So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,540
Default Using a 16A Schuko socket

On Mon, 27 Jan 2020 13:56:24 -0000, Grumps wrote:

So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.


A 13A socket can supply 3.2kW, near enough.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?


It's your house, do as you wish. Just put the right fuses in the right places, it's not rocket science.

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Using a 16A Schuko socket

In article ,
Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?


In terms of regs, no. (IMHO) In practice likely OK.

But would it really be that much more difficult to run a proper radial
from your CU?

--
*Toilet stolen from police station. Cops have nothing to go on.

Dave Plowman London SW
To e-mail, change noise into sound.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,904
Default Using a 16A Schuko socket

On Mon, 27 Jan 2020 13:56:24 +0000, Grumps wrote:

So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


What about a 32 amp Commando socket?
https://www.mkelectric.com/en-GB/Pro...s/default.aspx
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Using a 16A Schuko socket

On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I'd use a 25A MCB

Of course its ok. Cookers are run this way.

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.



--
"Strange as it seems, no amount of learning can cure stupidity, and
higher education positively fortifies it."

- Stephen Vizinczey



  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 14:36, The Natural Philosopher wrote:
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket
on a radial from the CU?

I'd use a 25A MCB

Of course its ok. Cookers are run this way.


And the use of a Schuko socket is OK too?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 14:34, Dave Plowman (News) wrote:
In article ,
Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?


In terms of regs, no. (IMHO) In practice likely OK.

But would it really be that much more difficult to run a proper radial
from your CU?


Which bit if the regs says you can't have a Schuko?
What do you mean by a "proper radial"?
Ta.

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default Using a 16A Schuko socket

On Monday, 27 January 2020 13:56:27 UTC, Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?


16A 'commando' would be better, as you're likely to find them elsewhere too (caravan sites mainly).

And if it's exterior, weatherproof versions more readily available in UK.

Owain

  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,037
Default Using a 16A Schuko socket

On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

You need a safety interlock to ensure that the cable only goes live once
it is plugged-in to the car. Charge points contain a protocol controller
to handle comms with the car and to enable a contactor once safe so to
do, they also have an RCD. Finally, they're supposed to be TT'd to
ensure that supply and car ground potentials are similar. It's probably
cheaper to buy a charge point (currently about £135 on fleabay) than
building one yourself.
  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 15:19, wrote:
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket
on a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

You need a safety interlock to ensure that the cable only goes live once
it is plugged-in to the car. Charge points contain a protocol controller
to handle comms with the car and to enable a contactor once safe so to
do, they also have an RCD. Finally, they're supposed to be TT'd to
ensure that supply and car ground potentials are similar. It's probably
cheaper to buy a charge point (currently about £135 on fleabay) than
building one yourself.


I was thinking of getting something similar to this:
https://www.amazon.co.uk/K-H-N-S-Cha.../dp/B07SSX23P1
It's just a higher powered version of the one that came with the car,
but needs more amps in! Hence the Q about using Schuko (which this unit
comes with).
I assume it has the "logic" that keeps the cable safe until it's
properly connected to the car charge port.

The only one I saw for that price on eBay was just a 13A 3-pin socket.
But then, I'm not the best at searching anywhere.
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,037
Default Using a 16A Schuko socket

On 27/01/2020 15:30, Grumps wrote:
On 27/01/2020 15:19, wrote:
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to
charge using more than a 13Amp socket can supply. The supplied
charging unit/cable limits to about 10A, but the car's on board
charger can accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a
beefier mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket
on a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

You need a safety interlock to ensure that the cable only goes live
once it is plugged-in to the car. Charge points contain a protocol
controller to handle comms with the car and to enable a contactor once
safe so to do, they also have an RCD. Finally, they're supposed to be
TT'd to ensure that supply and car ground potentials are similar. It's
probably cheaper to buy a charge point (currently about £135 on
fleabay) than building one yourself.


I was thinking of getting something similar to this:
https://www.amazon.co.uk/K-H-N-S-Cha.../dp/B07SSX23P1
It's just a higher powered version of the one that came with the car,
but needs more amps in! Hence the Q about using Schuko (which this unit
comes with).
I assume it has the "logic" that keeps the cable safe until it's
properly connected to the car charge port.

The only one I saw for that price on eBay was just a 13A 3-pin socket.
But then, I'm not the best at searching anywhere.


Aha, understood. As others have said, I doubt that you will find many
(waterproof?) Schuko outlets on the highways and byways; didn't the Leaf
come with a dedicated charging cable that connects to a charge point? My
M-B PHEV has both a 13A charging box (unused) and a cable.

I was wrong about the charge point I mentioned earlier, but there was
also a proper one listed for £200 when I looked earlier.
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 812
Default Using a 16A Schuko socket

As long as the cable does not cross a footway and remains in your own
premises, ie if you have a garage or hard standing, I'd imagine you can use
what you like. Obviously it has to be safe for visitors etc, ie coming out
of a window and snaking across in front of the door might be an issue if the
postman breaks his leg and sues!

Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"Grumps" wrote in message ...
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can accept
up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on a
radial from the CU?

I know I can get a proper home charge point installed, but that's not the
cheapest option.
TIA.



  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 15:47, wrote:
On 27/01/2020 15:30, Grumps wrote:
On 27/01/2020 15:19,
wrote:
On 27/01/2020 13:56, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to
charge using more than a 13Amp socket can supply. The supplied
charging unit/cable limits to about 10A, but the car's on board
charger can accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a
beefier mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket
on a radial from the CU?

I know I can get a proper home charge point installed, but that's
not the cheapest option.
TIA.

You need a safety interlock to ensure that the cable only goes live
once it is plugged-in to the car. Charge points contain a protocol
controller to handle comms with the car and to enable a contactor
once safe so to do, they also have an RCD. Finally, they're supposed
to be TT'd to ensure that supply and car ground potentials are
similar. It's probably cheaper to buy a charge point (currently about
£135 on fleabay) than building one yourself.


I was thinking of getting something similar to this:
https://www.amazon.co.uk/K-H-N-S-Cha.../dp/B07SSX23P1
It's just a higher powered version of the one that came with the car,
but needs more amps in! Hence the Q about using Schuko (which this
unit comes with).
I assume it has the "logic" that keeps the cable safe until it's
properly connected to the car charge port.

The only one I saw for that price on eBay was just a 13A 3-pin socket.
But then, I'm not the best at searching anywhere.


Aha, understood. As others have said, I doubt that you will find many
(waterproof?) Schuko outlets on the highways and byways;


Oh, it doesn't have to be waterproof. It'll be going in a garage.

didn't the Leaf
come with a dedicated charging cable that connects to a charge point?


Yes. A charging box with 3-pin plug (which charges at about 10A), and
the cable (type2 to type1 in my case).

My
M-B PHEV has both a 13A charging box (unused) and a cable.

I was wrong about the charge point I mentioned earlier, but there was
also a proper one listed for £200 when I looked earlier.


I saw that, thanks.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 15:56, Brian Gaff (Sofa 2) wrote:
As long as the cable does not cross a footway and remains in your own
premises, ie if you have a garage or hard standing, I'd imagine you can use
what you like. Obviously it has to be safe for visitors etc, ie coming out
of a window and snaking across in front of the door might be an issue if the
postman breaks his leg and sues!

Brian


If the postie trips over the cable, he shouldn't be in my garage!


  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Using a 16A Schuko socket

Grumps wrote:

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.


The schuko straight off the CU, by itself wouldn't give you proper
earthing for an EV.

  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,366
Default Using a 16A Schuko socket

Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


Unless you use a different charging cable youll still be limited to 10
amps. Big Clive did a teardown of one recently explaining a bit about how
they work.

https://youtu.be/DAij_wWeZiY

Tim

--
Please don't feed the trolls
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Using a 16A Schuko socket

Tim+ wrote:

Big Clive did a teardown of one recently explaining a bit about how
they work.


Mike's Electric Stuff has probably done better EVSE teardowns than Clive
in this instance
  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,366
Default Using a 16A Schuko socket

Andy Burns wrote:
Tim+ wrote:

Big Clive did a teardown of one recently explaining a bit about how
they work.


Mike's Electric Stuff has probably done better EVSE teardowns than Clive
in this instance


But at least I offered a link... ;-)

Tim

--
Please don't feed the trolls
  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Using a 16A Schuko socket

Tim+ wrote:

Andy Burns wrote:

Mike's Electric Stuff has probably done better EVSE teardowns than Clive
in this instance


But at least I offered a link... ;-)


The most recent three videos on his teardowns playlist

https://www.youtube.com/watch?v=O58KT117crs&list=PL0KZLmPyL6AnVxyvFZRKGsIf cpQlHx0xH


  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 27/01/2020 20:21, Tim+ wrote:
Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


Unless you use a different charging cable youll still be limited to 10
amps. Big Clive did a teardown of one recently explaining a bit about how
they work.

https://youtu.be/DAij_wWeZiY

Tim


Yeah, I have my eye on a different charging cable which will do up to 16A.
Thanks for the link.

  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 14,085
Default Using a 16A Schuko socket

On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote:

You need a safety interlock to ensure that the cable only goes

live
once it is plugged-in to the car.


That's interesting as they don't have such safety devices on caravan
sites.


Yeah, I was wondering about all this nanny interlocking. I guess it's
because a car charging the cable is most likely will be left
coonected all the time and just dumped on the floor in all weathers.
People are lazy, coiling up to store neatly or put in the car just
ain't going to happen, particulary in the wet and when they'll only
be uncoiling it a few hours later on their return. A caravan power
cable will travel with the van.

Can't see why the car has to talk to the supply point. Easy enough to
have a "no load" switch that isolates the cable under no load
conditions and a button to set it when the cable is connected. Car
needs to know how much opwer is available? If power is on this pin -
x kW, that pin - y kW both pins z kW. Simples. No need to have some
electronics always on consuming power...

--
Cheers
Dave.



  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,080
Default Using a 16A Schuko socket

On 27/01/2020 21:39, Dave Liquorice wrote:
On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote:

You need a safety interlock to ensure that the cable only goes

live
once it is plugged-in to the car.


That's interesting as they don't have such safety devices on caravan
sites.


Yeah, I was wondering about all this nanny interlocking. I guess it's
because a car charging the cable is most likely will be left
coonected all the time and just dumped on the floor in all weathers.
People are lazy, coiling up to store neatly or put in the car just
ain't going to happen, particulary in the wet and when they'll only
be uncoiling it a few hours later on their return. A caravan power
cable will travel with the van.


When used with a motorhome, it could be unplugged and left in a puddle
or on wet grass, in the rain, each day.

Can't see why the car has to talk to the supply point. Easy enough to
have a "no load" switch that isolates the cable under no load
conditions and a button to set it when the cable is connected. Car
needs to know how much opwer is available? If power is on this pin -
x kW, that pin - y kW both pins z kW. Simples. No need to have some
electronics always on consuming power...


Yes, nice and simple.

SteveW


  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Using a 16A Schuko socket

Dave Liquorice wrote:

bert wrote:

they don't have such safety devices on caravan sites.


Not many caravans can take 43kW

Can't see why the car has to talk to the supply point


AFAIK there's not much signalling from car-EVSE just a resistor divider
to let the car say it's connected and ready, or it's charging, or
there's an error. Also a diode so the EVSE can't be fooled by a short on
the signalling pin.

Signalling from EVSE-car is a 1kHz tone, where the duty ratio says how
many amps it's able to provide.


  #31   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Using a 16A Schuko socket


On 27/01/2020 21:39, Dave Liquorice wrote:
On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote:

You need a safety interlock to ensure that the cable only goes

live
once it is plugged-in to the car.


That's interesting as they don't have such safety devices on caravan
sites.


Yeah, I was wondering about all this nanny interlocking.

Pretty sure the IET regs have a prohibition on unshuttered sockets in a
domestic setting.

Commando with an interlocked isolator would technically be a departure
but at least trivial to justify.

That's my understanding anyway - could be wrong and welcome correction.
  #32   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Using a 16A Schuko socket

In article ,
Grumps wrote:
On 27/01/2020 14:34, Dave Plowman (News) wrote:
In article ,
Grumps wrote:
Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?


In terms of regs, no. (IMHO) In practice likely OK.

But would it really be that much more difficult to run a proper radial
from your CU?


Which bit if the regs says you can't have a Schuko?
What do you mean by a "proper radial"?


Ah - sorry, brain fart. Read it as if you were going to spur it off a ring.

--
*Why do they put Braille on the drive-through bank machines?

Dave Plowman London SW
To e-mail, change noise into sound.
  #33   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Using a 16A Schuko socket

On 27/01/2020 19:18, wrote:
On 27/01/2020 16:58, ARW wrote:
On 27/01/2020 15:19,
wrote:

You need a safety interlock to ensure that the cable only goes live
once it is plugged-in to the car. Charge points contain a protocol
controller to handle comms with the car and to enable a contactor
once safe so to do, they also have an RCD. Finally, they're supposed
to be TT'd to ensure that supply and car ground potentials are similar.


More specifically they have a type A RCD.

TT is not always a requirement. However when it is you often have to
TT more than the car charger.


I don't see how that lines-up with 722.411.4, which says (paraphrasing)
that a PME earth SHALL not be used for an outdoor vehicle charging
point, with a few exceptions that would not normally apply.


It's a while since I did the installation course and I have only fitted
one charging point since I went on it.

Actually the NICEIC bloke said to treat both TNS and TNC-S as the same
thing as the UK's electrical infrastructure is ****.

I believe that you are correct and "most if not all" of PME outdoor
installs required a TT installation. The big problem was that you also
had to TT any other circuits that you might be able to touch whilst
touching the car. You were then given a picture of a bloke with long
arms that could touch his car and then his outside lights, electric
gates or outside socket (not all at the same time he did not have 3 arms).

If I can find the installation book I'll quite happily scan it for you
and then the next time I have to install a car charging point (Christ
knows when) or the subject appears on the newsgroup you can look the
info up for me and send me the details whilst I am down the pub having a
pint:-)

Seriously, I will have to read that installation book again and if you
do want a copy I'll do one for you when I have time.

--
Adam
  #34   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,080
Default Using a 16A Schuko socket

On 28/01/2020 17:43, ARW wrote:
On 27/01/2020 19:18, wrote:
On 27/01/2020 16:58, ARW wrote:
On 27/01/2020 15:19,
wrote:

You need a safety interlock to ensure that the cable only goes live
once it is plugged-in to the car. Charge points contain a protocol
controller to handle comms with the car and to enable a contactor
once safe so to do, they also have an RCD. Finally, they're supposed
to be TT'd to ensure that supply and car ground potentials are similar.

More specifically they have a type A RCD.

TT is not always a requirement. However when it is you often have to
TT more than the car charger.


I don't see how that lines-up with 722.411.4, which says
(paraphrasing) that a PME earth SHALL not be used for an outdoor
vehicle charging point, with a few exceptions that would not normally
apply.


It's a while since I did the installation course and I have only fitted
one charging point since I went on it.

Actually the NICEIC bloke said to treat both TNS and TNC-S as the same
thing as the UK's electrical infrastructure is ****.

I believe that you are correct and "most if not all" of PME outdoor
installs required a TT installation. The big problem was that you also
had to TT any other circuits that you might be able to touch whilst
touching the car. You were then given a picture of a bloke with long
arms that could touch his car and then his outside lights


Use a double insulated light?

electric gates


Make the drive and sensors transformer isolated 24V?

or outside socket (not all at the same time he did not have 3 arms).


At least that can be moved to another location that even Mr. Tickle
can't reach

SteveW
  #35   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Using a 16A Schuko socket

On 28/01/2020 08:48, Tim Watts wrote:

On 27/01/2020 21:39, Dave Liquorice wrote:
On Mon, 27 Jan 2020 19:55:27 +0000, bert wrote:

You need a safety interlock to ensure that the cable only goes

live
once it is plugged-in to the car.

That's interesting as they don't have such safety devices on caravan
sites.


Yeah, I was wondering about all this nanny interlocking.


Pretty sure the IET regs have a prohibition on unshuttered sockets in a
domestic setting.


They do, although you can get shuttered Schuko style sockets.

Commando with an interlocked isolator would technically be a departure
but at least trivial to justify.


There is a commando where the isolation is included in the socket - such
that you can't energise it until the plug is in.

(quite pricey though)



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #36   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Using a 16A Schuko socket

On 27/01/2020 18:30, Andy Burns wrote:
Grumps wrote:

Is it OK, in terms of building regs etc, to have a Schuko 16A socket
on a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.


The schuko straight off the CU, by itself wouldn't give you proper
earthing for an EV.


In a garage, its arguable you could skip making it TT. The charge lead
will often include the type A RCD.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #37   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Using a 16A Schuko socket

On 27/01/2020 21:08, Andy Burns wrote:
Tim+ wrote:

Andy Burns wrote:

Mike's Electric Stuff has probably done better EVSE teardowns than Clive
in this instance


But at least I offered a link... ;-)


The most recent three videos on his teardowns playlist

https://www.youtube.com/watch?v=O58KT117crs&list=PL0KZLmPyL6AnVxyvFZRKGsIf cpQlHx0xH


And the 8 bit guy did quite a good summary of all the various variations
of charge connector and charging options in use :

https://www.youtube.com/watch?v=TcoLCTkM0ys

(although with a US centric perspective)


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #38   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Using a 16A Schuko socket

On 27/01/2020 21:12, Grumps wrote:
On 27/01/2020 20:21, Tim+ wrote:
Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


Unless you use a different charging cable youll still be limited to 10
amps. Big Clive did a teardown of one recently explaining a bit about how
they work.

https://youtu.be/DAij_wWeZiY

Tim


Yeah, I have my eye on a different charging cable which will do up to 16A.
Thanks for the link.


Would it not make more sense to hard wire in a proper 32A style charger?


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #39   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 45
Default Using a 16A Schuko socket

On Monday, 27 January 2020 13:56:27 UTC, Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.


Not sure if this is 100% relevant but may be of interest - David Savery doing a Tesla chrging point install: https://youtu.be/qQ4OSUusPOk
  #40   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 99
Default Using a 16A Schuko socket

On 29/01/2020 01:18, John Rumm wrote:
On 27/01/2020 21:12, Grumps wrote:
On 27/01/2020 20:21, Tim+ wrote:
Grumps wrote:
So, I have an EV (Leaf) which would benefit from the ability to charge
using more than a 13Amp socket can supply. The supplied charging
unit/cable limits to about 10A, but the car's on board charger can
accept up to 3.3kW (some say 3.6kW).
This would need a different EVSE than the supplied unit, AND a beefier
mains socket.

Is it OK, in terms of building regs etc, to have a Schuko 16A socket on
a radial from the CU?

I know I can get a proper home charge point installed, but that's not
the cheapest option.
TIA.

Unless you use a different charging cable youll still be limited to 10
amps. Big Clive did a teardown of one recently explaining a bit about
how
they work.

https://youtu.be/DAij_wWeZiY

Tim


Yeah, I have my eye on a different charging cable which will do up to
16A.
Thanks for the link.


Would it not make more sense to hard wire in a proper 32A style charger?


Yes, but...
The car is a company car and as yet they haven't decided if providing me
with a home charging point is something they want to pay for. Charging
at work is provided - free.
The car only has a 3.3kW on-board charger (excluding the quick charge
option) for connection to 230Vac. The supplied EVSE charge cable is
limited to 10Amps, 2.2-2.4kW.
But if I get a 16Amp EVSE, then that could be considered as an accessory
for the car, and the company would then pay. Only £100-£150. And I don't
mind stumping up a few pounds for a Schuko in the garage.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Schuko socket (further difficulty) Scott[_17_] UK diy 14 January 12th 19 12:09 AM
Schuko socket Scott[_17_] UK diy 45 November 26th 18 04:16 PM
Using a 16A appliance in a 13A socket? JP Coetzee UK diy 86 September 23rd 17 12:23 PM
schuko 2 pin wiring walkage UK diy 4 January 20th 05 12:17 PM
schuko 2 pin wiring Zikki Malambo UK diy 1 January 19th 05 12:05 PM


All times are GMT +1. The time now is 11:25 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"