Hi, I'm new here. Please excuse my ignorance as most of my adult life I have
lived in apartments and assisted living centers due to MS. Well, I was able
to get out of my wheelchair and got a grant to buy a house. Wow! what a
health benefit that has been. Question, My thermostat is a Honeywell (round,
heat only) 2 wire 24 volt, there is a sticker in there that says T87F1818 2
7921 and the furnace is a Luxaire model GSU082MF series NAGOE,(that could be
a Q) It's set up for propane. If I set the thermostat to say, 62º the
furnace will come on at 66º and shut off at 70º. Is this normal, or is it
time for a new thermostat. If time for a stat, are the programmable ones any
good?

Thank you

Stone
It's scary when you start making the same noises as your coffeemaker.


  #2   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


"Gary Stone" wrote in message
news
Hi, I'm new here. Please excuse my ignorance as most of my adult life I

have
lived in apartments and assisted living centers due to MS. Well, I was

able
to get out of my wheelchair and got a grant to buy a house. Wow! what a
health benefit that has been. Question, My thermostat is a Honeywell

(round,
heat only) 2 wire 24 volt, there is a sticker in there that says T87F1818

2
7921 and the furnace is a Luxaire model GSU082MF series NAGOE,(that could

be
a Q) It's set up for propane. If I set the thermostat to say, 62º the
furnace will come on at 66º and shut off at 70º. Is this normal, or is it
time for a new thermostat. If time for a stat, are the programmable ones

any
good?

Thank you

Stone
It's scary when you start making the same noises as your coffeemaker.



The T87F is the most popular and some argue, the best thermostat put out by
Honeywell, and with the right sub-base, can run a heat pump, electric heat,
oil..etc..
There is a normal 4F dead band in the stat, so your on at 66 and off at 70
is normal when set to 68F
you have one of two problems with the stat...one you can do, and one you
cant do...unless you have the right tool.

One, its not level. 99.9% of the time, thats the problem. level it and the
unit will work fine.
if its working as well in the dead band as you state, do NOT adjust the heat
anticipator unless after you level it, its overshooting by more than 2
degrees. then, the anticipator setting will be located on the gas valve on
the unit you have.


The second and least likely issue is that its out of calibration, and should
that be the case, you can buy a new one for less than what most will charge
for a calibration.

Digital stats are fine, as long as they dont say Lux, or Hunter on them.
Programmable....on a unit with no AC...up to you, but a waste really.

As far as that furnace goes, IF its the one that I find in my YorkNet
program, have it serviced by a licenced york, luxaire or coleman dealer and
it should go till it quits. Good units.


  #3   Report Post  
Gary Stone
 
Posts: n/a
Default


"Steve@carolinabreezehvac" wrote
in message ...

"Gary Stone" wrote in message
news
Hi, I'm new here. Please excuse my ignorance as most of my adult life I

have
lived in apartments and assisted living centers due to MS. Well, I was

able
to get out of my wheelchair and got a grant to buy a house. Wow! what a
health benefit that has been. Question, My thermostat is a Honeywell

(round,
heat only) 2 wire 24 volt, there is a sticker in there that says T87F1818

2
7921 and the furnace is a Luxaire model GSU082MF series NAGOE,(that could

be
a Q) It's set up for propane. If I set the thermostat to say, 62º the
furnace will come on at 66º and shut off at 70º. Is this normal, or is it
time for a new thermostat. If time for a stat, are the programmable ones

any
good?

Thank you

Stone
It's scary when you start making the same noises as your coffeemaker.



The T87F is the most popular and some argue, the best thermostat put out
by
Honeywell, and with the right sub-base, can run a heat pump, electric
heat,
oil..etc..
There is a normal 4F dead band in the stat, so your on at 66 and off at 70
is normal when set to 68F
you have one of two problems with the stat...one you can do, and one you
cant do...unless you have the right tool.

One, its not level. 99.9% of the time, thats the problem. level it and the
unit will work fine.
if its working as well in the dead band as you state, do NOT adjust the
heat
anticipator unless after you level it, its overshooting by more than 2
degrees. then, the anticipator setting will be located on the gas valve on
the unit you have.


The second and least likely issue is that its out of calibration, and
should
that be the case, you can buy a new one for less than what most will
charge
for a calibration.

Digital stats are fine, as long as they dont say Lux, or Hunter on them.
Programmable....on a unit with no AC...up to you, but a waste really.

As far as that furnace goes, IF its the one that I find in my YorkNet
program, have it serviced by a licenced york, luxaire or coleman dealer
and
it should go till it quits. Good units.

I had it checked out last fall, the guy doing the roof called the guy he
uses and he (heating contractor) said it was in great shape and had a newer
"Regulator?" in it. He didn't have to do much to it, just cleaned it up a
bit and only charged me $30.00. Question on leveling, I just took the
housing ring off it (stat) and the only way I see to check level is the top
2 (of 3) mounts for the housing ring, or is there a base plate I have to get
at behind there? If not, then it's slightly off level.

Stone


  #4   Report Post  
BGBevill
 
Posts: n/a
Default


I had it checked out last fall, the guy doing the roof called the guy he
uses and he (heating contractor) said it was in great shape and had a newer
"Regulator?" in it. He didn't have to do much to it, just cleaned it up a
bit and only charged me $30.00. Question on leveling, I just took the
housing ring off it (stat) and the only way I see to check level is the top
2 (of 3) mounts for the housing ring, or is there a base plate I have to get
at behind there? If not, then it's slightly off level.

Stone


I'm thinking once you get the ring off, there should be three screws holding
the stat to the base. Loosen those three screws until you can pull the stat
off the base. The base has two little pins across the top where you can lay a
little level. The screw holding it to the wall on the right should allow you
to loosen it and move it up or down as needed. Then put the stat back in
place, retighten the three screws and put the ring back. You should be good to
go.

Bobby


  #5   Report Post  
Gary Stone
 
Posts: n/a
Default

OK thanks, I figured there was probably something like that back there, but
thought I wait for response before proceeding.

Thanks

Stone

"BGBevill" wrote in message
...

I had it checked out last fall, the guy doing the roof called the guy he
uses and he (heating contractor) said it was in great shape and had a
newer
"Regulator?" in it. He didn't have to do much to it, just cleaned it up a
bit and only charged me $30.00. Question on leveling, I just took the
housing ring off it (stat) and the only way I see to check level is the
top
2 (of 3) mounts for the housing ring, or is there a base plate I have to
get
at behind there? If not, then it's slightly off level.

Stone


I'm thinking once you get the ring off, there should be three screws
holding
the stat to the base. Loosen those three screws until you can pull the
stat
off the base. The base has two little pins across the top where you can
lay a
little level. The screw holding it to the wall on the right should allow
you
to loosen it and move it up or down as needed. Then put the stat back in
place, retighten the three screws and put the ring back. You should be
good to
go.

Bobby






  #6   Report Post  
 
Posts: n/a
Default

Why anyone would fool around with an old mechanical thermost which when
set for 62 gives a temp that varies from 66 to 70 or pay someone $30 to
come look at it is beyond me. For a little more you can buy a nice
accurate and programmable digital one that's very simple to install.

  #7   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


wrote in message
oups.com...
Why anyone would fool around with an old mechanical thermost which when
set for 62 gives a temp that varies from 66 to 70 or pay someone $30 to
come look at it is beyond me. For a little more you can buy a nice
accurate and programmable digital one that's very simple to install.


Because the T87F will be working long after the digital has fried itself.
Read the replies, and also, a digital that is supposed to be accurate to 1F,
will also have a dead band in it, and will also have to have the
anticipation set in many cases, or will perform worse than the T87...thats
why.

  #8   Report Post  
69Rocketman
 
Posts: n/a
Default

What is the particular problem with the Hunter T-stats? I've had a couple of
them now. (one in each house I've owned) never seemed to be a problem. But I
am not a furnace/heating guy either.

Duane


"Steve@carolinabreezehvac" wrote
in message ...

"Gary Stone" wrote in message
news
Hi, I'm new here. Please excuse my ignorance as most of my adult life I

have
lived in apartments and assisted living centers due to MS. Well, I was

able
to get out of my wheelchair and got a grant to buy a house. Wow! what a
health benefit that has been. Question, My thermostat is a Honeywell

(round,
heat only) 2 wire 24 volt, there is a sticker in there that says

T87F1818
2
7921 and the furnace is a Luxaire model GSU082MF series NAGOE,(that

could
be
a Q) It's set up for propane. If I set the thermostat to say, 62º the
furnace will come on at 66º and shut off at 70º. Is this normal, or is

it
time for a new thermostat. If time for a stat, are the programmable ones

any
good?

Thank you

Stone
It's scary when you start making the same noises as your coffeemaker.



The T87F is the most popular and some argue, the best thermostat put out

by
Honeywell, and with the right sub-base, can run a heat pump, electric

heat,
oil..etc..
There is a normal 4F dead band in the stat, so your on at 66 and off at 70
is normal when set to 68F
you have one of two problems with the stat...one you can do, and one you
cant do...unless you have the right tool.

One, its not level. 99.9% of the time, thats the problem. level it and the
unit will work fine.
if its working as well in the dead band as you state, do NOT adjust the

heat
anticipator unless after you level it, its overshooting by more than 2
degrees. then, the anticipator setting will be located on the gas valve on


the unit you have.


The second and least likely issue is that its out of calibration, and

should
that be the case, you can buy a new one for less than what most will

charge
for a calibration.

Digital stats are fine, as long as they dont say Lux, or Hunter on them.
Programmable....on a unit with no AC...up to you, but a waste really.

As far as that furnace goes, IF its the one that I find in my YorkNet
program, have it serviced by a licenced york, luxaire or coleman dealer

and
it should go till it quits. Good units.




  #9   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


"69Rocketman" wrote in message
...
What is the particular problem with the Hunter T-stats? I've had a couple

of
them now. (one in each house I've owned) never seemed to be a problem. But

I
am not a furnace/heating guy either.

Duane


Hunter and Lux, both made in China, along with the new line found at Home
Depot, that appears to be a Lux sub, historically have been crap in the
sense that they work fine, and then one day, they either go into a runaway
heating cycle that never quits, or fail completely.
I have had customers that had one or both in the homes and they worked fine.
With any brand, you will get a few bad ones...but, the two mentioned here
have a much higher failure rate than the larger name brands such as
Honeywell, or Robershaw...and as someone that gets to go diagnose and repair
problems ona daily basis, I can tell you that we pull these unit off the
wall, more than we would like.

I know and have customers that have Goodman units that are 15 years old and
still running, but I damn sure wont have one on my home either.

"Steve@carolinabreezehvac" wrote
in message ...

"Gary Stone" wrote in message
news
Hi, I'm new here. Please excuse my ignorance as most of my adult life

I
have
lived in apartments and assisted living centers due to MS. Well, I was

able
to get out of my wheelchair and got a grant to buy a house. Wow! what

a
health benefit that has been. Question, My thermostat is a Honeywell

(round,
heat only) 2 wire 24 volt, there is a sticker in there that says

T87F1818
2
7921 and the furnace is a Luxaire model GSU082MF series NAGOE,(that

could
be
a Q) It's set up for propane. If I set the thermostat to say, 62º the
furnace will come on at 66º and shut off at 70º. Is this normal, or is

it
time for a new thermostat. If time for a stat, are the programmable

ones
any
good?

Thank you

Stone
It's scary when you start making the same noises as your coffeemaker.



The T87F is the most popular and some argue, the best thermostat put out

by
Honeywell, and with the right sub-base, can run a heat pump, electric

heat,
oil..etc..
There is a normal 4F dead band in the stat, so your on at 66 and off at

70
is normal when set to 68F
you have one of two problems with the stat...one you can do, and one you
cant do...unless you have the right tool.

One, its not level. 99.9% of the time, thats the problem. level it and

the
unit will work fine.
if its working as well in the dead band as you state, do NOT adjust the

heat
anticipator unless after you level it, its overshooting by more than 2
degrees. then, the anticipator setting will be located on the gas valve

on

the unit you have.


The second and least likely issue is that its out of calibration, and

should
that be the case, you can buy a new one for less than what most will

charge
for a calibration.

Digital stats are fine, as long as they dont say Lux, or Hunter on them.
Programmable....on a unit with no AC...up to you, but a waste really.

As far as that furnace goes, IF its the one that I find in my YorkNet
program, have it serviced by a licenced york, luxaire or coleman dealer

and
it should go till it quits. Good units.





  #10   Report Post  
m Ransley
 
Posts: n/a
Default

I have 2 relatively new Lux thermostats and have found the dial-option
switch so cheap it often wont engage unless I tap it, and the heat
anticipator lacking in operational comfort compared to a quality
Honywell Sure allot of features cheap, that is why I bought it,
features. I have a round Honywell also, it is one I know will never
fail, thats why it may be the longest produced thermostat on the
market, they work. On mine I have calibrated it with the wrench that
used to be supplied, it adjusts thermometer temp to the thermostat .
If it works adjust it and keep it.



  #11   Report Post  
Decency Advocate
 
Posts: n/a
Default

'If I set the thermostat to say, 62=BA the furnace will come on at 66=BA
and shut off at 70=BA. Is this normal, or is it time for a new
thermostat. If time for a stat, are the programmable ones any good?'

Either the thermometer portion of the thermostat is off, or, the
bimetal portion of the thermostat is out of calibration. Usually, either
can be adjusted. If you want very accurate precise control , then opt
for a programmable electronic one ; these will provide accurate cycling
of your furnace beyond what a bimetalic thermostat can. If you want a
cheap one, go to Home DePot or Menards. If you want a better one, go to
a hvac dealer in your locale.

  #12   Report Post  
U will be assimilated
 
Posts: n/a
Default

So dave the HVAC hack has decided to add a new nic to his very long
list of names he hides behind...

WHERE'S THE PROOF? ya lying internet FUICKHEAD

  #13   Report Post  
Goedjn
 
Posts: n/a
Default



Why anyone would fool around with an old mechanical thermost which when
set for 62 gives a temp that varies from 66 to 70 or pay someone $30 to
come look at it is beyond me. For a little more you can buy a nice
accurate and programmable digital one that's very simple to install.


I don't understand why OP cares, anyway. You set the thermostat
(during the heating season) to the lowest value that you're
comfortable in. Who gives a **** what that temperature is labled, on
the dial?


  #14   Report Post  
m Ransley
 
Posts: n/a
Default

Wrong again DaveDaveDave, My Lux digital super duper crapstat does not
have the incremental adjustments enjoyed on my honywell round . A
reason the Honeywell round has been around forever, reliability,and
accuracy.
I bet you recommend Lux or Hunter as you recommend Goodman. Of course,
then you have guarnteed a built in customer repair base for future
income.

  #15   Report Post  
Gary Stone
 
Posts: n/a
Default


wrote in message
oups.com...
Why anyone would fool around with an old mechanical thermost which when
set for 62 gives a temp that varies from 66 to 70 or pay someone $30 to
come look at it is beyond me. For a little more you can buy a nice
accurate and programmable digital one that's very simple to install.


That was last fall, the 30 bucks was for the service of checking out the
furnace to make sure it was ok as I had just moved in. That was in reference
to the furnace not the thermostat. That should have been clear from the
post.

Stone




  #16   Report Post  
Gary Stone
 
Posts: n/a
Default


"Goedjn" wrote in message
...


Why anyone would fool around with an old mechanical thermost which when
set for 62 gives a temp that varies from 66 to 70 or pay someone $30 to
come look at it is beyond me. For a little more you can buy a nice
accurate and programmable digital one that's very simple to install.


I don't understand why OP cares, anyway. You set the thermostat
(during the heating season) to the lowest value that you're
comfortable in. Who gives a **** what that temperature is labled, on
the dial?

Touché, got us there. Good one.

Stone


  #17   Report Post  
Steve@carolinabreezehvac
 
Posts: n/a
Default


"Decency Advocate" wrote in message
...
'If I set the thermostat to say, 62º the furnace will come on at 66º
and shut off at 70º. Is this normal, or is it time for a new
thermostat. If time for a stat, are the programmable ones any good?'

Either the thermometer portion of the thermostat is off, or, the
bimetal portion of the thermostat is out of calibration. Usually, either
can be adjusted. If you want very accurate precise control , then opt
for a programmable electronic one ; these will provide accurate cycling
of your furnace beyond what a bimetalic thermostat can. If you want a
cheap one, go to Home DePot or Menards. If you want a better one, go to
a hvac dealer in your locale.


You are a total, and complete idiot Dave.

You dont even know simple things about the most common stat in the world,
the T87F.
I have guys that I hired that knew that the first week in tech school about
the T87F as thats the stat they start on....dead band and all.

Just curious Davey....since Home Depot for example, wants over $40 now for a
T87F, and the charge that most companies charge for a calibration
only.....is over $70....what makes more sense? A new stat or calibration?

And if he wants a decent digital stat, hell..I can get him a Robertshaw for
less.....

Can you?

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Thermostat question HvacTech2 Home Repair 11 August 31st 04 08:32 PM
Looking for Programable Digital Thermostat w/ short remote probe Bill Velek Electronics Repair 4 August 9th 04 06:03 PM
replaced thermostat, EM/Aux always on. Giles Harney Home Ownership 0 January 19th 04 08:40 PM
Installing boiler thermostat question David Hearn UK diy 5 December 3rd 03 09:03 PM
Thermostat Location Matt Oliverius Home Repair 1 November 7th 03 02:47 AM


All times are GMT +1. The time now is 05:45 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"