Default Baxi 105 HE boiler flame fault, runs for 10s,

The "no flame" neon indicator is flashing (suggests flame failure or
condensate drain blockage).

The condensate drain is not blocked.

If I reset the boiler, and get it to restart, then running a hot water
tap or turning on the central heating starts up the flame and fan.

If there is demand, the flame

* comes on
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds

.... and then the boiler goes back into fault mode.

The repair manual suggests that the PCB could be the issue; in fact I
replaced that a few years ago, but I can't remember whether it was the
same fault.

Any immediate ideas?

Daniele
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,366
Default Baxi 105 HE boiler flame fault, runs for 10s,

D.M. Procida wrote:
The "no flame" neon indicator is flashing (suggests flame failure or
condensate drain blockage).

The condensate drain is not blocked.

If I reset the boiler, and get it to restart, then running a hot water
tap or turning on the central heating starts up the flame and fan.

If there is demand, the flame

* comes on
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds

... and then the boiler goes back into fault mode.

The repair manual suggests that the PCB could be the issue; in fact I
replaced that a few years ago, but I can't remember whether it was the
same fault.

Any immediate ideas?

Daniele


Ignition detection fault? Its possibly going through a cycle of ignition
attempts not detecting that the flame has lit.

If it has flame detecting electrodes, sometimes a clean/tweak of the
electrodes will restore flame detection.

Tim

--
Please don't feed the trolls
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Baxi 105 HE boiler flame fault, runs for 10s,

On 27/10/2019 10:46, Tim+ wrote:
D.M. Procida wrote:
The "no flame" neon indicator is flashing (suggests flame failure or
condensate drain blockage).

The condensate drain is not blocked.

If I reset the boiler, and get it to restart, then running a hot water
tap or turning on the central heating starts up the flame and fan.

If there is demand, the flame

* comes on
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds
* comes back on after about 25 seconds
* cuts out after 10 seconds

... and then the boiler goes back into fault mode.

The repair manual suggests that the PCB could be the issue; in fact I
replaced that a few years ago, but I can't remember whether it was the
same fault.

Any immediate ideas?

Daniele


Ignition detection fault? Its possibly going through a cycle of ignition
attempts not detecting that the flame has lit.

If it has flame detecting electrodes, sometimes a clean/tweak of the
electrodes will restore flame detection.


Make sure the earth connection in its power supply is good as well -
many will use flame rectification for flame sensing, and that needs an
earthed chassis.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 530
Default Baxi 105 HE boiler flame fault, runs for 10s,

D.M. Procida wrote:

The "no flame" neon indicator is flashing (suggests flame failure or
condensate drain blockage).

The condensate drain is not blocked.


However, I seem to have fixed it by removing the condensation tank, and
drying it, particularly near where the sensor wire is connected to it. I
think that it was damp, and sufficient current was leaking to trigger
the fault indication.

Daniele
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flame/fan/flue errors showing on Bax 105 Combination boiler D.M. Procida UK diy 4 January 19th 17 09:36 PM
10S Battery Controller Module help please T i m Electronics Repair 7 March 28th 16 05:19 PM
Baxi System Boiler - flame light flashes after 2 hours of running kmillar UK diy 2 January 30th 07 10:45 AM
Cost of keeping Baxi 105 Instant boiler on overnight Dave Fawthrop UK diy 4 January 22nd 07 09:02 PM
tv21ce4250/10s - accu 1kc Michael A. Terrell Electronics Repair 1 March 26th 05 09:10 PM


All times are GMT +1. The time now is 03:26 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"