Had an electrician do a periodic inspection on my place today - I
was very impressed by his thoroughness and knowledge. Got pulled on
a number of points so will have to cough up for a re-inspection as I
want to sell with a clean report:

1. No earth at bedroom light - traced to a broken connection

2. He didn't like me feeding the bathroom lights/shaver/fan through
a fused spur unit: running 6 x 1mm cables into the outlet terminal,
although they fit, is apparently not on. So a little rearrange
called for.

3. Heating/hot & cold pipes need to be cross bonded even though it's
all copper.

4. Didn't like wiring to boiler: I've got a FSU which isolates all
the heating, a three core and a two core flex coming through the
flex outlet (they fit tidily IMO), one feed in, the other back to
the MVs. Needs to be replaced by a four core flex.

5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.

The rest of you would never do any of the above of course, but just
in case you were tempted, this may save you trouble.

--
Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Periodic electrical inspection

In article ,
Tony Bryer writes:
5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.


I agree, except for a ring circuit, I always connect the two
ends of the earth to different terminals. It increases the
redundancy of the earthing, and it used to be a requirement
in the case of high earth leakage circuits in older versions
of the regs.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

Andrew Gabriel wrote:
In article ,
Tony Bryer writes:
5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.


I agree,


Yes, although I think Tony's inspector was being a wee bit anal on some
of the points. The requirement is only that the conductors can be
identified for testing, repair or alteration [514.1.2] and (IMHO)
connecting the neutrals and CPCs in the same running order as the MCBs
is OK. In any case the neutrals in a split-load board have to go to the
right group and it's not always possible to use "same numbers". For
complicated distribution boards it's good practice to keep documentation
and circuits can easily be mapped to terminal numbers in the schedule of
circuits.

except for a ring circuit, I always connect the two ends of the earth
to different terminals. It increases the redundancy of the earthing,
and it used to be a requirement in the case of high earth leakage
circuits in older versions of the regs.


It still is one of the options in the 17th ed. (used along with separate
termination of each CPC at each accessory). I don't recall much
changing in the high-integrity earthing section since it was first
introduced, except that "high earth leakage" was changed to "high
protective conductor current" to clarify that it doesn't apply where the
leakage doesn't flow via the CPC. In the new edition this has moved to
the main body of the regs [543.7] and is no longer a separate section.

--
Andy
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default Periodic electrical inspection

In article , Andy Wade spambucket@m
axwell.myzen.co.uk scribeth thus
Andrew Gabriel wrote:
In article ,
Tony Bryer writes:
5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.


I agree,


Yes, although I think Tony's inspector was being a wee bit anal on some
of the points.


Arse protecting;?.......

--
Tony Sayer



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

Tony Bryer wrote:

I'm wondering what Code numbers were given, and regulations cited, if any:

1. No earth at bedroom light


Code 1 (or Code 2 for a class 2 fitting)?

2. He didn't like me feeding the bathroom lights/shaver/fan through
a fused spur unit: running 6 x 1mm cables into the outlet terminal,


Regulation number? Code 2 or 4?

3. Heating/hot & cold pipes need to be cross bonded even though it's
all copper.


In bathroom, presumably - Code 2?

4. Didn't like wiring to boiler: I've got a FSU which isolates all
the heating, a three core and a two core flex coming through the
flex outlet (they fit tidily IMO), one feed in, the other back to
the MVs. Needs to be replaced by a four core flex.


Regulation number? Code 2 or 4?

5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.


Code 2 or 4?

You might want to read
http://www.esc.org.uk/pdfs//business...ry/BPG3_08.pdf

which gives advice on coding, with examples.

--
Andy


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

tony sayer wrote:

Arse protecting;?.......


That's what PI insurance is for.

--
Andy
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 435
Default Periodic electrical inspection

On Sun, 29 Jun 2008 09:57:34 +0100, tony sayer wrote:

In article , Andy Wade spambucket@m
axwell.myzen.co.uk scribeth thus
Andrew Gabriel wrote:
In article ,
Tony Bryer writes:
5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.

I agree,


Yes, although I think Tony's inspector was being a wee bit anal on some
of the points.


Arse protecting;?.......


Let's face it, choosing to be an inspector is bound to imply a degree of
obsessive compulsiveness - much like programming appeals to people with
mild Aspergers...
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,211
Default Periodic electrical inspection

On Sun, 29 Jun 2008 10:59:57 GMT PCPaul wrote :

Arse protecting;?.......


Let's face it, choosing to be an inspector is bound to imply a degree of
obsessive compulsiveness - much like programming appeals to people with
mild Aspergers...


I was quite happy with his approach, likewise he could see that if a few
details were lacking/not was he would have done it, all the key stuff was
right - bonds to incoming services, sleeving at accessories, ring
continuity etc etc. Also I made it clear to him that I wanted to sell on
knowing that everything was genuinely AOK, rather than just wanting a bit
of paper issued by someone who would sign anything.

--
Tony Bryer SDA UK 'Software to build on' http://www.sda.co.uk

  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Periodic electrical inspection

tony sayer wrote:
In article , Andy Wade spambucket@m
axwell.myzen.co.uk scribeth thus
Andrew Gabriel wrote:
In article ,
Tony Bryer writes:
5. In the new CU the earth and neutral connections must go to the
same numbered terminals as the MCBs - I filled from one end.
I agree,

Yes, although I think Tony's inspector was being a wee bit anal on some
of the points.


Arse protecting;?.......


Probably just a need to find something to make you feel you got your
money's worth!

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

wrote:

Shirley
http://www.esc.org.uk/pdfs//business-and-community/electrical-industry/BPG4_08.pdf
Would be more appropriate.


It certainly would. I copied the wrong URL, sorry.

--
Andy


  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

ARWadworth wrote:

The photo on page 13 of a typical RCD split load CU has been labelled my
a ****ed up man (or woman). The stickers are all to cock and on a MK CU
(as with many other manufacturers) it should be green headers carrying
on to the right after the RCD PROTECTED CIRCUITS sticker not red. The
correct stickers came in the box.


Yes I noticed that, but then the caption does say "in typical split load
etc." It wouldn't surprise me at all if that's typical of what's found
in the field. Not many years ago finding _any_ labelling was a rarity...

--
Andy
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,231
Default Periodic electrical inspection

On Tue, 01 Jul 2008 01:05:46 +0100, Andy Wade wrote:

ARWadworth wrote:

The photo on page 13 of a typical RCD split load CU has been labelled
my a ****ed up man (or woman). The stickers are all to cock and on a MK
CU (as with many other manufacturers) it should be green headers
carrying on to the right after the RCD PROTECTED CIRCUITS sticker not
red. The correct stickers came in the box.


Yes I noticed that, but then the caption does say "in typical split load
etc." It wouldn't surprise me at all if that's typical of what's found
in the field. Not many years ago finding _any_ labelling was a
rarity...


You thought you had done OK if found "lights" in pencil on the dark
bakerlite cover of a Wylex 6 way CU.


--
Ed Sirett - Property maintainer and registered gas fitter.
The FAQ for uk.diy is at http://www.diyfaq.org.uk
Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html
Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html
Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html



  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 43,017
Default Periodic electrical inspection

In article ,
Andy Wade wrote:
Yes I noticed that, but then the caption does say "in typical split load
etc." It wouldn't surprise me at all if that's typical of what's found
in the field. Not many years ago finding _any_ labelling was a rarity...


I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed it
out on sticky backed paper. Anorak? Never in a million years.

--
*Learn from your parents' mistakes - use birth control

Dave Plowman London SW
To e-mail, change noise into sound.
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed it
out on sticky backed paper.


I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?

Anorak? Never in a million years.


Of course not.

--
Andy
  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

Ed Sirett wrote:

You thought you had done OK if found "lights" in pencil on the dark
bakerlite cover of a Wylex 6 way CU.


That's about it, yes. I think some of the perpetrators have gone on to
become web site designers :~)

--
Andy
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,348
Default Periodic electrical inspection

On Tue, 1 Jul 2008 22:06:09 UTC, "Dave Plowman (News)"
wrote:

In article ,
Andy Wade wrote:
Yes I noticed that, but then the caption does say "in typical split load
etc." It wouldn't surprise me at all if that's typical of what's found
in the field. Not many years ago finding _any_ labelling was a rarity...


I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed it
out on sticky backed paper. Anorak? Never in a million years.


Last time I did something like that, I printed on plain paper, laminated
each label and then attached them with superglue!

--
The information contained in this post is copyright the
poster, and specifically may not be published in, or used by
http://www.diybanter.com
  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Periodic electrical inspection

Andy Wade wrote:
Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed it
out on sticky backed paper.


I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?


With some regret, I lobbed my[1] HP7475 in a skip a few months back
after having had it sat in a cupboard unused for getting on for 15 years....

[1] Bought at auction with three others for £65 a piece IIRC



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 435
Default Periodic electrical inspection

On Wed, 02 Jul 2008 04:27:06 +0100, John Rumm wrote:

Andy Wade wrote:
Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed
it out on sticky backed paper.


I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?


With some regret, I lobbed my[1] HP7475 in a skip a few months back
after having had it sat in a cupboard unused for getting on for 15
years....

[1] Bought at auction with three others for £65 a piece IIRC


Aww... Im sure they would make excellent small scale CNC machines/
engravers when fitted with a dremel...
  #22   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Periodic electrical inspection

PCPaul wrote:
On Wed, 02 Jul 2008 04:27:06 +0100, John Rumm wrote:

Andy Wade wrote:
Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed
it out on sticky backed paper.
I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?

With some regret, I lobbed my[1] HP7475 in a skip a few months back
after having had it sat in a cupboard unused for getting on for 15
years....

[1] Bought at auction with three others for £65 a piece IIRC


Aww... Im sure they would make excellent small scale CNC machines/
engravers when fitted with a dremel...


Possibly - they had quite substantial stepper motors for the platten and
turret axis. Not sure if the pen up/down mechanism would cope with a
dremel without serious modification though.

(brings back memories from years ago where I managed to annoy a whole
lab by running a DEC rebadged 7475 plotting radar flight path data from
a spreadsheet that was part of the old DOS "Smart" package. It did not
quite have the intelligence in the spreadsheet to work out that if you
wanted a line from point A to B and then a line from B to C that it
could do the next line without picking up the pen and putting it down
again. Hence each of 8000 short lines that made up the plot would be
drawn with a pen up and down between *every* segment. Sounded like a
demented woodpecker hammering away non stop for a couple of hours!)


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #23   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 435
Default Periodic electrical inspection

On Wed, 02 Jul 2008 14:38:05 +0100, John Rumm wrote:

(brings back memories from years ago where I managed to annoy a whole
lab by running a DEC rebadged 7475 plotting radar flight path data from
a spreadsheet that was part of the old DOS "Smart" package. It did not
quite have the intelligence in the spreadsheet to work out that if you
wanted a line from point A to B and then a line from B to C that it
could do the next line without picking up the pen and putting it down
again. Hence each of 8000 short lines that made up the plot would be
drawn with a pen up and down between *every* segment. Sounded like a
demented woodpecker hammering away non stop for a couple of hours!)


I remember writing a bit of HP-IB code in BBC Basic for exactly that
problem - it pretended to be a plotter, accepted the command stream and
rewrote it to avoid Pen up, Pen down without a move in between. Forward
it to the plotter and away you go..

That was a simple but extremely popular bit of code.. not as nice as the
one that took the BBC micro 'VDU' command stream (which always used a
virtual resolution of 1280x1024 regardless of screen mode) and sent it as
PCL to a Laserjet - much higher resolution than the usual screendumps,
and faster too. Also a fun project, basically building up a framebuffer
in RAM then sending it out as a PCL compressed raster file to fill an A4
page. I don't think I've ever had a project with such clear requirements
since :-(


  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 16
Default Periodic electrical inspection



"John Rumm" wrote in message
...
PCPaul wrote:
On Wed, 02 Jul 2008 04:27:06 +0100, John Rumm wrote:

Andy Wade wrote:
Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and printed
it out on sticky backed paper.
I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?
With some regret, I lobbed my[1] HP7475 in a skip a few months back
after having had it sat in a cupboard unused for getting on for 15
years....

[1] Bought at auction with three others for £65 a piece IIRC


Aww... Im sure they would make excellent small scale CNC machines/
engravers when fitted with a dremel...


Possibly - they had quite substantial stepper motors for the platten and
turret axis. Not sure if the pen up/down mechanism would cope with a
dremel without serious modification though.



Betcha it would cope with a flexi-drive attachment though!

http://www.amazon.co.uk/Rotacraft-Ro.../dp/B000B8JNYK


--
Keith



** Posted from http://www.teranews.com **
  #25   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 499
Default Periodic electrical inspection


"Owain" wrote in message
...
Ed Sirett wrote:
Not many years ago finding _any_ labelling was a
rarity...

You thought you had done OK if found "lights" in pencil on the dark
bakerlite cover of a Wylex 6 way CU.


6 way, eh.

My parents had (still have) a 4-way, with the ways labelled (be me, in
dymo tape)


4 way, you were spoilt as a child.

It was a lot worse in Yorkshire. I had a 2 way when I was a child.

http://www.youtube.com/watch?v=Xe1a1wHxTyo

Adam



  #26   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,122
Default Periodic electrical inspection

On 2008-07-02 19:07:39 +0100, "ARWadworth"
said:


"Owain" wrote in message
...
Ed Sirett wrote:
Not many years ago finding _any_ labelling was a
rarity...
You thought you had done OK if found "lights" in pencil on the dark
bakerlite cover of a Wylex 6 way CU.


6 way, eh.

My parents had (still have) a 4-way, with the ways labelled (be me, in
dymo tape)


4 way, you were spoilt as a child.

It was a lot worse in Yorkshire. I had a 2 way when I was a child.

http://www.youtube.com/watch?v=Xe1a1wHxTyo

Adam


Looksheree.....


  #27   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 435
Default Periodic electrical inspection

On Wed, 02 Jul 2008 20:14:49 +0300, Keith wrote:

"John Rumm" wrote in message
...
PCPaul wrote:
On Wed, 02 Jul 2008 04:27:06 +0100, John Rumm wrote:

Andy Wade wrote:
Dave Plowman (News) wrote:

I scanned the label for my new CU, did all the circuit naming in a
matching font, coloured cross hatching for RCD protected and
printed it out on sticky backed paper.
I've done similar. The house CU label here was drawn in autoCAD and
produced on a pen plotter. Remember pen plotters...?
With some regret, I lobbed my[1] HP7475 in a skip a few months back
after having had it sat in a cupboard unused for getting on for 15
years....

[1] Bought at auction with three others for £65 a piece IIRC

Aww... Im sure they would make excellent small scale CNC machines/
engravers when fitted with a dremel...


Possibly - they had quite substantial stepper motors for the platten
and turret axis. Not sure if the pen up/down mechanism would cope with
a dremel without serious modification though.



Betcha it would cope with a flexi-drive attachment though!

http://www.amazon.co.uk/Rotacraft-Ro...ccessories/dp/

B000B8JNYK

That's mopre like what I was thinking about.

Or a cutter head so you can do your own signwriting...
  #28   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Periodic electrical inspection

The message
from "ARWadworth" contains these words:

My parents had (still have) a 4-way, with the ways labelled (be me, in
dymo tape)


4 way, you were spoilt as a child.


It was a lot worse in Yorkshire. I had a 2 way when I was a child.


http://www.youtube.com/watch?v=Xe1a1wHxTyo


Not exactly back to my childhood but when I moved to my present hovel
(in Yorkshire as it happens) 30 years ago there was only a 3 way fuse
box. One ring circuit, one cooker point and the lights.

Some time later I found that the visible earth wire from the fuse box
actually terminated on a rusty nail loosely pushed into a joint in the
wall behind a cupboard. Being rather worried by this I bought a pukka
earth rod and banged that through the kitchen floor as a replacement for
the rusty nail.

Some further time later I found that there was also an earth wire link
back to the company fuse block but I have never got round to
disconnecting the earth road although from time to time I wonder whether
it is doing any good at all. Should I disconnect the earth rod?

--
Roger Chapman
  #29   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Periodic electrical inspection

Roger wrote:

[...]
Some further time later I found that there was also an earth wire link
back to the company fuse block but I have never got round to
disconnecting the earth road although from time to time I wonder whether
it is doing any good at all. Should I disconnect the earth rod?


You may as well leave it alone. It won't do any harm and it might do a
tiny little bit of good.

--
Andy
  #30   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,194
Default Periodic electrical inspection

The message
from Andy Wade contains these words:

Some further time later I found that there was also an earth wire link
back to the company fuse block but I have never got round to
disconnecting the earth road although from time to time I wonder whether
it is doing any good at all. Should I disconnect the earth rod?


You may as well leave it alone. It won't do any harm and it might do a
tiny little bit of good.


It can stay then at least until I decide to put some insulation and
screed on top of the existing floor. Even then it could stay but it
would look a bit odd with the insulated earth wire disappearing into the
concrete. I don't suppose for a moment I would be able to pull it up by
4" so the clamp stays above the surface.

--
Roger Chapman
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical wiring inspection - pre-check! Lobster UK diy 15 June 26th 07 07:11 PM
electrical inspection - appeal? Russ Home Repair 38 December 24th 05 07:23 PM
Electrical Periodic Inspection Reports Jonty G UK diy 5 December 31st 04 05:15 AM
Electrical inspection Markmon UK diy 19 October 13th 04 10:58 AM
What does an electrical inspection entail? chris French UK diy 26 September 6th 04 06:24 PM


All times are GMT +1. The time now is 02:02 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"