In message ,
"Laurie" wrote:

My builder states he will be using 8 inches of "rockwool" type insulation -
four inches running with the beams four running over.

I had thought it was good practice to

a: Cleat the cable to the ceiling joists for support, and
b. Ensure the cable runs over the insulation to prevent overheating of the
cable (related to fault current calculations).

In my situation above the two (a and b) seem to be contradictory as four
inches of insulation will be over all the joists. What do you guys do in
this situation???????


You would have problems if you put the cables on top of the first layer
and then put another layer on top of that, but if you go for option a:
you should be ok. Personally I'd tack the cable to one side of the
joists rather than on top, just in case I wanted to put some boarding
down at a later stage.

As I understand the regulations, so long as the cables are "in contact
with a thermally conducting surface on one side" you can cover the rest
in insulation and then apply the deratings as in table 4D5A (regs) or 6F
(On Site Guide). For the purpose of the regulations, the wood of the
joists should be sufficiently conductive (see regulations table 4A1,
note following method 4) supposing that the ceiling side is just a
layer of plasterboard or similar.

If you've followed all that you'll be pleased to hear that 1mm cable
commonly used for lighting and usually fused at 6A is rated to be able
to carry 12A under these conditions, and for all normal purposes should
be fine - when normal loads are connected there's plenty of "headroom"
and under large overloads (such as the "shorts" experienced when some
types of bulbs blow) an MCB will cut the power well before the cable is
damaged.

On the other hand, from my reading of fig. 3.4 in the regulations, it
might take 3 minutes for a type B MCB to trip if you or someone
else should happen to install enough lamps to take 12A (that's nearly
3kW of lighting). There's probably someone else here who can tell you
what 3 minutes at 12A will do to 1mm cable under such circumstances.
It's not very likely to happen, and you may not consider it neccessary
to design for the situation.

I'd probably play it safe though and install 1.5mm instead, fused at 6A.
This cable is hardly any more expensive and can carry 15A under the
circumstances described. 15A should trip a 6A MCB in well under a
minute.

No doubt if there's something glaringly obviously wrong in the above (I
don't *think* there is) someone will correct me, so perhaps you'd better
wait a day or two before acting on my advice!

Hwyl!

M.

--