So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On Mon, 27 Jan 2020 13:56:24 -0000, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. A 13A socket can supply 3.2kW, near enough. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? It's your house, do as you wish. Just put the right fuses in the right places, it's not rocket science. I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
In article ,
Grumps wrote: Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? In terms of regs, no. (IMHO) In practice likely OK. But would it really be that much more difficult to run a proper radial from your CU? -- *Toilet stolen from police station. Cops have nothing to go on. Dave Plowman London SW To e-mail, change noise into sound. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 14:34, Dave Plowman (News) wrote:
In article , Grumps wrote: Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? In terms of regs, no. (IMHO) In practice likely OK. But would it really be that much more difficult to run a proper radial from your CU? Which bit if the regs says you can't have a Schuko? What do you mean by a "proper radial"? Ta. |
#5
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
In article ,
Grumps wrote: On 27/01/2020 14:34, Dave Plowman (News) wrote: In article , Grumps wrote: Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? In terms of regs, no. (IMHO) In practice likely OK. But would it really be that much more difficult to run a proper radial from your CU? Which bit if the regs says you can't have a Schuko? What do you mean by a "proper radial"? Ah - sorry, brain fart. Read it as if you were going to spur it off a ring. -- *Why do they put Braille on the drive-through bank machines? Dave Plowman London SW To e-mail, change noise into sound. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On Mon, 27 Jan 2020 13:56:24 +0000, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. What about a 32 amp Commando socket? https://www.mkelectric.com/en-GB/Pro...s/default.aspx |
#7
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I'd use a 25A MCB Of course its ok. Cookers are run this way. I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. -- "Strange as it seems, no amount of learning can cure stupidity, and higher education positively fortifies it." - Stephen Vizinczey |
#8
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 14:36, The Natural Philosopher wrote:
On 27/01/2020 13:56, Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I'd use a 25A MCB Of course its ok. Cookers are run this way. And the use of a Schuko socket is OK too? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On Monday, 27 January 2020 13:56:27 UTC, Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? 16A 'commando' would be better, as you're likely to find them elsewhere too (caravan sites mainly). And if it's exterior, weatherproof versions more readily available in UK. Owain |
#10
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. It's probably cheaper to buy a charge point (currently about £135 on fleabay) than building one yourself. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
|
#13
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 15:30, Grumps wrote:
On 27/01/2020 15:19, wrote: On 27/01/2020 13:56, Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. It's probably cheaper to buy a charge point (currently about £135 on fleabay) than building one yourself. I was thinking of getting something similar to this: https://www.amazon.co.uk/K-H-N-S-Cha.../dp/B07SSX23P1 It's just a higher powered version of the one that came with the car, but needs more amps in! Hence the Q about using Schuko (which this unit comes with). I assume it has the "logic" that keeps the cable safe until it's properly connected to the car charge port. The only one I saw for that price on eBay was just a 13A 3-pin socket. But then, I'm not the best at searching anywhere. Aha, understood. As others have said, I doubt that you will find many (waterproof?) Schuko outlets on the highways and byways; didn't the Leaf come with a dedicated charging cable that connects to a charge point? My M-B PHEV has both a 13A charging box (unused) and a cable. I was wrong about the charge point I mentioned earlier, but there was also a proper one listed for £200 when I looked earlier. |
#14
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 15:47, wrote:
On 27/01/2020 15:30, Grumps wrote: On 27/01/2020 15:19, wrote: On 27/01/2020 13:56, Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. It's probably cheaper to buy a charge point (currently about £135 on fleabay) than building one yourself. I was thinking of getting something similar to this: https://www.amazon.co.uk/K-H-N-S-Cha.../dp/B07SSX23P1 It's just a higher powered version of the one that came with the car, but needs more amps in! Hence the Q about using Schuko (which this unit comes with). I assume it has the "logic" that keeps the cable safe until it's properly connected to the car charge port. The only one I saw for that price on eBay was just a 13A 3-pin socket. But then, I'm not the best at searching anywhere. Aha, understood. As others have said, I doubt that you will find many (waterproof?) Schuko outlets on the highways and byways; Oh, it doesn't have to be waterproof. It'll be going in a garage. didn't the Leaf come with a dedicated charging cable that connects to a charge point? Yes. A charging box with 3-pin plug (which charges at about 10A), and the cable (type2 to type1 in my case). My M-B PHEV has both a 13A charging box (unused) and a cable. I was wrong about the charge point I mentioned earlier, but there was also a proper one listed for £200 when I looked earlier. I saw that, thanks. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 16:58, ARW wrote:
On 27/01/2020 15:19, wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. More specifically they have a type A RCD. TT is not always a requirement. However when it is you often have to TT more than the car charger. I don't see how that lines-up with 722.411.4, which says (paraphrasing) that a PME earth SHALL not be used for an outdoor vehicle charging point, with a few exceptions that would not normally apply. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 19:18, wrote:
On 27/01/2020 16:58, ARW wrote: On 27/01/2020 15:19, wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. More specifically they have a type A RCD. TT is not always a requirement. However when it is you often have to TT more than the car charger. I don't see how that lines-up with 722.411.4, which says (paraphrasing) that a PME earth SHALL not be used for an outdoor vehicle charging point, with a few exceptions that would not normally apply. It's a while since I did the installation course and I have only fitted one charging point since I went on it. Actually the NICEIC bloke said to treat both TNS and TNC-S as the same thing as the UK's electrical infrastructure is ****. I believe that you are correct and "most if not all" of PME outdoor installs required a TT installation. The big problem was that you also had to TT any other circuits that you might be able to touch whilst touching the car. You were then given a picture of a bloke with long arms that could touch his car and then his outside lights, electric gates or outside socket (not all at the same time he did not have 3 arms). If I can find the installation book I'll quite happily scan it for you and then the next time I have to install a car charging point (Christ knows when) or the subject appears on the newsgroup you can look the info up for me and send me the details whilst I am down the pub having a pint:-) Seriously, I will have to read that installation book again and if you do want a copy I'll do one for you when I have time. -- Adam |
#18
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 28/01/2020 17:43, ARW wrote:
On 27/01/2020 19:18, wrote: On 27/01/2020 16:58, ARW wrote: On 27/01/2020 15:19, wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. More specifically they have a type A RCD. TT is not always a requirement. However when it is you often have to TT more than the car charger. I don't see how that lines-up with 722.411.4, which says (paraphrasing) that a PME earth SHALL not be used for an outdoor vehicle charging point, with a few exceptions that would not normally apply. It's a while since I did the installation course and I have only fitted one charging point since I went on it. Actually the NICEIC bloke said to treat both TNS and TNC-S as the same thing as the UK's electrical infrastructure is ****. I believe that you are correct and "most if not all" of PME outdoor installs required a TT installation. The big problem was that you also had to TT any other circuits that you might be able to touch whilst touching the car. You were then given a picture of a bloke with long arms that could touch his car and then his outside lights Use a double insulated light? electric gates Make the drive and sensors transformer isolated 24V? or outside socket (not all at the same time he did not have 3 arms). At least that can be moved to another location that even Mr. Tickle can't reach SteveW |
#19
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 28/01/2020 17:43, ARW wrote:
On 27/01/2020 19:18, wrote: On 27/01/2020 16:58, ARW wrote: On 27/01/2020 15:19, wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. Charge points contain a protocol controller to handle comms with the car and to enable a contactor once safe so to do, they also have an RCD. Finally, they're supposed to be TT'd to ensure that supply and car ground potentials are similar. More specifically they have a type A RCD. TT is not always a requirement. However when it is you often have to TT more than the car charger. I don't see how that lines-up with 722.411.4, which says (paraphrasing) that a PME earth SHALL not be used for an outdoor vehicle charging point, with a few exceptions that would not normally apply. It's a while since I did the installation course and I have only fitted one charging point since I went on it. Actually the NICEIC bloke said to treat both TNS and TNC-S as the same thing as the UK's electrical infrastructure is ****. I believe that you are correct and "most if not all" of PME outdoor installs required a TT installation. The big problem was that you also had to TT any other circuits that you might be able to touch whilst touching the car. You were then given a picture of a bloke with long arms that could touch his car and then his outside lights, electric gates or outside socket (not all at the same time he did not have 3 arms). If I can find the installation book I'll quite happily scan it for you and then the next time I have to install a car charging point (Christ knows when) or the subject appears on the newsgroup you can look the info up for me and send me the details whilst I am down the pub having a pint:-) Seriously, I will have to read that installation book again and if you do want a copy I'll do one for you when I have time. Thanks for the offer but I've already installed mine and, having moved house for the first time in 30+ years, have no desire to move again for sufficiently far in the future that I won't be installing my own charge point :-) OOI I just stumbled-across a relevant vid from John Ward: https://www.youtube.com/watch?v=q87H7aIujjA |
#21
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 18:32, Andy Burns wrote:
wrote: Grumps wrote: This would need a different EVSE You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's what the EVSE does. A fair cop - initially I thought he wanted to just connect the car to the mains using a straight cable, without any interlock. Note to self: RTFQ. |
#22
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
|
#23
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote:
You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's interesting as they don't have such safety devices on caravan sites. Yeah, I was wondering about all this nanny interlocking. I guess it's because a car charging the cable is most likely will be left coonected all the time and just dumped on the floor in all weathers. People are lazy, coiling up to store neatly or put in the car just ain't going to happen, particulary in the wet and when they'll only be uncoiling it a few hours later on their return. A caravan power cable will travel with the van. Can't see why the car has to talk to the supply point. Easy enough to have a "no load" switch that isolates the cable under no load conditions and a button to set it when the cable is connected. Car needs to know how much opwer is available? If power is on this pin - x kW, that pin - y kW both pins z kW. Simples. No need to have some electronics always on consuming power... -- Cheers Dave. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 21:39, Dave Liquorice wrote:
On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's interesting as they don't have such safety devices on caravan sites. Yeah, I was wondering about all this nanny interlocking. I guess it's because a car charging the cable is most likely will be left coonected all the time and just dumped on the floor in all weathers. People are lazy, coiling up to store neatly or put in the car just ain't going to happen, particulary in the wet and when they'll only be uncoiling it a few hours later on their return. A caravan power cable will travel with the van. When used with a motorhome, it could be unplugged and left in a puddle or on wet grass, in the rain, each day. Can't see why the car has to talk to the supply point. Easy enough to have a "no load" switch that isolates the cable under no load conditions and a button to set it when the cable is connected. Car needs to know how much opwer is available? If power is on this pin - x kW, that pin - y kW both pins z kW. Simples. No need to have some electronics always on consuming power... Yes, nice and simple. SteveW |
#25
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Dave Liquorice wrote:
bert wrote: they don't have such safety devices on caravan sites. Not many caravans can take 43kW Can't see why the car has to talk to the supply point AFAIK there's not much signalling from car-EVSE just a resistor divider to let the car say it's connected and ready, or it's charging, or there's an error. Also a diode so the EVSE can't be fooled by a short on the signalling pin. Signalling from EVSE-car is a 1kHz tone, where the duty ratio says how many amps it's able to provide. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 21:39, Dave Liquorice wrote: On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's interesting as they don't have such safety devices on caravan sites. Yeah, I was wondering about all this nanny interlocking. Pretty sure the IET regs have a prohibition on unshuttered sockets in a domestic setting. Commando with an interlocked isolator would technically be a departure but at least trivial to justify. That's my understanding anyway - could be wrong and welcome correction. |
#27
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 28/01/2020 08:48, Tim Watts wrote:
On 27/01/2020 21:39, Dave Liquorice wrote: On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote: You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's interesting as they don't have such safety devices on caravan sites. Yeah, I was wondering about all this nanny interlocking. Pretty sure the IET regs have a prohibition on unshuttered sockets in a domestic setting. They do, although you can get shuttered Schuko style sockets. Commando with an interlocked isolator would technically be a departure but at least trivial to justify. There is a commando where the isolation is included in the socket - such that you can't energise it until the plug is in. (quite pricey though) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#28
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
bert wrote:
In article , writes On 27/01/2020 13:56, Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. You need a safety interlock to ensure that the cable only goes live once it is plugged-in to the car. That's interesting as they don't have such safety devices on caravan sites. Snip Some do, at least in the UK. Some of the newer sites have outlets on the bollards which require you to twist the plug after inserting it and to press a button to release it. They confuse overseas visitors and those whove not seen them before - they try another socket, then start asking €˜neighbours if their power works etc. |
#29
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
As long as the cable does not cross a footway and remains in your own
premises, ie if you have a garage or hard standing, I'd imagine you can use what you like. Obviously it has to be safe for visitors etc, ie coming out of a window and snaking across in front of the door might be an issue if the postman breaks his leg and sues! Brian -- ----- -- This newsgroup posting comes to you directly from... The Sofa of Brian Gaff... Blind user, so no pictures please Note this Signature is meaningless.! "Grumps" wrote in message ... So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. |
#30
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 15:56, Brian Gaff (Sofa 2) wrote:
As long as the cable does not cross a footway and remains in your own premises, ie if you have a garage or hard standing, I'd imagine you can use what you like. Obviously it has to be safe for visitors etc, ie coming out of a window and snaking across in front of the door might be an issue if the postman breaks his leg and sues! Brian If the postie trips over the cable, he shouldn't be in my garage! |
#31
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. The schuko straight off the CU, by itself wouldn't give you proper earthing for an EV. |
#32
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 18:30, Andy Burns wrote:
Grumps wrote: Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. The schuko straight off the CU, by itself wouldn't give you proper earthing for an EV. In a garage, its arguable you could skip making it TT. The charge lead will often include the type A RCD. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#33
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. Unless you use a different charging cable youll still be limited to 10 amps. Big Clive did a teardown of one recently explaining a bit about how they work. https://youtu.be/DAij_wWeZiY Tim -- Please don't feed the trolls |
#34
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Tim+ wrote:
Big Clive did a teardown of one recently explaining a bit about how they work. Mike's Electric Stuff has probably done better EVSE teardowns than Clive in this instance |
#35
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Andy Burns wrote:
Tim+ wrote: Big Clive did a teardown of one recently explaining a bit about how they work. Mike's Electric Stuff has probably done better EVSE teardowns than Clive in this instance But at least I offered a link... ;-) Tim -- Please don't feed the trolls |
#36
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
Tim+ wrote:
Andy Burns wrote: Mike's Electric Stuff has probably done better EVSE teardowns than Clive in this instance But at least I offered a link... ;-) The most recent three videos on his teardowns playlist https://www.youtube.com/watch?v=O58KT117crs&list=PL0KZLmPyL6AnVxyvFZRKGsIf cpQlHx0xH |
#37
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 21:08, Andy Burns wrote:
Tim+ wrote: Andy Burns wrote: Mike's Electric Stuff has probably done better EVSE teardowns than Clive in this instance But at least I offered a link... ;-) The most recent three videos on his teardowns playlist https://www.youtube.com/watch?v=O58KT117crs&list=PL0KZLmPyL6AnVxyvFZRKGsIf cpQlHx0xH And the 8 bit guy did quite a good summary of all the various variations of charge connector and charging options in use : https://www.youtube.com/watch?v=TcoLCTkM0ys (although with a US centric perspective) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#38
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 20:21, Tim+ wrote:
Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. Unless you use a different charging cable youll still be limited to 10 amps. Big Clive did a teardown of one recently explaining a bit about how they work. https://youtu.be/DAij_wWeZiY Tim Yeah, I have my eye on a different charging cable which will do up to 16A. Thanks for the link. |
#39
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 27/01/2020 21:12, Grumps wrote:
On 27/01/2020 20:21, Tim+ wrote: Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. Unless you use a different charging cable youll still be limited to 10 amps. Big Clive did a teardown of one recently explaining a bit about how they work. https://youtu.be/DAij_wWeZiY Tim Yeah, I have my eye on a different charging cable which will do up to 16A. Thanks for the link. Would it not make more sense to hard wire in a proper 32A style charger? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#40
Posted to uk.d-i-y
|
|||
|
|||
Using a 16A Schuko socket
On 29/01/2020 01:18, John Rumm wrote:
On 27/01/2020 21:12, Grumps wrote: On 27/01/2020 20:21, Tim+ wrote: Grumps wrote: So, I have an EV (Leaf) which would benefit from the ability to charge using more than a 13Amp socket can supply. The supplied charging unit/cable limits to about 10A, but the car's on board charger can accept up to 3.3kW (some say 3.6kW). This would need a different EVSE than the supplied unit, AND a beefier mains socket. Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a radial from the CU? I know I can get a proper home charge point installed, but that's not the cheapest option. TIA. Unless you use a different charging cable youll still be limited to 10 amps. Big Clive did a teardown of one recently explaining a bit about how they work. https://youtu.be/DAij_wWeZiY Tim Yeah, I have my eye on a different charging cable which will do up to 16A. Thanks for the link. Would it not make more sense to hard wire in a proper 32A style charger? Yes, but... The car is a company car and as yet they haven't decided if providing me with a home charging point is something they want to pay for. Charging at work is provided - free. The car only has a 3.3kW on-board charger (excluding the quick charge option) for connection to 230Vac. The supplied EVSE charge cable is limited to 10Amps, 2.2-2.4kW. But if I get a 16Amp EVSE, then that could be considered as an accessory for the car, and the company would then pay. Only £100-£150. And I don't mind stumping up a few pounds for a Schuko in the garage. |