Since last week every time someone takes a bath the T&P valve
discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE |
#3
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
|
#4
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
No wrote:
wrote: Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE If the replaced T&p valve leaks (And its not defective and is a proper replacement) it means its doing its job, releasing too much pressure. Even though you have 60psi coming in water, as it heats, expands, creating more pressure. You could have a water heater that is over heating, try turning down he temp a bit. Also - an expansion tank may be in order if you do not have one. They are not expensive and easy to install if you can solder. Here is a picture of one. http://www.watts.com/prod_images/hi-res/det-20-m1.jpg If you do not have one thats where i would start if turning down the heat doesn't solve the problem. Inviato da X-Privat.Org - Registrazione gratuita http://www.x-privat.org/join.php You should also check to see if you have a backflow check valve or a pressure reducing valve with a built in check valve in your main water supply feed line. If you do, then its almost a certainty that you'd need an expansion tank to prevent what you're experiencing. Perhaps you have an expansion tank already and don't know it, and it's "waterlogged" and not doing its job, and/or it's the kind which has a rubber diphragm in it which has ruptured. I suspect that if you check, the valve isn't leaking "when" someone is taking a bath, but 10 minutes or so after they shut off the hot water tap and the new cold water which entered the heater gets warmed up and expands. And, from the description of the "rusty water" you're finding I'd say tthat heater is on its last legs too. HTH, Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Truth exists; only falsehood has to be invented." |
#6
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
"Jeff Wisnia" wrote in message et... No wrote: wrote: Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE If the replaced T&p valve leaks (And its not defective and is a proper replacement) it means its doing its job, releasing too much pressure. Even though you have 60psi coming in water, as it heats, expands, creating more pressure. You could have a water heater that is over heating, try turning down he temp a bit. Also - an expansion tank may be in order if you do not have one. They are not expensive and easy to install if you can solder. Here is a picture of one. http://www.watts.com/prod_images/hi-res/det-20-m1.jpg If you do not have one thats where i would start if turning down the heat doesn't solve the problem. Inviato da X-Privat.Org - Registrazione gratuita http://www.x-privat.org/join.php You should also check to see if you have a backflow check valve or a pressure reducing valve with a built in check valve in your main water supply feed line. If you do, then its almost a certainty that you'd need an expansion tank to prevent what you're experiencing. Perhaps you have an expansion tank already and don't know it, and it's "waterlogged" and not doing its job, and/or it's the kind which has a rubber diphragm in it which has ruptured. I suspect that if you check, the valve isn't leaking "when" someone is taking a bath, but 10 minutes or so after they shut off the hot water tap and the new cold water which entered the heater gets warmed up and expands. And, from the description of the "rusty water" you're finding I'd say tthat heater is on its last legs too. HTH, Jeff -- Jeffry Wisnia (W1BSV + Brass Rat '57 EE) "Truth exists; only falsehood has to be invented." If the valve leaks when the water is turned off, perhaps a water hammer arrestor has become waterlogged. you can drain the system and refill to recharge or you can add one near the bathroon valves. |
#7
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
Joseph Meehan wrote:
wrote: Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE The valve is doing it's job, it is releasing pressure or opening due to temperature. I would say that at 60 PSI, it is likely due to the pressure. Back that pressure back to 40-50 and that should take care of it. But that doesn't answer why the valve all of a sudden started leaking. Besides 60PSI is way below what a T&P valve is set for. Could be someone installed a back flow preventer, at the street or somewhere in the house line. Otherwise the original valve went bad. The real point is that one should never trip the TP valve with pressure in the line because it may not seat properly. The best bet as a first step with the new valve is to nearly close the supply valve to the hot water tank, open the T&P valve to let water flow for a bit to clean out any rust, close the supply valve tight, and then let the T&P valve snap shut. Might want open and let the T&P snap shut a couple of times. Then turn then open the water supply valve. Of course the new valve may be bad. But if doing what I said doesn't solve the problem, look for a change in the water supply line, house or at the street. |
#8
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
George E. Cawthon wrote:
Joseph Meehan wrote: wrote: Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE The valve is doing it's job, it is releasing pressure or opening due to temperature. I would say that at 60 PSI, it is likely due to the pressure. Back that pressure back to 40-50 and that should take care of it. But that doesn't answer why the valve all of a sudden started leaking. Besides 60PSI is way below what a T&P valve is set for. Could be someone installed a back flow preventer, at the street or somewhere in the house line. Otherwise the original valve went bad. The real point is that one should never trip the TP valve with pressure in the line because it may not seat properly. The best bet as a first step with the new valve is to nearly close the supply valve to the hot water tank, open the T&P valve to let water flow for a bit to clean out any rust, close the supply valve tight, and then let the T&P valve snap shut. Might want open and let the T&P snap shut a couple of times. Then turn then open the water supply valve. Of course the new valve may be bad. But if doing what I said doesn't solve the problem, look for a change in the water supply line, house or at the street. Do you have a check valve somewhere? -- Joseph Meehan Dia duit |
#9
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
Thank you all for the replies, I guess what I am trying to figure out
is why the valve started leaking suddenly. And this rusty water is also a bit puzzling. To answer your questions - I do have a check valve and no expansion tank here. I do not think that I need one because the water heater worked fine for 15 years ( maybe it's getting old ). I don't think 60 PSI is the problem here. I did lowered the thermostat setting from 130F to 120F to see if it helps. I will monitor the valve to see at what point it's leaking. Thanks again, GE |
#10
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
egou wrote:
.. To answer your questions - I do have a check valve and no expansion tank here. I do not think that I need one Water expands when it is heated. It needs somewhere to go. I suggest you go for that expansion tank you don't think you need. You are certainly not the first one here with that kind of problem. -- Joseph Meehan Dia duit |
#11
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
Joseph Meehan wrote:
George E. Cawthon wrote: Joseph Meehan wrote: wrote: Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE The valve is doing it's job, it is releasing pressure or opening due to temperature. I would say that at 60 PSI, it is likely due to the pressure. Back that pressure back to 40-50 and that should take care of it. But that doesn't answer why the valve all of a sudden started leaking. Besides 60PSI is way below what a T&P valve is set for. Could be someone installed a back flow preventer, at the street or somewhere in the house line. Otherwise the original valve went bad. The real point is that one should never trip the TP valve with pressure in the line because it may not seat properly. The best bet as a first step with the new valve is to nearly close the supply valve to the hot water tank, open the T&P valve to let water flow for a bit to clean out any rust, close the supply valve tight, and then let the T&P valve snap shut. Might want open and let the T&P snap shut a couple of times. Then turn then open the water supply valve. Of course the new valve may be bad. But if doing what I said doesn't solve the problem, look for a change in the water supply line, house or at the street. Do you have a check valve somewhere? Nope. Fortunately, there is no check valve or backflow preventer in my house or at the meter. So I never need to worry about pressure build up, it will just be whatever the city line is. Also, I have never lived where there was a pressure regulator. Might need too though since a friend of mine said they and a neighbor or two recently had the TP start leaking and so they checked the pressure. It was 190. They called the water company which denied any increase in pressure, but he knows they did increase the pressure to push water over a small hill to another subdivision. Fortunately for me that isn't part of my city water system. I didn't mean to address the problem of a check valve/backflow preventer and the possible need for an expansion tank since others had. Just that the OP needed to revue whatever may have been done recently to the system as part of his analysis of the problem. And that pressure valves sometimes won't seat properly when under pressure. |
#12
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
I had that exact problem a few months ago. The water heater worked fine for
years and then suddenly began to leak from the pressure relief valve. The leak would generally occur just after a heavy use of hot water. I figured the pressure relief valve had become defective so I replaced it. The new valve did exactly the same thing. So, I purchased an expansion tank, installed it and the leaking at the valve stopped and hasn't occurred since. When I installed the expansion tank, I also installed a pressure gauge to monitor the water pressure. It was initially at about 60 psi, so I reduced it at the pressure regulator valve to about 50 psi. I strongly suspect that the water company had increased the pressure or had installed a check valve in the line (possibly when changing the water meter). I also suspect that water companies are strongly opposed to any water being forced back into the main lines because of possible contamination problems and so they are prone to installing backflow preventors. For all I know, water meters have backflow presentors built in now days. Harry wrote in message oups.com... Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE |
#13
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
We are VEDO Valve Manufacturing Co.,Ltd in China. We supply vales with
good quality and good price. We are a professional manufacturer and exporter of various valves. We provide not only high quality products but also prompt delivery. We look forward to the cooperation with you and surely will be your reliable and trusty business partners in China. Our main products: Forged Steel Ball Valve, Gate Valve, Check Valve and Globe Valve. Please contact us to know details. We look forward to your early reply. Yours faithfully . Edison Xia Tel: 86- 577-67359999 Fax: 86-577-67993811 Url:http://www.vedo.cn |
#14
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
We are VEDO Valve Manufacturing Co.,Ltd in China. We supply vales with
good quality and good price. We are a professional manufacturer and exporter of various valves. We provide not only high quality products but also prompt delivery. We look forward to the cooperation with you and surely will be your reliable and trusty business partners in China. Our main products: Forged Steel Ball Valve, Gate Valve, Check Valve and Globe Valve. Please contact us to know details. We look forward to your early reply. Yours faithfully . Edison Xia Tel: 86- 577-67359999 Fax: 86-577-67993811 Url:http://www.vedo.cn |
#15
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
Thanks for the reply. What I am trying to figure out is why when I
open the T&P valve I get this rusty looking water for a few seconds and not when a faucet is opened. I am going to replace the anode rod to see if that helps next. GE HarryS wrote: I had that exact problem a few months ago. The water heater worked fine for years and then suddenly began to leak from the pressure relief valve. The leak would generally occur just after a heavy use of hot water. I figured the pressure relief valve had become defective so I replaced it. The new valve did exactly the same thing. So, I purchased an expansion tank, installed it and the leaking at the valve stopped and hasn't occurred since. When I installed the expansion tank, I also installed a pressure gauge to monitor the water pressure. It was initially at about 60 psi, so I reduced it at the pressure regulator valve to about 50 psi. I strongly suspect that the water company had increased the pressure or had installed a check valve in the line (possibly when changing the water meter). I also suspect that water companies are strongly opposed to any water being forced back into the main lines because of possible contamination problems and so they are prone to installing backflow preventors. For all I know, water meters have backflow presentors built in now days. Harry wrote in message oups.com... Since last week every time someone takes a bath the T&P valve discharges a small amount of water. When this happens, the water looks a bit rusty. If I pull lever on the valve, the rusty water will drain and for a day or so there'll be no more leaks, then it starts again. I checked the water line pressure and it's at 60 PSI. I've replaced the valve and flushed the tank for about 30 min - two days later the leak is back and water is rusty again when the lever is pulled. Any ideas? thanks, GE |
#16
Posted to alt.home.repair
|
|||
|
|||
pressure relief valve releasing water
"egou" wrote in message oups.com... Thanks for the reply. What I am trying to figure out is why when I open the T&P valve I get this rusty looking water for a few seconds and not when a faucet is opened. I am going to replace the anode rod to see if that helps next. GE The rusty water is probably caused by rusting of the spring and other parts in the outlet of the valve. Depending on how the outlet is pointed, some amount of water likely stays in the outlet where the spring is located. Opening of T&P valves is not generally recommended for this reason. Don Young |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
AquaTherm Furnace - No Hot Water Issue | Home Repair | |||