On 10/02/2014 17:14, Tim Watts wrote:
On Monday 10 February 2014 16:17 Harry Bloomfield wrote in uk.d-i-y: Phil L explained : paulfoel wrote: Currently got wiring in the attic that runs a light. Originally just a pull switch and bulb/holder but I've replaced with strip light. However, what I want to do now is have plug socket up there. Is it acceptable to run this wire into a double plug socket. (Then I can put plug on end of wiring for light also and just plug this is leaving me with one space socket). Or leave well alone because its a light circuit? It'll be on the lighting circuit. Meaning that if you turn all the sockets off at the CU, this socket will still be live. It also means that if whatever you have plugged into it trips, the whole lighting circuit will trip. Whether this is 'acceptable' is up to you and no one can stop you, but it's not really advisable....if it's only going to be used for occasional use, it's probably easier just to run an extension reel up there when required. I agree, you have to consider that someone may come along and assume it is safe to plug a 3Kw heater in there. Much safer would be to run a spur off the upstairs ring, to a twin 13 amp socket, then use one outlet for the light, via a suitably small fuse in the plug, leaving you one outlet for your angle grinder, wander light, or what ever. There is almost always an easy cable route from the 1st floor floor-level, upto the loft space - airing cupboard etc.. If you then somehow manage to trip that, you will still have some working light on the floor below. well, in the worst case, it will take out the protective device (fuse) - which will be annoying, but not actually dangerous... A 5A fuse in a spur probably won't blow before the 6A breaker in the CU anyway so its not actually going to improve protection. It may make the circuit easier to understand. |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
dennis@home wrote:
A 5A fuse in a spur probably won't blow before the 6A breaker in the CU anyway so its not actually going to improve protection. Thank you. -- Adam |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Mon, 10 Feb 2014 19:27:09 +0000, "dennis@home"
wrote: On 10/02/2014 17:14, Tim Watts wrote: On Monday 10 February 2014 16:17 Harry Bloomfield wrote in uk.d-i-y: Phil L explained : paulfoel wrote: Currently got wiring in the attic that runs a light. Originally just a pull switch and bulb/holder but I've replaced with strip light. However, what I want to do now is have plug socket up there. Is it acceptable to run this wire into a double plug socket. (Then I can put plug on end of wiring for light also and just plug this is leaving me with one space socket). Or leave well alone because its a light circuit? It'll be on the lighting circuit. Meaning that if you turn all the sockets off at the CU, this socket will still be live. It also means that if whatever you have plugged into it trips, the whole lighting circuit will trip. Whether this is 'acceptable' is up to you and no one can stop you, but it's not really advisable....if it's only going to be used for occasional use, it's probably easier just to run an extension reel up there when required. I agree, you have to consider that someone may come along and assume it is safe to plug a 3Kw heater in there. Much safer would be to run a spur off the upstairs ring, to a twin 13 amp socket, then use one outlet for the light, via a suitably small fuse in the plug, leaving you one outlet for your angle grinder, wander light, or what ever. There is almost always an easy cable route from the 1st floor floor-level, upto the loft space - airing cupboard etc.. If you then somehow manage to trip that, you will still have some working light on the floor below. well, in the worst case, it will take out the protective device (fuse) - which will be annoying, but not actually dangerous... A 5A fuse in a spur probably won't blow before the 6A breaker in the CU anyway so its not actually going to improve protection. It may make the circuit easier to understand. Electrically speaking, you can wire a 13A socket straight off the lighting wiring without compromising safety, provided the lighting circuit remains fused at its 6 amp maximum limit. If you're fitting a 13A socket in the loft or attic, it's usually for the purposes of providing power to something like a masthead amp or TV aerial distribution amp both of which would be more than amply served by a half amp fuse[1] which minimises the risk of a house fire should a fault develop on the (now fused) 13A socket spur. Of course, there still remains the risk of a fire from a fault in the amplifier kit itself but, provided it has been designed to the mandatory safety requirements for such 'domestic appliances' this aught to eliminate such risk. The only problem is that, unlike a radio or hairdrier, it is operating 'out of sight' of any human supervision. I'd be inclined to mount such devices on a metal shelf with heat resistant deflectors (steel sheeting) to stop any flamage from reaching any flamable construction materials and, for good measure, install a loud smoke detector above, but to one side of said kit, ideally with a repeater just outside of the loft hatchway or attic doorway. In my case, that last bit of paranoia has remained merely an idle inclination to this day (although I might try the smoke alarm idea). [1] If you needed to provide power for powertools, you'd just plug in a suitable mains lead extension into one of your regular 13A sockets unless you were planning on turning your attic into a workshop (in which case we wouldn't be discussing the use of a lighting circuit feed for a 13A socket now, would we?). Fitting a 13A fused box in the spur feed to the 13A socket allows you to fit a half or 1 amp fuse which will be more than ample for the socket's intended purpose yet reduce the risk of a fault on the spur from blacking out that lighting circuit. It's just a matter of "Good Practice" and common sense to splash out on such a 'luxury item'. The same applies to fusing up 30A ring main circuits with lower rated fuses when appropriate. My top floor ring main currently has a 15A fuse link fitted because the only loads are my son's "HiFi" and widescreen TV and computer stuff with no 2kW electric fan heaters in sight. The 15A fuse link has never blown in the past 7 or 8 years since I downgraded the circuit to a "15A Ring Main". The risk of a fire in the ring main circuit, though slight enough to be deemed acceptable according to the regulations is now somewhat safer again. I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. -- Regards, J B Good |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Tuesday, February 11, 2014 8:32:39 PM UTC, Johny B Good wrote:
If you're fitting a 13A socket in the loft or attic, it's usually for the purposes of providing power to something like a masthead amp or TV aerial distribution amp both of which would be more than amply served by a half amp fuse[1] which minimises the risk of a house fire should a fault develop on the (now fused) 13A socket spur. 2A and below suffer much more frequent failure, I expect one of the reasons for the choice of 3A fuses in the 40s. Of course, there still remains the risk of a fire from a fault in the amplifier kit itself but, provided it has been designed to the mandatory safety requirements for such 'domestic appliances' this aught to eliminate such risk. no ![]() The only problem is that, unlike a radio or hairdrier, it is operating 'out of sight' of any human supervision. I'd be inclined to mount such devices on a metal shelf with heat resistant deflectors (steel sheeting) to stop any flamage from reaching any flamable construction materials and, for good measure, install a loud smoke detector above, but to one side of said kit, ideally with a repeater just outside of the loft hatchway or attic doorway. Biscuit tins are relatively easy to apply. Snip & bend back the 3 tabs for each hole. They restrict airflow, so a signifcant fire size cant happen. Things can get hot, but fire heat wont add to it significantly. [1] If you needed to provide power for powertools, you'd just plug in a suitable mains lead extension into one of your regular 13A sockets unless you were planning on turning your attic into a workshop (in which case we wouldn't be discussing the use of a lighting circuit feed for a 13A socket now, would we?). I've seen whole flats here running on a 5A feed. A pain, but workable. In eastern europe its standard practice to have an 8A feed to flats. NT |
#5
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]() |
#6
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thursday, February 13, 2014 4:03:39 PM UTC, Adam Funk wrote:
On 2014-02-11, wrote: On Tuesday, February 11, 2014 8:32:39 PM UTC, Johny B Good wrote: If you're fitting a 13A socket in the loft or attic, it's usually for the purposes of providing power to something like a masthead amp or TV aerial distribution amp both of which would be more than amply served by a half amp fuse[1] which minimises the risk of a house fire should a fault develop on the (now fused) 13A socket spur. 2A and below suffer much more frequent failure, I expect one of the reasons for the choice of 3A fuses in the 40s. Has fuse manufacturing not improved in the past 70 years? AFAIK fuse wire is still the same material (tinned copper) it was 100 years ago. Its drawn differently, but afaik the result is the same. 3/13A cartridges have only changed in very minor details since their design in the 40s. BICBW. NT |
#7
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In message , Johny B Good
writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... -- Chris French |
#8
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Thu, 13 Feb 2014 15:02:32 +0000, chris French
wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. The practice of miswiring fuses with the wrong fuse wire seems to be one only followed by those aiming to earn a "Darwin Award". The fuse carriers are clearly marked with their fuse rating amperage and the fusewire card clearly identifies each wrap of fusewire and it's not exactly 'Rocket Science' to figure how to rewire a Wylex fuse carrier. The fact that Niglon cards of replacement fusewire were readily available from almost any hardware store or chandlers does suggest that this was a job that was deemed to be within the competence of the typical literate householder of the day. -- Regards, J B Good |
#9
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article , Johny B Good
scribeth thus On Thu, 13 Feb 2014 15:02:32 +0000, chris French wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. The practice of miswiring fuses with the wrong fuse wire seems to be one only followed by those aiming to earn a "Darwin Award". The fuse carriers are clearly marked with their fuse rating amperage and the fusewire card clearly identifies each wrap of fusewire and it's not exactly 'Rocket Science' to figure how to rewire a Wylex fuse carrier. The fact that Niglon cards of replacement fusewire were readily available from almost any hardware store or chandlers does suggest that this was a job that was deemed to be within the competence of the typical literate householder of the day. Theres people I know who'd have to get a man in to "change a damm light bulb";!... -- Tony Sayer |
#10
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article ,
tony sayer wrote: In article , Johny B Good scribeth thus On Thu, 13 Feb 2014 15:02:32 +0000, chris French wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. The practice of miswiring fuses with the wrong fuse wire seems to be one only followed by those aiming to earn a "Darwin Award". The fuse carriers are clearly marked with their fuse rating amperage and the fusewire card clearly identifies each wrap of fusewire and it's not exactly 'Rocket Science' to figure how to rewire a Wylex fuse carrier. The fact that Niglon cards of replacement fusewire were readily available from almost any hardware store or chandlers does suggest that this was a job that was deemed to be within the competence of the typical literate householder of the day. Theres people I know who'd have to get a man in to "change a damm light bulb";!... A friend had a local handyman in to hang her Christmas lights since her husband was still recovering from a hip operation. -- From KT24 Using a RISC OS computer running v5.18 |
#11
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article ,
Johny B Good wrote: On Thu, 13 Feb 2014 15:02:32 +0000, chris French wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. what's wrong with a 6" nail? -- From KT24 Using a RISC OS computer running v5.18 |
#12
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In message , charles
writes In article , Johny B Good wrote: On Thu, 13 Feb 2014 15:02:32 +0000, chris French wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. what's wrong with a 6" nail? Back in the good old days a brass volume control shaft was a good replacement for any value of fuse in a 13A plug. Never seen one blow. -- Bill |
#13
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article ,
Bill wrote: In message , charles writes In article , Johny B Good wrote: On Thu, 13 Feb 2014 15:02:32 +0000, chris French wrote: In message , Johny B Good writes I like the principle that you can replace a large fuse link in an existing fuse carrier with smaller rated fuse links (Wylex CU) since it makes it very simple to downgrade the ciruit capacity on an as needed basis without compromising safety (in this case, boosting safety), since it's a trivial exercise to refit the original larger fuse should the smaller one blow due to unanticipated overload. Of course the opposite is also easy.... If you mean fitting a larger fuse carrier in place of the smaller fuse carrier (e.g. fitting a 15A fuse carrier into a 5A fuse bridge) it's actually impossible without the assistance of a "Birmingham Screwdriver". Perhaps I'm a little out of the ordinary in keeping a set of correctly wired fuse carriers spare to facilitate fuse replacement. Perhaps I'm also a little unusual in only re-wiring a blown fuse with the correct fusewire. what's wrong with a 6" nail? Back in the good old days a brass volume control shaft was a good replacement for any value of fuse in a 13A plug. Never seen one blow. knew them well. -- From KT24 Using a RISC OS computer running v5.18 |