On Wed, 22 Feb 2006, wrote:

With a spur (from a ring) or the particular setup described by the OP
there is only one outlet and this is fused. Hence it is not possible to
load the cable beyond what the 13A fuse on the outlet will carry for a
sustained period.


Surely, if it's a double socket (still permitted I beleive) then that
could potentially be 2 x 13A if the spur is unfused.


Strangely enough, a double socket is only required to be designed to take
a total of (IIRC) 20 A. But yes, theoretically it could be loaded up to 26
A (or more - a BS 1362 13 A fuse will carry more than 13 A for quite some
time).

This is just about fine on a 2.5 mm2 T&E radial provided the cable isn't
buried in insulation etc etc, but definitely not recommended to run that
kind of load for an extended period, even on a double socket on a ring
main or 4 mm2 radial.

--