Default RCD tripping.

Woke up this morning to find the RCD in the split load CU had tripped.
Turned out to be something on the 1st floor ring. With that MCB off, no
problems. Put it to on, and the RCD tripped again.

Unplugged everything on it. Fine. Slowly re-instate things and haven't
found the problem one(s) yet. I suspect it is a current sensing 4 way
outlet in the spare room which feeds the AC system there.

It's only when you do this sort of thing you realise just how much stuff
you have. ;-)

Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.

--
*Experience is something you don't get until just after you need it.*

Dave Plowman London SW
To e-mail, change noise into sound.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default RCD tripping.

On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.


Any megger / insulation tester and test between (L+N) and E.

15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.

Permitted leakage for PAT:

Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA

https://www.pat-testing-training.net...ge-current.php

Owain
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default RCD tripping.

In article ,
wrote:
On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.


Any megger / insulation tester and test between (L+N) and E.


15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.


Permitted leakage for PAT:


Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA


https://www.pat-testing-training.net...ge-current.php


Owain


Thanks Owain. Did just wonder if there was a device you plugged the
appliance into which then gave a direct read out of leakage current.

--
*I was once a millionaire but my mom gave away my baseball cards

Dave Plowman London SW
To e-mail, change noise into sound.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default RCD tripping.

Brian Gaff (Sofa 2) wrote:

But hang on a moment, many devices have mains filters that as a transient
would fail those tests, as they have capacitors in them which have to
presumably charge and discharge on each cycle of the mains.
Brian


This is best analysed as an AC current (sic) rather than as transients,
and must meet the limits set. Hence filter capacitors to earth have to
have a lower value than capacitors across live and neutral, which latter
don't contribute to earth leakage.

--

Roger Hayter


  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default RCD tripping.

On 23/11/2019 13:37, Dave Plowman (News) wrote:
In article ,
wrote:
On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.


Any megger / insulation tester and test between (L+N) and E.


15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.


Permitted leakage for PAT:


Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA


https://www.pat-testing-training.net...ge-current.php


Owain


Thanks Owain. Did just wonder if there was a device you plugged the
appliance into which then gave a direct read out of leakage current.


You can get high sensitivity clamp meters that will (with the aid of a
short extension lead with the individual insulated wires made
accessible) allow direct measurement of leakage if its directly to the
circuit earth (obviously it won't see leakage via a parallel path to earth)


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default RCD tripping.

In article , Dave Plowman (News)
scribeth thus
In article ,
wrote:
On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.


Any megger / insulation tester and test between (L+N) and E.


15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.


Permitted leakage for PAT:


Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA


https://www.pat-testing-training.net...ge-current.php


Owain


Thanks Owain. Did just wonder if there was a device you plugged the
appliance into which then gave a direct read out of leakage current.


Don't overlook that odd Neutral to Earth leakage short which can cause
quite some fun and games as the load increases in the system!..
--
Tony Sayer


Man is least himself when he talks in his own person.

Give him a keyboard, and he will reveal himself.


  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default RCD tripping.

On Saturday, 23 November 2019 13:37:32 UTC, Dave Plowman (News) wrote:
In article ,
wrote:
On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.


Any megger / insulation tester and test between (L+N) and E.


15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.


Permitted leakage for PAT:


Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA


https://www.pat-testing-training.net...ge-current.php


Owain


Thanks Owain. Did just wonder if there was a device you plugged the
appliance into which then gave a direct read out of leakage current.


PAT tester or megger. Or you can do it at mains voltage with just a meter & protecting resistor. Or use a microwave turntable motor as a 0-1000v supply.

But a multimeter, they pick up a useful percentage of faults.


NT
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
RCD test button not tripping the RCD. Rednadnerb UK diy 4 July 17th 10 01:02 AM
Random RCD tripping N. Thornton UK diy 2 December 23rd 04 03:16 PM
Tripping RCD on main disribution board - Help Requested Steve Reeves UK diy 23 June 6th 04 10:08 AM
Help! RCD Keeps tripping on new wiring Seri UK diy 30 April 9th 04 07:41 PM
Indesit wdg1295w washer/drier tripping RCD on final fast spin spanner UK diy 6 February 6th 04 10:08 AM


All times are GMT +1. The time now is 05:22 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"