On Thu, 16 Sep 2004 19:41:38 +0100, Pete C
wrote: On Thu, 16 Sep 2004 19:00:42 +0100, Andy Hall wrote: That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. That depends on the temperature of the cold water. If it's 5-8 degrees as it would be in the winter, you won't have put enough in before the store runs out. Should just do it, the 60l at 60°C in the store will give 100l of bathwater at 38°C, leaving 60l of bathwater required for a 160l bath. See other post - the shortfall is rather more. The 28kW boiler will give 10l/min at 38°C, so would take 6 minutes to heat the rest of the bathwater. Which overall is pretty disappointing. I can fill the bath to equivalent volume in about 4 mins max. What would you consider a reasonable flow rate for a shower? Absolute minimum of 15lpm, preferably 20-25lpm per shower. Fairly high, how long would that be for, 10 mins? Not really - I find that sort of flow rate just about acceptable - typically for 15-20 minutes. cheers, Pete. ..andy To email, substitute .nospam with .gl |
#82
|
|||
|
|||
"Pete C" wrote in message ... On Thu, 16 Sep 2004 19:00:42 +0100, Andy Hall wrote: That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. That depends on the temperature of the cold water. If it's 5-8 degrees as it would be in the winter, you won't have put enough in before the store runs out. Should just do it, the 60l at 60°C in the store will give 100l of bathwater at 38°C, leaving 60l of bathwater required for a 160l bath. The 28kW boiler will give 10l/min at 38°C, so would take 6 minutes to heat the rest of the bathwater. Leaving aside the type of heater;- I have a "ComputaShower" computerised bath filler; The system mixes hot and cold water precisely and fills the bath to a preset (constant) level I've experimented with filling the bath with differing temperatures; it's anecdotes not data, but;- This 43deg C bath is too hot .. This 38 deg C bath is too cold This 41deg C bath is just right ...said the little bear, -- Brian |
#83
|
|||
|
|||
In message , IMM writes
"Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. It is exciting. It will do a shower and bath very well indeed, and "never" run out of hot water. So what do you think of the 28i Junior DIMM ? -- geoff |
#84
|
|||
|
|||
IMM wrote: It will do two as most showers are approx 7 to 8 litres/min. In our area, it won't do one at 6pm. The flow rate varies throughout the day between 12 and 6 litres/min dependent on the total demand. I have no intention of fitting new input pipes when the existing non combi system can provide 40l/m for the period required to run baths. We also average one water supply failure/yr, so I would not willingly give up the local loft tank facility. Regards Capitol Regards Capitol |
#85
|
|||
|
|||
"Capitol" wrote in message ... IMM wrote: It will do two as most showers are approx 7 to 8 litres/min. In our area, it won't do one at 6pm. The flow rate varies throughout the day between 12 and 6 litres/min dependent on the total demand. I have no intention of fitting new input pipes when the existing non combi system can provide 40l/m for the period required to run baths. We also average one water supply failure/yr, so I would not willingly give up the local loft tank facility. You need to move to an area with proper services. |
#86
|
|||
|
|||
"Pete C" wrote in message news On Thu, 16 Sep 2004 13:40:41 +0100, Andy Hall wrote: On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. Hi, That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. What would you consider a reasonable flow rate for a shower? Also when the cylinder is approx 25% depleted the boiler kicks in re-heating as hot water is being drawn-off. |
#87
|
|||
|
|||
"Andy Hall" wrote in message ... Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. |
#88
|
|||
|
|||
"Andy Hall" wrote in message ... On Thu, 16 Sep 2004 18:22:13 +0100, Pete C wrote: On Thu, 16 Sep 2004 13:40:41 +0100, Andy Hall wrote: On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. Hi, That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. What would you consider a reasonable flow rate for a shower? cheers, Pete. To be a bit more accurate: The formula for resultant temperature of mixing water is Vc[Tf - Tc] = Vh[Th - Tf] Where upper case V=volume T=temperature and lower case h=hot, c=cold and f=final The store holds 57 litres according to the manufacturer If the mains water temperature is 5 degrees: Vc[40 - 5] = 57[60 - 40] Solving for Vc gives 32 litres and a total of 89litres which is not enough even for an IMM bath of 100litres. For a reasonable bath of 150 litres It is only jut over half way there and at 11lpm will take a further 5 minutes or more to fill. At 10 degrees cold temperature, you could add 38 litres but still you would be at less than an IMM bath and still at nearly 5 mins to fill to produce a reasonable bath. You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. |
#89
|
|||
|
|||
"raden" wrote in message ... In message , IMM writes "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. It is exciting. It will do a shower and bath very well indeed, and "never" run out of hot water. So what do you think of the 28i Junior DIMM ? Maxie is Dim Lin the luscious far eastern lovely 28 years old? That is old my boy!! |
#90
|
|||
|
|||
In message , Brian Sharrock
writes "Pete C" wrote in message .. . On Thu, 16 Sep 2004 19:00:42 +0100, Andy Hall wrote: That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. That depends on the temperature of the cold water. If it's 5-8 degrees as it would be in the winter, you won't have put enough in before the store runs out. Should just do it, the 60l at 60°C in the store will give 100l of bathwater at 38°C, leaving 60l of bathwater required for a 160l bath. The 28kW boiler will give 10l/min at 38°C, so would take 6 minutes to heat the rest of the bathwater. Leaving aside the type of heater;- I have a "ComputaShower" computerised bath filler; The system mixes hot and cold water precisely and fills the bath to a preset (constant) level I've experimented with filling the bath with differing temperatures; it's anecdotes not data, but;- This 43deg C bath is too hot .. This 38 deg C bath is too cold This 41deg C bath is just right ...said the little bear, Did you mean bare ? -- geoff |
#91
|
|||
|
|||
In message , IMM writes
"raden" wrote in message ... In message , IMM writes "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. It is exciting. It will do a shower and bath very well indeed, and "never" run out of hot water. So what do you think of the 28i Junior DIMM ? Maxie is Dim Lin the luscious far eastern lovely 28 years old? That is old my boy!! I ask you a sensible question and you can't answer it -- geoff |
#92
|
|||
|
|||
"raden" wrote in message ... In message , IMM writes "raden" wrote in message ... In message , IMM writes "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. It is exciting. It will do a shower and bath very well indeed, and "never" run out of hot water. So what do you think of the 28i Junior DIMM ? Maxie is Dim Lin the luscious far eastern lovely 28 years old? That is old my boy!! I ask you a sensible question and you can't answer it OK I think she is fabulous, even though she is old. |
#93
|
|||
|
|||
In message , IMM writes
So what do you think of the 28i Junior DIMM ? Maxie is Dim Lin the luscious far eastern lovely 28 years old? That is old my boy!! I ask you a sensible question and you can't answer it OK I think she is fabulous, even though she is old. Should be just about right for you then answer the question -- geoff |
#94
|
|||
|
|||
"raden" wrote in message ... In message , IMM writes So what do you think of the 28i Junior DIMM ? Maxie is Dim Lin the luscious far eastern lovely 28 years old? That is old my boy!! I ask you a sensible question and you can't answer it OK I think she is fabulous, even though she is old. Should be just about right for you then answer the question Maxie I did. I think she is fabulous. |
#95
|
|||
|
|||
On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. Assuming that I were to use a whole 200 litre cylinder, which I seldom do, the energy required would be 12kWh - cost around 25-30p. ..andy To email, substitute .nospam with .gl |
#96
|
|||
|
|||
On Thu, 16 Sep 2004 23:50:29 +0100, "IMM" wrote:
"Andy Hall" wrote in message To be a bit more accurate: The formula for resultant temperature of mixing water is Vc[Tf - Tc] = Vh[Th - Tf] Where upper case V=volume T=temperature and lower case h=hot, c=cold and f=final The store holds 57 litres according to the manufacturer If the mains water temperature is 5 degrees: Vc[40 - 5] = 57[60 - 40] Solving for Vc gives 32 litres and a total of 89litres which is not enough even for an IMM bath of 100litres. For a reasonable bath of 150 litres It is only jut over half way there and at 11lpm will take a further 5 minutes or more to fill. At 10 degrees cold temperature, you could add 38 litres but still you would be at less than an IMM bath and still at nearly 5 mins to fill to produce a reasonable bath. You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. ..andy To email, substitute .nospam with .gl |
#97
|
|||
|
|||
On Thu, 16 Sep 2004 23:46:22 +0100, "IMM" wrote:
"Pete C" wrote in message news On Thu, 16 Sep 2004 13:40:41 +0100, Andy Hall wrote: On Thu, 16 Sep 2004 13:11:58 +0100, "IMM" wrote: The Alpha CB50 has a high flowrate and is wall mounted. The manufacturers quote 18lpm and since the maximum power rating is only 28kW, once the small 50 litre store is exhausted, it will drop to the typical 11lpm. Not very exciting at all. Hi, That 18lpm is at 60°C though and the store is 60l, which is enough to fill a bath in 6 mins. What would you consider a reasonable flow rate for a shower? Also when the cylinder is approx 25% depleted the boiler kicks in re-heating as hot water is being drawn-off. It makes little difference because the production rate at 40 degree output is only 11lpm. ..andy To email, substitute .nospam with .gl |
#98
|
|||
|
|||
"Andy Hall" wrote in message ... On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. It is! I will not engage with any defence of such irresponsibility. Mr Blair will be making war on the likes you. |
#99
|
|||
|
|||
"Andy Hall" wrote in message ... On Thu, 16 Sep 2004 23:50:29 +0100, "IMM" wrote: "Andy Hall" wrote in message To be a bit more accurate: The formula for resultant temperature of mixing water is Vc[Tf - Tc] = Vh[Th - Tf] Where upper case V=volume T=temperature and lower case h=hot, c=cold and f=final The store holds 57 litres according to the manufacturer If the mains water temperature is 5 degrees: Vc[40 - 5] = 57[60 - 40] Solving for Vc gives 32 litres and a total of 89litres which is not enough even for an IMM bath of 100litres. For a reasonable bath of 150 litres It is only jut over half way there and at 11lpm will take a further 5 minutes or more to fill. At 10 degrees cold temperature, you could add 38 litres but still you would be at less than an IMM bath and still at nearly 5 mins to fill to produce a reasonable bath. You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, Well they defy Andy's version. snip babble |
#100
|
|||
|
|||
On Fri, 17 Sep 2004 09:29:23 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. It is! I will not engage with any defence of such irresponsibility. Mr Blair will be making war on the likes you. If he can remember what the subject was for more than 10 seconds. ..andy To email, substitute .nospam with .gl |
#101
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 09:29:23 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. It is! I will not engage with any defence of such irresponsibility. Mr Blair will be making war on the likes you. If he can remember what the subject was for more than 10 seconds. Well those fascist violent people who want to kill for sport have been legislated against, and the Tories/royal family are implicated in breaching the Commons to commit violent acts against democracy. I am appalled and admire the way the government banned the scum. The level of violence perpetrated against our good policemen was appalling. Now to ban bargain hunting. |
#102
|
|||
|
|||
On Fri, 17 Sep 2004 10:26:27 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . On Fri, 17 Sep 2004 09:29:23 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. It is! I will not engage with any defence of such irresponsibility. Mr Blair will be making war on the likes you. If he can remember what the subject was for more than 10 seconds. Well those fascist violent people who want to kill for sport have been legislated against, This, of course, is what it is about - legislating against the people..... and the Tories/royal family are implicated in breaching the Commons to commit violent acts against democracy. I really don't think that one of the perpetrators being a friend of Prince Harry "implicates the royal family". That would be like saying that everything the my son does implicates the royal family because he played rugby with Prince Harry once. I am appalled and admire the way the government banned the scum. The level of violence perpetrated against our good policemen was appalling. I agree that this is inappropriate. Almost as inappropriate as the use of the Parliament Act and engineering the timetable in a pathetic attempt to avoid it being an election issue. Now of course it will become one - not because of animal welfare, but because of inappropriate interference in people's lives and the abuse of power to do so. Now to ban bargain hunting. So you're proposing to shut down Harrods? ..andy To email, substitute .nospam with .gl |
#103
|
|||
|
|||
On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall
wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. I'd say it represents fairly good value for money, how much did your boiler and store cost? Added to that there would be the cost of getting an installer in to connect them together. cheers, Pete. |
#104
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 10:26:27 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . On Fri, 17 Sep 2004 09:29:23 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . On Thu, 16 Sep 2004 23:48:10 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . Absolute minimum of 15lpm, preferably 20-25lpm per shower. 25 l/min per shower? Absolute irresponsible. The water used and energy used to heat that is ridiculous. No it isn't. It is! I will not engage with any defence of such irresponsibility. Mr Blair will be making war on the likes you. If he can remember what the subject was for more than 10 seconds. Well those fascist violent people who want to kill for sport have been legislated against, This, of course, is what it is about - legislating against the people..... Legislating against very bad killing people. and the Tories/royal family are implicated in breaching the Commons to commit violent acts against democracy. I really don't think that one of the perpetrators being a friend of Prince Harry "implicates the royal family". No smoke withOUT fire. I am appalled and admire the way the government banned the scum. The level of violence perpetrated against our good policemen was appalling. I agree that this is inappropriate. Of couse it is. Now of course it will become one - not because of animal welfare, but because of inappropriate interference in people's lives and the abuse of power to do so. Killing is killing, and it should not be for sport. Did you see the eyes on those murderers? Appalling. Now to ban bargain hunting. So you're proposing to shut down Harrods? That place is a pest when the sales are on. Have you the eyes of those bargain hunters when the doors open? |
#105
|
|||
|
|||
"Pete C" wrote in message ... On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. And that it can. His system can run out of hot water, and it will using 25 litres/min showers. The CB50 does not run out of hot water being two stage flowrate combi. I'd say it represents fairly good value for money, how much did your boiler and store cost? His costs the eath. He would have been better off having two combi's fed from the storage tank by a booster pump. Then all the house would be on high pressure hot and cold water. I did similar in a house with a poor mains flowrate. I instaled a Gledhilll Systemate heat bank and fed it off the cold water storage tank. Before there was an awful large cylkidner with pipes and valves hanging off all over the show making it look like a boiler room. It also had a noisy power shower pump that looked awful taking up space too. Now a nice square box with all pumps inside out of the way and a booster pump in the loft out of the way. clothes can be stored on top on the Systemate too. Looks like the one on the left he http://www.gledhill.net/docs/index.htm Full spec: http://www.gledhill.net/docs/sm2000.htm Added to that there would be the cost of getting an installer in to connect them together. |
#106
|
|||
|
|||
On Fri, 17 Sep 2004 12:19:04 +0100, "IMM" wrote:
Well those fascist violent people who want to kill for sport have been legislated against, This, of course, is what it is about - legislating against the people..... Legislating against very bad killing people. Not really. The fact that you term it "legislating against people" really does give the game away as to the motivation. and the Tories/royal family are implicated in breaching the Commons to commit violent acts against democracy. I really don't think that one of the perpetrators being a friend of Prince Harry "implicates the royal family". No smoke withOUT fire. Did the Sun say that? Now of course it will become one - not because of animal welfare, but because of inappropriate interference in people's lives and the abuse of power to do so. Killing is killing, and it should not be for sport. Did you see the eyes on those murderers? Appalling. So presumably anglers are the next on your agenda.? .... or would that limit your profession as a master baiter? Now to ban bargain hunting. So you're proposing to shut down Harrods? That place is a pest when the sales are on. Have you the eyes of those bargain hunters when the doors open? Day trippers from Milton Keynes presumably... ..andy To email, substitute .nospam with .gl |
#107
|
|||
|
|||
On Fri, 17 Sep 2004 11:42:21 +0100, Pete C
wrote: On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. You can work out how long the water will last from the store - about 90 litres when mixed with cold accounting for a 6 minute shower at 15lpm. After that, it drops to 11lpm The first is just about acceptable until the store runs out, the second is **** poor. There is no way in hell that this will feed two even modest showers unless you consider low end electric showers acceptable. I'd say it represents fairly good value for money, It depends on whether you think it does the job. I don't think that it does do anything beyond the needs of a fairly small house with one bathroom, so it doesn't matter how cheap it is if it isn't suitable. how much did your boiler and store cost? Boiler and cylinder together were about £1800. I can run two showers or a shower and a bath very quickly and not have to worry about them going cold or taking an eon to fill and run. Added to that there would be the cost of getting an installer in to connect them together. No because the cylinder isn't pressurised. ..andy To email, substitute .nospam with .gl |
#108
|
|||
|
|||
On Fri, 17 Sep 2004 12:53:36 +0100, "IMM" wrote:
"Pete C" wrote in message .. . On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. And that it can. His system can run out of hot water, and it will using 25 litres/min showers. The CB50 does not run out of hot water being two stage flowrate combi. Of course it will - as soon as the little store runs out. Then it's down to 11lpm of warm water. I'd say it represents fairly good value for money, how much did your boiler and store cost? His costs the eath. He would have been better off having two combi's fed from the storage tank by a booster pump. Then all the house would be on high pressure hot and cold water. Complete nonsense. Why on earth would I install two high flow rate combis? This would be the requirement to come close to the delivery capacity of the storage system and then an upgrade to the gas supply would be needed to run them. I did similar in a house with a poor mains flowrate. I instaled a Gledhilll Systemate heat bank and fed it off the cold water storage tank. Before there was an awful large cylkidner with pipes and valves hanging off all over the show making it look like a boiler room. It also had a noisy power shower pump that looked awful taking up space too. Now a nice square box with all pumps inside out of the way and a booster pump in the loft out of the way. clothes can be stored on top on the Systemate too. Looks like the one on the left he http://www.gledhill.net/docs/index.htm Are you the one on the right? ..andy To email, substitute .nospam with .gl |
#109
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 11:42:21 +0100, Pete C wrote: On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. You can work out how long the water will last from the store - about 90 litres when mixed with cold accounting for a 6 minute shower at 15lpm. After that, it drops to 11lpm Oh my God more mentalist. The store stores water at least at 60C, we shower approx at 38-40C as the water is being drawn off the boiler is simultaneously re-heating. You have been told this so pay attention. how much did your boiler and store cost? Boiler and cylinder together were about £1800. My God! a house gas supply can give 212 cy foot per hour. Yu can buy two combi's that consume close to that figure giving about 25 litre/min. And no cylinders and a backup if one drops out. Lateral thinking me boy. I can run two showers or a shower and a bath very quickly and not have to worry about them going cold or taking an eon to fill and run. Two combi's consuming 20 cu foot/hr will pour the water in me boy, pour it in. So two Alpha CB 50s would be well within a domestic gas supply and give you showers in abundance and NEVER run out of water, and no tanks or cylinders and natural,CH zoning of one down and one doing up. |
#110
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 12:53:36 +0100, "IMM" wrote: "Pete C" wrote in message .. . On Fri, 17 Sep 2004 08:03:27 +0100, Andy Hall wrote: You have clearly never seen a CB50 in action they fill 100 litres baths no problem, summer and winter. It's irrelevant. The machine can't defy physics, no matter how much you would like it o do so. The figures for filling even a drop-in-the-bottom 100l bath aren't brilliant, and if it's a proper sized 150l, the performance is pathetic. THey should either have designed it with a larger store (although then it wouldn't go on the wall) or a larger burner. As I say - a linsey-wolsey product. It looks like it can give a pretty decent shower by most peoples standards, or a couple of fairly modest showers at the same time. And that it can. His system can run out of hot water, and it will using 25 litres/min showers. The CB50 does not run out of hot water being two stage flowrate combi. Of course it will - as soon as the little store runs out. Then it's down to 11lpm of warm water. Hot water me boy. You need to know this. I'd say it represents fairly good value for money, how much did your boiler and store cost? His costs the eath. He would have been better off having two combi's fed from the storage tank by a booster pump. Then all the house would be on high pressure hot and cold water. Complete nonsense. A better solution for you no doubt. Why on earth would I install two high flow rate combis? To give high flowrates. This would be the requirement to come close to the delivery capacity of the storage system and then an upgrade to the gas supply would be needed to run them. Upgrade to the gas supply? The gas mains can provide 212 cu foot per hour, which is approx 200,000 btus input. I did similar in a house with a poor mains flowrate. I instaled a Gledhilll Systemate heat bank and fed it off the cold water storage tank. Before there was an awful large cylkidner with pipes and valves hanging off all over the show making it look like a boiler room. It also had a noisy power shower pump that looked awful taking up space too. Now a nice square box with all pumps inside out of the way and a booster pump in the loft out of the way. clothes can be stored on top on the Systemate too. Looks like the one on the left he http://www.gledhill.net/docs/index.htm Are you the one on the right? No it said left. |
#111
|
|||
|
|||
On Fri, 17 Sep 2004 13:39:41 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. Of course it will - as soon as the little store runs out. Then it's down to 11lpm of warm water. Hot water me boy. You need to know this. 40 degrees is skin temperature - I wouldn't describe it as hot. I'd say it represents fairly good value for money, how much did your boiler and store cost? His costs the eath. He would have been better off having two combi's fed from the storage tank by a booster pump. Then all the house would be on high pressure hot and cold water. Complete nonsense. A better solution for you no doubt. Why on earth would I install two high flow rate combis? To give high flowrates. This would be the requirement to come close to the delivery capacity of the storage system and then an upgrade to the gas supply would be needed to run them. Upgrade to the gas supply? The gas mains can provide 212 cu foot per hour, which is approx 200,000 btus input. I don't deal in deprecated units. This amounts to just under 60kW and is just about enough to run two entry level 28kW boilers leaving nothing for other appliances. An upgrade would be required. I did similar in a house with a poor mains flowrate. I instaled a Gledhilll Systemate heat bank and fed it off the cold water storage tank. Before there was an awful large cylkidner with pipes and valves hanging off all over the show making it look like a boiler room. It also had a noisy power shower pump that looked awful taking up space too. Now a nice square box with all pumps inside out of the way and a booster pump in the loft out of the way. clothes can be stored on top on the Systemate too. Looks like the one on the left he http://www.gledhill.net/docs/index.htm Are you the one on the right? No it said left. We certainly know that. ..andy To email, substitute .nospam with .gl |
#112
|
|||
|
|||
On Fri, 17 Sep 2004 13:35:31 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . You can work out how long the water will last from the store - about 90 litres when mixed with cold accounting for a 6 minute shower at 15lpm. After that, it drops to 11lpm Oh my God more mentalist. The store stores water at least at 60C, we shower approx at 38-40C as the water is being drawn off the boiler is simultaneously re-heating. You have been told this so pay attention. I did, and I also produced the complete calculation demonstrating how poor the performance really is. how much did your boiler and store cost? Boiler and cylinder together were about £1800. My God! a house gas supply can give 212 cy foot per hour. Yu can buy two combi's that consume close to that figure giving about 25 litre/min. And no cylinders and a backup if one drops out. Lateral thinking me boy. It is bad practice to use deprecated units. It is even worse to mix them. Your suggestion would produce 22lpm of warm water at 40 degrees and require the entire supply to do it, leaving nothing for other appliances. It would still need roof storage in my case and seemingly in a lot of other people's cases as well and still not protect against a failure in either the electricly nor the gas supply. In short no redundancy apart from appliance failure. I have complete backup for all services and appliances and can get superior performance so there is no point in worsening that. I can run two showers or a shower and a bath very quickly and not have to worry about them going cold or taking an eon to fill and run. Two combi's consuming 20 cu foot/hr will pour the water in me boy, pour it in. Trickle, more like. So two Alpha CB 50s would be well within a domestic gas supply Right on the edge and requiring upgrade to run anything else. and give you showers in abundance and NEVER run out of water, unless any single one of the services fails. and no tanks or cylinders and natural,CH zoning of one down and one doing up. I don't live in a one up, one down. ..andy To email, substitute .nospam with .gl |
#113
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 13:39:41 +0100, "IMM" wrote: "Andy Hall" wrote in message . Of course it will - as soon as the little store runs out. Then it's down to 11lpm of warm water. Hot water me boy. You need to know this. 40 degrees is skin temperature - I wouldn't describe it as hot. I'd say it represents fairly good value for money, how much did your boiler and store cost? His costs the eath. He would have been better off having two combi's fed from the storage tank by a booster pump. Then all the house would be on high pressure hot and cold water. Complete nonsense. A better solution for you no doubt. Why on earth would I install two high flow rate combis? To give high flowrates. This would be the requirement to come close to the delivery capacity of the storage system and then an upgrade to the gas supply would be needed to run them. Upgrade to the gas supply? The gas mains can provide 212 cu foot per hour, which is approx 200,000 btus input. I don't deal in deprecated units. This amounts to just under 60kW and is just about enough to run two entry level 28kW boilers leaving nothing for other appliances. An upgrade would be required. If a 1" gas main the meter can handle 100% overload. Easily 300 cu/foot hr. There you go. You cam use two 40kW W-B Greenstars giving 32 litres/min for 2K and natural CH zoning up and down. One does one bathroom one the other. Brilliant. |
#114
|
|||
|
|||
"Andy Hall" wrote in message ... On Fri, 17 Sep 2004 13:35:31 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . You can work out how long the water will last from the store - about 90 litres when mixed with cold accounting for a 6 minute shower at 15lpm. After that, it drops to 11lpm Oh my God more mentalist. The store stores water at least at 60C, we shower approx at 38-40C as the water is being drawn off the boiler is simultaneously re-heating. You have been told this so pay attention. I did, and I also produced the complete calculation demonstrating how poor the performance really is. It was wrong. how much did your boiler and store cost? Boiler and cylinder together were about £1800. My God! a house gas supply can give 212 cu foot per hour. You can buy two combi's that consume close to that figure giving about 25 litre/min. And no cylinders and a backup if one drops out. Lateral thinking me boy. It is bad practice to use deprecated units. It is even worse to mix them. Your suggestion would produce 22lpm of warm water Stop making things up. at 40 degrees and require the entire supply to do it, leaving nothing for other appliances. It would still need roof storage in my case and seemingly in a lot of other people's cases as well and still not protect against a failure in either the electricly nor the gas supply. In short no redundancy apart from appliance failure. I have complete backup for all services and appliances and can get superior performance so there is no point in worsening that. A;All that expensive kit and space it takes up. I can run two showers or a shower and a bath very quickly and not have to worry about them going cold or taking an eon to fill and run. Two combi's consuming 20 cu foot/hr will pour the water in me boy, pour it in. Trickle, more like. You really don't know. So two Alpha CB 50s would be well within a domestic gas supply Right on the edge and requiring upgrade to run anything else. and give you showers in abundance and NEVER run out of water, unless any single one of the services fails. And Krakatoa could erupt too. and no tanks or cylinders and natural,CH zoning of one down and one doing up. I don't live in a one up, one down. Gosh.... |
#115
|
|||
|
|||
So two Alpha CB 50s would be well within a domestic gas supply and give
you showers in abundance and NEVER run out of water, and no tanks or cylinders and natural,CH zoning of one down and one doing up. But would still take over 5 minutes to fill a bath. Christian. |
#116
|
|||
|
|||
On Fri, 17 Sep 2004 14:00:51 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . On Fri, 17 Sep 2004 13:39:41 +0100, "IMM" wrote: If a 1" gas main the meter can handle 100% overload. Easily 300 cu/foot hr. There you go. You cam use two 40kW W-B Greenstars giving 32 litres/min for 2K and natural CH zoning up and down. One does one bathroom one the other. Brilliant. So does Transco approve running their services in this way.? Perhaps you could call them and ask and then post the name and number of the person that you speak to so that people can check for themselves before putting themselves in danger. ..andy To email, substitute .nospam with .gl |
#117
|
|||
|
|||
On Fri, 17 Sep 2004 14:09:08 +0100, "IMM" wrote:
"Andy Hall" wrote in message .. . On Fri, 17 Sep 2004 13:35:31 +0100, "IMM" wrote: "Andy Hall" wrote in message .. . You can work out how long the water will last from the store - about 90 litres when mixed with cold accounting for a 6 minute shower at 15lpm. After that, it drops to 11lpm Oh my God more mentalist. The store stores water at least at 60C, we shower approx at 38-40C as the water is being drawn off the boiler is simultaneously re-heating. You have been told this so pay attention. I did, and I also produced the complete calculation demonstrating how poor the performance really is. It was wrong. Er no. The equation of Vc [Tf - Tc] = Vh [Th - Tf] is the correct one to apply when liquids of different temperatures are mixed. I know that division and multiplication are a bit more difficult than adding and taking away, but you'll get to that in next year's class. how much did your boiler and store cost? Boiler and cylinder together were about £1800. My God! a house gas supply can give 212 cu foot per hour. You can buy two combi's that consume close to that figure giving about 25 litre/min. And no cylinders and a backup if one drops out. Lateral thinking me boy. It is bad practice to use deprecated units. It is even worse to mix them. Your suggestion would produce 22lpm of warm water Stop making things up. The arithmetic is quite clear. at 40 degrees and require the entire supply to do it, leaving nothing for other appliances. It would still need roof storage in my case and seemingly in a lot of other people's cases as well and still not protect against a failure in either the electricly nor the gas supply. In short no redundancy apart from appliance failure. I have complete backup for all services and appliances and can get superior performance so there is no point in worsening that. A;All that expensive kit and space it takes up. I don't have a space problem for it, and more to the point is does the required job. I can run two showers or a shower and a bath very quickly and not have to worry about them going cold or taking an eon to fill and run. Two combi's consuming 20 cu foot/hr will pour the water in me boy, pour it in. Trickle, more like. You really don't know. You need to read through the sums. Don't worry about the multiplying and dividing - it's similar to the adding and taking away - you just do it more times. So two Alpha CB 50s would be well within a domestic gas supply Right on the edge and requiring upgrade to run anything else. and give you showers in abundance and NEVER run out of water, unless any single one of the services fails. And Krakatoa could erupt too. In the last year, I have had failures of all three services at different times. It is quite common so depending on something needing all three is a risk. ..andy To email, substitute .nospam with .gl |
#118
|
|||
|
|||
"Christian McArdle" wrote in message . net... So two Alpha CB 50s would be well within a domestic gas supply and give you showers in abundance and NEVER run out of water, and no tanks or cylinders and natural,CH zoning of one down and one doing up. But would still take over 5 minutes to fill a bath. Christian. I thought in general a bath was meant to be a relaxing experience, what is the obsession about having it filling in less than 2 min? And what happens to everyone when IMM enters a thread, OK, so he's an arse but he does actually have some decent info on high flow rate combi's. Andy and IMM need to take there personal wee chat over to e-mail after about 5 posts here, when they both then start to repeat themselves ad nauseum. David |
#119
|
|||
|
|||
On Fri, 17 Sep 2004 14:26:47 +0100, "David"
wrote: "Christian McArdle" wrote in message .net... So two Alpha CB 50s would be well within a domestic gas supply and give you showers in abundance and NEVER run out of water, and no tanks or cylinders and natural,CH zoning of one down and one doing up. But would still take over 5 minutes to fill a bath. Christian. I thought in general a bath was meant to be a relaxing experience, what is the obsession about having it filling in less than 2 min? Agreed, but imagine what happens when 4 people are competing to use the bathroom facilities and it takes nearly 15 minutes to fill a bath. And what happens to everyone when IMM enters a thread, OK, so he's an arse but he does actually have some decent info on high flow rate combi's. Check that one carefully. Andy and IMM need to take there personal wee chat over to e-mail after about 5 posts here, when they both then start to repeat themselves ad nauseum. I am happy to have an email conversation with anybody and frequently do. However this does require an email address to use. David ..andy To email, substitute .nospam with .gl |
#120
|
|||
|
|||
If a 1" gas main the meter can handle 100% overload. Easily 300 cu/foot
hr. There you go. You cam use two 40kW W-B Greenstars giving 32 litres/min for 2K and natural CH zoning up and down. One does one bathroom one the other. Brilliant. This doesn't even help with the bath filling problem, unless you've got a hose from one bathroom to the other. Even if both were connected together to combine their flows, the flow rate is still half that of a heat bank. Also, many people with gas boilers also choose to have cooked dinners. I hope you've left 15kW for the Sunday roast. Christian. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Bathroom fans improperly vented | Home Repair | |||
Installed Panasonic Bathroom Fans | Home Repair | |||
How to correctly size combi boilers | UK diy | |||
Combi Boilers | UK diy | |||
DC Fans - weird problem | Electronics Repair |