In article , Dave Plowman (News)
scribeth thus
In article ,
wrote:
On Saturday, 23 November 2019 11:06:56 UTC, Dave Plowman (News) wrote:
Wondered if there was some form of 'leakage' tester I could buy or make?
To find out the actual fault current in each and every thing which is
plugged in to it? And what is acceptable - as I realise some things will
have some anyway.
Any megger / insulation tester and test between (L+N) and E.
15 mA may trip a 30 mA RCD and that's 16 kOhm at 240 volts.
Permitted leakage for PAT:
Class Type Max Leakage Current
1 IT, Movable, Stationary, & Fixed 3.5mA
1 Heating & Cooking 0.75mA per kW*
2 All Types 0.25mA
* to a maximum of 5mA
https://www.pat-testing-training.net...ge-current.php
Owain
Thanks Owain. Did just wonder if there was a device you plugged the
appliance into which then gave a direct read out of leakage current.
Don't overlook that odd Neutral to Earth leakage short which can cause
quite some fun and games as the load increases in the system!..
--
Tony Sayer
Man is least himself when he talks in his own person.
Give him a keyboard, and he will reveal himself.