I believe someone was recently talking about voltage spikes, though I
can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM |
#2
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On 08/03/2011 09:09, MM wrote:
I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM Voltage in the UK was harmonised with Europe on 1st January 1995 and is supposed to be 230V +10%-6% (216.2–253 V). So, your fluctuations are within tolerance. Most equipment is designed to work at 110v - 220v (at 50 or 60Hz) look at the rating plate. That voltage is nominal and will not include the tolerance. Cheers Peter |
#3
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 08 Mar 2011 09:09:02 +0000, MM wrote:
I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. So only 3v change, depending on the quality of you supply you may well get a bigger fluctuantion when you drop a decent load on, say 5kW or more. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. They aren't spikes just norm fluctuation caused by local load variations, either in your imdeiate vicinty or in your home. The nominal UK voltage hasn't been 240v for years. See other post. Note that the "harmonised" range covers the old 240v spec so nothing had to change. The only comment I'd make about the voltage sitting at 250 odd is that incandescent light bulbs will have a much shorter life. We used to get through 40W candles in the living room (6 in use 18hrs/day) at about one per month and other odd 60W bulbs at several a year. Bought a UPS plugged it in and it went straight into "voltage trim" mode I thought it was faulty! Measured the volts up at 250 or so, reported it, men arrived in a couple of hours confirmed the reading and came back a day or two later to adjust the tapping on our transformer. Voltage now sits between 235 and 245 (was 245 to 255) and incandescent light bulbs last "forever". The post about voltage variation was probably mine from the 3rd March wondering if the grid had had a problem as our volts had risen to 253 for quite long periods overnight 2nd/3rd. Since then things have been with the normal 235 to 245 range. -- Cheers Dave. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In message , puffernutter
writes On 08/03/2011 09:09, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM Voltage in the UK was harmonised with Europe on 1st January 1995 and is supposed to be 230V +10%-6% (216.2€“253 V). So, your fluctuations are within tolerance. Most equipment is designed to work at 110v - 220v (at 50 or 60Hz) look at the rating plate. That voltage is nominal and will not include the tolerance. Some time before Christmas, I inherited from a deceased works colleague a purpose-built home-made meter for measuring the mains voltage (a 4" moving-coil meter + rectifier). After testing it and tweaking it slightly so that it read correctly at 230V, I left it plugged in, sitting on the desk, so that I could instantly see how the mains was doing. I have seen some considerable variations. Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. After the New Year, have noticed that the typical 'normal' seems to be 235V (even when it was still very cold), and I occasionally see as high as 245V. [Presumably someone decided to change the output tap at the substation.] However, a couple of nights ago, I noticed that, every 30 seconds or so, the lights were very obviously suddenly going alternately dim and bright. The mains was abruptly jumping between 230 and 220V, and I was rather concerned that this might indicate that a power cut was about to happen. However, an hour later, things settled down, and the mains was a steady 235V again. -- Ian |
#5
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 08 Mar 2011 10:08:39 +0000 (GMT), "Dave Liquorice"
wrote: The post about voltage variation was probably mine from the 3rd March wondering if the grid had had a problem as our volts had risen to 253 for quite long periods overnight 2nd/3rd. Since then things have been with the normal 235 to 245 range. Last time I looked (ten minutes ago) the read-out was reading 248v. MM |
#6
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Mar 8, 9:09*am, MM wrote:
I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM A voltage spike is 100s of volts big, and lasts for milliseconds. 240v is the target voltage, real voltage can be 10s of volts away from this. 1v variation isn't an issue. NT |
#7
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 10:27:33 +0000, Ian Jackson
wrote: Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. I don't measure the mains voltage but I do notice fluctuations. All the lights dim noticably in the house for a short time. It happens fairly frequently in the early evening. It does not appear to cause any problems to computers etc. -- (\__/) M. (='.'=) Due to the amount of spam posted via googlegroups and (")_(") their inaction to the problem. I am blocking some articles posted from there. If you wish your postings to be seen by everyone you will need use a different method of posting. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
|
#9
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
Tabby wrote:
On Mar 8, 9:09 am, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM A voltage spike is 100s of volts big, and lasts for milliseconds. 240v is the target voltage, real voltage can be 10s of volts away from this. 1v variation isn't an issue. I'll second that and just add that unless all the supply cables are superconductors then the voltage will vary according to the load in both MMs house and neighbouring houses. MM - It is not unusual for the voltage to drop by as much as 8 volts in a house when an electric shower is switched on depending upon the external resistance of the supply to the house. -- Adam |
#10
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 17:42:09 -0000, "ARWadsworth"
wrote: Tabby wrote: On Mar 8, 9:09 am, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM A voltage spike is 100s of volts big, and lasts for milliseconds. 240v is the target voltage, real voltage can be 10s of volts away from this. 1v variation isn't an issue. I'll second that and just add that unless all the supply cables are superconductors then the voltage will vary according to the load in both MMs house and neighbouring houses. MM - It is not unusual for the voltage to drop by as much as 8 volts in a house when an electric shower is switched on depending upon the external resistance of the supply to the house. When I first observed the 250v this morning there was only the PC on. MM |
#11
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
MM wrote:
On Tue, 8 Mar 2011 17:42:09 -0000, "ARWadsworth" wrote: Tabby wrote: On Mar 8, 9:09 am, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM A voltage spike is 100s of volts big, and lasts for milliseconds. 240v is the target voltage, real voltage can be 10s of volts away from this. 1v variation isn't an issue. I'll second that and just add that unless all the supply cables are superconductors then the voltage will vary according to the load in both MMs house and neighbouring houses. MM - It is not unusual for the voltage to drop by as much as 8 volts in a house when an electric shower is switched on depending upon the external resistance of the supply to the house. When I first observed the 250v this morning there was only the PC on. And did you go and ask all the neighbours what they were using? -- Adam |
#12
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Mar 8, 10:27*am, Ian Jackson
wrote: In message , puffernutter writes On 08/03/2011 09:09, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM Voltage in the UK was harmonised with Europe on 1st January 1995 and is supposed to be 230V +10%-6% (216.2–253 V). So, your fluctuations are within tolerance. *Most equipment is designed to work at 110v - 220v (at 50 or 60Hz) look at the rating plate. *That voltage is nominal and will not include the tolerance. Some time before Christmas, I inherited from a deceased works colleague a purpose-built home-made meter for measuring the mains voltage (a 4" moving-coil meter + rectifier). After testing it and tweaking it slightly so that it read correctly at 230V, I left it plugged in, sitting on the desk, so that I could instantly see how the mains was doing. I have seen some considerable variations. Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. After the New Year, have noticed that the typical 'normal' seems to be 235V (even when it was still very cold), and I occasionally see as high as 245V. [Presumably someone decided to change the output tap at the substation.] However, a couple of nights ago, I noticed that, every 30 seconds or so, the lights were very obviously suddenly going alternately dim and bright. The mains was abruptly jumping between 230 and 220V, and I was rather concerned that this might indicate that a power cut was about to happen. However, an hour later, things settled down, and the mains was a steady 235V again. -- Ian but did the frequency go down with the volts? I have a far eastern LED Lloytron clock that seems to sync to the mains. If the frequency goes down the clock runs slow. rusty |
#13
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In message
, therustyone writes On Mar 8, 10:27Â*am, Ian Jackson wrote: In message , puffernutter writes On 08/03/2011 09:09, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM Voltage in the UK was harmonised with Europe on 1st January 1995 and is supposed to be 230V +10%-6% (216.2€“253 V). So, your fluctuations are within tolerance. Â*Most equipment is designed to work at 110v - 220v (at 50 or 60Hz) look at the rating plate. Â*That voltage is nominal and will not include the tolerance. Some time before Christmas, I inherited from a deceased works colleague a purpose-built home-made meter for measuring the mains voltage (a 4" moving-coil meter + rectifier). After testing it and tweaking it slightly so that it read correctly at 230V, I left it plugged in, sitting on the desk, so that I could instantly see how the mains was doing. I have seen some considerable variations. Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. After the New Year, have noticed that the typical 'normal' seems to be 235V (even when it was still very cold), and I occasionally see as high as 245V. [Presumably someone decided to change the output tap at the substation.] However, a couple of nights ago, I noticed that, every 30 seconds or so, the lights were very obviously suddenly going alternately dim and bright. The mains was abruptly jumping between 230 and 220V, and I was rather concerned that this might indicate that a power cut was about to happen. However, an hour later, things settled down, and the mains was a steady 235V again. -- Ian but did the frequency go down with the volts? I have a far eastern LED Lloytron clock that seems to sync to the mains. If the frequency goes down the clock runs slow. No. I haven't been monitoring the mains frequency. I've only been keeping an eye on the volts (simply because I acquired the meter, which sits permanently plugged in, on a corner of the desk). I was surprised to see how low the voltage sometimes went (right down to the minimum limit). When it was really cold over Christmas and New Year, I expect the guys at the power stations were shovelling coal for all they were worth, and that the frequency (which is of less interest than the voltage) was well down on normal. Obviously, any type of clock which uses the mains frequency will run fast or slow if the frequency varies. My understanding is that the generating people are supposed make sure that, come hell or high water, during a 24 hour period the correct number of cycles are delivered, so that the clocks are correct at 8am. I'm not sure that they always achieve this! -- Ian |
#14
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 20:34:49 +0000, Ian Jackson wrote:
I was surprised to see how low the voltage sometimes went (right down to the minimum limit). When it was really cold over Christmas and New Year, I expect the guys at the power stations were shovelling coal for all they were worth, and that the frequency (which is of less interest than the voltage) was well down on normal. The frequency is very important, it's maintained at 50Hz +/- 1% ie 49.5 to 50.5 Hz nut National Grid work to an operational limit of +/- 0.4% (+/- 0.2Hz). Obviously, any type of clock which uses the mains frequency will run fast or slow if the frequency varies. My understanding is that the generating people are supposed make sure that, come hell or high water, during a 24 hour period the correct number of cycles are delivered, so that the clocks are correct at 8am. I'm not sure that they always achieve this! Oh they do! Questions get asked in the house if they don't. IIRC the last time they had to announce that mains driven clocks had the wrong time and would need to be corrected was during the winter of 1947... -- Cheers Dave. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 08 Mar 2011 21:26:01 +0000 (GMT), "Dave Liquorice"
wrote: On Tue, 8 Mar 2011 20:34:49 +0000, Ian Jackson wrote: I was surprised to see how low the voltage sometimes went (right down to the minimum limit). When it was really cold over Christmas and New Year, I expect the guys at the power stations were shovelling coal for all they were worth, and that the frequency (which is of less interest than the voltage) was well down on normal. The frequency is very important, it's maintained at 50Hz +/- 1% ie 49.5 to 50.5 Hz nut National Grid work to an operational limit of +/- 0.4% (+/- 0.2Hz). Obviously, any type of clock which uses the mains frequency will run fast or slow if the frequency varies. My understanding is that the generating people are supposed make sure that, come hell or high water, during a 24 hour period the correct number of cycles are delivered, so that the clocks are correct at 8am. I'm not sure that they always achieve this! Oh they do! Questions get asked in the house if they don't. IIRC the last time they had to announce that mains driven clocks had the wrong time and would need to be corrected was during the winter of 1947... Maybe 20-30 years ago it dropped to minus 4 secs or so on one occasion when there was a split system. It *might* have been October 1987. Not sure if they got the clocks back to zero error at +24hours. During winter on another occasion the frequency dropped to somewhere in the mid to high 47's before a system split and load shedding gave a high frequency in the north and midlands and a low one in the south. It took a hell of a lot of work to get the two systems back in sync, and as a consequence over the next couple of years they changed the synchronising relays associated with a very large number of circuit breakers across the 400kV and 275kV grid such that a second method of automatic closure was possible dependent on slip angle and rate of change of slip angle rather than just the slip angle. These could be primed and left for 15mins so that if the system either side of the breaker met the targets it would automatically close, previously the only method was a 2 minute timer for 'perfect sync' or a manual closure that ran the risk of exploding the breaker into copper and porcelain shrapnel. The long period of split running during this incident gave a clock error such that various bits of the country were out of sync by a second or more. None of this made the papers at the time -- |
#17
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In article o.uk,
says... The frequency is very important, it's maintained at 50Hz +/- 1% ie 49.5 to 50.5 Hz nut National Grid work to an operational limit of +/- 0.4% (+/- 0.2Hz). There's also a close tolerance on the total number of cycles in the day, too. Had a quick fossick for it, but found this instead... http://www.nationalgrid.com/uk/Elect...ncy/Freq60.htm -- Skipweasel - never knowingly understood. |
#18
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 08 Mar 2011 22:14:39 +0000, The Other Mike
wrote: Maybe 20-30 years ago it dropped to minus 4 secs or so on one occasion when there was a split system. It *might* have been October 1987. Not sure if they got the clocks back to zero error at +24hours. During winter on another occasion the frequency dropped to somewhere in the mid to high 47's before a system split and load shedding gave a high frequency in the north and midlands and a low one in the south. It took a hell of a lot of work to get the two systems back in sync, and as a consequence over the next couple of years they changed the synchronising relays associated with a very large number of circuit breakers across the 400kV and 275kV grid such that a second method of automatic closure was possible dependent on slip angle and rate of change of slip angle rather than just the slip angle. These could be primed and left for 15mins so that if the system either side of the breaker met the targets it would automatically close, previously the only method was a 2 minute timer for 'perfect sync' or a manual closure that ran the risk of exploding the breaker into copper and porcelain shrapnel. The long period of split running during this incident gave a clock error such that various bits of the country were out of sync by a second or more. None of this made the papers at the time Crikey, I never realised just what technology is needed to provide a country with an electricity grid! MM |
#19
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 18:16:14 -0000, "ARWadsworth"
wrote: MM wrote: On Tue, 8 Mar 2011 17:42:09 -0000, "ARWadsworth" wrote: Tabby wrote: On Mar 8, 9:09 am, MM wrote: I believe someone was recently talking about voltage spikes, though I can't find the thread in Google Groups to hang this on. I happened to be watching my consumption thingy this morning and noticed that it was constant at 249 volts. Then it went up to 250 for 30 seconds, back down to 249, then back up to 250 again. For a good five minutes it hovered around 249-250. Then it came down to 248, then 247. Aren't these spikes damaging to sensitive equipment? (TVs, DVD Players etc) I don't worry about the PC because I have a UPS on it. The voltage is ~supposed~ to be 240 in the UK. MM A voltage spike is 100s of volts big, and lasts for milliseconds. 240v is the target voltage, real voltage can be 10s of volts away from this. 1v variation isn't an issue. I'll second that and just add that unless all the supply cables are superconductors then the voltage will vary according to the load in both MMs house and neighbouring houses. MM - It is not unusual for the voltage to drop by as much as 8 volts in a house when an electric shower is switched on depending upon the external resistance of the supply to the house. When I first observed the 250v this morning there was only the PC on. And did you go and ask all the neighbours what they were using? Well, no! MM |
#20
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
Dave Liquorice wrote:
Oh they do! Questions get asked in the house if they don't. IIRC the last time they had to announce that mains driven clocks had the wrong time and would need to be corrected was during the winter of 1947... Back in the late 60s, I spent some time at Eggborough power station. There was an interesting clock on the wall of the control room. It clearly had two inputs - one was from the station mains frequency which was driving its second hand (can't remember if there were actually any others) forward, whilst it was driven backwards by the station instrumentation feed, from a pendulum clock which produced pulses ever second (and minute, quarter hour etc for various printing recorders). So the hand moved around the dial, twitching back every second, generally hovered around 12 o'clock, but did move around a little over time. Chris -- Chris J Dixon Nottingham UK Have dancing shoes, will ceilidh. |
#21
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In message , MM
writes On Tue, 08 Mar 2011 22:14:39 +0000, The Other Mike wrote: Maybe 20-30 years ago it dropped to minus 4 secs or so on one occasion when there was a split system. It *might* have been October 1987. Not sure if they got the clocks back to zero error at +24hours. During winter on another occasion the frequency dropped to somewhere in the mid to high 47's before a system split and load shedding gave a high frequency in the north and midlands and a low one in the south. It took a hell of a lot of work to get the two systems back in sync, and as a consequence over the next couple of years they changed the synchronising relays associated with a very large number of circuit breakers across the 400kV and 275kV grid such that a second method of automatic closure was possible dependent on slip angle and rate of change of slip angle rather than just the slip angle. These could be primed and left for 15mins so that if the system either side of the breaker met the targets it would automatically close, previously the only method was a 2 minute timer for 'perfect sync' or a manual closure that ran the risk of exploding the breaker into copper and porcelain shrapnel. The long period of split running during this incident gave a clock error such that various bits of the country were out of sync by a second or more. None of this made the papers at the time Crikey, I never realised just what technology is needed to provide a country with an electricity grid! A long time ago, one of my set lab experiments was to run up fairly large three-phase generator, synchronise it with the mains, get it generating power and do various test measurements. Fortunately, my professional career was more concerned with valves and transistors, and I never needed to do it again! -- Ian |
#22
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
MM wrote:
On Tue, 8 Mar 2011 18:16:14 -0000, "ARWadsworth" wrote: I'll second that and just add that unless all the supply cables are superconductors then the voltage will vary according to the load in both MMs house and neighbouring houses. MM - It is not unusual for the voltage to drop by as much as 8 volts in a house when an electric shower is switched on depending upon the external resistance of the supply to the house. When I first observed the 250v this morning there was only the PC on. And did you go and ask all the neighbours what they were using? Well, no! Well there you are. Short of logging all the neighbours supplies you will never know who turned on or off their electical devices:-) Your electricity supply is normal. Cheers -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 17:18:17 -0000, Skipweasel
wrote: In article , says... I don't measure the mains voltage but I do notice fluctuations. All the lights dim noticably in the house for a short time. It happens fairly frequently in the early evening. It does not appear to cause any problems to computers etc. Nor should it - SMPS should be very tolerant of such things - after all, they're usually considerably over rated in PC applications and only have to up the duty-cycle briefly. I was using this more as an indication of how long the light dimmed for ;-) I am more interested if there is a problem with the supply. -- (\__/) M. (='.'=) Due to the amount of spam posted via googlegroups and (")_(") their inaction to the problem. I am blocking some articles posted from there. If you wish your postings to be seen by everyone you will need use a different method of posting. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Mar 8, 10:27*pm, Skipweasel
wrote: In article o.uk, says... The frequency is very important, it's maintained at 50Hz +/- 1% ie 49.5 to 50.5 Hz nut National Grid work to an operational limit of +/- 0.4% (+/- 0.2Hz). There's also a close tolerance on the total number of cycles in the day, too. Had a quick fossick for it, but found this instead... http://www.nationalgrid.com/uk/Elect...ncy/Freq60.htm Surprised no one has posted this yet http://www.dynamicdemand.co.uk/grid.htm MBQ |
#25
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In message
on Wed, 9 Mar 2011 02:19:24 -0800 (PST) Man at B&Q wrote: On Mar 8, 10:27Â*pm, Skipweasel wrote: In article o.uk, says... The frequency is very important, it's maintained at 50Hz +/- 1% ie 49.5 to 50.5 Hz nut National Grid work to an operational limit of +/- 0.4% (+/- 0.2Hz). There's also a close tolerance on the total number of cycles in the day, too. Had a quick fossick for it, but found this instead... http://www.nationalgrid.com/uk/Elect...ncy/Freq60.htm Surprised no one has posted this yet http://www.dynamicdemand.co.uk/grid.htm This site shows lots of useful info on one page: http://www.bmreports.com/bsp/bsp_home.htm -- Terry |
#26
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On 9 Mar,
Chris J Dixon wrote: Dave Liquorice wrote: Oh they do! Questions get asked in the house if they don't. IIRC the last time they had to announce that mains driven clocks had the wrong time and would need to be corrected was during the winter of 1947... Back in the late 60s, I spent some time at Eggborough power station. There was an interesting clock on the wall of the control room. It clearly had two inputs - one was from the station mains frequency which was driving its second hand (can't remember if there were actually any others) forward, whilst it was driven backwards by the station instrumentation feed, from a pendulum clock which produced pulses ever second (and minute, quarter hour etc for various printing recorders). So the hand moved around the dial, twitching back every second, generally hovered around 12 o'clock, but did move around a little over time. Mains driven clocks are allowed to drift off by so many seconds a day. Before privatisation it was kept very close to zero, but needed to catch up (or even anticipate future slow running) at night. Since then the full range of drift has been more likely to occur. If memory serves (probably not) the legal requirement was about 30 seconds. The clock will have been to show the difference. We had seperate clocks at work which showed the difference. -- B Thumbs Change lycos to yahoo to reply |
#27
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
|
#28
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
In article , MM
writes Crikey, I never realised just what technology is needed to provide a country with an electricity grid! There was an excellent series (of 3 programmes) called the Secret Life of the National Grid shown before Christmas. You may be able to find it with the BBC iPlayer. -- Mike Tomlinson |
#29
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Mar 9, 2:23*pm, Mike Tomlinson wrote:
In article , MM writes Crikey, I never realised just what technology is needed to provide a country with an electricity grid! There was an excellent series (of 3 programmes) called the Secret Life of the National Grid shown before Christmas. *You may be able to find it with the BBC iPlayer. Well, it was a bit lacking in real technical content. MBQ |
#31
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 08 Mar 2011 22:14:39 +0000, The Other Mike
wrote: During winter on another occasion the frequency dropped to somewhere in the mid to high 47's Make that 48's! -- |
#32
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Tue, 8 Mar 2011 10:27:33 +0000, Ian Jackson wrote:
Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. Routine load shedding, it's been happening for decades. 5% then 10% load shed, acheived by a voltage reduction, I'll let you work out the percentage reduction in voltage to get the reduction in load. After that it's rota disconnection as happened in the 1970s. -- The Wanderer Computers are incredibly fast, accurate, and stupid; humans are incredibly slow, inaccurate and brilliant; together they are powerful beyond imagination. |
#33
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
The Wanderer wrote:
On Tue, 8 Mar 2011 10:27:33 +0000, Ian Jackson wrote: Before Christmas, the typical 'normal' voltage was 230V, occasionally going up to 235. However, when the really cold weather started, after around 5pm, the voltage would start to drop and, on several days, regularly fell to 215V. The lowest (checked on a couple of digital meters) was 214.4V. Routine load shedding, it's been happening for decades. 5% then 10% load shed, acheived by a voltage reduction, I'll let you work out the percentage reduction in voltage to get the reduction in load. After that it's rota disconnection as happened in the 1970s. Yep. Think of the grid as a huge generators to which lots of little engines are geared. As demand goes up the voltage and frequency start to fall..the whole contraption is 'climbing a hill' Throttles are opened on all the engines online, and new ones are geared to it to help a bit. Meanwhile the word goes out for anyone who can do without the grid to get off it, and if anyone has any backup power units spare, could they please start them.. If the whole shebang cant make it over the top, then passengers are thrown out till it can. You will get far more familiar with this as more silly wind power is added to the grid. |
#34
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Thu, 10 Mar 2011 11:31:59 +0000, The Natural Philosopher wrote:
You will get far more familiar with this as more silly wind power is added to the grid. I'm not overly keen on this frequency based automatic load shedding (as in switching off) either. Sounds like a recipe for grid instabilty if you ask me. Frequency drops, lots of stuff drops off line, Whe Hey! too much capacity frequency goes up, stuff comes back online, frequency drops... And how much stuff is about that can be switched off for an indeterminate period without warning? Not a lot, storage heaters maybe but they aren't on when there is peak demand and you could only switch 'em off for a limited period otherwise people would be cold(er) the next evening. Some form of dynamic load directly controlled by the grid would work but I'm skeptical about an open loop system. -- Cheers Dave. |
#35
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
Dave Liquorice wrote:
On Thu, 10 Mar 2011 11:31:59 +0000, The Natural Philosopher wrote: You will get far more familiar with this as more silly wind power is added to the grid. I'm not overly keen on this frequency based automatic load shedding (as in switching off) either. Sounds like a recipe for grid instabilty if you ask me. Frequency drops, lots of stuff drops off line, Whe Hey! too much capacity frequency goes up, stuff comes back online, frequency drops... No, that's not a problem really..as there are time delays and hysteresis built in. But the whole thing is pretty silly really as the amount of kit that can be load dumped in this way is probably vanishingly small. And how much stuff is about that can be switched off for an indeterminate period without warning? Exactly. Not a lot, storage heaters maybe but they aren't on when there is peak demand and you could only switch 'em off for a limited period otherwise people would be cold(er) the next evening. Some form of dynamic load directly controlled by the grid would work but I'm skeptical about an open loop system. Actually it isn't open loop, the feedback control is in the frequency. I am very mixed about this, On the one hand its a small effect, and wont save the planet, on the other hand its actually bloody simple and cheap to build into - say a fridge freezer - the intelligence to do it and to move the largest part of that load to off peak times. Probably a far fare better way to modulate demand, would be for people to work 24x7, preferably from home, and spread the 'human activity' part of the load throughout the night as well as the day.. Frankly this is just another bit of 'this will help a teeny bit, but such a teeny bit its barely worth spending money on' like switching off the telly at night, that's been blown up to 'This will save the planet' by the eco-fantasists and the 'green' big business interests. |
#36
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
"Dave Liquorice" wrote in message ll.co.uk... On Thu, 10 Mar 2011 11:31:59 +0000, The Natural Philosopher wrote: You will get far more familiar with this as more silly wind power is added to the grid. I'm not overly keen on this frequency based automatic load shedding (as in switching off) either. Sounds like a recipe for grid instabilty if you ask me. Frequency drops, lots of stuff drops off line, Whe Hey! too much capacity frequency goes up, stuff comes back online, frequency drops... And how much stuff is about that can be switched off for an indeterminate period without warning? I suspect that in the average household, not a lot but I have a friend who works for a water company and they regularly get paid for NOT pumping at certain times. Tim |
#37
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
Tim Downie wrote:
"Dave Liquorice" wrote in message ll.co.uk... On Thu, 10 Mar 2011 11:31:59 +0000, The Natural Philosopher wrote: You will get far more familiar with this as more silly wind power is added to the grid. I'm not overly keen on this frequency based automatic load shedding (as in switching off) either. Sounds like a recipe for grid instabilty if you ask me. Frequency drops, lots of stuff drops off line, Whe Hey! too much capacity frequency goes up, stuff comes back online, frequency drops... And how much stuff is about that can be switched off for an indeterminate period without warning? I suspect that in the average household, not a lot but I have a friend who works for a water company and they regularly get paid for NOT pumping at certain times. He must work at Dinorwig :-) Whilst there are a few industrial processes that are not critical when they use power, by and large electricity is currently (sic!) used BECAUSE it is always there, always on tap, when you need it. "The train at platform five will be leaving when a squall hits the outer Hebrides, and we can suck enough power off the grid to get it going, or when everyone has finished watching Corrie, whichever is the soonest" Tim |
#38
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Thu, 10 Mar 2011 13:38:50 +0000 (GMT), "Dave Liquorice"
wrote: On Thu, 10 Mar 2011 11:31:59 +0000, The Natural Philosopher wrote: You will get far more familiar with this as more silly wind power is added to the grid. I'm not overly keen on this frequency based automatic load shedding (as in switching off) either. Sounds like a recipe for grid instabilty if you ask me. Frequency drops, lots of stuff drops off line, Whe Hey! too much capacity frequency goes up, stuff comes back online, frequency drops... It doesn't work like that. If the frequency drops then the first response is the governors on all the generators on the system. They will always actively control the energy input such that the frequency is maintained at the target of 50Hz. If the frequency still drops then load that is on a disconnection agreement is removed in a controlled manner. This is usually commercial heating / cooling / non critical processes. Then there is voltage reduction in a number of stages to further reduce load that isn't on a disconnection agreement (most domestic load for instance) If the frequency drops further then load gets shed in defined blocks it could be an entire city, or an area , or a particularly large industrial user - that load then stays off, there is no automatic reconnection. If by this stage the frequency is still dropping then the generators automatically disconnect to protect themselves. The grid is then dead. Then sometime later certain contracted for 'black start' sites commence generation. Starting with a diesel generator, to power the fuel pumps etc to run up a gas turbine (kerosine fueled) which then runs the auxiliaries to run the main generation at that particular site (usually coal but could be gas or oil) You might get some hydro running too. Once part of the grid is energised it is interconnected with other generation and load, controlling generation and load such that the frequency and voltage is within limits. Gradually everything is reconnected. What happens at each stage is defined in advance, as are the frequency targets (beyond the published +/- 0.5Hz) and the voltage reductions. Consumers on a disconnection agreement know that they could be disconnected at little or no notice. -- |
#39
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
On Thu, 10 Mar 2011 17:09:04 +0000, The Other Mike wrote:
If the frequency still drops then load that is on a disconnection agreement is removed in a controlled manner. This is usually commercial heating / cooling / non critical processes. Then there is voltage reduction in a number of stages to further reduce load that isn't on a disconnection agreement (most domestic load for instance) Two stages, as I said earlier, 5% and then 10%. Carried out very easily these days with the automated control systems in use. It's worth noting, however, that the load reduction is usually carried out by the Distribution companies through their control rooms. If the frequency drops further then load gets shed in defined blocks it could be an entire city, or an area , or a particularly large industrial user - that load then stays off, there is no automatic reconnection. Unlikely to be a whole city, unless it's an emergency load shed. Normally the rota disconnections are planned on an 11kv feeder by feeder basis, again carried out these days by a simple command from a central control room. I disagree with your comment that there's no automatic reconnection, rota shedding is usually for 3 hour periods. If we're talking emergency load shedding, that usually implies something catastrophic has happened, eith on the generation or transmission systems. I seem to recollect it happened some years ago during summer, when part of the grid was out for maintenance and there was another failure on either a 275 or 400kv cable somewhere around north London meaning effectively that the country was electricaslly split in two. Lasted for several hours if memory serves correctly. Let's also be fair though, for the conditions you mention we are talking an absolute catastrophe. That we don't get therm is why control engineers suffer high blood pressure..... BTDTGTTS. -- The Wanderer I cannot teach anybody anything, I can only make them think. ~Socrates |
#40
Posted to uk.d-i-y
|
|||
|
|||
Voltage spikes
|
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Anti-Perching spikes. | UK diy | |||
Welding on rail road spikes | Metalworking | |||
Gas fire thermostat locking up, spikes? | UK diy | |||
power spikes on second level of the house | Home Repair | |||
Question about loose gutter spikes | Home Ownership |