Hi,

I've been reading many of the threads regarding shed or greenhouse
electrics, but I'm still not 100% on the way to go, so I thought it
best to clarify some things before I proceed.

I have a split-load consumer unit. From the CU to the outside of the
house it approx 8m. From the outside of the house to the brick built
shed it is approx another 8m. I am planning to have a double socket
and a light. The double socket will be used for the occassional use of
a power tool such as a jigsaw or a lawnmower (about 2000w max). The
light will be a standard 100w. Also I plan to power a water feature (2
metres from shed, 25w), a pond pump (15m from shed, 25w), a security
light (500w) attached to the outside of the shed and also have a
single waterproof socket (15m from shed, by pond) just incase I need
to plug something in at the top of my garden.

My questions are (sorry there are a lot of them) :

1. I'm going to use a spare 20Amp 'B' type MCB on the non-RCD
protected side of the CU using 4mm T+E cable. Can I use normal T+E
cable for the first 8m (up to the outside of the house) and then
connect it using a junction box, to 8m of SWA 4mm cable to the shed?

2. I was planning to place the RCD spur unit inside the shed at the
end of the SWA cable. Can I then continue the radial circuit using
normal 4mm T+E or could I use a Fused Connection Unit after the RCD
and continue with 2.5mm T+E?

3. Can I use a plastic back box for the double socket or are there
special 'shed' style sockets?

4. I have estimated a total of 10m of cable being used inside the
shed. Does this have any impact of whether I should use a separate
earth rod or can I just connect the power to the house earth?

Just so you know, I was going to spur to use a 5amp FCU for the shed
light and the security light. Also, all the outside cabling is SWA and
will be in that 20mm blue plastic piping that you can buy from Wickes,
buried deep deep underground.

Thank you in advance!

Paul
  #2   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On 21 May 2004 08:09:02 -0700, in uk.d-i-y (Paul)
strung together this:

1. I'm going to use a spare 20Amp 'B' type MCB on the non-RCD
protected side of the CU using 4mm T+E cable. Can I use normal T+E
cable for the first 8m (up to the outside of the house) and then
connect it using a junction box, to 8m of SWA 4mm cable to the shed?

Yep, all looking good so far.

2. I was planning to place the RCD spur unit inside the shed at the
end of the SWA cable. Can I then continue the radial circuit using
normal 4mm T+E or could I use a Fused Connection Unit after the RCD
and continue with 2.5mm T+E?

Why not use a 'garage unit'. A 25A RCD with a 16A and 6A MCB. Run the
lighting in 1mm from the 6A and the power in 2.5mm from the 16A.
(screwfix.com Cat No. 63138).

3. Can I use a plastic back box for the double socket or are there
special 'shed' style sockets?


You can use plastic sockets, if they're not likely to get battered. I
usually fit metalclad accessories in out buildings and the like.

4. I have estimated a total of 10m of cable being used inside the
shed. Does this have any impact of whether I should use a separate
earth rod or can I just connect the power to the house earth?

As it's only over a relatively short distance I would export the house
earth to the shed.

Just so you know, I was going to spur to use a 5amp FCU for the shed
light and the security light.


Yep, that or the way I suggested above.

Also, all the outside cabling is SWA and
will be in that 20mm blue plastic piping that you can buy from Wickes,
buried deep deep underground.

You don't need to enclose SWA in anything, if you do make sure it
isn't in a water pipe! It only confuses people in the future. I would
bury the SWA as it is.
--

SJW
A.C.S. Ltd.
  #3   Report Post  
BigWallop
 
Posts: n/a
Default Shed Electrics


"Paul" wrote in message
om...
Hi,

snipped

My questions are (sorry there are a lot of them) :

1. I'm going to use a spare 20Amp 'B' type MCB on the non-RCD
protected side of the CU using 4mm T+E cable. Can I use normal T+E
cable for the first 8m (up to the outside of the house) and then
connect it using a junction box, to 8m of SWA 4mm cable to the shed?


Any external wiring should be protected as much as possible, so I'd personally
advise you to use the RCD side of the CU.

It's also best and safest if you can make the SWA in a single run all the way
between the two points. Joints in anything, by nature, make them less
efficient. And I'd also go for 6 mm csa' SWA on that full length to make sure
that supply is adequate enough to take any fault currents.


2. I was planning to place the RCD spur unit inside the shed at the
end of the SWA cable. Can I then continue the radial circuit using
normal 4mm T+E or could I use a Fused Connection Unit after the RCD
and continue with 2.5mm T+E?


The circuits you intend to install from the shed supply are not going to be huge
loads, so 2.5 mm csa' should be enough for radial connection to them.

You might also find that you need to install quite a large, not huge, junction
box inside the shed to take all the seperate circuit connections you want to
make. Not just now, but in the future.


3. Can I use a plastic back box for the double socket or are there
special 'shed' style sockets?


Try to go for industrial socket plates and light fittings because they are
slightly safer for outdoor use. They also take more of a bashing in extreme
weather conditions. Weather proof is even better for building that are not
going to be at constant temperature and humidities.



4. I have estimated a total of 10m of cable being used inside the
shed. Does this have any impact of whether I should use a separate
earth rod or can I just connect the power to the house earth?


Relying on the Wire Armour is never a good thing really. So I'd advise that a
seperate local spike be driven. You should then be using a separate CU in the
shed and make your individual circuits from that.


Just so you know, I was going to spur to use a 5amp FCU for the shed
light and the security light. Also, all the outside cabling is SWA and
will be in that 20mm blue plastic piping that you can buy from Wickes,
buried deep deep underground.

Thank you in advance!

Paul



---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.688 / Virus Database: 449 - Release Date: 18/05/04


  #4   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On Fri, 21 May 2004 15:46:37 GMT, in uk.d-i-y "BigWallop"
strung together this:

Any external wiring should be protected as much as possible, so I'd personally
advise you to use the RCD side of the CU.

Ignore this bit, it is unneccesary and adds to the nuisance tripping.

It's also best and safest if you can make the SWA in a single run all the way
between the two points. Joints in anything, by nature, make them less
efficient. And I'd also go for 6 mm csa' SWA on that full length to make sure
that supply is adequate enough to take any fault currents.

Somewhat excessive that is. 4mm is plenty adequate, and as for the
joints, 1 mid point connection isn't going to have any influence on
the current carrying capacity of the circuit or its reliability.

Relying on the Wire Armour is never a good thing really. So I'd advise that a
seperate local spike be driven. You should then be using a separate CU in the
shed and make your individual circuits from that.

He never asked if he could use the SWA as an earth, just whether he
can use an external earth rod. If he uses 3 core SWA cable then the
third core is the earth.
--

SJW
A.C.S. Ltd.
  #5   Report Post  
BigWallop
 
Posts: n/a
Default Shed Electrics


"Lurch" wrote in message
...
On Fri, 21 May 2004 15:46:37 GMT, in uk.d-i-y "BigWallop"
strung together this:

Any external wiring should be protected as much as possible, so I'd

personally
advise you to use the RCD side of the CU.

Ignore this bit, it is unneccesary and adds to the nuisance tripping.

It's also best and safest if you can make the SWA in a single run all the way
between the two points. Joints in anything, by nature, make them less
efficient. And I'd also go for 6 mm csa' SWA on that full length to make

sure
that supply is adequate enough to take any fault currents.

Somewhat excessive that is. 4mm is plenty adequate, and as for the
joints, 1 mid point connection isn't going to have any influence on
the current carrying capacity of the circuit or its reliability.

Relying on the Wire Armour is never a good thing really. So I'd advise that

a
seperate local spike be driven. You should then be using a separate CU in

the
shed and make your individual circuits from that.

He never asked if he could use the SWA as an earth, just whether he
can use an external earth rod. If he uses 3 core SWA cable then the
third core is the earth.

SJW
A.C.S. Ltd.


But you know what like these DIYers are. They say they'll only put a certain
load on things, and then, before you know it, they're running disco's in the
garden for the kids. :-))


---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.688 / Virus Database: 449 - Release Date: 18/05/04




  #6   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On Fri, 21 May 2004 19:52:09 GMT, in uk.d-i-y "BigWallop"
strung together this:

But you know what like these DIYers are. They say they'll only put a certain
load on things, and then, before you know it, they're running disco's in the
garden for the kids. :-))

Well, quite! I've just re-read my post and it sounded a bit angry,
sorry about that!
But, I've run complete DJ rigs, including most if not all of the
lighting, from 13A extension leads before now. I don't think a kids
disco is going to pull more than a couple of amps.
--

SJW
A.C.S. Ltd.
  #7   Report Post  
steve
 
Posts: n/a
Default Shed Electrics

(Lurch) wrote in message ...
On 21 May 2004 08:09:02 -0700, in uk.d-i-y
(Paul)
strung together this:

1. I'm going to use a spare 20Amp 'B' type MCB on the non-RCD
protected side of the CU using 4mm T+E cable. Can I use normal T+E
cable for the first 8m (up to the outside of the house) and then
connect it using a junction box, to 8m of SWA 4mm cable to the shed?

Yep, all looking good so far.

2. I was planning to place the RCD spur unit inside the shed at the
end of the SWA cable. Can I then continue the radial circuit using
normal 4mm T+E or could I use a Fused Connection Unit after the RCD
and continue with 2.5mm T+E?

Why not use a 'garage unit'. A 25A RCD with a 16A and 6A MCB. Run the
lighting in 1mm from the 6A and the power in 2.5mm from the 16A.
(screwfix.com Cat No. 63138).

3. Can I use a plastic back box for the double socket or are there
special 'shed' style sockets?


You can use plastic sockets, if they're not likely to get battered. I
usually fit metalclad accessories in out buildings and the like.

4. I have estimated a total of 10m of cable being used inside the
shed. Does this have any impact of whether I should use a separate
earth rod or can I just connect the power to the house earth?

As it's only over a relatively short distance I would export the house
earth to the shed.

Just so you know, I was going to spur to use a 5amp FCU for the shed
light and the security light.


Yep, that or the way I suggested above.

Also, all the outside cabling is SWA and
will be in that 20mm blue plastic piping that you can buy from Wickes,
buried deep deep underground.

You don't need to enclose SWA in anything, if you do make sure it
isn't in a water pipe! It only confuses people in the future. I would
bury the SWA as it is.


With ELECTRIC CABLE BELOW tape
http://www.screwfix.com/app/sfd/cat/...10422&ts=78647 over the
top of the cable not directly on top a good few inches above it for
obv reasons and might be a good idea to put an accurate map of garden
with the cable run marked on it near the CU for future referance

Steve
  #8   Report Post  
John Rumm
 
Posts: n/a
Default Shed Electrics

Lurch wrote:

But you know what like these DIYers are. They say they'll only put a certain
load on things, and then, before you know it, they're running disco's in the
garden for the kids. :-))


Well, quite! I've just re-read my post and it sounded a bit angry,
sorry about that!
But, I've run complete DJ rigs, including most if not all of the
lighting, from 13A extension leads before now. I don't think a kids
disco is going to pull more than a couple of amps.


Not only that - if the OP selects the correct MCB rating at the house
end then one of its jobs will be to protect the SWA from overloading.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On 21 May 2004 15:35:24 -0700, (steve) strung together
this:

With ELECTRIC CABLE BELOW tape
http://www.screwfix.com/app/sfd/cat/...10422&ts=78647 over the
top of the cable not directly on top a good few inches above it for
obv reasons and might be a good idea to put an accurate map of garden
with the cable run marked on it near the CU for future referance

Erm, yes. I thought that at the time but the thought never travelled as far as
my fingers! Good advice.
--

SJW
A.C.S. Ltd
  #11   Report Post  
Joe Lee
 
Posts: n/a
Default Shed Electrics


"Lurch" wrote in message
...
On Fri, 21 May 2004 15:46:37 GMT, in uk.d-i-y "BigWallop"
strung together this:

Any external wiring should be protected as much as possible, so I'd

personally
advise you to use the RCD side of the CU.

Ignore this bit, it is unneccesary and adds to the nuisance tripping.


Wrong. also please explain how it adds to nuisance tripping.

snip

Joe Lee

SJW
A.C.S. Ltd.




  #13   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On Sat, 22 May 2004 03:03:28 +0100, "Joe Lee" strung
together this:

No. It must be RCD protected.

Nope, you're talking ********. The sockets at the end of it needs RCD
protecting, the cable doesn't. (Unless we were on about a TT system).
--

SJW
A.C.S. Ltd
  #15   Report Post  
Lurch
 
Posts: n/a
Default Shed Electrics

On Sat, 22 May 2004 03:03:48 +0100, "Joe Lee" strung
together this:

Any external wiring should be protected as much as possible, so I'd
personally
advise you to use the RCD side of the CU.

Ignore this bit, it is unneccesary and adds to the nuisance tripping.


Wrong.


Correct, sort of.

also please explain how it adds to nuisance tripping.

Well, I didn't mean it simply trips the RCD all the time, what I meant was as
it's power equipment in the shed and garden it's more likely to be the cause of
tripping the RCD. That's why it's better with it's own RCD at the shed end, you
don't lose power to half the house when the pond pump goes u\s.
--

SJW
A.C.S. Ltd


  #16   Report Post  
John Rumm
 
Posts: n/a
Default Shed Electrics

Joe Lee wrote:

Ignore this bit, it is unneccesary and adds to the nuisance tripping.



Wrong. also please explain how it adds to nuisance tripping.


Good advice I thought. "Wrong" seems rather too strong even if the
argument were balanced with pro's and con's

If you add a circuit (any circuit for that matter) to the RCD protected
side of your house CU, then you are by definition adding a new source of
earth leakage that can eat into your total combined "budget" of 30mA
allowed by the RCD. Even perfectly wired circuits may have some small
leakage due to inductive or capacitive coupling in either the circuit
itself, or more likely, the appliances used on them. Electrical
instalations sited in outbuildings are also more likely to experience
dampness from time to time which will also raise the likelihood of them
generating a leakage related trip. Every trip of this type is going to
take out all the RCD protected circuits on your split load CU - sounds
like a nuisance to me.

Since there is very little likelihood that you will be accidentally
chopping through your SWA cable with the hedge trimmers, there is no
great need for it to be RCD protected.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shed Electrics (Oh no, this again...!) Wilf UK diy 2 May 4th 04 02:03 PM
Shed Electrics Quigs UK diy 20 January 26th 04 09:56 AM
shed electrics Matt Pearson UK diy 7 January 20th 04 09:32 PM
On the subject of a garden shed Andrew McKay UK diy 3 August 27th 03 04:31 PM


All times are GMT +1. The time now is 06:44 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"