#41
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
We are running multiple schools on ground source heat pumps. Each
building has a single loop with individual Trane heat pumps running in each classroom tapped onto that loop. There is NO auxiliary heat. There are NO heat strips. Our Energy Czar believes in night set backs and holding temperatures at minimums until someone gripes. The systems are computerized to central control and the units can only be changed from the central location other than a small allowance at the thermostats. Each building, or even portions of buildings, have different thermal mass/draft and air leakage issues/poor glazing/etc that each requires its own start up time. Some take 2 hours, some almost 4 hours if they have been allowed to get too far out of design or conditions are extreme. The water loop is circulated full time through the well field, but the compressors at each heat pump function by thermostat. The buildings have become so much easier to control that we continue to install these systems as money permits. The buildings are so much more stable that we tend to ignore old fashioned insulation/draft/weatherstrip conditions - perhaps we will get back to them as energy costs continue to spiral. Our HVAC technicians would prefer just letting the systems run full time and maintain a steady temperature, especially when equipment is new just to run it through its paces while under warranty. The Energy Czar tends to win. I will try to remember to ask tomorrow about the whys. Each well field happens to have hit multiple water tables, so each field is way under capacity as they are originally designed on the assumption of no significant water zones and rely on ground contact through the custom gel only. We have two sites without well fields that run the loop through a cooling tower (no chiller) and small redundant boilers with plate frame exchangers. These were the first 2 sites when too many folks were afraid of the ground source. Who knows on a 20 to 50 year cycle, but right now groundsource is far and away the most efficient, cleanest, lowest maintenance system out there. We're not walking, we're running! -- ______________________________ Keep the whole world singing . . . . DanG (remove the sevens) "J. Clarke" wrote in message ... Kenneth wrote: On Tue, 27 Nov 2007 11:31:32 -0500, "J. Clarke" wrote: But the time at lower setpoint more than compensates for the differential loss. It's well-established in general that a setback lowers overall heating costs in general. It would take unusual circumstances for that to not be so. It's not something one should just assume. Especially with alternative energy. Hi John, Might you know of some reasons that the general principle of savings through setbacks would not apply to my geothermal source...? As I have said before here, I certainly do not (know enough to) disagree, but I have no understanding of why that should be true. Sincere thanks, I don't know enough details of your setup or the structure to be able to run the numbers. The main objection I'm seeing is that it's likely to cause the resistance elements in the heat pump to kick in but you say that you don't have any, but there might be something else unique to your situation. -- -- --John to email, dial "usenet" and validate (was jclarke at eye bee em dot net) |
#42
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Tue, 27 Nov 2007 18:56:19 -0500, Jim Behning
wrote: Why do you need a second electric meter to excrement with? You can read your own meter every day at the same time. As long as you record when you are drying clothes or other significant electricity burning events you should be able to test for no hardware costs. Are you torturing the group by not doing your own meter reading and reporting back? Hi Jim, I am lost... How would reading my meter at the same time every day tell me my heat-related energy consumption? Thanks, -- Kenneth If you email... Please remove the "SPAMLESS." |
#43
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Wed, 28 Nov 2007 09:46:22 -0500, Kenneth
wrote: On Tue, 27 Nov 2007 18:56:19 -0500, Jim Behning wrote: Why do you need a second electric meter to excrement with? You can read your own meter every day at the same time. As long as you record when you are drying clothes or other significant electricity burning events you should be able to test for no hardware costs. Are you torturing the group by not doing your own meter reading and reporting back? Hi Jim, I am lost... How would reading my meter at the same time every day tell me my heat-related energy consumption? Thanks, Day zero meter reads 1480 Day one with no thermostat changes reads 1520 Day two no thermostat change 1570 day 3 no thermostat change 1620 Day 4 after thermostat rollback 1680 day 5 with thermostat rollback 1740 day6 with thermostat rollback 1800 day 7 no thermostat change 1850 day 8 thermostat rollback 1910 day 9 thermostat rollback 1970 day 10 no thermostat change 2020 and so on. Just read the meter every day at the same time. Do the math. Do it over enough days to factor out clothes dryers and baking festivals. If there is indeed any significant energy saving to be had by thermostat rollback it will show up with a month of measuring. Especially if you do rollback every other night. That said I think when I feel rich I will buy http://www.theenergydetective.com/store or one of these with the split core http://eyomenergy.com/Merchant2/merc...gory_C ode=ES |
#44
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Wed, 28 Nov 2007 18:56:46 -0500, Jim Behning
wrote: On Wed, 28 Nov 2007 09:46:22 -0500, Kenneth wrote: On Tue, 27 Nov 2007 18:56:19 -0500, Jim Behning wrote: Why do you need a second electric meter to excrement with? You can read your own meter every day at the same time. As long as you record when you are drying clothes or other significant electricity burning events you should be able to test for no hardware costs. Are you torturing the group by not doing your own meter reading and reporting back? Hi Jim, I am lost... How would reading my meter at the same time every day tell me my heat-related energy consumption? Thanks, Day zero meter reads 1480 Day one with no thermostat changes reads 1520 Day two no thermostat change 1570 day 3 no thermostat change 1620 Day 4 after thermostat rollback 1680 day 5 with thermostat rollback 1740 day6 with thermostat rollback 1800 day 7 no thermostat change 1850 day 8 thermostat rollback 1910 day 9 thermostat rollback 1970 day 10 no thermostat change 2020 and so on. Just read the meter every day at the same time. Do the math. Do it over enough days to factor out clothes dryers and baking festivals. If there is indeed any significant energy saving to be had by thermostat rollback it will show up with a month of measuring. Especially if you do rollback every other night. That said I think when I feel rich I will buy http://www.theenergydetective.com/store or one of these with the split core http://eyomenergy.com/Merchant2/merc...gory_C ode=ES You are not measuring how much you spend on heating, you are measuring much less or more you are spending by trying different thermostat strategies. You also need to note wind, sunshine and outside temp. My heat does not run on a 50 degree day with sun and little to no wind. |
#45
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Jim Behning wrote:
On Wed, 28 Nov 2007 18:56:46 -0500, Jim Behning wrote: On Wed, 28 Nov 2007 09:46:22 -0500, Kenneth wrote: On Tue, 27 Nov 2007 18:56:19 -0500, Jim Behning wrote: Why do you need a second electric meter to excrement with? You can read your own meter every day at the same time. As long as you record when you are drying clothes or other significant electricity burning events you should be able to test for no hardware costs. Are you torturing the group by not doing your own meter reading and reporting back? Hi Jim, I am lost... How would reading my meter at the same time every day tell me my heat-related energy consumption? Thanks, Day zero meter reads 1480 Day one with no thermostat changes reads 1520 Day two no thermostat change 1570 day 3 no thermostat change 1620 Day 4 after thermostat rollback 1680 day 5 with thermostat rollback 1740 day6 with thermostat rollback 1800 day 7 no thermostat change 1850 day 8 thermostat rollback 1910 day 9 thermostat rollback 1970 day 10 no thermostat change 2020 and so on. Just read the meter every day at the same time. Do the math. Do it over enough days to factor out clothes dryers and baking festivals. If there is indeed any significant energy saving to be had by thermostat rollback it will show up with a month of measuring. Especially if you do rollback every other night. That said I think when I feel rich I will buy http://www.theenergydetective.com/store or one of these with the split core http://eyomenergy.com/Merchant2/merc...gory_C ode=ES You are not measuring how much you spend on heating, you are measuring much less or more you are spending by trying different thermostat strategies. You also need to note wind, sunshine and outside temp. My heat does not run on a 50 degree day with sun and little to no wind. Just for some perspective, last week the temperature here was 60 degrees, which melted the snow that had come down a couple of days previously. -- -- --John to email, dial "usenet" and validate (was jclarke at eye bee em dot net) |
#46
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
[...asking about setback and subject...] Don't know if you gave up or got an answer but I mentioned the OSU site earlier. Being bored, I went and found it -- here's the current link. Didn't find a specific answer in the faq's, but they have a couple of contact ways you can get to them. http://www.igshpa.okstate.edu/index.htm hth... -- |
#47
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
Howdy, This is way OT...(again), but: We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? Sincere thanks, hi all! i sent this email to Alliant Energy Geothermal =============== there is a discussion underway with this as topic: - We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? could you help me understand the issues involved? thanks in advance for any input! chuck b:-) ============== and i got this reply ----------------------- Dear Chuck, Set-up of a Geo system temperature during the cooling time of year should allow a Geo system to recover the cooling and dehumidify as quickly and more efficiently than other air sourced cooling systems. Set-back is not typically recommended during the heating time of year due to 1) a slower recovery time for heating, 2) the potential for the back up electric elements kicking in to boost the reheating rate but, at an added electric expense to you, 3) dependent on if you use a straight well water open loop or only a minimal to non freeze protected closed loop fluid, the lack of normal flows may allow for a potential for a loop to freeze up and 4) many people who own set-back thermostats are easily confused by the instructions for operating them and re-setting them. All of these can cause contractor callbacks, they hate callbacks. We do have a few of our regional Geo system owners who do a slight setback for heating at maybe 2 to 4 degrees F maximum for 4 to 6 hours but, all must realize the potential results. During AC season and the daytime hours of unoccupied homes, they might also do set up to minimize On Peak energy charges when they choose Time of Use electric rate options. I hope this helps. Thanks for the inquiry. Leo From: Alliant Energy Geothermal Web Forms ] Sent: Wednesday, November 28, 2007 9:29 PM To: Geothermal Cc: Webmaster Subject: Alliant Energy Geothermal -- Contact Us Form chuck b:-) |
#48
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Fri, 30 Nov 2007 20:56:41 GMT, chuckb wrote:
Kenneth wrote: Howdy, This is way OT...(again), but: We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? Sincere thanks, hi all! i sent this email to Alliant Energy Geothermal =============== there is a discussion underway with this as topic: - We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? could you help me understand the issues involved? thanks in advance for any input! chuck b:-) ============== and i got this reply ----------------------- Dear Chuck, Set-up of a Geo system temperature during the cooling time of year should allow a Geo system to recover the cooling and dehumidify as quickly and more efficiently than other air sourced cooling systems. Set-back is not typically recommended during the heating time of year due to 1) a slower recovery time for heating, 2) the potential for the back up electric elements kicking in to boost the reheating rate but, at an added electric expense to you, 3) dependent on if you use a straight well water open loop or only a minimal to non freeze protected closed loop fluid, the lack of normal flows may allow for a potential for a loop to freeze up and 4) many people who own set-back thermostats are easily confused by the instructions for operating them and re-setting them. All of these can cause contractor callbacks, they hate callbacks. We do have a few of our regional Geo system owners who do a slight setback for heating at maybe 2 to 4 degrees F maximum for 4 to 6 hours but, all must realize the potential results. During AC season and the daytime hours of unoccupied homes, they might also do set up to minimize On Peak energy charges when they choose Time of Use electric rate options. I hope this helps. Thanks for the inquiry. Leo From: Alliant Energy Geothermal Web Forms ] Sent: Wednesday, November 28, 2007 9:29 PM To: Geothermal Cc: Webmaster Subject: Alliant Energy Geothermal -- Contact Us Form chuck b:-) Now that has a few good answers. I would not have thought about the freezing closed loops. |
#49
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning
wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, -- Kenneth If you email... Please remove the "SPAMLESS." |
#50
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. .... Any responsibly designed system protects against such freezing... .... My thinking precisely. The response basically is a bunch of weasel-words. The upshot basically is if the aux heat issue is taken care of properly and one doesn't mind the recovery time, setback will save. For a reasonable source capacity, our experience was that while the outlet temperatures aren't equivalent to gas, they're sufficiently high the air feels "warm enough" circulating as opposed to the and as compared to air-air heat pump that felt cool... If there's freeze-up w/ a few degrees setback so the unit runs a little less at night, there's going to be freeze up on other days as well... -- |
#51
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
chuckb wrote:
Kenneth wrote: On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, but on the other hand: from your OP "The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged." any system that is operated outside it's design criteria risks failure! ... A few degrees lower is "outside the design" for a residential hvac system? I still think there's been no rational basis for the proscription given unless, as Ken says, there's a problem--and if there's a problem, I think there will be a problem irrespective of the setback. -- |
#52
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, but on the other hand: from your OP "The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged." any system that is operated outside it's design criteria risks failure! good luck with yours! chuck b:-) |
#53
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
chuckb wrote:
dpb wrote: chuckb wrote: Kenneth wrote: On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, but on the other hand: from your OP "The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged." any system that is operated outside it's design criteria risks failure! .. A few degrees lower is "outside the design" for a residential hvac system? I still think there's been no rational basis for the proscription given unless, as Ken says, there's a problem--and if there's a problem, I think there will be a problem irrespective of the setback. .... you seem to be reading things that i didn't say or if i did i certainly did not mean to.. oh well, have a good day! Well, what _did_ you mean, then??? -- |
#54
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
dpb wrote:
chuckb wrote: Kenneth wrote: On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, but on the other hand: from your OP "The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged." any system that is operated outside it's design criteria risks failure! .. A few degrees lower is "outside the design" for a residential hvac system? I still think there's been no rational basis for the proscription given unless, as Ken says, there's a problem--and if there's a problem, I think there will be a problem irrespective of the setback. -- you seem to be reading things that i didn't say or if i did i certainly did not mean to.. oh well, have a good day! chuck b:-) |
#55
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
In article ,
Kenneth wrote: On Tue, 27 Nov 2007 18:07:39 -0000, (Robert Bonomi) wrote: Hi Robert, I thank you for your detailed response... Perhaps I am not understanding what you have written, but allow me to ask something further. Please see my comments inline below: I wrote: If the internal temperature of the house is allowed to drop, two things happen. First, there is the direct energy savings because it takes fewer BTUs to keep the house at the lower temp; You responded: _THOSE_ BTUs are just 'deferred spending'. you spend exactly that amount to raise the temp back to the original setting. I wrote: but perhaps less obviously, the rate of heat loss to the outside environment is decreased. (Because the greater the temperature differential, the more rapid the rate of equalization.) You responded: That is the -totality- of the energy savings -- the lowered losses. from the reduced temperature. In my attempt to understand this... Suppose I lowered the temperature of the house 10 degrees, but not merely overnight. Instead, I left them lower for a month. Would I not have very significant savings for that month? Relative to what you would have 'spent' at the 10degree higher temperature yes. If so, would not the reasons for those savings apply as well to my overnight lowering of the house's internal temperature (though with decreased benefit because of the diminished duration)? Yes and no. grin There are three intervals to consider. 1) while the temperature is falling from 'X' to 'X-10', 2) while the temperature is stable at 'X-10', 3) while the temperature is rising from 'X-10' to 'X'. As the house cools from 'X' to 'X-10', you aren't providing any heat input at that time. *THAT* 'savings', is cancelled by the 'extra' energy you have to put back into the building the next day, to raise the temperature from 'X-10' back to 'X'. For complicated reasons, it usually takes a little more energy to go from 'X-10' to 'X' than was 'saved' by letting things fall from 'X' to 'X-10'. This differential is usually fairly minor, however it can be magnified if the -rates- at which the temperature falls and rises are different. The heat input required to maintain the house at a constant "X" is exactly the heat losses being radiated by the house to the exterior. The heat input required to maintain the house at a constant "X-10" is exactly the heat losses being radiated by the house to the exterior. In both cases the rate of loss is a function of (a) the temperature differential, _and_ the quality of the insulation. The point is, however, that the difference in heat input is exactly the difference in thermal losses, at a constant temperature. You cannot count a savings for less heat input, -and- a savings for lower thermal losses. |
#56
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
In article , DanG wrote:
We are running multiple schools on ground source heat pumps. Each building has a single loop with individual Trane heat pumps running in each classroom tapped onto that loop. There is NO auxiliary heat. There are NO heat strips. Our Energy Czar believes in night set backs and holding temperatures at minimums until someone gripes. The systems are computerized to central control and the units can only be changed from the central location other than a small allowance at the thermostats. Each building, or even portions of buildings, have different thermal mass/draft and air leakage issues/poor glazing/etc that each requires its own start up time. Some take 2 hours, some almost 4 hours if they have been allowed to get too far out of design or conditions are extreme. The water loop is circulated full time through the well field, but the compressors at each heat pump function by thermostat. The buildings have become so much easier to control that we continue to install these systems as money permits. The buildings are so much more stable that we tend to ignore old fashioned insulation/draft/weatherstrip conditions - perhaps we will get back to them as energy costs continue to spiral. Our HVAC technicians would prefer just letting the systems run full time and maintain a steady temperature, especially when equipment is new just to run it through its paces while under warranty. The Energy Czar tends to win. I will try to remember to ask tomorrow about the whys. A 'medium-insulated' school building full of people doesn't need _any_ additional heat source until the outside temperature gets below about -20F. Look up how much heat an 'at rest' human body gives off, and multiply by the 25-30 bodies preset in the average classroom. Getting the heat _out_ of the building is the issue. At 'above zero' temperatures, it's _common_ to be venting hot air outside and pulling in cold outside air for 'make-up'. Not infrequently, the chillers will be running, in addition. |
#57
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Robert, as you said, bodies and lights make a huge load on a
building. Our Energy Czar (EC) lets the buildings get cold enough that they typically require a morning warm up before the occupant load takes over. We have one 2 pipe school that requires a full conversion to either heat or cool that can be quite troublesome on those moderate days. We turn all chillers off and dump the cooling towers as we head into the freezing months. The buildings can usually be tempered by outside air. The geothermal schools eliminate this problem and allow partial usage of buildings for special events and summer school type needs. I did ask about the setback issues. We had one series of heat pumps whose open/close valves did not have stops installed. These machines have a sensor that says if the water is too cold it prevents the unit from running rather than make ice - this issue was rectified by installing stops that never allow the valves to completely close which keeps the water circulating back to the loop. We now install all systems to run the well field pumps continuously as we have one that turns off the circulating pumps if there is no demand anywhere on the system which can allow some of the loop to reach that same "don't run" temperature. Believe it or not, the pumps have shut down several times because the building is that stable. As Robert says, lights and people can keep a large building quite warm or too warm when the rest of us need heat. We do continue to have a problem with people wanting cooling on warm afternoons turning the thermostat down to the bottom at 55°: the computer limits the units so the 55 never happens, but the units also don't come up on morning warm-up, though the rooms seem to recover quickly if the rest of the building is satisfied. He swears emphatically that no matter what system is used, intense run time in the mornings uses less energy than the start/stop cycle of leaving the system at temperature around the clock. They have put in-line monitors with recording capability on units set up each way on highly similar usage, run them for a week, then reversed the study for another week on the same units. Setback with a substantial run time to recover uses less energy than maintaining the temperature during non critical times. The setback needs to be able to protect critical needs as in not freezing water lines or baking cookies in the attic. ______________________________ Keep the whole world singing . . . . DanG (remove the sevens) "Robert Bonomi" wrote in message ... In article , DanG wrote: We are running multiple schools on ground source heat pumps. Each building has a single loop with individual Trane heat pumps running in each classroom tapped onto that loop. There is NO auxiliary heat. There are NO heat strips. Our Energy Czar believes in night set backs and holding temperatures at minimums until someone gripes. The systems are computerized to central control and the units can only be changed from the central location other than a small allowance at the thermostats. Each building, or even portions of buildings, have different thermal mass/draft and air leakage issues/poor glazing/etc that each requires its own start up time. Some take 2 hours, some almost 4 hours if they have been allowed to get too far out of design or conditions are extreme. The water loop is circulated full time through the well field, but the compressors at each heat pump function by thermostat. The buildings have become so much easier to control that we continue to install these systems as money permits. The buildings are so much more stable that we tend to ignore old fashioned insulation/draft/weatherstrip conditions - perhaps we will get back to them as energy costs continue to spiral. Our HVAC technicians would prefer just letting the systems run full time and maintain a steady temperature, especially when equipment is new just to run it through its paces while under warranty. The Energy Czar tends to win. I will try to remember to ask tomorrow about the whys. A 'medium-insulated' school building full of people doesn't need _any_ additional heat source until the outside temperature gets below about -20F. Look up how much heat an 'at rest' human body gives off, and multiply by the 25-30 bodies preset in the average classroom. Getting the heat _out_ of the building is the issue. At 'above zero' temperatures, it's _common_ to be venting hot air outside and pulling in cold outside air for 'make-up'. Not infrequently, the chillers will be running, in addition. |
#58
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Robert Bonomi wrote:
.... snip Our HVAC technicians would prefer just letting the systems run full time and maintain a steady temperature, especially when equipment is new just to run it through its paces while under warranty. The Energy Czar tends to win. I will try to remember to ask tomorrow about the whys. A 'medium-insulated' school building full of people doesn't need _any_ additional heat source until the outside temperature gets below about -20F. Look up how much heat an 'at rest' human body gives off, and multiply by the 25-30 bodies preset in the average classroom. From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. Depending upon age, kids in a school would most likely be considerably less. Getting the heat _out_ of the building is the issue. At 'above zero' temperatures, it's _common_ to be venting hot air outside and pulling in cold outside air for 'make-up'. Not infrequently, the chillers will be running, in addition. -- If you're going to be dumb, you better be tough |
#59
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Mark & Juanita wrote in
: From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. Depending upon age, kids in a school would most likely be considerably less. You haven't seen my 11 year-old granddaughter - 250 Watt is more like it. -- Best regards Han email address is invalid |
#60
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
In article ,
Mark & Juanita wrote: Robert Bonomi wrote: ... snip Our HVAC technicians would prefer just letting the systems run full time and maintain a steady temperature, especially when equipment is new just to run it through its paces while under warranty. The Energy Czar tends to win. I will try to remember to ask tomorrow about the whys. A 'medium-insulated' school building full of people doesn't need _any_ additional heat source until the outside temperature gets below about -20F. Look up how much heat an 'at rest' human body gives off, and multiply by the 25-30 bodies preset in the average classroom. From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. That's a bit on the low side -- about right for sleeping. 'resting' is more in the 110-120 range. Circa 125 is frequently used for estimating purposes. Call it 12,000 BTU/hr per room, plus another few thousand for the lighting. Scale up by a factor of 4, for equivalent footage to a medium house, and you've got the equivalent of an 80% efficient 150,000 BTU/hr furnace running at a _50%_ duty cycle. Depending upon age, kids in a school would most likely be considerably less. Surprisingly small differences. lower elementary ages are about 75-80% of adult. Getting the heat _out_ of the building is the issue. At 'above zero' temperatures, it's _common_ to be venting hot air outside and pulling in cold outside air for 'make-up'. Not infrequently, the chillers will be running, in addition. |
#61
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
In article ,
Han wrote: Mark & Juanita wrote in : From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. Depending upon age, kids in a school would most likely be considerably less. You haven't seen my 11 year-old granddaughter - 250 Watt is more like it. Depending on activity level, you can _triple_ (or somewhat more) the base number, which is in the 100-140 watt range. A 250 watt kid is -not- all that extreme! grin |
#62
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
|
#63
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
In article ,
Han wrote: (Robert Bonomi) wrote in : In article , Han wrote: Mark & Juanita wrote in : From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. Depending upon age, kids in a school would most likely be considerably less. You haven't seen my 11 year-old granddaughter - 250 Watt is more like it. Depending on activity level, you can _triple_ (or somewhat more) the base number, which is in the 100-140 watt range. A 250 watt kid is -not- all that extreme! grin Also, I think that heat dissipation would be equivalent to body surfacce area, which would make skinny kids radiate more (proportionally) than chunky ones ... While you might think so, reality is somewhat counter-intuitive. Total heat output is relatively -independant- of surface area. Less skin just means more output per unit area. |
#64
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Han wrote:
Mark & Juanita wrote in : From EDEE 101 (or Physics 112), we were told that the average human body is equivalent to 100 watt light bulb as far as heat output. Depending upon age, kids in a school would most likely be considerably less. You haven't seen my 11 year-old granddaughter - 250 Watt is more like it. You know, I know exactly what you are saying -- our son has been like that also. -- If you're going to be dumb, you better be tough |
#65
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Sat, 01 Dec 2007 15:11:19 GMT, chuckb
wrote: Kenneth wrote: On Fri, 30 Nov 2007 22:21:13 -0500, Jim Behning wrote: Now that has a few good answers. I would not have thought about the freezing closed loops. Howdy, Any responsibly designed system protects against such freezing... All the best, but on the other hand: from your OP "The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged." any system that is operated outside it's design criteria risks failure! good luck with yours! chuck b:-) Hi Chuck, It would seem that I have not communicated clearly... Indeed, the design folks tell me not to use any setback, but they seem unable to tell me "why." Their lack of a meaningful explanation was the cause of my original question about the setback issue. All the best, -- Kenneth If you email... Please remove the "SPAMLESS." |
#66
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Nov 26, 11:48 pm, Kenneth
wrote: Howdy, This is way OT...(again), but: We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? The rate at which your house loses heat to the environment depends in an almost linear fashion on the temperature difference between your house and the outside environment. So as your house cools, the rate at which it loses heat will decrease. Keeping the house at the higher temperature means it will constantly lose heat at that higher rate, and all of that heat lost must be mad eup to maintain the temperature. If you let it cool down and heat it back up the 'stored' heat that is lost to the environment while cooling is exactly equal to the extra heat needed to heat it back up. But the heat loss to the enviornment is less the whol time during which the house is cooler than normal. Ergo, it ALWAY will use less heat to let it cool down and heat it back up than to maintain it at the higher temperature. What comes into play is the cost of pumping that heat into your house at the higher rate for the short period of time during which it heats back up. If that is down with auxillary electric resistance heat that MAY cost more or use more energy overall than just keeping it warm. The presumption that you have an auxiliary heating system may be part of the reason why you get advice to the contrary. Another concern may be that cycling the temperature may result in persistent cold spots or condensation problems that could lead to overall dissatisfaction with the system. But mostly I doubt you have ever spoken on the phone with anyone who actually studied heat transfer phenomenon or even took a physics course ever. The other possibility suggested is that extracting heat too fast from the groundwater could create a pool of cooled water underground with a resultant lower efficiency of heat extraction. That would depend largely on the groundwater environment and how extensive the heat exchange area is underground. I doubt that a definitive general answer can be given regarding that last concern. It would be highly dependent on the specific situation. -- FF |
#67
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Nov 27, 12:44 am, "Lew Hodgett" wrote:
"Kenneth" wrote: We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? In a nutshell, thermal inertia. Once the system is balanced, it requires minimum energy to maintain the balance. Change the set point to a lower level, remain there for a while, then return to the higher level requires a lot of thermal work. Heat intensive industries such as steel, refineries, etc, run 24/7 for just this reason. No, the reason is that it costs them money to keep it warm and it also costs them money to warm it up , but they can produce a product while it is warm and not while it is warming up. It is not how much they are spending on energy, it is their return on that investment--less than zero (due to other operating costs) while warming up, and greater than zero (hopefully) when at operating temperature. There are other considerations such as thermal stresses during warm-up and cooling down. -- FF |
#68
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Nov 27, 7:26 am, Robatoy wrote:
... I was going to try to equate this with the reason why when you increase the waterflow through your car's radiator by taking out the thermostat, your engine will overheat. The water HAS to spend time in the rad to be able to give up its heat. So the thermostat slows down the waterflow. Conventional thinking would suggest that by increasing the waterflow, it should cool better. (There are a few caveats in there too, so everybody keep their shirts on.) That is the first I ever heard of that. The higher the flow rate the higher the Reynolds number and therefor the higher the convective heat-transfer coefficient. You may get less heat transferred per gram of water flowing through the radiator, but not in inverse proportion to the rate at which grams of water flow through. IOW you might get only 75% of the heat loss per gram of water but will have twice as many grams of water flowing through. -- FF |
#69
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Fred the Red Shirt wrote:
On Nov 27, 7:26 am, Robatoy wrote: ... I was going to try to equate this with the reason why when you increase the waterflow through your car's radiator by taking out the thermostat, your engine will overheat. The water HAS to spend time in the rad to be able to give up its heat. So the thermostat slows down the waterflow. Conventional thinking would suggest that by increasing the waterflow, it should cool better. (There are a few caveats in there too, so everybody keep their shirts on.) That is the first I ever heard of that. The higher the flow rate the higher the Reynolds number and therefor the higher the convective heat-transfer coefficient. You may get less heat transferred per gram of water flowing through the radiator, but not in inverse proportion to the rate at which grams of water flow through. IOW you might get only 75% of the heat loss per gram of water but will have twice as many grams of water flowing through. Yes, it's simply wrong in general. If one didn't get additional cooling capacity when the thermostat opened as compared to when it is closed, there would be insufficient cooling capacity to prevent overheating at almost any operating condition. Whatever "caveats" were suggested to counteract that would have to be extreme, indeed... -- |
#70
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Dec 2, 6:18 pm, dpb wrote:
Fred the Red Shirt wrote: On Nov 27, 7:26 am, Robatoy wrote: ... I was going to try to equate this with the reason why when you increase the waterflow through your car's radiator by taking out the thermostat, your engine will overheat. The water HAS to spend time in the rad to be able to give up its heat. So the thermostat slows down the waterflow. Conventional thinking would suggest that by increasing the waterflow, it should cool better. (There are a few caveats in there too, so everybody keep their shirts on.) That is the first I ever heard of that. The higher the flow rate the higher the Reynolds number and therefor the higher the convective heat-transfer coefficient. You may get less heat transferred per gram of water flowing through the radiator, but not in inverse proportion to the rate at which grams of water flow through. IOW you might get only 75% of the heat loss per gram of water but will have twice as many grams of water flowing through. Yes, it's simply wrong in general. If one didn't get additional cooling capacity when the thermostat opened as compared to when it is closed, there would be insufficient cooling capacity to prevent overheating at almost any operating condition. Whatever "caveats" were suggested to counteract that would have to be extreme, indeed... If he's talking bout a new engine them maybe removing the radiator could confuse the computer and really screw things up--but since normal operation is for the thermostat to open when the water gets hot--how COULD it overheat by leaving ti open? Once it gets hot, it would open anyways. Sound's like an old wive's) mechanic's tale. -- FF |
#71
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Dec 2, 7:56 pm, Fred the Red Shirt wrote:
On Dec 2, 6:18 pm, dpb wrote: Fred the Red Shirt wrote: ... Whatever "caveats" were suggested to counteract that would have to be extreme, indeed... If he's talking bout a new engine them maybe removing the radiator Er, I meant removing the 'thermostat'. There is little doubt that removing the radiator will cause the engine to overheat... -- FF |
#72
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Sun, 2 Dec 2007 09:55:59 -0800 (PST), Fred the Red Shirt
wrote: On Nov 26, 11:48 pm, Kenneth wrote: Howdy, This is way OT...(again), but: We heat and cool our home geothermally (water to air system.) We would, of course, like to decrease our costs further if we can, and so have explored the benefits of setting our thermostat lower at those times when the house (or parts of it) are not occupied. The folks who designed the heating system say that with these systems, it is best to leave the set temp unchanged. Of course, I have asked "why", but when I do, it seems that smoke starts to come out of the phone. In essence, they say that it is "best" but seem unable to say why. Might any of you know what would be best in this regard , and particularly whether the issue of thermostat setback is actually any different for geothermal systems? The rate at which your house loses heat to the environment depends in an almost linear fashion on the temperature difference between your house and the outside environment. So as your house cools, the rate at which it loses heat will decrease. Keeping the house at the higher temperature means it will constantly lose heat at that higher rate, and all of that heat lost must be mad eup to maintain the temperature. If you let it cool down and heat it back up the 'stored' heat that is lost to the environment while cooling is exactly equal to the extra heat needed to heat it back up. But the heat loss to the enviornment is less the whol time during which the house is cooler than normal. Ergo, it ALWAY will use less heat to let it cool down and heat it back up than to maintain it at the higher temperature. What comes into play is the cost of pumping that heat into your house at the higher rate for the short period of time during which it heats back up. If that is down with auxillary electric resistance heat that MAY cost more or use more energy overall than just keeping it warm. The presumption that you have an auxiliary heating system may be part of the reason why you get advice to the contrary. Another concern may be that cycling the temperature may result in persistent cold spots or condensation problems that could lead to overall dissatisfaction with the system. But mostly I doubt you have ever spoken on the phone with anyone who actually studied heat transfer phenomenon or even took a physics course ever. The other possibility suggested is that extracting heat too fast from the groundwater could create a pool of cooled water underground with a resultant lower efficiency of heat extraction. That would depend largely on the groundwater environment and how extensive the heat exchange area is underground. I doubt that a definitive general answer can be given regarding that last concern. It would be highly dependent on the specific situation. Hello to all (again), Well, I am the OP on this "Will I save if I use a thermostat setback on my geothermal system" thread, and I believe that I now have an answer: Part of the hassle I faced in experimenting with this was that for some reason, I kept thinking only of my house. We have a number of electrical appliances there that are used (essentially) randomly, and their use would certainly throw off any comparisons that I could make over a relatively short period of time. I commented on that to my wife, and she said "So do the experiment in the barn." (She did not actually say "So do the experiment in the barn, you idiot", but that is what I heard.) Our office-barn is heated with exactly the same system as is our house (water to air geo with no backup resistance heat) and there is no variability of electrical consumption other than the heating system for most of each day. So, with that information, I did a very simple experiment. I have run it only for six days but, as you will see, the pattern seems quite clear: I set the programmable thermostat to drop the "call heat" temperature by 10 degrees F for 12 hours on alternating nights. Each morning, at the same time, I read the barn's electric meter. Finally, I got the degree days, and wind speed, from a weather service site. With that, I could calculate the ratio of KWH to Degree Day. I have also included in the table below the reported max wind speed for the day. KWH/DD WS Day 1: 1.2 (setback) 14 Day 2: 1.6 (no setback) 17 Day 3: 1.0 (setback) 8 Day 4: 1.3 (no setback) 0 Day 5: 1.0 (setback) 12 Day 6: 1.2 (no setback) 3 So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. All the best, -- Kenneth If you email... Please remove the "SPAMLESS." |
#73
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
.... So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. As at least one other poster noted, they're concerned w/ other factors that aren't applicable in your case (primarily dominated by the use of resistance electric heat in many/most systems)... There are others including the potential freezeup, etc., that are possible but imo they're mostly cya kinds of responses. Did you try the Water Furnace people directly or contact the Okla State or some of the other resources for other input? -- |
#74
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Sat, 08 Dec 2007 09:22:52 -0600, dpb
wrote: Kenneth wrote: ... So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. As at least one other poster noted, they're concerned w/ other factors that aren't applicable in your case (primarily dominated by the use of resistance electric heat in many/most systems)... There are others including the potential freezeup, etc., that are possible but imo they're mostly cya kinds of responses. Did you try the Water Furnace people directly or contact the Okla State or some of the other resources for other input? Howdy, The CYA analysis makes sense to me, but as you probably know, there is no real "freeze up" danger at all. These systems simply turn themselves off is the incoming water is too cold. Also, as you may know "Water Furnace" is a brand name. Our equipment is ClimateMaster. I have communicated about all this at some length with the ClimateMaster folks, with the geo folks from my electric utility, and with the installer of the equipment. They all have said "no setback" is best. All the best, -- Kenneth If you email... Please remove the "SPAMLESS." |
#75
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
On Sat, 08 Dec 2007 09:22:52 -0600, dpb wrote: Kenneth wrote: ... So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. As at least one other poster noted, they're concerned w/ other factors that aren't applicable in your case (primarily dominated by the use of resistance electric heat in many/most systems)... There are others including the potential freezeup, etc., that are possible but imo they're mostly cya kinds of responses. Did you try the Water Furnace people directly or contact the Okla State or some of the other resources for other input? Howdy, The CYA analysis makes sense to me, but as you probably know, there is no real "freeze up" danger at all. These systems simply turn themselves off is the incoming water is too cold. The problem I've normally seen is on the once-through water exchange systems (which is also what I think I recall being mentioned in one of the earlier postings of a problem--whether it was yours or another I don't recall) is the freezeup of the outlet when systems aren't running. My opinion remains as I noted there is that if that's a problem for a given system, it will be so whether there's a setback or not unless the system is so undersized as to run continuously; hence my assessment of that as a response as being in the "CYA" category. Also, as you may know "Water Furnace" is a brand name. Our equipment is ClimateMaster. Yes, I had thought that was who you had said earlier...I don't know ClimateMaster; had a Water Furnace system earlier and was pretty impressed w/ their factory rep service/technical support. I have communicated about all this at some length with the ClimateMaster folks, with the geo folks from my electric utility, and with the installer of the equipment. They all have said "no setback" is best. I think again all of those folks are addressing the general case still rather than the specifics of a given installation and are still using the answer that is easiest for them. It would be interesting if could get to one of the actual research facilities that might address a specific system rather than the general consumer response. If you were still interested in pursuing it from that standpoint I'd again suggest ORNL, TVA R&D (not power) or OSU might be more likely to answer a real question. -- |
#76
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Sat, 08 Dec 2007 10:00:24 -0600, dpb
wrote: Kenneth wrote: On Sat, 08 Dec 2007 09:22:52 -0600, dpb wrote: Kenneth wrote: ... So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. As at least one other poster noted, they're concerned w/ other factors that aren't applicable in your case (primarily dominated by the use of resistance electric heat in many/most systems)... There are others including the potential freezeup, etc., that are possible but imo they're mostly cya kinds of responses. Did you try the Water Furnace people directly or contact the Okla State or some of the other resources for other input? Howdy, The CYA analysis makes sense to me, but as you probably know, there is no real "freeze up" danger at all. These systems simply turn themselves off is the incoming water is too cold. The problem I've normally seen is on the once-through water exchange systems (which is also what I think I recall being mentioned in one of the earlier postings of a problem--whether it was yours or another I don't recall) is the freezeup of the outlet when systems aren't running. My opinion remains as I noted there is that if that's a problem for a given system, it will be so whether there's a setback or not unless the system is so undersized as to run continuously; hence my assessment of that as a response as being in the "CYA" category. Also, as you may know "Water Furnace" is a brand name. Our equipment is ClimateMaster. Yes, I had thought that was who you had said earlier...I don't know ClimateMaster; had a Water Furnace system earlier and was pretty impressed w/ their factory rep service/technical support. I have communicated about all this at some length with the ClimateMaster folks, with the geo folks from my electric utility, and with the installer of the equipment. They all have said "no setback" is best. I think again all of those folks are addressing the general case still rather than the specifics of a given installation and are still using the answer that is easiest for them. It would be interesting if could get to one of the actual research facilities that might address a specific system rather than the general consumer response. If you were still interested in pursuing it from that standpoint I'd again suggest ORNL, TVA R&D (not power) or OSU might be more likely to answer a real question. Hi again, For me there are two (essentially unrelated) issues: First, I am concerned with my system(s) and whatever savings I might realize with the setbacks. Second, I am a curious sort, and often enjoy understanding this sort of thing. Right now, my energies are focused on #1, and with my very simple experiment, I do believe I have my answer. #2 will have to wait a bit! All the best, -- Kenneth If you email... Please remove the "SPAMLESS." |
#77
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
.... First, I am concerned with my system(s) and whatever savings I might realize with the setbacks. Second, I am a curious sort, and often enjoy understanding this sort of thing. Right now, my energies are focused on #1, and with my very simple experiment, I do believe I have my answer. #2 will have to wait a bit! The answer to the first is clear -- a lower setpoint is less total integrated demand as compared to no setback so unless there are mitigating factors such as the higher-rate aux heat (that you don't have), then a setback will invariably be less input. The other issues are also system-specific but the design issues have been dealt with by the various research groups. I never had a convenient water source so didn't pursue the logistics of them that much. -- |
#78
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
Hello to all (again), Well, I am the OP on this "Will I save if I use a thermostat setback on my geothermal system" thread, and I believe that I now have an answer: Part of the hassle I faced in experimenting with this was that for some reason, I kept thinking only of my house. We have a number of electrical appliances there that are used (essentially) randomly, and their use would certainly throw off any comparisons that I could make over a relatively short period of time. I commented on that to my wife, and she said "So do the experiment in the barn." (She did not actually say "So do the experiment in the barn, you idiot", but that is what I heard.) Our office-barn is heated with exactly the same system as is our house (water to air geo with no backup resistance heat) and there is no variability of electrical consumption other than the heating system for most of each day. So, with that information, I did a very simple experiment. I have run it only for six days but, as you will see, the pattern seems quite clear: I set the programmable thermostat to drop the "call heat" temperature by 10 degrees F for 12 hours on alternating nights. Each morning, at the same time, I read the barn's electric meter. Finally, I got the degree days, and wind speed, from a weather service site. With that, I could calculate the ratio of KWH to Degree Day. I have also included in the table below the reported max wind speed for the day. KWH/DD WS Day 1: 1.2 (setback) 14 Day 2: 1.6 (no setback) 17 Day 3: 1.0 (setback) 8 Day 4: 1.3 (no setback) 0 Day 5: 1.0 (setback) 12 Day 6: 1.2 (no setback) 3 So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. All the best, What was the recovery time after the setback days? |
#79
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
Kenneth wrote:
Hello to all (again), Well, I am the OP on this "Will I save if I use a thermostat setback on my geothermal system" thread, and I believe that I now have an answer: Part of the hassle I faced in experimenting with this was that for some reason, I kept thinking only of my house. We have a number of electrical appliances there that are used (essentially) randomly, and their use would certainly throw off any comparisons that I could make over a relatively short period of time. I commented on that to my wife, and she said "So do the experiment in the barn." (She did not actually say "So do the experiment in the barn, you idiot", but that is what I heard.) Our office-barn is heated with exactly the same system as is our house (water to air geo with no backup resistance heat) and there is no variability of electrical consumption other than the heating system for most of each day. So, with that information, I did a very simple experiment. I have run it only for six days but, as you will see, the pattern seems quite clear: I set the programmable thermostat to drop the "call heat" temperature by 10 degrees F for 12 hours on alternating nights. Each morning, at the same time, I read the barn's electric meter. Finally, I got the degree days, and wind speed, from a weather service site. With that, I could calculate the ratio of KWH to Degree Day. I have also included in the table below the reported max wind speed for the day. KWH/DD WS Day 1: 1.2 (setback) 14 Day 2: 1.6 (no setback) 17 Day 3: 1.0 (setback) 8 Day 4: 1.3 (no setback) 0 Day 5: 1.0 (setback) 12 Day 6: 1.2 (no setback) 3 So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. All the best, I'm wondering if your savings aren't as great as you think. The reason is that on a setback day, you have zero electrical usage as the house coasts down to the setback temp. The next day's usage gets nailed with the recovery time usage. Perhaps week long vs day long alternating periods might mitigate some of this effect? |
#80
Posted to rec.woodworking
|
|||
|
|||
OT - Geothermal Heat issue...?
On Dec 8, 6:57 pm, Doug Winterburn wrote:
Kenneth wrote: Hello to all (again), Well, I am the OP on this "Will I save if I use a thermostat setback on my geothermal system" thread, and I believe that I now have an answer: Part of the hassle I faced in experimenting with this was that for some reason, I kept thinking only of my house. We have a number of electrical appliances there that are used (essentially) randomly, and their use would certainly throw off any comparisons that I could make over a relatively short period of time. I commented on that to my wife, and she said "So do the experiment in the barn." (She did not actually say "So do the experiment in the barn, you idiot", but that is what I heard.) Our office-barn is heated with exactly the same system as is our house (water to air geo with no backup resistance heat) and there is no variability of electrical consumption other than the heating system for most of each day. So, with that information, I did a very simple experiment. I have run it only for six days but, as you will see, the pattern seems quite clear: I set the programmable thermostat to drop the "call heat" temperature by 10 degrees F for 12 hours on alternating nights. Each morning, at the same time, I read the barn's electric meter. Finally, I got the degree days, and wind speed, from a weather service site. With that, I could calculate the ratio of KWH to Degree Day. I have also included in the table below the reported max wind speed for the day. KWH/DD WS Day 1: 1.2 (setback) 14 Day 2: 1.6 (no setback) 17 Day 3: 1.0 (setback) 8 Day 4: 1.3 (no setback) 0 Day 5: 1.0 (setback) 12 Day 6: 1.2 (no setback) 3 So, on the days with setback, the mean KWH/DD was 1.06. On the days with no setback, that mean was 1.36. The resulting savings are approximately 22%. I do remain baffled by the reasons the geothermal folks (installers, designers, sellers) seem to be consistent in suggesting that such setbacks are not of value. All the best, I'm wondering if your savings aren't as great as you think. The reason is that on a setback day, you have zero electrical usage as the house coasts down to the setback temp. The next day's usage gets nailed with the recovery time usage. Perhaps week long vs day long alternating periods might mitigate some of this effect? So long as he reads the meter after his house i swarmed up, it doesn't matter. But it should be well after it has warmed up as lingering cold spots away from the thermostat will have the effect you suggest. It would be better to read the meter at the same time every night, right before the setback. -- FF |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
geothermal heat pump insufficient | Home Repair | |||
Geothermal heat pump condensate problem. | Home Repair | |||
replacing my geothermal heat pump... | Home Repair | |||
Geothermal Heat Pump | Home Repair | |||
Problems with Geothermal Heat Pump Systems | Home Repair |