While trying to troubleshoot why some kitchen electrical outlets in this
junction box weren't working, I did a bit of research. Apparently, there is
supposed to be a ground connection (other than the screw going through the
frame of the outlet to the box) from the GFCI outlet to the junction box.
(see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg ) Can I
just run some wire from the green screw terminal on the GFCI outlet to the
box? Where would I attach it to the box? By the way, the problem with the
outlet was that the breaker tripped in the GFCI. There are three pairs of
wires in the photo. One is the incoming AC. One feeds another GFCI outlet
down the line. The last pair goes to a switch in the same junction box which
turns on some lights in the kitchen.

Thanks for your reply.
--
David Farber
Los Osos, CA


  #2   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 75
Default Electrical box ground wiring.

While trying to troubleshoot why some kitchen electrical outlets in this
junction box weren't working, I did a bit of research. Apparently, there is
supposed to be a ground connection (other than the screw going through the
frame of the outlet to the box) from the GFCI outlet to the junction box.
(see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg ) Can I
just run some wire from the green screw terminal on the GFCI outlet to the
box? Where would I attach it to the box? By the way, the problem with the
outlet was that the breaker tripped in the GFCI. There are three pairs of
wires in the photo. One is the incoming AC. One feeds another GFCI outlet
down the line. The last pair goes to a switch in the same junction box which
turns on some lights in the kitchen.


Well, let's see.

Having a ground-wire connection to the GFCI itself is a good idea, if
a good ground is available. It's not (I believe) strictly required -
a GFCI can be used on a two-wire circuit.

In your case, it does appear that the outlet box is probably grounded;
I see what appear to be bare ground wires entering at the back. These
wires *should* be securely bonded to the junction box - this would
probably be done right at the back, where the screws and wire clamps
are located. I can't tell if those ground wires are in fact securely
bonded to the box, or whether they're just sitting there.

If you're going to ground the GFCI, you'd run a wire from the green
screw terminal, to a connection point with one of those ground
wires... e.g. if the existing bare ground wire is screwed to the box
at some point, you'd want to connect the ground wire to that screw or
to another box-mounted screw not too far from it.

Now, the lack of a ground wire from the GFCI shouldn't tend to cause
the GFCI to "trip" mistakenly. A proper GFCI operates by measuring
"current imbalance" between the hot and neutral wires. If more flows
through one than through the other, then it's almost certain that some
current is flowing to ground (somewhere) rather than back through
neutral... and this is a Bad Thing (shock hazard, or shock occurring).

A GFCI's protection does *not* depend on measuring current flowing
through its own ground wire. That's why they can be used to protect
two-wire circuits, where there isn't even a good ground connection
available... this makes them useful for retrofitting older house
circuits for improved safety.

Having a good ground on a GFCI circuit is actually likely to make the
GFCI trip sooner, rather than later, if an electrical fault exists.
For example, if you have an appliance with a grounded case, and a leak
or short develops between "hot" and the case, the GFCI will trip
instantly. If the case isn't grounded through the third prong
(e.g. if there is no ground prong, or if it's cut off or defeated with
a "cheater", or if it's plugged into a 3-wire outlet with no actual
ground) then the fault won't result in current flow to ground... until
somebody touches the case and also touches something grounded. At
that point they'll get a shock, and (knock on wood) the GFCI will trip
fast enough to protect them from anything more than a scare.

So, if your GFCI is tripping, then I don't expect that grounding the
GFCI more securely is likely to change this. You may actually have a
current-leak-to-ground on one of the circuits you are protecting. Or,
possibly, interference from a strong local radio transmitter is
"falsing" the GFCI - it does happen.



  #3   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 579
Default Electrical box ground wiring.

David Platt wrote:
While trying to troubleshoot why some kitchen electrical outlets in
this junction box weren't working, I did a bit of research.
Apparently, there is supposed to be a ground connection (other than
the screw going through the frame of the outlet to the box) from the
GFCI outlet to the junction box. (see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg )
Can I just run some wire from the green screw terminal on the GFCI
outlet to the box? Where would I attach it to the box? By the way,
the problem with the outlet was that the breaker tripped in the
GFCI. There are three pairs of wires in the photo. One is the
incoming AC. One feeds another GFCI outlet down the line. The last
pair goes to a switch in the same junction box which turns on some
lights in the kitchen.


Well, let's see.

Having a ground-wire connection to the GFCI itself is a good idea, if
a good ground is available. It's not (I believe) strictly required -
a GFCI can be used on a two-wire circuit.

In your case, it does appear that the outlet box is probably grounded;
I see what appear to be bare ground wires entering at the back. These
wires *should* be securely bonded to the junction box - this would
probably be done right at the back, where the screws and wire clamps
are located. I can't tell if those ground wires are in fact securely
bonded to the box, or whether they're just sitting there.

If you're going to ground the GFCI, you'd run a wire from the green
screw terminal, to a connection point with one of those ground
wires... e.g. if the existing bare ground wire is screwed to the box
at some point, you'd want to connect the ground wire to that screw or
to another box-mounted screw not too far from it.

Now, the lack of a ground wire from the GFCI shouldn't tend to cause
the GFCI to "trip" mistakenly. A proper GFCI operates by measuring
"current imbalance" between the hot and neutral wires. If more flows
through one than through the other, then it's almost certain that some
current is flowing to ground (somewhere) rather than back through
neutral... and this is a Bad Thing (shock hazard, or shock occurring).

A GFCI's protection does *not* depend on measuring current flowing
through its own ground wire. That's why they can be used to protect
two-wire circuits, where there isn't even a good ground connection
available... this makes them useful for retrofitting older house
circuits for improved safety.

Having a good ground on a GFCI circuit is actually likely to make the
GFCI trip sooner, rather than later, if an electrical fault exists.
For example, if you have an appliance with a grounded case, and a leak
or short develops between "hot" and the case, the GFCI will trip
instantly. If the case isn't grounded through the third prong
(e.g. if there is no ground prong, or if it's cut off or defeated with
a "cheater", or if it's plugged into a 3-wire outlet with no actual
ground) then the fault won't result in current flow to ground... until
somebody touches the case and also touches something grounded. At
that point they'll get a shock, and (knock on wood) the GFCI will trip
fast enough to protect them from anything more than a scare.

So, if your GFCI is tripping, then I don't expect that grounding the
GFCI more securely is likely to change this. You may actually have a
current-leak-to-ground on one of the circuits you are protecting. Or,
possibly, interference from a strong local radio transmitter is
"falsing" the GFCI - it does happen.


Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?

Thanks for your reply.
--
David Farber
Los Osos, CA


  #4   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,630
Default Electrical box ground wiring.

Those things work with or without a ground. It could be nuisance tripping, it happens with anything. If that is the case it is defective. To be sure disconnect the load side and see if it still trips.

If it does and there is nothing plugged into it, it is bad, if it does not trip, it is something off the line coming out of it that it is supposed to protect, and actually is probably doing its job.

The way to find out all what runs off it is to disconnect the OUTPUT neutral and with the branch circuit turned off, go to every neutrl around. I have wired them to protect lights, you have to for the over the sink lights. In some places you can't even do that, you have to install a GFCI breaker and run all new to the kitchen or sometimes bath. The NEC does ot necessarily require it, but some rehab codes do.

But who cares. You want the thing to work.

Take the load off and see what happens.
  #5   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,630
Default Electrical box ground wiring.

"This was the first time this GFCI has tripped. "

If it continues to work it was a nuisance trip. they are quite sensitive. A little spray of water into anything runniong off it can trip it. In fact certain funny loading appliances can make it trip due to certain harmonics on the power line, depending on how they are designed, even if they are not plugged into it sometimes.

I though you meant it kept on tripping.


  #6   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 75
Default Electrical box ground wiring.

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.


OK, understood. Yes, those trip/reset arrangements can be "stiff". I
think they may put a lot of tension on the springs inside, to make
sure that the disconnect opens reliably and quickly.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box.


It's fairly common for romex cable (heavy, flexible in-wall wiring) to
have two insulated connectors (hot/black and neutral/white), and one
bare ground wire between them. That's what you may be dealing with
there.

If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?


Yes, it can be done, but it's a bit tricky.

The simplest sort of tester is a small plug-like device you connect to
the outlet, which has several LEDs or neon bulbs inside. What you
would want to see, usually, is a couple of lights lit (indicating
that a voltage differential exists between line/neutral and
line/ground), and one or more other lights not lit (e.g. the "hot and
neutral are reversed" light). This will catch a couple of common
wiring faults (no ground at all, and ground/neutral reversal).

These simple testers are cheap, some even come with a "deliberately
trip the GFCI by leaking a bit of current" button, and they're a good
thing to have in your home-repairs drawer.

Gardner Bender GFI-3501 is one such (currently $8 at Home Depot);
there are many other brands.

These won't necessarily tell you that you have a *good* ground on the
circuit, though, because this sort of tester is designed to draw
almost no current at all through the circuit. It may tell you that
ground is connected, when its only connection to the actual building
ground is through corroded conduit and when the "ground" won't
actually carry much current reliably during a fault.

And, it won't catch the case in which ground and neutral have simply
been connected together at the outlet (i.e. no "real" ground). This
is a code violation and can be a safety issue.

Doing a *good* test for these faults usually requires measuring
voltages between the three terminals, while also pulling a substantial
current load on the circuit. Other tests would require powering down
the circuit (e.g. at the main breaker) and measuring resistances.
It's probably best to have a professional electrician perform these
sorts of tests, if you have doubts about the circuit.



  #7   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 199
Default Electrical box ground wiring.

A GFCI outlet should trip if there is a voltage difference between the ground wire and neutral. Any flow there indicates a potential problem and should cause it to trip off. Without a ground connected, this effectively prevents the GFCI from working properly. The holes at the rear of the box are for ground screws. You should connect the ground to there. Also, it looks like the ground wire is "grounded" to the box by being folded back into the entry hole with contact at that point. This installation was not likely done by an electrician. Proper grounding is necessary for proper functioning of the GFCI outlet.

Dan
  #9   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 75
Default Electrical box ground wiring.

A GFCI outlet should trip if there is a voltage difference between the
ground wire and neutral. Any flow there indicates a potential problem
and should cause it to trip off. Without a ground connected, this
effectively prevents the GFCI from working properly.


I believe that your description of how a GFCI works, is incorrect.

Everything I have read about them, says that they trip when they sense
a *current* imbalance, between "hot" and "neutral". They do not sense
voltage differences between ground and neutral. They can operate
without any ground connection at all.

Basically, they run these two wires through an inductive transformer
core in a "balanced" arrangement, and have a secondary sense wire in
the same core. If the current flow in hot and neutral is the same,
the fields around the two conductors are equal but opposite in phase,
they cancel out, and no current is induced in the sense wire. If
there's any hot-to-ground current flow "downstream" of the sensing
transformer, then the current flow in the neutral wire is reduced, the
two currents don't cancel out entirely, a current is induced into the
sense wire, and the GFCI detects this current and trips.

Citation: http://www.cpsc.gov//PageFiles/118853/099.pdf from the
U.S. Consumer Products Safety Commission. This fact sheet
describes the current sensing design, and specifically points out that
a GFCI can be used to protect a two-wire circuit which has no ground
connection at all. All of the other references I have seen, agree
with what the CPSC is saying here.

[An episode of "CSI", years ago, got this wrong... the lead story was
a murder which was arranged by tampering with a drill that was
plugged into a GFCI - cutting off the ground prong on the plug and
then arranging for a current leak. In fact, a GFCI would have
tripped under these circumstances, even with an un-grounded tool case
and even if the ground connection on the GFCI itself had been cut.]

  #10   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 126
Default Electrical box ground wiring.

David Farber wrote:
David Platt wrote:
While trying to troubleshoot why some kitchen electrical outlets in
this junction box weren't working, I did a bit of research.
Apparently, there is supposed to be a ground connection (other than
the screw going through the frame of the outlet to the box) from the
GFCI outlet to the junction box. (see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg )
Can I just run some wire from the green screw terminal on the GFCI
outlet to the box? Where would I attach it to the box? By the way,
the problem with the outlet was that the breaker tripped in the
GFCI. There are three pairs of wires in the photo. One is the
incoming AC. One feeds another GFCI outlet down the line. The last
pair goes to a switch in the same junction box which turns on some
lights in the kitchen.


Well, let's see.

Having a ground-wire connection to the GFCI itself is a good idea, if
a good ground is available. It's not (I believe) strictly required -
a GFCI can be used on a two-wire circuit.

In your case, it does appear that the outlet box is probably grounded;
I see what appear to be bare ground wires entering at the back. These
wires *should* be securely bonded to the junction box - this would
probably be done right at the back, where the screws and wire clamps
are located. I can't tell if those ground wires are in fact securely
bonded to the box, or whether they're just sitting there.

If you're going to ground the GFCI, you'd run a wire from the green
screw terminal, to a connection point with one of those ground
wires... e.g. if the existing bare ground wire is screwed to the box
at some point, you'd want to connect the ground wire to that screw or
to another box-mounted screw not too far from it.

Now, the lack of a ground wire from the GFCI shouldn't tend to cause
the GFCI to "trip" mistakenly. A proper GFCI operates by measuring
"current imbalance" between the hot and neutral wires. If more flows
through one than through the other, then it's almost certain that some
current is flowing to ground (somewhere) rather than back through
neutral... and this is a Bad Thing (shock hazard, or shock occurring).

A GFCI's protection does *not* depend on measuring current flowing
through its own ground wire. That's why they can be used to protect
two-wire circuits, where there isn't even a good ground connection
available... this makes them useful for retrofitting older house
circuits for improved safety.

Having a good ground on a GFCI circuit is actually likely to make the
GFCI trip sooner, rather than later, if an electrical fault exists.
For example, if you have an appliance with a grounded case, and a leak
or short develops between "hot" and the case, the GFCI will trip
instantly. If the case isn't grounded through the third prong
(e.g. if there is no ground prong, or if it's cut off or defeated with
a "cheater", or if it's plugged into a 3-wire outlet with no actual
ground) then the fault won't result in current flow to ground... until
somebody touches the case and also touches something grounded. At
that point they'll get a shock, and (knock on wood) the GFCI will trip
fast enough to protect them from anything more than a scare.

So, if your GFCI is tripping, then I don't expect that grounding the
GFCI more securely is likely to change this. You may actually have a
current-leak-to-ground on one of the circuits you are protecting. Or,
possibly, interference from a strong local radio transmitter is
"falsing" the GFCI - it does happen.


Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?

Thanks for your reply.


There are usually threaded holes in the back of metal outlet boxes for
ground wire attachment.

See those 2 holes in the center of the box near the sides? They should
be for grounding the box. Try an 8-32 screw. Also it doesn't appear
that the ground wire is *firmly* bonded to the box. It looks like it's
just sort of pushed in with the romex under the clamp.



  #11   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 132
Default Electrical box ground wiring.

In article ,
says...
Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?

Thanks for your reply.
--
David Farber
Los Osos, CA



The ground wire is connected to the ground screw of the duplex, your
outlet in most cases, if not, it's connected to the metal box and when
the duplex is screwed into the box, it then gets connected to ground.
You can also have it both ways which is better but takes longer to
install.

Ground wires are part of the romix wire so it gets connected to your
main ground in your home back at the sub panel box, where your breakers
live. In there the ground wire is attached to the same bus strip as the
neutral wire.. Somewhere around there you should have a real earth
ground connecting to the sub panel.

Although a GFCI will trip with an older non grounded system, it's not
advisable, because in order for this to happen, the circuit has to
become
unbalanced and if it is the appliance that is shorting, you maybe
touching it at the time. Grounds are there to isolate you from the
high potential when things go wrong. Having no ground plug means the
appliance is not grounded.


As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset.

jamie
  #12   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,630
Default Electrical box ground wiring.

"As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset. "


I have found this not to be true. However, to test, it does require power.

Also, I stand corrected her or in the othe rgroup, that the ground is not even reqquired for the test button to work, originally I thought it was.

All of them I ever installed were properly grounded so whatever. I thought it took current to the ground for test. It does not, it simpley takes it to BEFORE the GF circuit and that causes the imbalance that makes it trip and prove itsel
  #14   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 12,924
Default Electrical box ground wiring.


"Maynard A. Philbrook Jr." wrote:

In article ,
says...
Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?

Thanks for your reply.
--
David Farber
Los Osos, CA



The ground wire is connected to the ground screw of the duplex, your
outlet in most cases, if not, it's connected to the metal box and when
the duplex is screwed into the box, it then gets connected to ground.
You can also have it both ways which is better but takes longer to
install.

Ground wires are part of the romix wire so it gets connected to your
main ground in your home back at the sub panel box, where your breakers
live. In there the ground wire is attached to the same bus strip as the
neutral wire.. Somewhere around there you should have a real earth
ground connecting to the sub panel.

Although a GFCI will trip with an older non grounded system, it's not
advisable, because in order for this to happen, the circuit has to
become
unbalanced and if it is the appliance that is shorting, you maybe
touching it at the time. Grounds are there to isolate you from the
high potential when things go wrong. Having no ground plug means the
appliance is not grounded.

As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset.

jamie



Sigh, why do you post so much crap?

GFCI are allowed on non grounded outlets. If the device is 'shorted'
it will trip a circuit breaker. If it has developed a fault path to the
case, you won't trip it unless you are touching the defective device and
a suitably grounded item.
--
Anyone wanting to run for any political office in the US should have to
have a DD214, and a honorable discharge.
  #16   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 12,924
Default Electrical box ground wiring.


bud-- wrote:

On 10/16/2014 8:27 AM, Michael A. Terrell wrote:

wrote:

"As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset. "

I have found this not to be true. However, to test, it does require power.

Also, I stand corrected her or in the othe rgroup, that the ground is not even reqquired for the test button to work, originally I thought it was.

All of them I ever installed were properly grounded so whatever. I thought it took current to the ground for test. It does not, it simpley takes it to BEFORE the GF circuit and that causes the imbalance that makes it trip and prove itsel



The test button does nothing without a connection to ground. It
causes an imbalace between line and neutral by diverting a few mA to
ground form neutral.


The test button does not require a ground. The hot and neutral go
through a current transformer. The test button connects a resistor to
the hot ahead of the CT and the neutral downstream from the CT (or
vice-versa). Plug-in GFCI testes do not work without a ground.

I agree with everything else you have written here.

------------------------------
Interesting feature -
There is a second CT that tries to create a common-mode current on the
hot and neutral. If there is a plugged-in or downstream N-G connection
the GFCI trips.



The ones I've opened were as I described. They were very early
models, and failed in high humidity locations.
--
Anyone wanting to run for any political office in the US should have to
have a DD214, and a honorable discharge.
  #17   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,910
Default Electrical box ground wiring.

David Farber wrote:
David Platt wrote:
While trying to troubleshoot why some kitchen electrical outlets in
this junction box weren't working, I did a bit of research.
Apparently, there is supposed to be a ground connection (other than
the screw going through the frame of the outlet to the box) from the
GFCI outlet to the junction box. (see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg )
Can I just run some wire from the green screw terminal on the GFCI
outlet to the box? Where would I attach it to the box? By the way,
the problem with the outlet was that the breaker tripped in the
GFCI. There are three pairs of wires in the photo. One is the
incoming AC. One feeds another GFCI outlet down the line. The last
pair goes to a switch in the same junction box which turns on some
lights in the kitchen.


Well, let's see.

Having a ground-wire connection to the GFCI itself is a good idea, if
a good ground is available. It's not (I believe) strictly required -
a GFCI can be used on a two-wire circuit.

In your case, it does appear that the outlet box is probably grounded;
I see what appear to be bare ground wires entering at the back. These
wires *should* be securely bonded to the junction box - this would
probably be done right at the back, where the screws and wire clamps
are located. I can't tell if those ground wires are in fact securely
bonded to the box, or whether they're just sitting there.

If you're going to ground the GFCI, you'd run a wire from the green
screw terminal, to a connection point with one of those ground
wires... e.g. if the existing bare ground wire is screwed to the box
at some point, you'd want to connect the ground wire to that screw or
to another box-mounted screw not too far from it.

Now, the lack of a ground wire from the GFCI shouldn't tend to cause
the GFCI to "trip" mistakenly. A proper GFCI operates by measuring
"current imbalance" between the hot and neutral wires. If more flows
through one than through the other, then it's almost certain that some
current is flowing to ground (somewhere) rather than back through
neutral... and this is a Bad Thing (shock hazard, or shock occurring).

A GFCI's protection does *not* depend on measuring current flowing
through its own ground wire. That's why they can be used to protect
two-wire circuits, where there isn't even a good ground connection
available... this makes them useful for retrofitting older house
circuits for improved safety.

Having a good ground on a GFCI circuit is actually likely to make the
GFCI trip sooner, rather than later, if an electrical fault exists.
For example, if you have an appliance with a grounded case, and a leak
or short develops between "hot" and the case, the GFCI will trip
instantly. If the case isn't grounded through the third prong
(e.g. if there is no ground prong, or if it's cut off or defeated with
a "cheater", or if it's plugged into a 3-wire outlet with no actual
ground) then the fault won't result in current flow to ground... until
somebody touches the case and also touches something grounded. At
that point they'll get a shock, and (knock on wood) the GFCI will trip
fast enough to protect them from anything more than a scare.

So, if your GFCI is tripping, then I don't expect that grounding the
GFCI more securely is likely to change this. You may actually have a
current-leak-to-ground on one of the circuits you are protecting. Or,
possibly, interference from a strong local radio transmitter is
"falsing" the GFCI - it does happen.


Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?


sort of. My tester is a 200 watt bulb, but larger would be better. Connect
one lead to hot and the other to the box of your ground. With the load on,
measure the voltage across the bulb. If it's not the same as the bulb
connected to hot and neutral, you have a faulty ground. The connectivity
and resistance should be as good as your neutral itself.

A plain volt meter test from hot to ground is not valid, and neither are
those little pocket testers. They don't run a real current through ground,
which is something that has to happen if your equipment faults. For old
installations like in that photo, you have no idea what's really going on
or how many times it's been messed with in the past, and how secure the
connections are now.

  #18   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 579
Default Electrical box ground wiring.


"Cydrome Leader" wrote in message
...
David Farber wrote:
David Platt wrote:
While trying to troubleshoot why some kitchen electrical outlets in
this junction box weren't working, I did a bit of research.
Apparently, there is supposed to be a ground connection (other than
the screw going through the frame of the outlet to the box) from the
GFCI outlet to the junction box. (see photo:
http://webpages.charter.net/mrfixite...nction_box.jpg )
Can I just run some wire from the green screw terminal on the GFCI
outlet to the box? Where would I attach it to the box? By the way,
the problem with the outlet was that the breaker tripped in the
GFCI. There are three pairs of wires in the photo. One is the
incoming AC. One feeds another GFCI outlet down the line. The last
pair goes to a switch in the same junction box which turns on some
lights in the kitchen.

Well, let's see.

Having a ground-wire connection to the GFCI itself is a good idea, if
a good ground is available. It's not (I believe) strictly required -
a GFCI can be used on a two-wire circuit.

In your case, it does appear that the outlet box is probably grounded;
I see what appear to be bare ground wires entering at the back. These
wires *should* be securely bonded to the junction box - this would
probably be done right at the back, where the screws and wire clamps
are located. I can't tell if those ground wires are in fact securely
bonded to the box, or whether they're just sitting there.

If you're going to ground the GFCI, you'd run a wire from the green
screw terminal, to a connection point with one of those ground
wires... e.g. if the existing bare ground wire is screwed to the box
at some point, you'd want to connect the ground wire to that screw or
to another box-mounted screw not too far from it.

Now, the lack of a ground wire from the GFCI shouldn't tend to cause
the GFCI to "trip" mistakenly. A proper GFCI operates by measuring
"current imbalance" between the hot and neutral wires. If more flows
through one than through the other, then it's almost certain that some
current is flowing to ground (somewhere) rather than back through
neutral... and this is a Bad Thing (shock hazard, or shock occurring).

A GFCI's protection does *not* depend on measuring current flowing
through its own ground wire. That's why they can be used to protect
two-wire circuits, where there isn't even a good ground connection
available... this makes them useful for retrofitting older house
circuits for improved safety.

Having a good ground on a GFCI circuit is actually likely to make the
GFCI trip sooner, rather than later, if an electrical fault exists.
For example, if you have an appliance with a grounded case, and a leak
or short develops between "hot" and the case, the GFCI will trip
instantly. If the case isn't grounded through the third prong
(e.g. if there is no ground prong, or if it's cut off or defeated with
a "cheater", or if it's plugged into a 3-wire outlet with no actual
ground) then the fault won't result in current flow to ground... until
somebody touches the case and also touches something grounded. At
that point they'll get a shock, and (knock on wood) the GFCI will trip
fast enough to protect them from anything more than a scare.

So, if your GFCI is tripping, then I don't expect that grounding the
GFCI more securely is likely to change this. You may actually have a
current-leak-to-ground on one of the circuits you are protecting. Or,
possibly, interference from a strong local radio transmitter is
"falsing" the GFCI - it does happen.


Hi David,

I should have been clearer in my description. After noticing that the
power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there
was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's
when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to
apply
quite a bit of force to get it to reset. I tried again and it finally
reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the
box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if
a
junction box is grounded?


sort of. My tester is a 200 watt bulb, but larger would be better. Connect
one lead to hot and the other to the box of your ground. With the load on,
measure the voltage across the bulb. If it's not the same as the bulb
connected to hot and neutral, you have a faulty ground. The connectivity
and resistance should be as good as your neutral itself.

A plain volt meter test from hot to ground is not valid, and neither are
those little pocket testers. They don't run a real current through ground,
which is something that has to happen if your equipment faults. For old
installations like in that photo, you have no idea what's really going on
or how many times it's been messed with in the past, and how secure the
connections are now.


I was thinking exactly the same thing! Without a decent amount of current
going through the ground circuit, how can you tell if the ground connection
is really firmly attached? I was thinking of using a coffee maker as the
load. I'm going to the hardware store to get the appropriate sized ground
wire, attach it to the box, then measure the voltage difference with the pot
running off hot and ground, then hot and neutral.

Thanks to everyone for all your great replies.
--
David Farber
Los Osos, CA


  #19   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,630
Default Electrical box ground wiring.

"If it's not the same as the bulb
connected to hot and neutral, you have a faulty ground. "


Not necessarily. There is some voltage on neutrals in some places. This is caused by heavy loading on one side of the 240 compared to the other. It can be worse if common neutrals are used.

Saw one place that had like 20 volts on the neutral because of two 110 volt window AC units that happened to be on one side of the line.
  #21   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 75
Default Electrical box ground wiring.

In article ,
Cydrome Leader wrote:

But still, if you're in the US, have 20 volts on neutral relative to
ground, you probably have a bad neutral, which is also a big deal. This
problem could even exist outside your home, over at the distribution
transformer or wiring from there to your meter.

If your neutral "drifts" by 20 volts from ground, where it should be
bonded at the service entrance, and you have split phase 240 (120+120)
service you've got half the house with 100 volts at the oulets and other
side with 140 volts. That's not good for any devices or appliances you
have.


Yup. In 20 years we've had that problem occur twice at our house,
with the usual weird symptoms (e.g. lights getting *brighter* when you
turn on something else). In both cases it was due to a squirrel
chewing through the neutral wire, in the drop between the pole-pig
transformer and our service panel.

In both cases, reporting a "low voltage / high voltage" situation to
the power company resulted in a rapid response... the last time
it happened there was a truck rolling up outside our door within about
20 minutes. PG&E considers this a problem which requires a rather
urgent repair, due to the potential for equipment damage, fires, and
so forth.

If the neutral isn't actually open, then a persistent 20-volt
neutral-to-good-ground differential would indicate a really huge
current draw on the circuit... probably well more than the wiring is
rated for. The National Electric Code seems to allow for only a 5%
voltage drop for a fully-loaded circuit.




  #22   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 390
Default Electrical box ground wiring.

On 10/17/2014 12:19 PM, David Platt wrote:
In article ,
Cydrome Leader wrote:

But still, if you're in the US, have 20 volts on neutral relative to
ground, you probably have a bad neutral, which is also a big deal. This
problem could even exist outside your home, over at the distribution
transformer or wiring from there to your meter.

If your neutral "drifts" by 20 volts from ground, where it should be
bonded at the service entrance, and you have split phase 240 (120+120)
service you've got half the house with 100 volts at the oulets and other
side with 140 volts. That's not good for any devices or appliances you
have.


Yup. In 20 years we've had that problem occur twice at our house,
with the usual weird symptoms (e.g. lights getting *brighter* when you
turn on something else). In both cases it was due to a squirrel
chewing through the neutral wire, in the drop between the pole-pig
transformer and our service panel.


If you live in an urban area with all-metal water distribution pipes
this can be masked somewhat. If you have an open service neutral the
neutral return path can become service panel neutral to the N-G bond, to
the water service pipe (earthing electrode), to adjacent houses through
the metal water distribution system, through their N-G service bonds,
and back to the transformer through the service neutral at those houses.

There was a thread where someone had significant current on the
conductor to the earthing electrodes and it turned out either he, or a
neighbor, had an open service neutral.


In both cases, reporting a "low voltage / high voltage" situation to
the power company resulted in a rapid response... the last time
it happened there was a truck rolling up outside our door within about
20 minutes. PG&E considers this a problem which requires a rather
urgent repair, due to the potential for equipment damage, fires, and
so forth.


I have seen other people say the same thing.


If the neutral isn't actually open, then a persistent 20-volt
neutral-to-good-ground differential would indicate a really huge
current draw on the circuit... probably well more than the wiring is
rated for.


High current should trip the breaker.

If you had a really long circuit you could possibly come up with a 20V
drop. A competent electrician would increase the wire size for really
long circuits.

The National Electric Code seems to allow for only a 5%
voltage drop for a fully-loaded circuit.


The NEC recommends, but does not require, 5%.

  #23   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 173
Default Electrical box ground wiring.

David:

You have an old box. Note the bare copper wires under the strain reliefs. You need to dig them out.

These http://www.zoro.com/i/G3705676/?utm_...Zo7 AodHwgAKQ ground clips are eused in that situation.

They are a bit difficult to attach, but The secure a solid pigtail to the side of the box. e.g. the edge that's exposed.

What I use in this case is an ground Ideal Term-a-nut. See http://www.grainger.com/product/IDEA...ctor-Nut-4YD75

So, you can dig out the bare ground. Install the term-a-nut and a solid pigtail. The solid pigtail goes to the ground clip and the free end of the term-a-nut (fork terminal goes to the green screw on the outlet),

With multiple GFCI's you would want to not series the GFCI. e.g. One GFCI protects the outlets down stream.

What can cause nuisance tripping is shared neutrals. The term is shared, but think of it as neutrals attached as "T-splices"

GFCI's do not need a ground, but if they don;t have one, they must be labeled that there is no ground.

You are not supposed to rely on the screw connection from the box to to the outlet, although some outlets are designed so it's OK.

Your house looks like it had original had two prong outlets and the upgrade wasn't done correctly. The conversion can be a pain, but the term-a-nuts make the job much easier.

When there is a threaded hole in the box that can accept a ground screw, then other ways are possible.

So far, I've never tapped a ground hole.
  #24   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 173
Default Electrical box ground wiring.

I generally like the Term-a-nut process for wiring. One white, one black and one green. The parallel connections don't rely on the screw terminal pigtails.

Seasoned electricians pigtail the connections in the box with a wirnut.

The term-a-nuts I think can be purchased in stranded or solid. Not sure though. I use the stranded type.
  #25   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 579
Default Electrical box ground wiring.

Ron D. wrote:
David:

You have an old box. Note the bare copper wires under the strain
reliefs. You need to dig them out.

These
http://www.zoro.com/i/G3705676/?utm_...Zo7 AodHwgAKQ
ground clips are eused in that situation.

They are a bit difficult to attach, but The secure a solid pigtail to
the side of the box. e.g. the edge that's exposed.

What I use in this case is an ground Ideal Term-a-nut. See
http://www.grainger.com/product/IDEA...ctor-Nut-4YD75

So, you can dig out the bare ground. Install the term-a-nut and a
solid pigtail. The solid pigtail goes to the ground clip and the
free end of the term-a-nut (fork terminal goes to the green screw on
the outlet),

With multiple GFCI's you would want to not series the GFCI. e.g. One
GFCI protects the outlets down stream.

What can cause nuisance tripping is shared neutrals. The term is
shared, but think of it as neutrals attached as "T-splices"

GFCI's do not need a ground, but if they don;t have one, they must be
labeled that there is no ground.

You are not supposed to rely on the screw connection from the box to
to the outlet, although some outlets are designed so it's OK.

Your house looks like it had original had two prong outlets and the
upgrade wasn't done correctly. The conversion can be a pain, but the
term-a-nuts make the job much easier.

When there is a threaded hole in the box that can accept a ground
screw, then other ways are possible.

So far, I've never tapped a ground hole.


Hi Ron,

I put a screw into the box and ran a wire from the screw to the GFCI's
ground. But first I checked the line voltage with the neutral wire on the
neutral side of the plug with a hair dryer running. Then I exchanged the
neutral wire with the new ground wire and checked the voltage again with the
hair dryer running. The voltages were exactly the same. That proved to me
that the ground wire is making a good connection back to the service panel.
Do you see an alternate explanation that would disprove my conclusion?

Thanks for your reply.
--
David Farber
Los Osos, CA




  #26   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 173
Default Electrical box ground wiring.

Yu might find this odd, but you can sometimes check connections, by measuring across the connection. e.g. At the service panel, you can measure from the wire (probe actually touching the wire) and the main bus.

So, your looking for small voltages in the range of millivolts. That sort of check can check the sanity of a breakers contact resistance too. You do have to do this test with a load.

There are "phantom voltages" that occur when high impedance meters are used to measure line voltage. Large resistance leakage paths sometimes "fool" a conventional DVM with an input Z of 10 meg ohms. One of Fluke's meters does have a low Z mode.

I typically use an Ideal Sure Test http://www.amazon.com/Ideal-Industri.../dp/B000LDKWSG

A very cool device.

==

The "shared neutral" causes grief with GFCI's and AFCI;s/ See http://www.google.com/url?sa=t&rct=j...,d.cWc&cad=rja for a better explanation.


  #27   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 12,924
Default Electrical box ground wiring.


"Ron D." wrote:

I generally like the Term-a-nut process for wiring. One white, one black and one green. The parallel connections don't rely on the screw terminal pigtails.

Seasoned electricians pigtail the connections in the box with a wirnut.

The term-a-nuts I think can be purchased in stranded or solid. Not sure though. I use the stranded type.



Are they legal in every jurisdiction? A lot of things aren't allowed
under local codes.


--
Anyone wanting to run for any political office in the US should have to
have a DD214, and a honorable discharge.
  #28   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 173
Default Electrical box ground wiring.

On Monday, October 20, 2014 12:31:24 AM UTC-4, Michael Terrell wrote:
"Ron D." wrote:



Are they legal in every jurisdiction? A lot of things aren't allowed

under local codes.



I can buy them locally at a real electrical supply house, so I would suppose they are legal in mine. They are not much different than a wire nut.
  #29   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,910
Default Electrical box ground wiring.

Ron D. wrote:
David:

You have an old box. Note the bare copper wires under the strain reliefs. You need to dig them out.

These http://www.zoro.com/i/G3705676/?utm_...Zo7 AodHwgAKQ ground clips are eused in that situation.

They are a bit difficult to attach, but The secure a solid pigtail to the side of the box. e.g. the edge that's exposed.


I have to ask. How the hell do you attach or use those things?


  #30   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,910
Default Electrical box ground wiring.

bud-- wrote:
On 10/16/2014 8:27 AM, Michael A. Terrell wrote:

wrote:

"As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset. "

I have found this not to be true. However, to test, it does require power.

Also, I stand corrected her or in the othe rgroup, that the ground is not even reqquired for the test button to work, originally I thought it was.

All of them I ever installed were properly grounded so whatever. I thought it took current to the ground for test. It does not, it simpley takes it to BEFORE the GF circuit and that causes the imbalance that makes it trip and prove itsel



The test button does nothing without a connection to ground. It
causes an imbalace between line and neutral by diverting a few mA to
ground form neutral.


The test button does not require a ground. The hot and neutral go
through a current transformer. The test button connects a resistor to
the hot ahead of the CT and the neutral downstream from the CT (or
vice-versa). Plug-in GFCI testes do not work without a ground.

I agree with everything else you have written here.

------------------------------
Interesting feature -
There is a second CT that tries to create a common-mode current on the
hot and neutral. If there is a plugged-in or downstream N-G connection
the GFCI trips.


Maybe you can explain this one-

A friend's apt has a ceiling fan in a room that trips the GFCI in the
bathroom if you exercise the fan speed or light switch fast enough.
They're on separate circuits as far as I can tell, but the wiring is old
and crappy to start with so I'm not even going to take off some covers to
look around.

I still have no idea how this happens. Anybody seen un-connected devices
trip a GFCI outlet?



  #31   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,910
Default Electrical box ground wiring.

Michael A. Terrell wrote:

"Maynard A. Philbrook Jr." wrote:

In article ,
says...
Hi David,

I should have been clearer in my description. After noticing that the power
was off to the outlet, I pushed the GFCI reset button but I didn't hear a
click. At that point I figured either the GFCI hadn't tripped and there was
an internal problem, or it had tripped and there was something wrong with
the resetting mechanism. I removed the outlet from the wall and that's when
I noticed the missing ground connection. Regarding the GFCI, there was
nothing wrong with it. I read on a message board that you may have to apply
quite a bit of force to get it to reset. I tried again and it finally reset.
This was the first time this GFCI has tripped.

I looked again at the ground wiring you see in the picture. It exits the box
through a hole in the top of the box. If it's secured to anything outside
the box I can't tell. Is there some official test to perform to check if a
junction box is grounded?

Thanks for your reply.
--
David Farber
Los Osos, CA



The ground wire is connected to the ground screw of the duplex, your
outlet in most cases, if not, it's connected to the metal box and when
the duplex is screwed into the box, it then gets connected to ground.
You can also have it both ways which is better but takes longer to
install.

Ground wires are part of the romix wire so it gets connected to your
main ground in your home back at the sub panel box, where your breakers
live. In there the ground wire is attached to the same bus strip as the
neutral wire.. Somewhere around there you should have a real earth
ground connecting to the sub panel.

Although a GFCI will trip with an older non grounded system, it's not
advisable, because in order for this to happen, the circuit has to
become
unbalanced and if it is the appliance that is shorting, you maybe
touching it at the time. Grounds are there to isolate you from the
high potential when things go wrong. Having no ground plug means the
appliance is not grounded.

As for the reset on the GFCI outlet, for most units your power has to
be on before it'll reset.

jamie



Sigh, why do you post so much crap?

GFCI are allowed on non grounded outlets. If the device is 'shorted'
it will trip a circuit breaker. If it has developed a fault path to the
case, you won't trip it unless you are touching the defective device and
a suitably grounded item.


Well, technically, a GFCI device doesn't need a ground prong or a ground
to function. Notice I say GCFI devive, not receptacle. Take for instance
hair dryers or electric blankets these days. They have a GFCI module in
the plug, which is polarized, but not grounded.

On the other hand, if you're installing a GFCI outlet, they all have
ground prongs, and to not ground it would be improper. Downstream outlets
could be old receptacles with no ground prong, if you're doing some sort
of retrofit or hacky upgrade. I have no doubt both have been done by
people at home, but a real electrician would do the same might be a
different story. Anybody know what the NEC says about this?




  #32   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 75
Default Electrical box ground wiring.


In article ,
Cydrome Leader wrote:
Well, technically, a GFCI device doesn't need a ground prong or a ground
to function. Notice I say GCFI devive, not receptacle. Take for instance
hair dryers or electric blankets these days. They have a GFCI module in
the plug, which is polarized, but not grounded.


On the other hand, if you're installing a GFCI outlet, they all have
ground prongs, and to not ground it would be improper. Downstream outlets
could be old receptacles with no ground prong, if you're doing some sort
of retrofit or hacky upgrade. I have no doubt both have been done by
people at home, but a real electrician would do the same might be a
different story. Anybody know what the NEC says about this?


Ummm... as I pointed out a week or so ago, the Consumer Products
Safety Commission *specifically* points out that you can use a GFCI
receptacle on a circuit which has no ground. It will protect its own
jacks, and any other outlets which are wired "downstream", against
ground faults.

This is an accepted and approved method for adding safety to a
two-wire circuit which has no ground wire accessible.

I agree, it's not as good a solution as re-wiring with a good
ground... but it's a lot better than leaving a two-wire circuit
without ground-fault protection!

The CPSC (and I believe the NEC) requires that any GFCI outlets which
don't have an actual ground, must be installed with a sticker which
says so, so that the user is aware that the ground prong is "open".



  #33   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 12,924
Default Electrical box ground wiring.


Cydrome Leader wrote:

Well, technically, a GFCI device doesn't need a ground prong or a ground
to function. Notice I say GCFI devive, not receptacle. Take for instance
hair dryers or electric blankets these days. They have a GFCI module in
the plug, which is polarized, but not grounded.

On the other hand, if you're installing a GFCI outlet, they all have
ground prongs, and to not ground it would be improper. Downstream outlets
could be old receptacles with no ground prong, if you're doing some sort
of retrofit or hacky upgrade. I have no doubt both have been done by
people at home, but a real electrician would do the same might be a
different story. Anybody know what the NEC says about this?



The NEC requires the protected outlets be marked as non grounded. The
labels come with the GFCI.


--
Anyone wanting to run for any political office in the US should have to
have a DD214, and a honorable discharge.
  #34   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 1,910
Default Electrical box ground wiring.

David Platt wrote:

In article ,
Cydrome Leader wrote:
Well, technically, a GFCI device doesn't need a ground prong or a ground
to function. Notice I say GCFI devive, not receptacle. Take for instance
hair dryers or electric blankets these days. They have a GFCI module in
the plug, which is polarized, but not grounded.


On the other hand, if you're installing a GFCI outlet, they all have
ground prongs, and to not ground it would be improper. Downstream outlets
could be old receptacles with no ground prong, if you're doing some sort
of retrofit or hacky upgrade. I have no doubt both have been done by
people at home, but a real electrician would do the same might be a
different story. Anybody know what the NEC says about this?


Ummm... as I pointed out a week or so ago, the Consumer Products
Safety Commission *specifically* points out that you can use a GFCI
receptacle on a circuit which has no ground. It will protect its own
jacks, and any other outlets which are wired "downstream", against
ground faults.

This is an accepted and approved method for adding safety to a
two-wire circuit which has no ground wire accessible.

I agree, it's not as good a solution as re-wiring with a good
ground... but it's a lot better than leaving a two-wire circuit
without ground-fault protection!

The CPSC (and I believe the NEC) requires that any GFCI outlets which
don't have an actual ground, must be installed with a sticker which
says so, so that the user is aware that the ground prong is "open".


Ok- that would make sense- as stupid as a sticker may be, you need
something to indicate an abnormal condition. I've only see the industrial
versions of these warning tags though- never seen one screwed into a wall
in an old bathtoom, at least yet.


  #35   Report Post  
Posted to sci.electronics.repair
external usenet poster
 
Posts: 390
Default Electrical box ground wiring.

On 10/23/2014 1:26 AM, Michael A. Terrell wrote:

Cydrome Leader wrote:

Well, technically, a GFCI device doesn't need a ground prong or a ground
to function. Notice I say GCFI devive, not receptacle. Take for instance
hair dryers or electric blankets these days. They have a GFCI module in
the plug, which is polarized, but not grounded.

On the other hand, if you're installing a GFCI outlet, they all have
ground prongs, and to not ground it would be improper. Downstream outlets
could be old receptacles with no ground prong, if you're doing some sort
of retrofit or hacky upgrade. I have no doubt both have been done by
people at home, but a real electrician would do the same might be a
different story. Anybody know what the NEC says about this?



The NEC requires the protected outlets be marked as non grounded. The
labels come with the GFCI.


Trivial addition - downstream receptacles also need the "GFCI protected"
label.

As I think you have written, the NEC explicitly allows a (grounded) GFCI
receptacle to be used on an ungrounded circuit, and allows grounded
receptacles downstream, all with the label in your post. When used this
way, ground terminals are not to be connected together. Ungrounded
receptacles can also be used downstream.

The ground terminal on a GFCI connects only to the ground contacts for
what is plugged-in. There is no connection to the protection circuit.

==============================
A few changes from the 2011 NEC

If you are replacing a receptacle where it is now required to be tamper
resistant (child proof), the replacement has to now be tamper resistant
(most of a house).

Same with weather-resistant.

If you are extending an existing circuit in an area where AFCI
protection is now required, the entire extension is required to be AFCI
protected. (AFCI receptacles are now available.)

If you are replacing an ordinary receptacle in an area where GFCI
protection is now required, the new receptacle is required to be GFCI
protected. (Several ways to do it.)

If you are replacing an ordinary receptacle in an area where AFCI
protection is now required, the new receptacle is required to be AFCI
protected. (Also several ways to do it.) (Other than this, AFCI is
intended to protect the branch circuit wiring in addition to the
receptacle and what is plugged in.)




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
3 way switch ground wiring (ignor my neutral wiring thread) Doug[_14_] Home Repair 4 February 25th 12 02:09 PM
electrical wiring/hot water ground timO' Home Repair 13 May 14th 07 05:02 AM
electrical ground rod A & P D Home Repair 7 August 20th 06 08:03 PM
Electrical ground fault nj_dilettante Home Repair 11 May 26th 06 01:22 PM
Grounding Of Ground Wires In An Electrical Gang Box (how to handle the green ground wires) Robert11 Home Repair 7 March 8th 05 03:45 PM


All times are GMT +1. The time now is 09:22 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"