Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.

Cheers

Martin
--
Martin Carroll
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Cable derating



"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2" plasterboard.



  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default Cable derating

In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2" plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.
--
Martin Carroll
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Cable derating



"Martin Carroll" wrote in message
...
In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2"
plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.


That doesn't satisfy the new regs AFAIK



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default Cable derating

In article , dennis@home
writes


"Martin Carroll" wrote in message
...
In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.

You can't do that unless the cable is protected or you have 2"
plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.


That doesn't satisfy the new regs AFAIK

Why not? AIUI as long as a cable runs in a line horizontally or
vertically to an accessory or within 150mm of top of wall or angle
formed by two walls.

Martin
--
Martin Carroll


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 64
Default Cable derating

Martin Carroll wrote:

Why not? AIUI as long as a cable runs in a line horizontally or
vertically to an accessory or within 150mm of top of wall or angle
formed by two walls.


Used to be, now 17th edition requires either

cable is buried more than 50mm

or

cable is not buried at all

or

conductors are fully enclosed by an earth (e.g. T&E within earthed metal
capping, or a cable such as SWA, or BS8436 cable with foil screen, or
pyro etc)

or

protected by 30mA RCD or RCBO

or

something else I missed?

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default Cable derating

In fact, one PC may be
enough to trip a 30mA RCD because of the feedback to earth from the
switching PSU. Try it, though.




Must be a really duff PC to be leaking that much!.....
--
Tony Sayer

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Cable derating

In article ,
BigWallop wrote:
To comply with the 30mA RCD ruling, you won't be able to run a fan
heater or anything else of that nature on the final ring.


Eh? The type of element normally used in fan heaters isn't associated with
earth leakage which might cause an RCD to trip.

In fact, one PC may be enough to trip a 30mA RCD because of the
feedback to earth from the switching PSU. Try it, though.


The value of 'feedback' to earth is such that many SMPS can be used on one
RCD - far more than likely in a domestic environment. The effect is
additive. You might well have problems in an office, though, with lots of
them.

--
*Keep honking...I'm reloading.

Dave Plowman London SW
To e-mail, change noise into sound.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Cable derating

Dave Plowman (News) wrote:

The value of 'feedback' to earth is such that many SMPS can be used on one
RCD - far more than likely in a domestic environment. The effect is
additive. You might well have problems in an office, though, with lots of
them.


Indeed, I think the amount of leakage from such things is often
overstated. I must have at least a dozen SMPS in this room alone, and
there are two other socket circuits on the RCD that serves this circuit
as well. In addition I can still stick at least another 15mA leakage
into the thing with my RCD tester and not trip it. (under test it trips
in 26ms at 30mA leakage)

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Cable derating

In article ,
John Rumm wrote:
Dave Plowman (News) wrote:


The value of 'feedback' to earth is such that many SMPS can be used on
one RCD - far more than likely in a domestic environment. The effect
is additive. You might well have problems in an office, though, with
lots of them.


Indeed, I think the amount of leakage from such things is often
overstated. I must have at least a dozen SMPS in this room alone, and
there are two other socket circuits on the RCD that serves this circuit
as well. In addition I can still stick at least another 15mA leakage
into the thing with my RCD tester and not trip it. (under test it trips
in 26ms at 30mA leakage)


The figures have been pointed out elsewhere - it's effectively the thick
end of 10 watts needed to trip an RCD. That is a lot of heat to dissipate
unnecessarily from a power supply which would add to its cost. And such
high current resistors ain't cheap compared to what's used - as well as
bulky.

--
*I speak fluent patriarchy but it's not my mother tongue

Dave Plowman London SW
To e-mail, change noise into sound.


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,538
Default Cable derating

Dave Plowman (News) coughed up some electrons that declared:

The figures have been pointed out elsewhere - it's effectively the thick
end of 10 watts needed to trip an RCD. That is a lot of heat to dissipate
unnecessarily from a power supply which would add to its cost. And such
high current resistors ain't cheap compared to what's used - as well as
bulky.


Shouldn't that be "10VA" - the leakage might be largely reactive, and
probably will with things that employ mains conditioning filters.

Just a thought.

Cheers

Tim
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Cable derating



"BigWallop" wrote in message
om...


To comply with the 30mA RCD ruling, you won't be able to run a fan heater
or
anything else of that nature on the final ring. In fact, one PC may be
enough to trip a 30mA RCD because of the feedback to earth from the
switching PSU. Try it, though.


I recommend you get the appliance tested.
No PC or fan heater or fridge or anything else I have has every tripped a 30
ma rcd and I don't see why they should.

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Cable derating

In article ,
Tim S wrote:
Dave Plowman (News) coughed up some electrons that declared:


The figures have been pointed out elsewhere - it's effectively the
thick end of 10 watts needed to trip an RCD. That is a lot of heat to
dissipate unnecessarily from a power supply which would add to its
cost. And such high current resistors ain't cheap compared to what's
used - as well as bulky.


Shouldn't that be "10VA" - the leakage might be largely reactive, and
probably will with things that employ mains conditioning filters.


There are all sorts of ways - but many SMPS do use just simple resistors.

Just a thought.


--
*Never underestimate the power of very stupid people in large groups *

Dave Plowman London SW
To e-mail, change noise into sound.
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 357
Default Cable derating

BigWallop wrote:

To comply with the 30mA RCD ruling, you won't be able to run a fan heater or
anything else of that nature on the final ring. In fact, one PC may be
enough to trip a 30mA RCD because of the feedback to earth from the
switching PSU. Try it, though.


Rubbish. My whole house is on a 30mA RCD. I wouldn't do it like that if
I were rewiring, but it is there and it doesn't give me nuisance trips.

Pete
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,235
Default Cable derating

On Nov 17, 11:19*pm, "BigWallop"
wrote:
"Martin Carroll" wrote in message

...



In article , Andy Burns
writes
Martin Carroll wrote:


Why not? *AIUI as long as a cable runs in a line horizontally or
vertically to an accessory or within 150mm of top of wall or angle
formed by two walls.


Used to be, now 17th edition requires either


cable is buried more than 50mm


or


cable is not buried at all


or


conductors are fully enclosed by an earth (e.g. T&E within earthed metal
capping, or a cable such as SWA, or BS8436 cable with foil screen, or
pyro etc)


or


protected by 30mA RCD or RCBO


or


something else I missed?


In the 17th Edition OSG, (page 60)


A cable installed in a wall or partition must:


i * *be at least 50mm from surface
ii * have earthed armouring.....
iii *be enclosed in earthed steel conduit....
iv * be provided with mechanical protection......
v * *be installed either horizontally.........


In domestic and similar installations, cables not installed as per i,
ii, iii or iv but complying with v shall be protected by 30mA RCD.


So as long as there is an RCD in CU protecting the circuit cable can be
unprotected in the "safe" zones.


Cheers


Martin


To comply with the 30mA RCD ruling, you won't be able to run a fan heater or
anything else of that nature on the final ring. *In fact, one PC may be
enough to trip a 30mA RCD because of the feedback to earth from the
switching PSU. *Try it, though.


First it was burning transformers with 10% overload, now SMPSs that
will trip 30mA RCDs.

What next?

MBQ
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermal/acoustic insulation and cable derating Martin Carroll UK diy 4 November 11th 08 05:02 PM
Derating lighting cable Staffbull UK diy 3 October 1st 06 02:34 PM
Solid state relay derating for motors Bob Engelhardt Metalworking 2 December 11th 05 05:35 PM
Intermittent static when viewing cable, cable ready problem? [email protected] Electronics Repair 22 October 15th 05 11:04 PM
Fixing loft boarding *through* insulation and derating cable. Mike Hall UK diy 11 January 9th 04 03:45 PM


All times are GMT +1. The time now is 06:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"