Default Cable derating

Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.

Cheers

Martin
--
Martin Carroll
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Cable derating



"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2" plasterboard.



  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default Cable derating

In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2" plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.
--
Martin Carroll
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default Cable derating



"Martin Carroll" wrote in message
...
In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.


You can't do that unless the cable is protected or you have 2"
plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.


That doesn't satisfy the new regs AFAIK



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 92
Default Cable derating

In article , dennis@home
writes


"Martin Carroll" wrote in message
...
In article , dennis@home
writes


"Martin Carroll" wrote in message
...
Just wanted to check that I was reading the OSG correctly!

If I use Reference method A (i.e. enclosed in conduit in insulated wall)
then 2.5mm flat T+E cable will be sufficient for a ring circuit.

Presumably I cannot put 2 cables in the conduit (i.e. to and from the
socket) as this will derate the circuit under 20A and I would need to
increase the size of the cable.

The alternative is to ensure that the cable is touching the inner
surface of the plasterboard and that the two cables do not run in close
proximity to each other.

You can't do that unless the cable is protected or you have 2"
plasterboard.

Or the cable run is in the zone horizontally/vertically to the socket.


That doesn't satisfy the new regs AFAIK

Why not? AIUI as long as a cable runs in a line horizontally or
vertically to an accessory or within 150mm of top of wall or angle
formed by two walls.

Martin
--
Martin Carroll


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 64
Default Cable derating

Martin Carroll wrote:

Why not? AIUI as long as a cable runs in a line horizontally or
vertically to an accessory or within 150mm of top of wall or angle
formed by two walls.


Used to be, now 17th edition requires either

cable is buried more than 50mm

or

cable is not buried at all

or

conductors are fully enclosed by an earth (e.g. T&E within earthed metal
capping, or a cable such as SWA, or BS8436 cable with foil screen, or
pyro etc)

or

protected by 30mA RCD or RCBO

or

something else I missed?

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermal/acoustic insulation and cable derating Martin Carroll UK diy 4 November 11th 08 05:02 PM
Derating lighting cable Staffbull UK diy 3 October 1st 06 02:34 PM
Solid state relay derating for motors Bob Engelhardt Metalworking 2 December 11th 05 05:35 PM
Intermittent static when viewing cable, cable ready problem? [email protected] Electronics Repair 22 October 15th 05 11:04 PM
Fixing loft boarding *through* insulation and derating cable. Mike Hall UK diy 11 January 9th 04 03:45 PM


All times are GMT +1. The time now is 07:03 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"