  #1   Report Post  
jay
 
Posts: n/a
Default Bathroom exhausts sharing single duct?!

I just hired my condo management company (a job performed, at my request,
for my unit only, at my own expense, which was almost $300 after tax) to
extend the two upstairs bathroom exhausts so that they exhaust to the
exterior (through the side) of the unit. (These bathroom exhausts were
previously vented directly into the attic before which had been damaging the
roof's sheathing)

I was not expecting it to be done this way, but the two exhausts are very
close in proximity to each other, and the person who did the work decided to
use a shared vent for both exhausts. In other words, what he did was
connect a flexible aluminum duct to each vent, and then used some type of
"T - connector" to join the two ducts together so they are both sharing the
same shared flexible aluminum duct that leads to the exterior the unit.

I happened to notice that when one of the two fans is running, it actually
causes some air flow to be exhausted out of the other bathroom's idle fan.
If the fan in the main bath is running in the main bathroom, I can actually
observe the blades of the fan in the master bath start to spin. Clearly air
is being pushed from the main bath into the master bath when this happens.
If I briefly turn on the master bath's fan and shut it off I can observe it
switch direction after it stops turning in the normal direction.

In the opposite situation (master bath's fan running when the main bath is
idle), the problem, to me, seems like it could be less severe. The blades
do not move in the main bath's fan. There does seem to be a little bit of
air flow though the fan opening, but I suspect not as much as in the
previously described situation.

Anyway, I just want to get opinions on whether or not this is worth
complaining about, or am I just being too picky? It seems to me that if
running one fan causes air to be pushed out of the other fan, this will,
most likely, cause some mosture to be transerred into the other bath (how
much I don't yet know) rather than the exterior. This seems like a less
than ideal setup.

Is this type of shared vent setup for bathroom exhausts considered to be
normal/common?

Which of the following do you recommend:

1) Immediately complain about this to the management company tomorrow, since
clearly there is a problem with the duct setup chosen for this job

OR

2) should I perform a test to see how much steam actually gets into the
master bath when the main bath's fan is running (while showering in the main
bath) BEFORE complaining about this?

OR

3) Do nothing, since this is a common setup, and likely not worth
complaining about.

Let me know what you think.

Thanks,

J.




  #2   Report Post  
jay
 
Posts: n/a
Default

Clearly air is being pushed from the main bath into the master bath when
this happens.
If I briefly turn on the master bath's fan and shut it off I can observe it
switch direction after it stops turning in the normal direction.

In other words, if just the main bath's fan is currently turned on, I can
actually see the blades of the master bath's fan spin as the result of air
being pushed from the main bath's fan through the master bath's idle fan.
If I then briefly turn on the master bath's fan for 5 seconds, the motor of
the master bath's fan will wind down after being shut off, but then the
blades will start spinning in the opposite direction since the main bath's
fan is exhausting air in the direction of the master bath's fan.

J.


  #3   Report Post  
Speedy Jim
 
Posts: n/a
Default

jay wrote:
I just hired my condo management company (a job performed, at my request,
for my unit only, at my own expense, which was almost $300 after tax) to
extend the two upstairs bathroom exhausts so that they exhaust to the
exterior (through the side) of the unit. (These bathroom exhausts were
previously vented directly into the attic before which had been damaging the
roof's sheathing)

I was not expecting it to be done this way, but the two exhausts are very
close in proximity to each other, and the person who did the work decided to
use a shared vent for both exhausts. In other words, what he did was
connect a flexible aluminum duct to each vent, and then used some type of
"T - connector" to join the two ducts together so they are both sharing the
same shared flexible aluminum duct that leads to the exterior the unit.

I happened to notice that when one of the two fans is running, it actually
causes some air flow to be exhausted out of the other bathroom's idle fan.
If the fan in the main bath is running in the main bathroom, I can actually
observe the blades of the fan in the master bath start to spin. Clearly air
is being pushed from the main bath into the master bath when this happens.
If I briefly turn on the master bath's fan and shut it off I can observe it
switch direction after it stops turning in the normal direction.

In the opposite situation (master bath's fan running when the main bath is
idle), the problem, to me, seems like it could be less severe. The blades
do not move in the main bath's fan. There does seem to be a little bit of
air flow though the fan opening, but I suspect not as much as in the
previously described situation.

Anyway, I just want to get opinions on whether or not this is worth
complaining about, or am I just being too picky? It seems to me that if
running one fan causes air to be pushed out of the other fan, this will,
most likely, cause some mosture to be transerred into the other bath (how
much I don't yet know) rather than the exterior. This seems like a less
than ideal setup.

Is this type of shared vent setup for bathroom exhausts considered to be
normal/common?

Which of the following do you recommend:

1) Immediately complain about this to the management company tomorrow, since
clearly there is a problem with the duct setup chosen for this job

OR

2) should I perform a test to see how much steam actually gets into the
master bath when the main bath's fan is running (while showering in the main
bath) BEFORE complaining about this?

OR

3) Do nothing, since this is a common setup, and likely not worth
complaining about.

Let me know what you think.

Thanks,

J.




It is not a common setup and may be prohibited.
It *is* done though but the results are unpredictable.
Each fan normally has some kind of "flapper" valve
inside to prevent backdrafting. You could see if
that is present and working.

In the end, I suspect that it won't be a big problem;
see what your "steam test" shows.

But you paid for it; it's your call...

Jim
  #4   Report Post  
MUADIB®
 
Posts: n/a
Default

There's your answer...............let 'em know it's not satisfactory.
Give 'em a chance to fix it, or charge them back for the work they
originally did if they won't do anything about it.
Be nice to them, and they will reciprocate usually. Just use some tact
(of which I am learning I have none apparently..LOL ) and things will
work out.

1) Immediately complain about this to the management company tomorrow, since
clearly there is a problem with the duct setup chosen for this job




Remove "YOURPANTIES" to reply

MUADIB®

http://www.angelfire.com/retro/sster...IN%20PAGE.html

one small step for man,.....
One giant leap for attorneys.
  #5   Report Post  
jay
 
Posts: n/a
Default

It is not a common setup and may be prohibited.
It *is* done though but the results are unpredictable.
Each fan normally has some kind of "flapper" valve
inside to prevent backdrafting. You could see if
that is present and working.

Thanks. Will look into this. Most likely there is no flapper. These are
Broan fans if that means anything to you. Perhaps, the flapper, if present,
doesn't work as well for the master bath's fan because it is mounted
sideways in a skylight's opening, rather than on the ceiling. It could be
that, when idle, the flow from the 2nd fan, although powerful enough to make
the blades spin, still isn't powerful enough to close the flapper, but I'd
bet that the flapper is just absent. Will see what I can find.

In the end, I suspect that it won't be a big problem;
see what your "steam test" shows.

But you paid for it; it's your call...

Thanks. I will see what happens with the steam test. By the way, cross
flow from the active to the idle fan, although it obviously exists, seems
relatively weak when I hold my hand near the idle fan. I will try the steam
test and see if this issue really is a problem or not.

By the way, even though I just spent close to $300 extending the exhausts,
I'm skeptical that these fans, even when properly installed, really help
that much. These Broan fans, even though they SOUND like they work, each
can BARELY cause a sheet or two of toilet paper to defy gravity if I place a
piece or two across the opening. In other words, I'm skeptical that these
fans really suck enough air to get rid of anywhere near ALL the excess
moisture/humidity when taking a shower. Perhaps it's only 25% of the excess
moisture/humidity tops.

Jeff




  #6   Report Post  
Art
 
Posts: n/a
Default

I'm surprised it damaged the sheathing. I found in my previous house that
they were just dumping into the attic for many years with no apparent
damage. Your attic probably has inadequate ventilation. Fans are available
in different sizes but some require bigger duct work which you probably
don't want to change now. You might be better off just hooking a timer
switch in so the fan stays on 15 minutes after your shower is done and then
turns off automatically. They sell fan timers where they sell the fans.


"jay" wrote in message
news:_ADJd.20374$rs2.6071@trndny07...
It is not a common setup and may be prohibited.
It *is* done though but the results are unpredictable.
Each fan normally has some kind of "flapper" valve
inside to prevent backdrafting. You could see if
that is present and working.

Thanks. Will look into this. Most likely there is no flapper. These are
Broan fans if that means anything to you. Perhaps, the flapper, if
present, doesn't work as well for the master bath's fan because it is
mounted sideways in a skylight's opening, rather than on the ceiling. It
could be that, when idle, the flow from the 2nd fan, although powerful
enough to make the blades spin, still isn't powerful enough to close the
flapper, but I'd bet that the flapper is just absent. Will see what I can
find.

In the end, I suspect that it won't be a big problem;
see what your "steam test" shows.

But you paid for it; it's your call...

Thanks. I will see what happens with the steam test. By the way, cross
flow from the active to the idle fan, although it obviously exists, seems
relatively weak when I hold my hand near the idle fan. I will try the
steam test and see if this issue really is a problem or not.

By the way, even though I just spent close to $300 extending the exhausts,
I'm skeptical that these fans, even when properly installed, really help
that much. These Broan fans, even though they SOUND like they work, each
can BARELY cause a sheet or two of toilet paper to defy gravity if I place
a piece or two across the opening. In other words, I'm skeptical that
these fans really suck enough air to get rid of anywhere near ALL the
excess moisture/humidity when taking a shower. Perhaps it's only 25% of
the excess moisture/humidity tops.

Jeff



  #7   Report Post  
twfsa
 
Posts: n/a
Default

I would complain about the ducting of two fans into one. If some one stinks
up one room it spreads to the other room.

I replaced the fan in my main bath with a Nautilus 130 CFM from a 50CFM day
and night difference, there is actually a un-comfortable draft in the room,
when drying off after a shower.I don't think you could stand the water temp
to be up high enough to steam up the room during a shower.When the fan is on
and the door is partially shut, the fan pulls the door open a bit.

Tom


"jay" wrote in message
news:qlCJd.19345$Vx2.18165@trndny01...
I just hired my condo management company (a job performed, at my request,
for my unit only, at my own expense, which was almost $300 after tax) to
extend the two upstairs bathroom exhausts so that they exhaust to the
exterior (through the side) of the unit. (These bathroom exhausts were
previously vented directly into the attic before which had been damaging
the roof's sheathing)

I was not expecting it to be done this way, but the two exhausts are very
close in proximity to each other, and the person who did the work decided
to use a shared vent for both exhausts. In other words, what he did was
connect a flexible aluminum duct to each vent, and then used some type of
"T - connector" to join the two ducts together so they are both sharing
the same shared flexible aluminum duct that leads to the exterior the
unit.

I happened to notice that when one of the two fans is running, it actually
causes some air flow to be exhausted out of the other bathroom's idle fan.
If the fan in the main bath is running in the main bathroom, I can
actually observe the blades of the fan in the master bath start to spin.
Clearly air is being pushed from the main bath into the master bath when
this happens. If I briefly turn on the master bath's fan and shut it off I
can observe it switch direction after it stops turning in the normal
direction.

In the opposite situation (master bath's fan running when the main bath is
idle), the problem, to me, seems like it could be less severe. The blades
do not move in the main bath's fan. There does seem to be a little bit of
air flow though the fan opening, but I suspect not as much as in the
previously described situation.

Anyway, I just want to get opinions on whether or not this is worth
complaining about, or am I just being too picky? It seems to me that if
running one fan causes air to be pushed out of the other fan, this will,
most likely, cause some mosture to be transerred into the other bath (how
much I don't yet know) rather than the exterior. This seems like a less
than ideal setup.

Is this type of shared vent setup for bathroom exhausts considered to be
normal/common?

Which of the following do you recommend:

1) Immediately complain about this to the management company tomorrow,
since clearly there is a problem with the duct setup chosen for this job

OR

2) should I perform a test to see how much steam actually gets into the
master bath when the main bath's fan is running (while showering in the
main bath) BEFORE complaining about this?

OR

3) Do nothing, since this is a common setup, and likely not worth
complaining about.

Let me know what you think.

Thanks,

J.






  #8   Report Post  
Joseph Meehan
 
Posts: n/a
Default

Art wrote:
I'm surprised it damaged the sheathing. I found in my previous house
that they were just dumping into the attic for many years with no
apparent damage. Your attic probably has inadequate ventilation. Fans are
available in different sizes but some require bigger duct
work which you probably don't want to change now. You might be
better off just hooking a timer switch in so the fan stays on 15
minutes after your shower is done and then turns off automatically. They
sell fan timers where they sell the fans.


It does not always do damage, but it does often enough that I would not
allow it in my home. It is very poor work in my opinion. I am glad you
have not had any problems.

You are right about the possibility or marginal ventilation. Of course
it may have been only be marginal because of the bath vents.



--
Joseph Meehan

26 + 6 = 1 It's Irish Math


  #9   Report Post  
Andy Hill
 
Posts: n/a
Default

While it's not a case of out-and-out incompetent installation (unlike the
original "vent into attic" setup), it wouldn't be my first choice. Some
folks prefer to minimize the number of holes in their roof, 'tho.

Personally, I'd probably just pull down the fan unit that is getting spun by the
air current, and put a flapper inline with the outlet (many already have such a
beast...sounds like either this one doesn't, or it's not in the best of shape).
  #10   Report Post  
jay
 
Posts: n/a
Default

I'm surprised it damaged the sheathing. I found in my previous house that
they were just dumping into the attic for many years with no apparent
damage. Your attic probably has inadequate ventilation.

I believe the previous owner likely ran the shower at a high volume setting.
This is because when I moved into the house, I noticed that my shower faucet
has no volume adjustment, but the shower head itself (Speakman 2000) has an
adjustment and happened to be set at what, to me, seemed a REALLY high
volume setting. Granted the showhead, even at full blast, is supposed to be
regulated at 2.5gpm but at the setting the previous own had, I can guarantee
this generated a LOT of steam if he took a shower for more than a few
minutes at anything above lukewarm.

J.




  #11   Report Post  
Alan Sung
 
Posts: n/a
Default

"jay" wrote in message
news:qlCJd.19345$Vx2.18165@trndny01...
I was not expecting it to be done this way, but the two exhausts are very
close in proximity to each other, and the person who did the work decided

to
use a shared vent for both exhausts. In other words, what he did was
connect a flexible aluminum duct to each vent, and then used some type of
"T - connector" to join the two ducts together so they are both sharing

the
same shared flexible aluminum duct that leads to the exterior the unit.

I happened to notice that when one of the two fans is running, it actually
causes some air flow to be exhausted out of the other bathroom's idle fan.
If the fan in the main bath is running in the main bathroom, I can

actually
observe the blades of the fan in the master bath start to spin. Clearly

air
is being pushed from the main bath into the master bath when this happens.
If I briefly turn on the master bath's fan and shut it off I can observe

it
switch direction after it stops turning in the normal direction.

In the opposite situation (master bath's fan running when the main bath is
idle), the problem, to me, seems like it could be less severe. The blades
do not move in the main bath's fan. There does seem to be a little bit of
air flow though the fan opening, but I suspect not as much as in the
previously described situation.

Anyway, I just want to get opinions on whether or not this is worth
complaining about, or am I just being too picky? It seems to me that if
running one fan causes air to be pushed out of the other fan, this will,
most likely, cause some mosture to be transerred into the other bath (how
much I don't yet know) rather than the exterior. This seems like a less
than ideal setup.

Is this type of shared vent setup for bathroom exhausts considered to be
normal/common?

Which of the following do you recommend:

1) Immediately complain about this to the management company tomorrow,

since
clearly there is a problem with the duct setup chosen for this job

OR

2) should I perform a test to see how much steam actually gets into the
master bath when the main bath's fan is running (while showering in the

main
bath) BEFORE complaining about this?

OR

3) Do nothing, since this is a common setup, and likely not worth
complaining about.

Let me know what you think.


Venting two adjacent bathrooms thru a single combined vent is common and
works well if done properly. All that is needed in your current setup is to
add a backdraft damper on the each inflow side of the "Y" adapter. A diagram
of one can be seen at http://rewci.com/416splobada.html

-al sung
Rapid Realm Technology, Inc.
Hopkinton, MA


  #12   Report Post  
Clark W. Griswold, Jr.
 
Posts: n/a
Default

"jay" wrote:

Is this type of shared vent setup for bathroom exhausts considered to be
normal/common?


I wanted to have a central exhaust fan installed to reduce the noise of fans in
each bath, but was told by the local code enforcement person that separate
exhausts were required. Since that killed the economics of doing a central fan,
I just went with standard fans.

Which of the following do you recommend:


Neither. Call your code people and ask them.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a 480V Single Phase Circuit Joshua Home Repair 58 June 8th 20 02:39 PM
Bathroom fans improperly vented jeff Home Repair 11 June 4th 04 05:30 PM
Bathroom Mirror. Terry Home Repair 2 May 2nd 04 10:42 PM
How to Put 6" Duct to 1.5 HP Dust Collector? Jay Chan Woodworking 17 March 16th 04 04:11 PM
Bathroom exhaust fan and dryer fan [email protected] Home Ownership 1 September 4th 03 06:03 PM


All times are GMT +1. The time now is 11:40 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"