In a post to another news group about wiring a 3-way switch leg with a
GFCI someone mentioned that the reason the GFCI was tripping when the
light was lit via the 3-ways is because the return current for the
lighting circuit returned to the panel via the neutral of another
circuit. The fix was to ungather the neutral for the lighting circuit
and direct it back through the appropriate neutral. OK. Fair enough.

But there was also some discussion of having to unbundle the bare wire
ground for the lighting circuit for the lighting circuit from the
second circuit also. I surely don't understand why.

As that thread has died out and I'm not getting any more information
about this and as I still need to complete that repair I thought I'd
ask here about the unbundling or ungathering of the bare neutral
wires. Why would it be necessary to have the ground wire grounded to
it's own circuit rather than through a second circuit. I've seen
bundled grounds all over the house even when there is more than one
circuit in the box.

Thanks

David
  #2   Report Post  
The Masked Marvel
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

Yes, unbundle the bare grounding wire from the neutral (white) wire!
While the neutral is grounded, it should be grounded (connected to the same
bus bar) ONLY at the main service panel for the building per the National
Electric Code. After that point they should always be seperate (even there
is (virtually) no voltage differance between them). The neutral is a curent
carrying conductor, the bare or green grounding wire normally is not -- only
when a fault occurs does it carry current, and on a circuit w/ a GFCI the
GFCI will see that the neutral is not carrying the current it should and
trip. In any case it is desirted (required to keep then seperated except for
the one point at the service enterance.

Further questions or clarifications on grounding, neutrals, 3 ways, GFCI's,
other?

"David W. Walters" wrote in message
om...
In a post to another news group about wiring a 3-way switch leg with a
GFCI someone mentioned that the reason the GFCI was tripping when the
light was lit via the 3-ways is because the return current for the
lighting circuit returned to the panel via the neutral of another
circuit. The fix was to ungather the neutral for the lighting circuit
and direct it back through the appropriate neutral. OK. Fair enough.

But there was also some discussion of having to unbundle the bare wire
ground for the lighting circuit for the lighting circuit from the
second circuit also. I surely don't understand why.

As that thread has died out and I'm not getting any more information
about this and as I still need to complete that repair I thought I'd
ask here about the unbundling or ungathering of the bare neutral
wires. Why would it be necessary to have the ground wire grounded to
it's own circuit rather than through a second circuit. I've seen
bundled grounds all over the house even when there is more than one
circuit in the box.

Thanks

David



  #3   Report Post  
zxcvbob
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

I think he's talking about 2 different circuits run in the same raceway
sharing a ground wire. I don't see anything wrong with it -- especially
if they are already sharing a neutral wire.

120v GFCI's are oblivous to the ground wire (I *think* 240v GFCI's are
oblivious to it also.) They only measure the difference between the hot
and neutral wire. They should be grounded, like any other device with a
ground connection, but that's a totally separate issue.

-Bob

The Masked Marvel wrote:

Yes, unbundle the bare grounding wire from the neutral (white) wire!
While the neutral is grounded, it should be grounded (connected to the same
bus bar) ONLY at the main service panel for the building per the National
Electric Code. After that point they should always be seperate (even there
is (virtually) no voltage differance between them). The neutral is a curent
carrying conductor, the bare or green grounding wire normally is not -- only
when a fault occurs does it carry current, and on a circuit w/ a GFCI the
GFCI will see that the neutral is not carrying the current it should and
trip. In any case it is desirted (required to keep then seperated except for
the one point at the service enterance.

Further questions or clarifications on grounding, neutrals, 3 ways, GFCI's,
other?

"David W. Walters" wrote in message
om...

In a post to another news group about wiring a 3-way switch leg with a
GFCI someone mentioned that the reason the GFCI was tripping when the
light was lit via the 3-ways is because the return current for the
lighting circuit returned to the panel via the neutral of another
circuit. The fix was to ungather the neutral for the lighting circuit
and direct it back through the appropriate neutral. OK. Fair enough.

But there was also some discussion of having to unbundle the bare wire
ground for the lighting circuit for the lighting circuit from the
second circuit also. I surely don't understand why.

As that thread has died out and I'm not getting any more information
about this and as I still need to complete that repair I thought I'd
ask here about the unbundling or ungathering of the bare neutral
wires. Why would it be necessary to have the ground wire grounded to
it's own circuit rather than through a second circuit. I've seen
bundled grounds all over the house even when there is more than one
circuit in the box.

Thanks

David




  #4   Report Post  
Toller
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

99.99% of the time there is nothing wrong with it. However, there can be a
situation where you open the breaker, verify the circuit is dead, and then
find out there is voltage on the ground from the other circuit.
Unlikely, but possible.


  #5   Report Post  
Harry K
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

"Toller" wrote in message ...
99.99% of the time there is nothing wrong with it. However, there can be a
situation where you open the breaker, verify the circuit is dead, and then
find out there is voltage on the ground from the other circuit.
Unlikely, but possible.


Not at all unlikely. I found that out the hard way but getting
shocked off the white wire. Feed to outside yard light runs
underground and has common white with another underground feed to a
shed. Circuit is non fixable without replacing the underground feeds.
At leas now, every box the two circuits run through are prominently
marked warning anyone working in them to pull -both- breakers.

Harry K


  #6   Report Post  
Toller
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?


Not at all unlikely. I found that out the hard way but getting
shocked off the white wire. Feed to outside yard light runs
underground and has common white with another underground feed to a
shed. Circuit is non fixable without replacing the underground feeds.
At leas now, every box the two circuits run through are prominently
marked warning anyone working in them to pull -both- breakers.


Yes, it is unlikely; just not impossible as you found. Since the white it
grounded, it ought to be a great deal better ground than anyone touching it;
unless there is a problem, there should never be any voltage on it..

However, we are talking about the bare wire here, the grounding conductor.
Unless there is a problem there should never be any current on it, and
unless there is a second problem, there should never be any voltage on it.


  #7   Report Post  
The Masked Marvel
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

Two *differant* circuits with a common neutral (hot, neutral, hot) assuming
the two hots are opposite phases (240V between them) are fine -- in fact
superior to two seperate pairs of hot + neutral, as the neutral carries only
the *differance* in the current in the two hot legs, whereas two seperate
hot neutral pairs the neutral carries all the current in its hot pair. Also,
for a hot, neutral, hot set, as long as they are together, a single
bare/green ground should be fine.

The GFCI can work even w/ no ground, in fact is required for old work whare
no ground is available, the fault current can flow through *you*, through a
grounding wire, through spilled water, anything, and the GFCI will see that
the current coming to it does not equal the current leaving it and it will
trip.

If you had, hypothethicly, two GFCI circuits in a single square box, fed w/
three wires (+ ground) thone one one hot and the neutral, the other on the
other hot and the neutral each GFCI is unaware the other tis there or that
there is another phase anywhere in the world, its own j-box included, and
will trip as required or not, if not required. However if current is drawn
by both, th ereturn currents in thr neutral will be 180 degrees out of phase
and they will cancel each other, reducing the current in the neutral. The
GFCI doesn't see this or care though. In the case of a balanced load, say
two 150W, 120V light bulbs, one on each circuit you could cut the neutral
wire and nothing would happen as the current to the first bulb cancels the
current from the second bulb in the neutral wire, all th ecurrent comes in
one hot and out the other. The bulbs are effectively in series, each using
1/2 the 240V. HOWEVER if one burns out, or if one is a 15W and the other
still 150W then there is trouble, either no light at all, or the 15W bulb is
way too bright and the 150W way too dim. Now you NEED the neutral wire to
carry the differance in current and keep the midpoint between the two bulbs
at 120V with respect to the two hots.

*****
I'm not sure how the 3 way circuits come into this, though sonetimes there
are two (potentially) hot and a neutral wire (+ground) in a three way
circuit, but it is one circuit, not a pair of circuits as in the example
above, and only one of the two hot wires is live at a time --and only if
*both* switches have that one live hot wire connected to the load/lamp does
it light, if th eother switch is switched to the dead "hot" wire the lmp is
off. Only by switching it to the live one (or by switching the other switch
to change which is live) does the light light. Again there is only one
neutral (and it may not even be run to the switch's junction box), and it is
never switched, and there is only one grounding wire.

To further complicate life though, when the neutral is not run to a switch's
j-box the white wire in the cable is used instead as a part time live hot
lead. In this case it should be permanantly recolored black, red, blue, etc.
not white or light gray and not green, since it is NOT neutral.



"zxcvbob" wrote in message
...
I think he's talking about 2 different circuits run in the same raceway
sharing a ground wire. I don't see anything wrong with it -- especially
if they are already sharing a neutral wire.

120v GFCI's are oblivous to the ground wire (I *think* 240v GFCI's are
oblivious to it also.) They only measure the difference between the hot
and neutral wire. They should be grounded, like any other device with a
ground connection, but that's a totally separate issue.

-Bob

The Masked Marvel wrote:

Yes, unbundle the bare grounding wire from the neutral (white) wire!
While the neutral is grounded, it should be grounded (connected to the

same
bus bar) ONLY at the main service panel for the building per the

National
Electric Code. After that point they should always be seperate (even

there
is (virtually) no voltage differance between them). The neutral is a

curent
carrying conductor, the bare or green grounding wire normally is not --

only
when a fault occurs does it carry current, and on a circuit w/ a GFCI

the
GFCI will see that the neutral is not carrying the current it should and
trip. In any case it is desirted (required to keep then seperated except

for
the one point at the service enterance.

Further questions or clarifications on grounding, neutrals, 3 ways,

GFCI's,
other?

"David W. Walters" wrote in message
om...

In a post to another news group about wiring a 3-way switch leg with a
GFCI someone mentioned that the reason the GFCI was tripping when the
light was lit via the 3-ways is because the return current for the
lighting circuit returned to the panel via the neutral of another
circuit. The fix was to ungather the neutral for the lighting circuit
and direct it back through the appropriate neutral. OK. Fair enough.

But there was also some discussion of having to unbundle the bare wire
ground for the lighting circuit for the lighting circuit from the
second circuit also. I surely don't understand why.

As that thread has died out and I'm not getting any more information
about this and as I still need to complete that repair I thought I'd
ask here about the unbundling or ungathering of the bare neutral
wires. Why would it be necessary to have the ground wire grounded to
it's own circuit rather than through a second circuit. I've seen
bundled grounds all over the house even when there is more than one
circuit in the box.

Thanks

David






  #8   Report Post  
Toller
 
Posts: n/a
Default Two Circuits, Neutrals and Bare Wire Grounds Gathered, Problem?

Giving it a bit more thought; grounds are crossed all the time. If you have
a metal box with two outlets on different circuits, the grounds are crossed
through the grounding straps.
However there are then TWO grounded conductors, so it is actually safer than
if they were not crossed. If there was only one, then they would be more
dangerous, though only nomially.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
240 volt wiring Charles Home Repair 11 December 30th 03 11:13 PM


All times are GMT +1. The time now is 04:50 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"