Regarding the earth.

So, you take the cable from the house csu to the shed and do you
connect the earth to the shed csu or direct to the earthing rod.

The which? book doesn't make this clear and actualy says not to
connect the houseshed cable earth wire to the shed csu, connect the
shed csu to an earth rod, but what would you do with the houseshed
earth?

It's probably obvious to you all but not to me.

Always make the system separately earthed from the house circuits, but

this
doesn't mean separating the bonding on the SWA cable between the two

points.
Use the house earth to protect the outer skin of the cable between the two
consumer units, but have a separate earthing rod into the ground locally

to
the shed and connected directly to the earthing bar in the shed consumer
unit. It doesn't interfere with any of the systems proper working

profiles
and just gives the added local protection needed for this type of
installation. Make sure that the impedance between the rod and the ground
is as low as humanly possible, so this night mean you have to bang in a

two
metre length of 15mm copper pipe to have a proper protective local earth.


--


-------------------------------------------------------------------------
FIGHT BACK AGAINST SPAM!
Download Spam Inspector, the Award Winning Anti-Spam Filter
http://mail.giantcompany.com



  #2   Report Post  
BigWallop
 
Posts: n/a
Default shed electrics


"Matt Pearson" wrote in message
...
Regarding the earth.

So, you take the cable from the house csu to the shed and do you
connect the earth to the shed csu or direct to the earthing rod.

The which? book doesn't make this clear and actualy says not to
connect the houseshed cable earth wire to the shed csu, connect the
shed csu to an earth rod, but what would you do with the houseshed
earth?

It's probably obvious to you all but not to me.


The cable you use as the supply should be connected at both ends regardless.
The only thing you need then is to connect the earth bar in the consumer
unit to an earth rod in the ground local to the shed. The requirement is
not to rely on the length of cable your using as the supply as the main
earthing point of the shed, because if this breaks down in any way it is not
supplying a proper earth point to the shed.



Always make the system separately earthed from the house circuits, but

this
doesn't mean separating the bonding on the SWA cable between the two

points.
Use the house earth to protect the outer skin of the cable between the

two
consumer units, but have a separate earthing rod into the ground locally

to
the shed and connected directly to the earthing bar in the shed consumer
unit. It doesn't interfere with any of the systems proper working

profiles
and just gives the added local protection needed for this type of
installation. Make sure that the impedance between the rod and the

ground
is as low as humanly possible, so this night mean you have to bang in a

two
metre length of 15mm copper pipe to have a proper protective local

earth.

--


-------------------------------------------------------------------------
FIGHT BACK AGAINST SPAM!
Download Spam Inspector, the Award Winning Anti-Spam Filter
http://mail.giantcompany.com





---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.563 / Virus Database: 355 - Release Date: 17/01/04


  #3   Report Post  
Matt Pearson
 
Posts: n/a
Default shed electrics


How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.

Also what, in your opinion, supply cable mm2 size should I use 4 or 6mm2?
Should a 4mm2 use 30/32A and 6mm2 use 40A. Plus what earth cable to rod
should i use?

Many thnx


The cable you use as the supply should be connected at both ends

regardless.
The only thing you need then is to connect the earth bar in the consumer
unit to an earth rod in the ground local to the shed. The requirement is
not to rely on the length of cable your using as the supply as the main
earthing point of the shed, because if this breaks down in any way it is

not
supplying a proper earth point to the shed.



Always make the system separately earthed from the house circuits, but

this
doesn't mean separating the bonding on the SWA cable between the two

points.
Use the house earth to protect the outer skin of the cable between the

two
consumer units, but have a separate earthing rod into the ground

locally
to
the shed and connected directly to the earthing bar in the shed

consumer
unit. It doesn't interfere with any of the systems proper working

profiles
and just gives the added local protection needed for this type of
installation. Make sure that the impedance between the rod and the

ground
is as low as humanly possible, so this night mean you have to bang in

a
two
metre length of 15mm copper pipe to have a proper protective local

earth.

--



-------------------------------------------------------------------------
FIGHT BACK AGAINST SPAM!
Download Spam Inspector, the Award Winning Anti-Spam Filter
http://mail.giantcompany.com





---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.563 / Virus Database: 355 - Release Date: 17/01/04




  #4   Report Post  
Dave Stanton
 
Posts: n/a
Default shed electrics

On Mon, 19 Jan 2004 15:28:34 +0000, Matt Pearson wrote:


How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.


What value do you put on your life ?

Dave
  #5   Report Post  
BigWallop
 
Posts: n/a
Default shed electrics


"Matt Pearson" wrote in message
...

How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.

Also what, in your opinion, supply cable mm2 size should I use 4 or 6mm2?
Should a 4mm2 use 30/32A and 6mm2 use 40A. Plus what earth cable to rod
should i use?

Many thnx


If you go with a 6mm csa' SWA cable with a 40amps breaker in the house, then
you can literally fit and forget it, because it is heavy enough to take any
sort of load you put on, within reason of course, and the difference in the
price between 2core X 4mm and 2core X 6mm isn't that much for a more safety
conscious supply that is going to last for many, many years.

The earthing cable between the CU and the rod should be taken in 16mm which
is the heaviest needed by any installation and introduces the least
impedance (resistance) to any fault current. This 16mm cable combined with
a 2mtr length of copper pipe hammered into the ground, and a proper earthing
strap wrapped around it, is going to give you a very safe supply which will
keep its integrity through many a large fault condition if it needs to.
What you want from a local earthing point is that the impedance is as low as
possible between the consumer unit and the ground. So taking 2mtrs of
copper into the ground is about the right amount to keep good contact
between rod and ground in almost all conditions.

The consumer unit should also have an RCD main switch fitted which will drop
the supply at the slightest hint of a local fault in the outbuilding without
causing nuisance tripping back at the house.



The cable you use as the supply should be connected at both ends

regardless.
The only thing you need then is to connect the earth bar in the consumer
unit to an earth rod in the ground local to the shed. The requirement

is
not to rely on the length of cable your using as the supply as the main
earthing point of the shed, because if this breaks down in any way it is

not
supplying a proper earth point to the shed.



Always make the system separately earthed from the house circuits,

but
this
doesn't mean separating the bonding on the SWA cable between the two
points.
Use the house earth to protect the outer skin of the cable between

the
two
consumer units, but have a separate earthing rod into the ground

locally
to
the shed and connected directly to the earthing bar in the shed

consumer
unit. It doesn't interfere with any of the systems proper working
profiles
and just gives the added local protection needed for this type of
installation. Make sure that the impedance between the rod and the

ground
is as low as humanly possible, so this night mean you have to bang

in
a
two
metre length of 15mm copper pipe to have a proper protective local

earth.

--




-------------------------------------------------------------------------
FIGHT BACK AGAINST SPAM!
Download Spam Inspector, the Award Winning Anti-Spam Filter
http://mail.giantcompany.com





---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.563 / Virus Database: 355 - Release Date: 17/01/04








  #6   Report Post  
mp
 
Posts: n/a
Default shed electrics

many thnx for your advice, it's all clearer now


"BigWallop" wrote in message ..
"Matt Pearson" wrote in message
...

How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.

Also what, in your opinion, supply cable mm2 size should I use 4 or 6mm2?
Should a 4mm2 use 30/32A and 6mm2 use 40A. Plus what earth cable to rod
should i use?

Many thnx


If you go with a 6mm csa' SWA cable with a 40amps breaker in the house, then
you can literally fit and forget it, because it is heavy enough to take any
sort of load you put on, within reason of course, and the difference in the
price between 2core X 4mm and 2core X 6mm isn't that much for a more safety
conscious supply that is going to last for many, many years.

The earthing cable between the CU and the rod should be taken in 16mm which
is the heaviest needed by any installation and introduces the least
impedance (resistance) to any fault current. This 16mm cable combined with
a 2mtr length of copper pipe hammered into the ground, and a proper earthing
strap wrapped around it, is going to give you a very safe supply which will
keep its integrity through many a large fault condition if it needs to.
What you want from a local earthing point is that the impedance is as low as
possible between the consumer unit and the ground. So taking 2mtrs of
copper into the ground is about the right amount to keep good contact
between rod and ground in almost all conditions.

The consumer unit should also have an RCD main switch fitted which will drop
the supply at the slightest hint of a local fault in the outbuilding without
causing nuisance tripping back at the house.



The cable you use as the supply should be connected at both ends

regardless.
The only thing you need then is to connect the earth bar in the consumer
unit to an earth rod in the ground local to the shed. The requirement

is
not to rely on the length of cable your using as the supply as the main
earthing point of the shed, because if this breaks down in any way it is

not
supplying a proper earth point to the shed.



Always make the system separately earthed from the house circuits,

but
this
doesn't mean separating the bonding on the SWA cable between the two

points.
Use the house earth to protect the outer skin of the cable between

the
two
consumer units, but have a separate earthing rod into the ground

locally
to
the shed and connected directly to the earthing bar in the shed

consumer
unit. It doesn't interfere with any of the systems proper working

profiles
and just gives the added local protection needed for this type of
installation. Make sure that the impedance between the rod and the

ground
is as low as humanly possible, so this night mean you have to bang

in
a
two
metre length of 15mm copper pipe to have a proper protective local

earth.

--




-------------------------------------------------------------------------
FIGHT BACK AGAINST SPAM!
Download Spam Inspector, the Award Winning Anti-Spam Filter
http://mail.giantcompany.com





---
http://www.basecuritysystems.no-ip.com

Outgoing mail is certified Virus Free.
Checked by AVG anti-virus system (http://www.grisoft.com).
Version: 6.0.563 / Virus Database: 355 - Release Date: 17/01/04




  #7   Report Post  
John Rumm
 
Posts: n/a
Default shed electrics

Matt Pearson wrote:

How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.


2m is likely to be excessive. The recommendations say at least 450mm but
more if it is likely to be heavily dug over - say 800mm.

Normal practice is to bury the cable - back fill 150mm or so, and then
lay a warning tape, then backfill the rest. That way if someone does get
carried away recreating their very own air raid shelter in the future
they should reach the tape before they get chance to damage the cable.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Chris Oates
 
Posts: n/a
Default shed electrics


"John Rumm" wrote in message
...
Matt Pearson wrote:

How deep should I go, I heard 2m but that seems a lot for 2 or 3 double
sockets and 1 or 2 lights.


2m is likely to be excessive. The recommendations say at least 450mm but
more if it is likely to be heavily dug over - say 800mm.

Normal practice is to bury the cable


in sand

- back fill 150mm or so, and then
lay a warning tape, then backfill the rest. That way if someone does get
carried away recreating their very own air raid shelter in the future
they should reach the tape before they get chance to damage the cable.




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shed Electrics Quigs UK diy 20 January 26th 04 09:56 AM
Fitting a Wylex Consumer unit with spur to shed [email protected] UK diy 3 December 10th 03 01:05 PM
existing base for garden shed....break it? john west++++ UK diy 2 October 9th 03 01:47 PM
On the subject of a garden shed Andrew McKay UK diy 3 August 27th 03 04:31 PM
Spur feed to garden shed... Me UK diy 4 August 6th 03 10:13 AM


All times are GMT +1. The time now is 06:28 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"