single 2.5mm wire in a 32A MCB
Just opened the CU at work, as we need to add another circuit for some A/C
in the server room. There is a 32A breaker marked as Spare with a single 2.5mm wire inserted (So it isn't spare then I assume!) Now, one part of me says this is wrong, it should be a 20A MCB as it must be a radial, but if this were a ring circuit, then I could spur off of it, so the spur would be protected with a 32A breaker. The installation has passed safety inspections, should it have? Sparks... |
#2
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
On Tue, 21 Feb 2006 16:17:04 -0000 someone who may be "Sparks"
wrote this:- There is a 32A breaker marked as Spare with a single 2.5mm wire inserted (So it isn't spare then I assume!) Do you know where this cable goes? Is the MCB on or off? Now, one part of me says this is wrong, it should be a 20A MCB as it must be a radial, Correct. but if this were a ring circuit, then I could spur off of it, so the spur would be protected with a 32A breaker. Non-fused spurs can only serve a single or double socket, or one fixed appliance. Incidentally the Wiring Regulations are silent on a spur serving one fixed appliance and one socket side by side, which is essentially the same as a double socket. As a result of this the current that can be drawn down the spur is limited. However, the 30/32A protective device doesn't protect the spur cable properly. Spurs are a balance of risks, as indeed is any other form of wiring. If houses were bursting into flames regularly because of problems with spurs there would no doubt be a change. There was a change many moons ago, because at one time spurs could feed two single sockets (which meant somebody might think they were on the ring). On a radial circuit any number of sockets could be wired up. Thus the size of the protective must be smaller to protect the cable. The installation has passed safety inspections, should it have? That rather depends on what was inspected. If the consumer unit was inspected then no. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54 |
#3
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
"David Hansen" wrote in message ... On Tue, 21 Feb 2006 16:17:04 -0000 someone who may be "Sparks" wrote this:- There is a 32A breaker marked as Spare with a single 2.5mm wire inserted (So it isn't spare then I assume!) Do you know where this cable goes? Is the MCB on or off? MCB is on, but I am waiting until everyone goes home before I turn it off (Although, it would probably be quicker to turn it off and see who shouts! Now, one part of me says this is wrong, it should be a 20A MCB as it must be a radial, Correct. but if this were a ring circuit, then I could spur off of it, so the spur would be protected with a 32A breaker. Non-fused spurs can only serve a single or double socket, or one fixed appliance. Incidentally the Wiring Regulations are silent on a spur serving one fixed appliance and one socket side by side, which is essentially the same as a double socket. As a result of this the current that can be drawn down the spur is limited. However, the 30/32A protective device doesn't protect the spur cable properly. Spurs are a balance of risks, as indeed is any other form of wiring. If houses were bursting into flames regularly because of problems with spurs there would no doubt be a change. There was a change many moons ago, because at one time spurs could feed two single sockets (which meant somebody might think they were on the ring). On a radial circuit any number of sockets could be wired up. Thus the size of the protective must be smaller to protect the cable. The installation has passed safety inspections, should it have? That rather depends on what was inspected. If the consumer unit was inspected then no. I will find out what was tested then! Thanks! Sparks... |
#4
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
"David Hansen" wrote in message ... On Tue, 21 Feb 2006 16:17:04 -0000 someone who may be "Sparks" wrote this:- There is a 32A breaker marked as Spare with a single 2.5mm wire inserted (So it isn't spare then I assume!) Do you know where this cable goes? Is the MCB on or off? Now, one part of me says this is wrong, it should be a 20A MCB as it must be a radial, Correct. but if this were a ring circuit, then I could spur off of it, so the spur would be protected with a 32A breaker. Non-fused spurs can only serve a single or double socket, or one fixed appliance. Incidentally the Wiring Regulations are silent on a spur serving one fixed appliance and one socket side by side, which is essentially the same as a double socket. The OSG states that a non-fused spur feeds only one single or one twin or one permanently connected equipment As a result of this the current that can be drawn down the spur is limited. However, the 30/32A protective device doesn't protect the spur cable properly. It should protect against short circiuts on a correctly designed circuit. Adam |
#5
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
Sparks wrote:
MCB is on, but I am waiting until everyone goes home before I turn it off (Although, it would probably be quicker to turn it off and see who shouts! Time to buy a clamp meter? There is a very useful new type which we use at work in our machine room. It can measure (to a reasonable approximation) the current flowing in a cable with the clamp around the entire cable, rather than just a load carrying core as the "old" type could only do by design. Needs to be told the cable type under test, presumably does some clever trickery with the fact that the magnetic field isn't zero in close proximity to parts of the cable surface, despite having a balanced flow and return of current overall. I'll find out the make tomorrow if you mail me (addy above valid). Extremely useful for measuring circuit loads in and out of UPS's as well as total load on circuits back to the DB and to answer such questions as "how many of *those* servers + disk arrays dare we put in this rack. Cheers Tim |
#6
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
In article ,
David Hansen writes: However, the 30/32A protective device doesn't protect the spur cable properly. Spurs are a balance of risks, as indeed is any other form of wiring. If houses were bursting into flames regularly because of problems with spurs there would no doubt be a change. There was a change many The 32A MCB provides suitable fault current protection for 2.5mm˛ T&E cable, and the BS1362 fuse in the plug or FCU provides the overload protection for the 2.5mm˛ T&E. The cable is properly protected, but the fault current and overload current protection have been separated. This is permitted by the regs previding the fault current protection is at the beginning of the circuit, and the overload current protection is before any branches, which it is in the case of a spur. moons ago, because at one time spurs could feed two single sockets 14th edition regs. -- Andrew Gabriel |
#7
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
Andrew Gabriel wrote: In article , David Hansen writes: However, the 30/32A protective device doesn't protect the spur cable properly. Spurs are a balance of risks, as indeed is any other form of wiring. If houses were bursting into flames regularly because of problems with spurs there would no doubt be a change. There was a change many The 32A MCB provides suitable fault current protection for 2.5mm˛ T&E cable, and the BS1362 fuse in the plug or FCU provides the overload protection for the 2.5mm˛ T&E. The cable is properly protected, but the fault current and overload current protection have been separated. This is permitted by the regs previding the fault current protection is at the beginning of the circuit, and the overload current protection is before any branches, which it is in the case of a spur. Can you expand on that please Andrew for the hard of thinking like myself. Are you saying that 30/32A protection is fine for a circuit run from a single piece of 2.5mm T & E if it only consists of sockets linked to each other in a bus configuration or with just one device on each spur? Or are you referring to spurs on rings (which is what *might* be being about above, but wasn't the op's original question. Not being funny here, just trying to understand what you are saying. |
#9
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
John Rumm wrote: wrote: snip With a spur (from a ring) or the particular setup described by the OP there is only one outlet and this is fused. Hence it is not possible to load the cable beyond what the 13A fuse on the outlet will carry for a sustained period. Hmm, Thanks for that John, but...... Surely, if it's a double socket (still permitted I beleive) then that could potentially be 2 x 13A if the spur is unfused. Also, in the case the OP quoted, the main problem he has is he doesn't know what or how many outlets he has on the cable. |
#10
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
wrote in message oups.com... John Rumm wrote: wrote: snip With a spur (from a ring) or the particular setup described by the OP there is only one outlet and this is fused. Hence it is not possible to load the cable beyond what the 13A fuse on the outlet will carry for a sustained period. Hmm, Thanks for that John, but...... Surely, if it's a double socket (still permitted I beleive) then that could potentially be 2 x 13A if the spur is unfused. You are correct. There may be 26 amps passing through the spur cable at maximum load. I am not sure what people will find to plug in to create such a load but where there will there is a way. Fortunately on many installations the 2.5 T&E is conveniently rated at 27 amps. Adam |
#11
Posted to uk.d-i-y
|
|||
|
|||
single 2.5mm wire in a 32A MCB
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Three way switches with 12/2 wire? | Home Repair | |||
Specific 555 circuit | Electronics | |||
Repairing Lightning Damaged Tv's | Electronics Repair | |||
Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem? | Home Repair | |||
How to reduce current on a cheapo mig welder? | Metalworking |