UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,970
Default Conduit fixed below joists OK?

Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).

--
Chris Green
·
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,829
Default Conduit fixed below joists OK?

Chris Green wrote:

Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists?


What of the new 18th Ed requirements to fix cables such that they don't
droop down in the event of a fire?

https://www.shop.niceic.com/18edition-news/18th-edition-cable-fixings
  #3   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Conduit fixed below joists OK?

On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all round
band inside the trunking to secure the cable in the event of a fire.



--
Adam
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,019
Default Conduit fixed below joists OK?

On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).

You could just clip the cable straight across the underside, and then
use the metal normally used to protect cables under plaster in protected
zones "over" (or rather under?) it, if you see what I mean?. Also a
little bit mechanically stronger in the event of accidentally swinging a
tool between the joists.
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,970
Default Conduit fixed below joists OK?

ARW wrote:
On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all round
band inside the trunking to secure the cable in the event of a fire.

Trunking, yes. Conduit you have to poke it through don't you.

.... and yes, thanks for the new 18th edition requirement which means
I'll need to put metal clips of some sort round the trunking. Are
clips like this now available or will I have to improvise something?

--
Chris Green
·


  #6   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Conduit fixed below joists OK?

On 26/01/2019 12:55, Chris Green wrote:
ARW wrote:
On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all round
band inside the trunking to secure the cable in the event of a fire.

Trunking, yes. Conduit you have to poke it through don't you.

... and yes, thanks for the new 18th edition requirement which means
I'll need to put metal clips of some sort round the trunking. Are
clips like this now available or will I have to improvise something?


Anything metal will do [1] so use all round band, P clips or google for
"clips for trunking" that will bring up some metal U shaped clips
designed for trunking.

[1] It probably has to be steel. Sodium and mercury etc just do not cut
the mustard:-)
--
Adam
  #7   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Conduit fixed below joists OK?

On 26/01/2019 12:55, Chris Green wrote:
ARW wrote:
On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all round
band inside the trunking to secure the cable in the event of a fire.

Trunking, yes. Conduit you have to poke it through don't you.

... and yes, thanks for the new 18th edition requirement which means
I'll need to put metal clips of some sort round the trunking. Are
clips like this now available or will I have to improvise something?


Inside the trunking!

--
Adam
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default Conduit fixed below joists OK?

On Saturday, 26 January 2019 09:33:05 UTC, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists?
It's to run a couple of 2.5sq mm feeds across the ceiling of a garage


If you use 20mm plastic conduit it will take 2 x 2.5 mm T&E, and you can use metal conduit saddles to satisfy the fire support requirements.

Drawback with conduit is that you have to thread the cables through rather than laying the trunking over them.

Owain
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 355
Default Conduit fixed below joists OK?

On 26/01/2019 10:10, ARW wrote:
On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists?Â* I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed.Â* Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all round
band inside the trunking to secure the cable in the event of a fire.




Last time I looked, there didn't seem to be any aimed specifically at
plastic conduit - I assume one just buys metal conduit clips that's sold
for metal conduit...

--
Email does not work


  #11   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Conduit fixed below joists OK?

On 26/01/2019 14:59, Tim Watts wrote:
On 26/01/2019 10:10, ARW wrote:
On 26/01/2019 09:22, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists?Â* I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed.Â* Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


Trunking not conduit if it has a clip on cover?

Either is fine but you should put some metal clips/p clips or all
round band inside the trunking to secure the cable in the event of a
fire.




Â*Last time I looked, there didn't seem to be any aimed specifically at
plastic conduit - I assume one just buys metal conduit clips that's sold
for metal conduit...


Yep.

--
Adam
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,970
Default Conduit fixed below joists OK?

Brian Gaff wrote:
Is there a car in said garage, and what height is it?
Brian

It's a 3 car (wide) garage, there's a motorbike in slot 1, a car in
slot 2 and a mower in slot 3. The roof joists are quite high, 2.5
metres or so I would guess.

--
Chris Green
·
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 12,364
Default Conduit fixed below joists OK?

On Saturday, 26 January 2019 09:33:05 UTC, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).


You could, but it makes more sense to clip the cable to the sides of the joists without trunking.


NT
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,970
Default Conduit fixed below joists OK?

newshound wrote:
On 28/01/2019 16:34, Robin wrote:
On 28/01/2019 16:03, newshound wrote:
On 27/01/2019 11:16, Chris Green wrote:
wrote:
On Saturday, 26 January 2019 09:33:05 UTC, Chris GreenÂ* wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists?Â* I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed.Â* Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).

You could, but it makes more sense to clip the cable to the sides of
the joists without trunking.

The run is *across* the joists, not in the same direction as the
joists run.

Any particular reason not to run it naked through 12 mm holes?


300mm max cable support spacing[1]?Â* I wouldn't claim to comply always
and everywhere but it'd be a bit obvious in a garage roof.

[1] for 10 to 15mm diameter

Fair point, although I don't see much "electrical" risk. I still thing
the quickest and easiest way might be to use metal capping as a sort of
mini "cable tray".


I'm probably going to take it outside but, if not, I think cable trays
will be the way to go, much less hassle than clipping or trunking I
think - and looks don't matter in the garage.

--
Chris Green
·
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 5,061
Default Conduit fixed below joists OK?

In article ,
newshound wrote:
On 28/01/2019 16:34, Robin wrote:
On 28/01/2019 16:03, newshound wrote:
On 27/01/2019 11:16, Chris Green wrote:
wrote:
On Saturday, 26 January 2019 09:33:05 UTC, Chris Green wrote:
Is it acceptaple to run cables in (probably standard plastic clip on
cover) conduit fixed to the underside of exposed joists? I can't see
any reason why it shouldn't be OK but want to check.

It's to run a couple of 2.5sq mm feeds across the ceiling of a garage
which has a room above it but where the joists are exposed. Going
round the edge at the top of the walls is possible but rather messier
with obstructions and such (and would also use more cable).

You could, but it makes more sense to clip the cable to the sides of
the joists without trunking.

The run is *across* the joists, not in the same direction as the
joists run.

Any particular reason not to run it naked through 12 mm holes?


300mm max cable support spacing[1]? I wouldn't claim to comply always
and everywhere but it'd be a bit obvious in a garage roof.

[1] for 10 to 15mm diameter

Fair point, although I don't see much "electrical" risk. I still thing
the quickest and easiest way might be to use metal capping as a sort of
mini "cable tray".


cable support is not to deal electrical problems but with the blocking of
an escape route by drooping, burning cables. I understood, from a
presentation on the new REgs, that a firefighter lost his life having been
trapped.

--
from KT24 in Surrey, England
"I'd rather die of exhaustion than die of boredom" Thomas Carlyle
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
dumb question - what's the purpose of electrical conduit below theplaster? tonyjeffs[_2_] UK diy 23 October 8th 08 08:52 PM
Blocked Conduit - Need to See in 3/4" Conduit - Fibre optic Camera? Scott Townsend Home Repair 15 October 15th 06 06:35 PM
100% financing for scores below 600, 90% for below 550 LoanOfficer39 Home Ownership 0 October 7th 06 05:47 AM
What are the led strips below window sill? Rich UK diy 2 August 6th 03 08:54 PM
Stationary planers - fixed head or fixed table? Steve Turner Woodworking 5 July 12th 03 02:15 AM


All times are GMT +1. The time now is 01:06 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"