RCDs in series
A friend of mine has a pond with pump & lights wired into a fused spur from
the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. I wondered about changing the existing fused spur for another RCD (like this one http://www.screwfix.com/app/sfd/cat/...00509&id=83049) but I see that it has the same 30mA trip current as the existing one in the main fusebox Would I be right in thinking that this wouldn't necessarily stop the main fusebox RCD tripping? Would one with a lower (20mA say) trip current work (and do such things exist)? Tim |
#2
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Tue, 21 Aug 2007 13:55:12 +0100 someone who may be "Tim Downie"
wrote this:- A friend of mine has a pond with pump & lights wired into a fused spur from the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. [snip] Would I be right in thinking that this wouldn't necessarily stop the main fusebox RCD tripping? Yes. Would one with a lower (20mA say) trip current work (and do such things exist)? It would work in that it would disconnect the supply. However, it is likely that the main one would also work. In this sort of situation you need a time delayed one on the main board, but this gives rise to other difficulties. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#3
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
David Hansen wrote:
On Tue, 21 Aug 2007 13:55:12 +0100 someone who may be "Tim Downie" wrote this:- A friend of mine has a pond with pump & lights wired into a fused spur from the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. [snip] Would I be right in thinking that this wouldn't necessarily stop the main fusebox RCD tripping? Yes. Would one with a lower (20mA say) trip current work (and do such things exist)? It would work in that it would disconnect the supply. However, it is likely that the main one would also work. In this sort of situation you need a time delayed one on the main board, but this gives rise to other difficulties. Hmm, sounds like it will be easier to wire the pond into a circuit & RCD of its own. I was hoping for a "lazy-man's" solution. ;-) Tim |
#4
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"Tim Downie" wrote in message
... Hmm, sounds like it will be easier to wire the pond into a circuit & RCD of its own. I was hoping for a "lazy-man's" solution. ;-) Isolate pond circuit when going away on holiday? cheers, clive |
#5
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On 21 Aug, 14:33, David Hansen
wrote: On Tue, 21 Aug 2007 13:55:12 +0100 someone who may be "Tim Downie" wrote this:- A friend of mine has a pond with pump & lights wired into a fused spur from the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. [snip] Would I be right in thinking that this wouldn't necessarily stop the main fusebox RCD tripping? Yes. Would one with a lower (20mA say) trip current work (and do such things exist)? It would work in that it would disconnect the supply. However, it is likely that the main one would also work. In this sort of situation you need a time delayed one on the main board, but this gives rise to other difficulties. ....such as the fact that they are scarily expensive. Cheapest I found was from CPC a couple of years back. £85 + VAT IIRC. Jon. |
#6
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On 21 Aug, 15:45, "Clive George" wrote:
"Tim Downie" wrote in message ... Hmm, sounds like it will be easier to wire the pond into a circuit & RCD of its own. I was hoping for a "lazy-man's" solution. ;-) Isolate pond circuit when going away on holiday? cheers, clive Or put the deep freeze on its own unprotected circuit as I have done. Interersting post though as my garage, workshop and greenhouse systems are all on their own rcd's but seperate from the house one. Rob |
#7
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
robgraham wrote:
Or put the deep freeze on its own unprotected circuit as I have done. Interersting post though as my garage, workshop and greenhouse systems are all on their own rcd's but seperate from the house one. Same here on both points. Also computer & lan stuff on their own circuit. |
#8
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Tue, 21 Aug 2007 15:04:32 +0100, "Tim Downie"
wrote: Hmm, sounds like it will be easier to wire the pond into a circuit & RCD of its own. I was hoping for a "lazy-man's" solution. ;-) Run the pond stuff off a 1:1 isolating transformer (with an RCD on the secondary if you wish). -- Peter Parry. http://www.wpp.ltd.uk/ |
#9
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
In article ,
"Tim Downie" writes: A friend of mine has a pond with pump & lights wired into a fused spur from the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. You don't want any outdoor circuits sharing an RCD with anything indoors, for this sort of reason. Also a fridge/freezer is not something which needs to be RCD protected at all. You have a fault and the RCD appropriately detected it, but the circuit design for the property would not appear to limited the effects of that fault in a desirable way. Both issues need fixing. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#10
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"robgraham" wrote in message oups.com... On 21 Aug, 15:45, "Clive George" wrote: "Tim Downie" wrote in message ... Hmm, sounds like it will be easier to wire the pond into a circuit & RCD of its own. I was hoping for a "lazy-man's" solution. ;-) Isolate pond circuit when going away on holiday? cheers, clive Or put the deep freeze on its own unprotected circuit as I have done. Interersting post though as my garage, workshop and greenhouse systems are all on their own rcd's but seperate from the house one. Best have a CU with double pole RCBOs on it instead of and have Continental radial system instead of the silly at times ring circuits. If any problem only the one RCBO trips not the whole house. |
#11
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
Best have a CU with double pole RCBOs on it instead of and have Continental radial system instead of the silly at times ring circuits. If any problem only the one RCBO trips not the whole house. Separating these risky circuits out such that they are protected by independent RCDs is generally a good thing to do. RCBOs are one of several ways of doing this. The use of a ring or radial circuit does not really have any relevance though. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#12
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Tim Downie wrote:
A friend of mine has a pond with pump & lights wired into a fused spur from the house ring-main (which is RCD protected). After some recent heavy rain (which probably managed to penetrate a supposedly "water-tight" outside junction-box, the RCD tripped, which wouldn't have been a problem if he hadn't been away on holiday at the time and the fact that the freezer was on same circuit. Yup, you don't want to start from there! ;-) I wondered about changing the existing fused spur for another RCD (like this one http://www.screwfix.com/app/sfd/cat/...00509&id=83049) but I see that it has the same 30mA trip current as the existing one in the main fusebox Would I be right in thinking that this wouldn't necessarily stop the main fusebox RCD tripping? You would. Would one with a lower (20mA say) trip current work (and do such things exist)? alas no. Read the sections on discrimination, mitigating the effects of nuisance trips, and system design using RCDs he http://wiki.diyfaq.org.uk/index.php?title=RCD to get a feel for the available options. There is also a fair bit or relevant info in this one: http://wiki.diyfaq.org.uk/index.php?...ricity_outside -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#13
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: Best have a CU with double pole RCBOs on it instead of and have Continental radial system instead of the silly at times ring circuits. If any problem only the one RCBO trips not the whole house. Separating these risky circuits out such that they are protected by independent RCDs is generally a good thing to do. RCBOs are one of several ways of doing this. The use of a ring or radial circuit does not really have any relevance though. True an RCBO can be on a ring. Rings are still silly and cheap; one of the reasons they were adopted..and to have higher currents for electric heaters post war as the nuclear policy was all electric using unmetered nuclear power. Although radials may have high currents at the sockets too. I recall a German looking at a British system; the RCD protecting all of the house and the fused spurs above the worktops with a fuesd plug hidden behind the appliance. He thought the system was mad and said it was clearly cheap at the CU but expensive (and ugly) in fused spurs. About time we went the same way as the rest of the world. On the Continent each appliance has an RCBO at the CU. So much easier to isolate. The only advantage of the UK system is that 3kW kettles are common, whereas in Europe they only go to around 2kW max. BUt they fill their kettles with hot water from the combi to make the heat up cheaper and faster. |
#14
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
Best have a CU with double pole RCBOs on it instead of and have Continental radial system instead of the silly at times ring circuits. If any problem only the one RCBO trips not the whole house. Separating these risky circuits out such that they are protected by independent RCDs is generally a good thing to do. RCBOs are one of several ways of doing this. The use of a ring or radial circuit does not really have any relevance though. True an RCBO can be on a ring. Rings are still silly and cheap; one of Today's ring circuits represent a very good bit of engineering design. the reasons they were adopted..and to have higher currents for electric Even if this were true originally, one has to look at how design has evolved and been refined to where we are today. The ring final circuit we have now is very well suited to diverse power provision over a wide area. heaters post war as the nuclear policy was all electric using unmetered nuclear power. Although radials may have high currents at the sockets too. I recall a German looking at a British system; the RCD protecting all of the house and the fused spurs above the worktops with a fuesd plug No sure what his nationality has to do with it. The system you describe would not be to standard in the UK wiring regulations, and would rightly be due criticism. Appliances in kitchens with concealed sockets etc should have independent switching above the worktop. Use of whole house RCDs is also long since deprecated. hidden behind the appliance. He thought the system was mad and said it was clearly cheap at the CU but expensive (and ugly) in fused spurs. Rich coming from a German, have you seen their plugs and sockets? About time we went the same way as the rest of the world. On the Continent each appliance has an RCBO at the CU. So much easier to isolate. The only advantage of the UK system is that 3kW kettles are common, whereas in Europe they only go to around 2kW max. BUt they fill their kettles with hot water from the combi to make the heat up cheaper and faster. Your logic seems as confused as ever. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#15
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: Best have a CU with double pole RCBOs on it instead of and have Continental radial system instead of the silly at times ring circuits. If any problem only the one RCBO trips not the whole house. Separating these risky circuits out such that they are protected by independent RCDs is generally a good thing to do. RCBOs are one of several ways of doing this. The use of a ring or radial circuit does not really have any relevance though. True an RCBO can be on a ring. Rings are still silly and cheap; one of Today's ring circuits represent a very good bit of engineering design. Engineering? Daisy-chaining sockets together? Are you kidding? I said to this guy we have two ways back to the meter in earthing. He said if you are that paranoid run another earth back from the furthest socket on a radial circuit. He said "use 4 core cable and use the 4th core for the return earth, that will do it". He was amazed we had an unsheathed eath wire in the T&E cable. He said "that is cheap". the reasons they were adopted..and to have higher currents for electric Even if this were true originally, one has to look at how design has evolved and been refined to where we are today. The ring final circuit we have now is very well suited to diverse power provision over a wide area. You mean a high current circuit on a 32A MCB. Duh! heaters post war as the nuclear policy was all electric using unmetered nuclear power. Although radials may have high currents at the sockets too. I recall a German looking at a British system; the RCD protecting all of the house and the fused spurs above the worktops with a fuesd plug No sure what his nationality has to do with it. The system you describe would not be to standard in the UK wiring regulations, and would rightly be due criticism. Appliances in kitchens with concealed sockets etc should have independent switching above the worktop. With a socket under the worktop with an inaccessible fuse in the plug, that might blow. Duh!! The fused spurs looks hideous as well. Use of whole house RCDs is also long since deprecated. Long since? Like a few years then. hidden behind the appliance. He thought the system was mad and said it was clearly cheap at the CU but expensive (and ugly) in fused spurs. Rich coming from a German, have you seen their plugs and sockets? Fused spurs can ruin an nice kitchen worktop. About time we went the same way as the rest of the world. On the Continent each appliance has an RCBO at the CU. So much easier to isolate. The only advantage of the UK system is that 3kW kettles are common, whereas in Europe they only go to around 2kW max. BUt they fill their kettles with hot water from the combi to make the heat up cheaper and faster. Your logic seems as confused as ever. Get to know the merits of a system the rest of the world use. Duh! |
#16
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
True an RCBO can be on a ring. Rings are still silly and cheap; one of Today's ring circuits represent a very good bit of engineering design. Engineering? Daisy-chaining sockets together? Are you kidding? I said Mo, not at all. Do the sums and see how it out performs other circuit topologies under wide ranging loads and the majority of fault conditions. This with economy of materials. Anyone can build cheap and anyone can build strong, but it takes engineering finesse to do both at once. to this guy we have two ways back to the meter in earthing. He said if you are that paranoid run another earth back from the furthest socket on a radial circuit. Which is also standard practice in the UK for high integrity radial circuits. He said "use 4 core cable and use the 4th core for the return earth, that will do it". Does not get you the advantages of dual conductor paths for the phase an neutral though does it? You would also need 6mm^2 cable in many circuits to make and equivalent radial. Far less practical from an installers point of view. He was amazed we had an unsheathed eath wire in the T&E cable. He said "that is cheap". Which is good obviously. No sure what his nationality has to do with it. The system you describe would not be to standard in the UK wiring regulations, and would rightly be due criticism. Appliances in kitchens with concealed sockets etc should have independent switching above the worktop. With a socket under the worktop with an inaccessible fuse in the plug, that might blow. Duh!! The fused spurs looks hideous as well. You don't need a fused spur on the wall, just a switch. These look perfectly acceptable: http://www.tlc-direct.co.uk/Main_Ind..._20/index.html Use of whole house RCDs is also long since deprecated. Long since? Like a few years then. some 20 odd, yes. hidden behind the appliance. He thought the system was mad and said Fuses in plugs don't routinely blow unless the appliance develops a fault. You probably won't be repairing that in situ under the worktop either, so not really a problem is it. it was clearly cheap at the CU but expensive (and ugly) in fused spurs. Rich coming from a German, have you seen their plugs and sockets? Fused spurs can ruin an nice kitchen worktop. So don't use them - no need. About time we went the same way as the rest of the world. On the What and lower our standards and safety record to match theirs you mean? Your logic seems as confused as ever. Get to know the merits of a system the rest of the world use. Duh! You could start with understanding ours before you go trying to compare with others. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#17
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: True an RCBO can be on a ring. Rings are still silly and cheap; one of Today's ring circuits represent a very good bit of engineering design. Engineering? Daisy-chaining sockets together? Are you kidding? I said Mo, not at all. Do the sums and see how it out performs other circuit topologies under wide ranging loads and the majority of fault conditions. This with economy of materials. Anyone can build cheap and anyone can build strong, but it takes engineering finesse to do both at once. to this guy we have two ways back to the meter in earthing. He said if you are that paranoid run another earth back from the furthest socket on a radial circuit. Which is also standard practice in the UK for high integrity radial circuits. He said "use 4 core cable and use the 4th core for the return earth, that will do it". Does not get you the advantages of dual conductor paths for the phase an neutral though does it? You would also need 6mm^2 cable in many circuits to make and equivalent radial. They do not have countless sockets on one radial. In France it is 8 maximum on a 16A MCB. Far less practical from an installers point of view. You mean cheap, having all the downsrairs sockets on one 32A MCB. They would have that split into many 16 MCBs. Better. Divider and rule. He was amazed we had an unsheathed eath wire in the T&E cable. He said "that is cheap". Which is good obviously. No sure what his nationality has to do with it. The system you describe would not be to standard in the UK wiring regulations, and would rightly be due criticism. Appliances in kitchens with concealed sockets etc should have independent switching above the worktop. With a socket under the worktop with an inaccessible fuse in the plug, that might blow. Duh!! The fused spurs looks hideous as well. You don't need a fused spur on the wall, just a switch. These look perfectly acceptable: http://www.tlc-direct.co.uk/Main_Ind..._20/index.html Use of whole house RCDs is also long since deprecated. Long since? Like a few years then. some 20 odd, yes. More a few years. I have seen many new builds with RCDs on the whole CU. hidden behind the appliance. He thought the system was mad and said Fuses in plugs don't routinely blow unless the appliance develops a fault. You probably won't be repairing that in situ under the worktop either, so not really a problem is it. They CAN blow and when they do an appliance has to be dragged out. it was clearly cheap at the CU but expensive (and ugly) in fused spurs. Rich coming from a German, have you seen their plugs and sockets? Fused spurs can ruin an nice kitchen worktop. So don't use them - no need. About time we went the same way as the rest of the world. On the What and lower our standards and safety record to match theirs you mean? Theirs superior. Your logic seems as confused as ever. Get to know the merits of a system the rest of the world use. Duh! You could start with understanding ours before you go trying to compare with others. I understand ours and it is cheap and nasty. In France to isolate a dishwasher you go to the CU and throw the RCBO. Any problems and they throws. |
#18
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... With a socket under the worktop with an inaccessible fuse in the plug, that might blow. Duh!! The fused spurs looks hideous as well. You don't need a fused spur on the wall, just a switch. These look perfectly acceptable: http://www.tlc-direct.co.uk/Main_Ind..._20/index.html They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. |
#19
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: True an RCBO can be on a ring. Rings are still silly and cheap; one of Today's ring circuits represent a very good bit of engineering design. Engineering? Daisy-chaining sockets together? Are you kidding? I said Mo, not at all. Do the sums and see how it out performs other circuit topologies under wide ranging loads and the majority of fault conditions. This with economy of materials. As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. He was right. |
#20
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Wed, 22 Aug 2007 17:57:57 +0100, "Doctor Drivel"
wrote: As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. Would this explain why, proportionately to population, the number of people killed by electrical accidents in Germany is 3 times greater than the UK and in France is about 10 times greater? -- Peter Parry. http://www.wpp.ltd.uk/ |
#21
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"Peter Parry" wrote in message ... On Wed, 22 Aug 2007 17:57:57 +0100, "Doctor Drivel" wrote: As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. Would this explain why, proportionately to population, the number of people killed by electrical accidents in Germany is 3 times greater than the UK and in France is about 10 times greater? No it would not. There is no reason for those figures to relate to the types of electrical systems. It is more a culture towards safety than the systems. |
#22
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
They do not have countless sockets on one radial. In France it is 8 maximum on a 16A MCB. Which exemplifies why low capacity radials are not well suited to general power provision in a home. Far less practical from an installers point of view. You mean cheap, having all the downsrairs sockets on one 32A MCB. They would have that split into many 16 MCBs. Better. Divider and rule. One ring circuit for the kitchen, another for the other downstairs sockets, plus a non RCD protected radial for any circuits with low trip tolerance would seem more than adequate in most domestic situations. Use of whole house RCDs is also long since deprecated. Long since? Like a few years then. some 20 odd, yes. More a few years. I have seen many new builds with RCDs on the whole CU. Whole house RCDs were briefly allowed in the 15th edition IIUC. So since that covered the '80s basically, the scope when that was acceptable was limited. It fairly soon became apparent that it was not a good solution. hidden behind the appliance. He thought the system was mad and said Fuses in plugs don't routinely blow unless the appliance develops a fault. You probably won't be repairing that in situ under the worktop either, so not really a problem is it. They CAN blow and when they do an appliance has to be dragged out. They can, but rarely if ever do in the absence of a fault. I don't recall the last time I need to replace a fuse for a non faulty appliance. What and lower our standards and safety record to match theirs you mean? Theirs superior. Figures? I understand ours and it is cheap and nasty. In France to isolate a dishwasher you go to the CU and throw the RCBO. Any problems and they throws. Here you would throw the switch above the counter marked "Dishwasher", seems somewhat better to me. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#23
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. Requiring dedicated circuit wiring for each and every appliance.... hmmm novel. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#24
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. He was as clueless as you. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#25
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Aug 22, 9:44 pm, Peter Parry wrote:
On Wed, 22 Aug 2007 17:57:57 +0100, "Doctor Drivel" wrote: As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. Would this explain why, proportionately to population, the number of people killed by electrical accidents in Germany is 3 times greater than the UK and in France is about 10 times greater? AIUI in Holland proportionately to population, the number of people killed by electrical accidents is /half/ that of the UK, and I don't think they have ring mains... do they? cheers, Pete. |
#26
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On 2007-08-23 00:02:42 +0100, Pete C said:
On Aug 22, 9:44 pm, Peter Parry wrote: On Wed, 22 Aug 2007 17:57:57 +0100, "Doctor Drivel" wrote: As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. Would this explain why, proportionately to population, the number of people killed by electrical accidents in Germany is 3 times greater than the UK and in France is about 10 times greater? AIUI in Holland proportionately to population, the number of people killed by electrical accidents is /half/ that of the UK, and I don't think they have ring mains... do they? cheers, Pete. Final circuits in Holland are radial. The numbers are low in all cases, so it would be necessary to look at individual accidents to see whether the cause was related to circuit protection or other causes |
#27
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: They do not have countless sockets on one radial. In France it is 8 maximum on a 16A MCB. Which exemplifies why low capacity radials are not well suited to general power provision in a home. ??????? Far less practical from an installers point of view. You mean cheap, having all the downsrairs sockets on one 32A MCB. They would have that split into many 16 MCBs. Better. Divide and rule. One ring circuit for the kitchen, another for the other downstairs sockets, plus a non RCD protected radial for any circuits with low trip tolerance would seem more than adequate in most domestic situations. They split it up well. Use of whole house RCDs is also long since deprecated. Long since? Like a few years then. some 20 odd, yes. More a few years. I have seen many new builds with RCDs on the whole CU. Whole house RCDs were briefly allowed in the 15th edition IIUC. So since that covered the '80s basically, the scope when that was acceptable was limited. It fairly soon became apparent that it was not a good solution. I have seen them on new builds of only 5 years ago and less. hidden behind the appliance. He thought the system was mad and said Fuses in plugs don't routinely blow unless the appliance develops a fault. You probably won't be repairing that in situ under the worktop either, so not really a problem is it. They CAN blow and when they do an appliance has to be dragged out. They can, but rarely if ever do in the absence of a fault. I don't recall the last time I need to replace a fuse for a non faulty appliance. But can do and behind an appliance. What and lower our standards and safety record to match theirs you mean? Theirs superior. Figures? I understand ours and it is cheap and nasty. In France to isolate a dishwasher you go to the CU and throw the RCBO. Any problems and they throws. Here you would throw the switch above the counter marked "Dishwasher", seems somewhat better to me. Which looks crap and is not an RCBO. |
#28
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. Requiring dedicated circuit wiring for each and every appliance.... hmmm novel. No. The standard in the rest of the world and safer. Ours is cheap - and nasty. |
#29
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: As one German said to me when I said rings are legal in Germany. "why run a ring off one MCB when this can be run in two runs (radials) and have two MCBs protecting each. To him it just did not add up. He was as clueless as you. It seems the UK is out of step with the rest of them (but thinks it is in step)...as is your brain. |
#30
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On 2007-08-23 08:31:26 +0100, "Doctor Drivel" said:
"John Rumm" wrote in message ... Doctor Drivel wrote: They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. Requiring dedicated circuit wiring for each and every appliance.... hmmm novel. No. The standard in the rest of the world and safer. Ours is cheap - and nasty. Have you seen French electrical fittings and wiring practices? They are better than the U.S., but that is all that can be said. The UK system can't be described as cheap or nasty in the sense of the fittings used or the electrical design. In other countries, the radial design does result in the need for many more circuit breakers in an installation, which increases the cost on that side somewhat. |
#31
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Wed, 22 Aug 2007 16:02:42 -0700, Pete C
wrote: AIUI in Holland proportionately to population, the number of people killed by electrical accidents is /half/ that of the UK, and I don't think they have ring mains... do they? The numbers killed in electrical accidents isn't recorded very consistently between countries. For example some record only electrocution deaths, some would record deaths in a fire caused by electrical faults as "caused by electricity" others as a fire death. There are certain countries in the EU with dire standards - France, Spain, Portugal, Italy, Greece and most of the old East Europeans states amongst them. In these countries deaths primarily caused by electrocution are fairly common. From a hazard point of view fixed wiring (even French) doesn't cause many accidents directly. The direct difference between ring and radial is also minimal. However, the consequential hazards are not. A characteristic of many continental installations is that there are a smaller number of sockets in a house than for a house of similar age in the UK and consequently much more use of trailing extensions. These are inherently more hazardous than wall sockets and contribute to far more fires of electric origin than does fixed wiring. The lack of any form of appliance lead protection coupled with high trip currents also makes fires caused by equipment failure more common on the continent than in the UK. All countries using the CEE 7/4 (Shuko) plugs tend to have a number of child fatalities each year caused by objects being poked into the unprotected openings. The UK has virtually no such accidents with the shielded 13A socket. The Schutzkontakt (Shuko) plug socket pair is designed to be safe in that the side earth contact must mate before the pins and the recessed socket prevents fingers touching the pins as they are being inserted. Unfortunately there are a number of other systems using the same or similar pin sizing and spacing as Shuko but without the earth connection or recessed socket. As a result there are accidents caused by plugging Shuko plugs into sockets where the earth is either absent or ineffective as it doesn't touch the side contacts. A further catch is that in such situations the side contacts on the plug become live so giving a shock to anyone who tries to remove it in such fault conditions. This commonly occurs with the two pin CEE 7/16 (Europlug 2.5 A/250 V) unearthed socket which isn't supposed to fit a Shuko plug but many will. The French 2 pin plug with female earth will also usually fit a Shuko socket - but without the earth making. The CEE 7/7 is a cross between the Shuko and French systems with side contacts and a female earth receptacle and usually supplied with new equipment. Although rated at 16A it is also possible to buy Shuko plugs with considerably lower current carrying capacity and many "Shuko" plugs are of poor quality and prone to overheating when running at high loads. I have seen some dire examples around of very poorly made Shuko plugs and nothing like the same poor quality in even the cheapest BS 1363 plugs (probably because BS1363 plugs require third party certification whilst manufacturers can self certify Shuko). Another issue with the continental two pin plugs is that the wiring of the live and neutral is random (and even if it were not the plugs can be inserted any way around). Usually this isn't an issue but it becomes one when freestanding lamps using Edison Screw (the continental standard) fittings. The threaded part of the shell can be left live and shocks while changing bulbs and accidentally touching the bulb thread are common. The shock isn't usually fatal, the fall off the ladder more often is! There is no question that BS 1363 is a fundamentally much safer system than the Shuko and its variants. This is hardly unexpected as the Shuko design dates from the 1920's. The improved safety of the ring over the radial stems largely from secondary effects of the greater number of fixed sockets and fuse protection of the appliance lead. Together these reduce the number of fires caused by overloaded and damaged extensions. There is of course nothing to stop you wiring a BS1363 layout in radial form - but there would be no advantage in doing so. -- Peter Parry. http://www.wpp.ltd.uk/ |
#32
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
"John Rumm" wrote in message ... Doctor Drivel wrote: They do not have countless sockets on one radial. In France it is 8 maximum on a 16A MCB. Which exemplifies why low capacity radials are not well suited to general power provision in a home. ??????? Because you end up needing at least half a dozen circuits per floor just for sockets, with all the cost and wiring complexity that entails. You are also stuck with no more practical load than one high current device per circuit - a right PITA in a kitchen for example. Whole house RCDs were briefly allowed in the 15th edition IIUC. So since that covered the '80s basically, the scope when that was acceptable was limited. It fairly soon became apparent that it was not a good solution. I have seen them on new builds of only 5 years ago and less. Are you: 1) Sure you know what you were looking at 2) Sure it was not a TT install 3) Not just making up this stuff like normal They can, but rarely if ever do in the absence of a fault. I don't recall the last time I need to replace a fuse for a non faulty appliance. But can do and behind an appliance. can in theory. I have never had it happen. In fact I have not had a fuse blow in anything in the last 15 years that I can recall. What and lower our standards and safety record to match theirs you mean? Theirs superior. Figures? Still waiting... Here you would throw the switch above the counter marked "Dishwasher", seems somewhat better to me. Which looks crap and is not an RCBO. You are aware that there is no particular advantage to having RCD protection on fixed appliances such as dishwashers? (TT excepted) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#33
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Doctor Drivel wrote:
"John Rumm" wrote in message ... Doctor Drivel wrote: They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. Requiring dedicated circuit wiring for each and every appliance.... hmmm novel. No. The standard in the rest of the world and safer. Ours is cheap - and nasty. Figures? Ours is certainly not cheap, and IME the quality of accessories is usually noticeably higher. The accident statistics do not support your claims either. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#34
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
Andy Hall wrote:
AIUI in Holland proportionately to population, the number of people killed by electrical accidents is /half/ that of the UK, and I don't think they have ring mains... do they? cheers, Pete. Final circuits in Holland are radial. The numbers are low in all cases, so it would be necessary to look at individual accidents to see whether the cause was related to circuit protection or other causes Much also depends on if they record accidents with electrical appliances separately from those for fixed wiring, and how they record things like fires started by electrical faults. Without detailed analysis of the stats recording process they as usual tell you a small part of the story. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#35
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Thu, 23 Aug 2007 14:34:21 +0100 someone who may be John Rumm
wrote this:- Figures? Still waiting... I'm waiting for these too, despite the various claims in other parts of the thread. Which looks crap and is not an RCBO. You are aware that there is no particular advantage to having RCD protection on fixed appliances such as dishwashers? (TT excepted) Keep up the good work by pointing out the flaws in Mr Dribble's assertions. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#36
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
On Thu, 23 Aug 2007 14:16:13 +0100 someone who may be Peter Parry
wrote this:- There is no question that BS 1363 is a fundamentally much safer system than the Shuko and its variants. This is hardly unexpected as the Shuko design dates from the 1920's. This is something I entirely agree with you on. Wiring is something that the UK has got right for a long time, unlike say plumbing which was decidedly dodgy until say the 1960s and the adoption of single pipe drainage almost universally. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#37
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"Andy Hall" wrote in message ... On 2007-08-23 08:31:26 +0100, "Doctor Drivel" said: "John Rumm" wrote in message ... Doctor Drivel wrote: They have one MCB or RCBO at the CU to isolate the appliance. Nice and neat, out of the way and accessible. The best way. Requiring dedicated circuit wiring for each and every appliance.... hmmm novel. No. The standard in the rest of the world and safer. Ours is cheap - and nasty. Have you seen French electrical fittings and wiring practices? They are better than the U.S., but that is all that can be said. Have you seen the electrics in a remote village in Slovakia? They are definately cheap and nasty. The old high rise flats in the citys are not much better. I wonder what the authorities here would say if a British villager decided to make their own electrical connection to an overhead supply. Adam |
#38
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
In article ,
David Hansen writes: On Thu, 23 Aug 2007 14:16:13 +0100 someone who may be Peter Parry wrote this:- There is no question that BS 1363 is a fundamentally much safer system than the Shuko and its variants. This is hardly unexpected as the Shuko design dates from the 1920's. This is something I entirely agree with you on. Wiring is something that the UK has got right for a long time, unlike say plumbing which was decidedly dodgy until say the 1960s and the adoption of single pipe drainage almost universally. BS1363 family is the most recently designed domestic plug and socket system in the world. It was the result of some 10 years of competition between manufacturers to design a new standard. It has been adopted in whole or part by more countries in the world than any other domestic plug and socket standard. The standard has been further improved a number of times over its 60 year history, and the mandatory testing required is very rigorous. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#39
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
David Hansen wrote:
Keep up the good work by pointing out the flaws in Mr Dribble's assertions. Not much of a challenge is it! Still he seems to have sloped off tail between legs again for now. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#40
Posted to uk.d-i-y
|
|||
|
|||
RCDs in series
"John Rumm" wrote in message ... Doctor Drivel wrote: "John Rumm" wrote in message ... Doctor Drivel wrote: They do not have countless sockets on one radial. In France it is 8 maximum on a 16A MCB. Which exemplifies why low capacity radials are not well suited to general power provision in a home. ??????? Because you end up needing at least half a dozen circuits per floor just for sockets, So that is 8 x 6 which 48 sockets. A lot of sockets per floor. with all the cost and wiring complexity that entails. Ah cost!! Yes rings are cheap....and nasty. You are also stuck with no more practical load than one high current device per circuit - a right PITA in a kitchen for example. In a kitchen individual circuit for high load appliances is a great advantage in many ways. Whole house RCDs were briefly allowed in the 15th edition IIUC. So since that covered the '80s basically, the scope when that was acceptable was limited. It fairly soon became apparent that it was not a good solution. I have seen them on new builds of only 5 years ago and less. Are you: 1) Sure you know what you were looking at Yes. A CU. 2) Sure it was not a TT install 3) Not just making up this stuff like normal I know what I see, You make things up as you are from Essex. They can, but rarely if ever do in the absence of a fault. I don't recall the last time I need to replace a fuse for a non faulty appliance. But can do and behind an appliance. can in theory. I have never had it happen. I have. In fact I have not had a fuse blow in anything in the last 15 years that I can recall. Lucky man. How about the RCSs tripping the whole house when a 230V downlighter blows. Great eh!!! What and lower our standards and safety record to match theirs you mean? Theirs superior. Figures? Still waiting... Look at the systems. Theirs is superior. Not a cheap ring effort to reduce MCBs. and have a small CU. Here you would throw the switch above the counter marked "Dishwasher", seems somewhat better to me. Which looks crap and is not an RCBO. You are aware that there is no particular advantage to having RCD protection on fixed appliances such as dishwashers? (TT excepted) There IS!!!!!!!! |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
RCDs in all their glory | UK diy | |||
RCDs - sourcing of. | UK diy | |||
RCDs | UK diy | |||
Carrier Performance series vs. Ruud Achiever series home AC? | Home Repair | |||
Discrimination (RCDs) | UK diy |