I guess you aren't following this thread very carefully. The poster
was wondering why the wiring inside a fixture did not have to be as
large as the circuit TO the fixture. My point is that the code
specifies wire gauge in the supply circuit, not inside devices.


Actually, the OP wants to know why he can't use 14 gauge wiring on a 20 amp
circuit.


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 63
Default Let me belabor the 12 gauge - 14 guage discussion

In article -
media.com on Tue, 03 Jun 2008 20:09:30 -0500, Jim Redelfs wrote:

If I recall correctly, NFPA charges A LOT to access the NEC on-line.


It's available on-line for *free*.

2008 NEC:
http://www.nfpa.org/freecodes/free_a....asp?id=7008SB


2005 NEC:
http://www.nfpa.org/freecodes/free_a....asp?id=7005SB


--
Seth Goodman
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,469
Default Let me belabor the 12 gauge - 14 guage discussion

On 6/3/2008 8:26 PM Seth Goodman spake thus:

In article -
media.com on Tue, 03 Jun 2008 20:09:30 -0500, Jim Redelfs wrote:

If I recall correctly, NFPA charges A LOT to access the NEC on-line.


It's available on-line for *free*.

2008 NEC:
http://www.nfpa.org/freecodes/free_a....asp?id=7008SB


Sure, if you don't mind the ridiculous restrictions of "RealRead". (In
all fairness, it's probably the only reasonable choice they had to
publish it online; if they simply made PDFs available, I'm sure that
would cut significantly into their hardcopy sales.)


--
The best argument against democracy is a five-minute
conversation with the average voter.

- Attributed to Winston Churchill
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using 15A breaker for 12 guage cable Mikepier Home Repair 5 September 29th 07 09:27 PM
Can I stick two 4 gauge and one 6 gauge wire into a 3/4" conduit Ignoramus29948 Home Repair 11 September 13th 06 12:32 PM
Wiring guage and amps Mulan Home Repair 15 July 17th 06 06:26 PM
220 Wire Guage help BSmith Home Repair 28 May 23rd 06 04:55 PM
16 guage steel EBG Metalworking 2 September 19th 04 05:11 AM


All times are GMT +1. The time now is 10:02 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"