Home Ownership (misc.consumers.house)

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Mikhael47
 
Posts: n/a
Default Lifetime of an outdoor GFCI

I have an outdoor GFCI outlet. About every two years, I have to replace the
outlet. It doesn't trip very often (if at all) between the time I install
the new one, and the time it finally starts to trip constantly. I do run
pond equipment on this circuit all summer. It seems to fail in the winter
time when I either plug my truck's block heater in, or I try and start my
snowblower. It doesn't trip if I plug my xmas lights into it.

I am not an expert electrician, however when I built our home, I was present
when the wiring for the house was done. I can confirm that there is no
damage to the circuit cabling. This leads me to believe that the GFCI
itself is failing. If I replace the GFCI it will work as expected.

My question is, is it reasonable to only expect 2 years of regular service
out of a GFCI? What are the recommended brands for outdoor use?

Thanks

Mike


  #2   Report Post  
Marc Bissonnette
 
Posts: n/a
Default

"Mikhael47" wrote in
:

I have an outdoor GFCI outlet. About every two years, I have to
replace the outlet. It doesn't trip very often (if at all) between
the time I install the new one, and the time it finally starts to
trip constantly. I do run pond equipment on this circuit all summer.
It seems to fail in the winter time when I either plug my truck's
block heater in, or I try and start my snowblower. It doesn't trip if
I plug my xmas lights into it.

I am not an expert electrician, however when I built our home, I was
present when the wiring for the house was done. I can confirm that
there is no damage to the circuit cabling. This leads me to believe
that the GFCI itself is failing. If I replace the GFCI it will work
as expected.

My question is, is it reasonable to only expect 2 years of regular
service out of a GFCI? What are the recommended brands for outdoor
use?


Couple of questions: (I'm not an electrician, but I've done my share of
household wiring)

What gauge is the wiring for the outlet ?
What amperage is the breaker at the box for this circuit?
Is it a dedicated circuit ?
Have you opened the casing around the outlet to confirm there is no
moisture/insect/rodent damage ?

At a guess, I'd say either the gauge on the circuit is too small or the
breaker too low an amperage, given the conditions in which it's tripping.

Dunno about brands specifically, but does Honeywell make em ? I know they
make some pretty decent thermostats, which we've always been happy with

--
Marc Bissonnette
CGI / Database / Web Management Tools: http://www.internalysis.com
Looking for a new ISP? http://www.canadianisp.com
  #3   Report Post  
John R Weiss
 
Posts: n/a
Default

"Mikhael47" wrote...

My question is, is it reasonable to only expect 2 years of regular service
out of a GFCI? What are the recommended brands for outdoor use?


I have several installed, both inside and outside. I've replaced 1 in 9 years,
and most of them predate my moving in by 5+ years.

I have no idea what brand the outdoor units are.


  #4   Report Post  
Eunoia Eigensinn
 
Posts: n/a
Default

Mik;

I'm not an electrician, but have done house wiring more than a few
times, including my own home. I've never had a GFI receptacle fail in
almost 20 years of their having been installed in my home.

One failure of a receptable might constitute a faulty unit. Failures of
two would be incredible odds.

Any more than than one and I would tend to suspect that the wiring was
done improperly.

ie Undersized wire overloaded circuit, improperly designed circuits.

Mikhael47 wrote:
I have an outdoor GFCI outlet. About every two years, I have to

replace the
outlet. It doesn't trip very often (if at all) between the time I

install
the new one, and the time it finally starts to trip constantly. I

do run
pond equipment on this circuit all summer. It seems to fail in the

winter
time when I either plug my truck's block heater in, or I try and

start my
snowblower. It doesn't trip if I plug my xmas lights into it.

I am not an expert electrician, however when I built our home, I was

present
when the wiring for the house was done. I can confirm that there is

no
damage to the circuit cabling. This leads me to believe that the

GFCI
itself is failing. If I replace the GFCI it will work as expected.

My question is, is it reasonable to only expect 2 years of regular

service
out of a GFCI? What are the recommended brands for outdoor use?

Thanks

Mike


  #5   Report Post  
Herb Tarlek
 
Posts: n/a
Default

Eunoia Eigensinn wrote:
Mik;

I'm not an electrician, but have done house wiring more than a few
times, including my own home.* I've never had a GFI receptacle fail in
almost 20 years of their having been installed in my home.**


* This may or may not be true. Euni is a famous prankster! Beware.
** This may or may not be true.


One failure of a receptable might constitute a faulty unit.* Failures of
two would be incredible odds.**


* This may or may not be true.
** This may or may not be true.

Any more than than one and I would tend to suspect that the wiring was
done improperly.*


* This may or may not be true.

ie Undersized wire overloaded circuit, improperly designed circuits.*


* This may or may not be true.

Another Herb PSA


Mikhael47 wrote:

I have an outdoor GFCI outlet. About every two years, I have to


replace the

outlet. It doesn't trip very often (if at all) between the time I


install

the new one, and the time it finally starts to trip constantly. I


do run

pond equipment on this circuit all summer. It seems to fail in the


winter

time when I either plug my truck's block heater in, or I try and


start my

snowblower. It doesn't trip if I plug my xmas lights into it.

I am not an expert electrician, however when I built our home, I was


present

when the wiring for the house was done. I can confirm that there is


no

damage to the circuit cabling. This leads me to believe that the


GFCI

itself is failing. If I replace the GFCI it will work as expected.

My question is, is it reasonable to only expect 2 years of regular


service

out of a GFCI? What are the recommended brands for outdoor use?

Thanks

Mike





  #6   Report Post  
Mikhael47
 
Posts: n/a
Default


"Eunoia Eigensinn" wrote in message
ups.com...
Mik;

I'm not an electrician, but have done house wiring more than a few
times, including my own home. I've never had a GFI receptacle fail in
almost 20 years of their having been installed in my home.

One failure of a receptable might constitute a faulty unit. Failures of
two would be incredible odds.

Any more than than one and I would tend to suspect that the wiring was
done improperly.

ie Undersized wire overloaded circuit, improperly designed circuits.

Yes, I've checked all that. I have other GFCI's that are wired identically.
I have not checked for rodent/insect damage yet this time, however, last
time it seemed fine. I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike


  #7   Report Post  
Eunoia Eigensinn
 
Posts: n/a
Default


Mikhael47 wrote:
[snip]
I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike


Mike;

That may not be a good idea.

I have GFI breakers at the panel for all of my outdoor circuits and
interior circuits like those to bathroom & kitchen outlets.

But I also have GFI outlet receptacles installed.

The GFI breakers protect the wiring but will not do much to prevent
someone from being electrocuted at the point of use.

Do some Googling on the subject and you should find an authoritative
explanation.

  #8   Report Post  
Joe Canuck
 
Posts: n/a
Default

Eunoia Eigensinn wrote:

Mikhael47 wrote:
[snip]

I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike



Mike;

That may not be a good idea.

I have GFI breakers at the panel for all of my outdoor circuits and
interior circuits like those to bathroom & kitchen outlets.

But I also have GFI outlet receptacles installed.

The GFI breakers protect the wiring but will not do much to prevent
someone from being electrocuted at the point of use.

Do some Googling on the subject and you should find an authoritative
explanation.


One must, of course, be able to discern the wheat from the chaff out
there on the 'net.

Since you seem to be the authority on the subject, perhaps you already
have some sites in mind you can recommend?

....or haven't you Googled enough yet yourself to find them yet?



  #9   Report Post  
Herb Tarlek
 
Posts: n/a
Default

Joe Canuck wrote:
Eunoia Eigensinn wrote:

Mikhael47 wrote:
[snip]

I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike




Mike;

That may not be a good idea.

I have GFI breakers at the panel for all of my outdoor circuits and
interior circuits like those to bathroom & kitchen outlets.

But I also have GFI outlet receptacles installed.

The GFI breakers protect the wiring but will not do much to prevent
someone from being electrocuted at the point of use.

Do some Googling on the subject and you should find an authoritative
explanation.


One must, of course, be able to discern the wheat from the chaff out
there on the 'net.

Since you seem to be the authority on the subject, perhaps you already
have some sites in mind you can recommend?

...or haven't you Googled enough yet yourself to find them yet?



Yes, and don't forget to Google for "Eigensinn + hoax" while you're at
it! You'll hit the lottery of Google hits!

http://tinyurl.com/63bfj

Make sure you are well grounded and well linsured before taking any tips
to heart from this ****-stick.

Herb
  #10   Report Post  
Doug Miller
 
Posts: n/a
Default

In article .com, "Eunoia Eigensinn" wrote:

Mikhael47 wrote:
[snip]
I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike


Mike;

That may not be a good idea.

I have GFI breakers at the panel for all of my outdoor circuits and
interior circuits like those to bathroom & kitchen outlets.

But I also have GFI outlet receptacles installed.


A pointless waste of time and money, as those circuits _already_have_ ground
fault protection from the GFI breakers. What do you suppose the GFI
receptacles provide, that the GFI breakers do not?

The GFI breakers protect the wiring but will not do much to prevent
someone from being electrocuted at the point of use.


Half right, anyway: GFI breakers do protect the wiring. But they also provide
ground-fault protection against electrocution.

Think about it for just two seconds: you described accurately the behavior of
a *standard* (non-GFI) breaker. Now how might a GFI breaker behave
differently?

Hint: what do the letters GFI stand for?

Do some Googling on the subject and you should find an authoritative
explanation.

You seem to be in need of one yourself...


  #11   Report Post  
Eunoia Eigensinn
 
Posts: n/a
Default


Doug Miller wrote:
In article .com,

"Eunoia Eigensinn" wrote:

Mikhael47 wrote:
[snip]
I also have a breaker on this circuit. I may just
swap it out for a GFCI breaker instead.

Mike


Mike;

That may not be a good idea.

I have GFI breakers at the panel for all of my outdoor circuits and
interior circuits like those to bathroom & kitchen outlets.

But I also have GFI outlet receptacles installed.


A pointless waste of time and money, as those circuits _already_have_

ground
fault protection from the GFI breakers. What do you suppose the GFI
receptacles provide, that the GFI breakers do not?

The GFI breakers protect the wiring but will not do much to prevent
someone from being electrocuted at the point of use.


Half right, anyway: GFI breakers do protect the wiring. But they also

provide
ground-fault protection against electrocution.

Think about it for just two seconds: you described accurately the

behavior of
a *standard* (non-GFI) breaker. Now how might a GFI breaker behave
differently?

Hint: what do the letters GFI stand for?

Do some Googling on the subject and you should find an authoritative
explanation.

You seem to be in need of one yourself...



Actually, you would benefit from your own advice: Think about it.

For instance, it's not unreasonable for an outdoor receptacle point of
use to be 100 ft from the breaker panel.
I'll leave you to take it from there.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
RIDGID Lifetime warranty on power tools StacyW Home Repair 29 December 14th 16 01:39 AM
Cordless drills Alan Woodworking 33 November 21st 03 07:12 PM
Sears Craftsman lifetime warranty John Holbrook Metalworking 8 September 30th 03 12:51 AM


All times are GMT +1. The time now is 05:03 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"