My builder states he will be using 8 inches of "rockwool" type insulation -
four inches running with the beams four running over.

I had thought it was good practice to

a: Cleat the cable to the ceiling joists for support, and
b. Ensure the cable runs over the insulation to prevent overheating of the
cable (related to fault current calculations).

In my situation above the two (a and b) seem to be contradictory as four
inches of insulation will be over all the joists. What do you guys do in
this situation???????

Many thanks for all your help

Laurie





  #2   Report Post  
Andy Hall
 
Posts: n/a
Default Electrical wire over or under loft insulation??????? Please help!

On Sun, 24 Aug 2003 21:21:38 +0100, "Laurie"
wrote:

My builder states he will be using 8 inches of "rockwool" type insulation -
four inches running with the beams four running over.

I had thought it was good practice to

a: Cleat the cable to the ceiling joists for support, and
b. Ensure the cable runs over the insulation to prevent overheating of the
cable (related to fault current calculations).

In my situation above the two (a and b) seem to be contradictory as four
inches of insulation will be over all the joists. What do you guys do in
this situation???????

Many thanks for all your help

Laurie



You can actually achieve both scenarios quite easily.

It is reasonable to clip the cables to the ceiling joists, the
important thing is to size the cable adequately for the load.

For the most part, cabling in a roof space will be for a lighting
circuit; however watch out in case power ring circuit, immersion
heater or electric shower circuits run through the space.

A good book for working this all out is the Electrician's Guide to the
16th Edition of the Wiring Regulations by Whitfield.

It's worth buying, although conveniently almost all of it is
reproduced on TLC's web site in the technical section.

www.tlc-direct.co.uk

If you refer to Chapter 4, all is revealed. There are tables of
current carring capacity for various scenarios, including insulation
around the cable.

The worked example 4.1 covers the deratings for insulation and high
ambient temperature in a loft for an immersion heater cable. You can
easily adapt it for other types of circuit.

I suspect that most electricians would just ignore all of this and
just go ahead and run 1.0 or 1.5 sqmm cable for lighting anyway, but
it is a good idea to check.




..andy

To email, substitute .nospam with .gl
  #3   Report Post  
Martin Angove
 
Posts: n/a
Default Electrical wire over or under loft insulation??????? Please help!

In message ,
"Laurie" wrote:

My builder states he will be using 8 inches of "rockwool" type insulation -
four inches running with the beams four running over.

I had thought it was good practice to

a: Cleat the cable to the ceiling joists for support, and
b. Ensure the cable runs over the insulation to prevent overheating of the
cable (related to fault current calculations).

In my situation above the two (a and b) seem to be contradictory as four
inches of insulation will be over all the joists. What do you guys do in
this situation???????


You would have problems if you put the cables on top of the first layer
and then put another layer on top of that, but if you go for option a:
you should be ok. Personally I'd tack the cable to one side of the
joists rather than on top, just in case I wanted to put some boarding
down at a later stage.

As I understand the regulations, so long as the cables are "in contact
with a thermally conducting surface on one side" you can cover the rest
in insulation and then apply the deratings as in table 4D5A (regs) or 6F
(On Site Guide). For the purpose of the regulations, the wood of the
joists should be sufficiently conductive (see regulations table 4A1,
note following method 4) supposing that the ceiling side is just a
layer of plasterboard or similar.

If you've followed all that you'll be pleased to hear that 1mm cable
commonly used for lighting and usually fused at 6A is rated to be able
to carry 12A under these conditions, and for all normal purposes should
be fine - when normal loads are connected there's plenty of "headroom"
and under large overloads (such as the "shorts" experienced when some
types of bulbs blow) an MCB will cut the power well before the cable is
damaged.

On the other hand, from my reading of fig. 3.4 in the regulations, it
might take 3 minutes for a type B MCB to trip if you or someone
else should happen to install enough lamps to take 12A (that's nearly
3kW of lighting). There's probably someone else here who can tell you
what 3 minutes at 12A will do to 1mm cable under such circumstances.
It's not very likely to happen, and you may not consider it neccessary
to design for the situation.

I'd probably play it safe though and install 1.5mm instead, fused at 6A.
This cable is hardly any more expensive and can carry 15A under the
circumstances described. 15A should trip a 6A MCB in well under a
minute.

No doubt if there's something glaringly obviously wrong in the above (I
don't *think* there is) someone will correct me, so perhaps you'd better
wait a day or two before acting on my advice!

Hwyl!

M.

--
Martin Angove: http://www.tridwr.demon.co.uk/
Don't fight technology, live with it: http://www.livtech.co.uk/
.... Please Tell Me if you Don't Get This Message
  #4   Report Post  
Laurie
 
Posts: n/a
Default Electrical wire over or under loft insulation??????? Please help!

Wow,

Thank you both for your answers, the roof space in question is only ever
going to carry lighting and the max loading at present is 800w therefore
3and a bit Amps max under normal conditions, so will apply regs/OSG as
suggested, but expect you are both right and I can put cables under
insulation. Will probably tack to side of joists as well.

Happiness is a bank holiday spent wiring!!!!!

Laurie


"Martin Angove" wrote in message
...
In message ,
"Laurie" wrote:

My builder states he will be using 8 inches of "rockwool" type

insulation -
four inches running with the beams four running over.

I had thought it was good practice to

a: Cleat the cable to the ceiling joists for support, and
b. Ensure the cable runs over the insulation to prevent overheating of

the
cable (related to fault current calculations).

In my situation above the two (a and b) seem to be contradictory as four
inches of insulation will be over all the joists. What do you guys do in
this situation???????


You would have problems if you put the cables on top of the first layer
and then put another layer on top of that, but if you go for option a:
you should be ok. Personally I'd tack the cable to one side of the
joists rather than on top, just in case I wanted to put some boarding
down at a later stage.

As I understand the regulations, so long as the cables are "in contact
with a thermally conducting surface on one side" you can cover the rest
in insulation and then apply the deratings as in table 4D5A (regs) or 6F
(On Site Guide). For the purpose of the regulations, the wood of the
joists should be sufficiently conductive (see regulations table 4A1,
note following method 4) supposing that the ceiling side is just a
layer of plasterboard or similar.

If you've followed all that you'll be pleased to hear that 1mm cable
commonly used for lighting and usually fused at 6A is rated to be able
to carry 12A under these conditions, and for all normal purposes should
be fine - when normal loads are connected there's plenty of "headroom"
and under large overloads (such as the "shorts" experienced when some
types of bulbs blow) an MCB will cut the power well before the cable is
damaged.

On the other hand, from my reading of fig. 3.4 in the regulations, it
might take 3 minutes for a type B MCB to trip if you or someone
else should happen to install enough lamps to take 12A (that's nearly
3kW of lighting). There's probably someone else here who can tell you
what 3 minutes at 12A will do to 1mm cable under such circumstances.
It's not very likely to happen, and you may not consider it neccessary
to design for the situation.

I'd probably play it safe though and install 1.5mm instead, fused at 6A.
This cable is hardly any more expensive and can carry 15A under the
circumstances described. 15A should trip a 6A MCB in well under a
minute.

No doubt if there's something glaringly obviously wrong in the above (I
don't *think* there is) someone will correct me, so perhaps you'd better
wait a day or two before acting on my advice!

Hwyl!

M.

--
Martin Angove: http://www.tridwr.demon.co.uk/
Don't fight technology, live with it: http://www.livtech.co.uk/
... Please Tell Me if you Don't Get This Message



  #5   Report Post  
Conrad Edwards
 
Posts: n/a
Default Electrical wire over or under loft insulation??????? Please help!

"Laurie" wrote in message ...
Wow,

Thank you both for your answers, the roof space in question is only ever
going to carry lighting and the max loading at present is 800w therefore
3and a bit Amps max under normal conditions, so will apply regs/OSG as
suggested, but expect you are both right and I can put cables under
insulation. Will probably tack to side of joists as well.

Happiness is a bank holiday spent wiring!!!!!

Laurie



In my loft there wasn't too much cable leeway so I insulated between
the joists, then insulated over the top with a second layer leaving a
small channel for the cable runs to go along. Where there were
bathroom halogen lights, I left this bit uncovered. It's now pretty
obvious where the cable runs are if I need to trace one.


  #6   Report Post  
Laurie
 
Posts: n/a
Default Electrical wire over or under loft insulation??????? Please help!

Good idea, thanks

Laurie

"Conrad Edwards" wrote in message
m...
"Laurie" wrote in message

...
Wow,

Thank you both for your answers, the roof space in question is only ever
going to carry lighting and the max loading at present is 800w therefore
3and a bit Amps max under normal conditions, so will apply regs/OSG as
suggested, but expect you are both right and I can put cables under
insulation. Will probably tack to side of joists as well.

Happiness is a bank holiday spent wiring!!!!!

Laurie



In my loft there wasn't too much cable leeway so I insulated between
the joists, then insulated over the top with a second layer leaving a
small channel for the cable runs to go along. Where there were
bathroom halogen lights, I left this bit uncovered. It's now pretty
obvious where the cable runs are if I need to trace one.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Loft door hardware Andrew McKay UK diy 3 August 25th 03 12:50 AM
Power to loft. Spur of 60A shower feed? Will Cooke UK diy 1 August 5th 03 12:15 AM
Forthcoming Building Regulations on electrical work (Part P) Andrew McKay UK diy 42 July 30th 03 08:05 AM
Fitting A Loft Ladder Andrew McKay UK diy 4 July 14th 03 06:10 PM


All times are GMT +1. The time now is 05:40 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"