Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I am
hoping to get some clarification in this case. I understand that in the end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William


  #2   Report Post  
SQLit
 
Posts: n/a
Default


"William Deans" wrote in message
news:1104952543.3a4494f94d81e6df76883bae38f1fea8@t eranews...
Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William


All wiring subject to physical damage has to be protected. If you have
children up there then protect the wire. If the area is subject to only
authorized (intelligent) people then no protection is needed. Sorry to be
such a kill joy.

Outlets/lighting are required for equipment only. If you converting his
into an game room or bedroom then you have to follow the those rules.
Basically a outlet within 3 feet of a door and within 12 feet of each other
for all other walls. Your home you get to pick the height. Some local
jurisdictions require an switched light.

GFCI's are only required around water, and outside. Arc fault breakers are
now required for bedrooms.

If this is an unfinished space there are no requirements that I am aware of
for outlets other than for equipment.



  #3   Report Post  
B
 
Posts: n/a
Default

For code compliance, the sloped ceiling can't get less than 5 feet from the
floor. If you will finish the ceiling some day, put your new wires at the
four-foot level and eventually put the knee wall in front of it. Then you
won't have any wire or conduit on the ceiling at all.
-B
..
"William Deans" wrote in message
news:1104952543.3a4494f94d81e6df76883bae38f1fea8@t eranews...
Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William




  #4   Report Post  
 
Posts: n/a
Default

On Wed, 5 Jan 2005 13:32:02 -0700, "SQLit"
wrote:


"William Deans" wrote in message
news:1104952543.3a4494f94d81e6df76883bae38f1fea8@ teranews...
Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William


All wiring subject to physical damage has to be protected. If you have
children up there then protect the wire. If the area is subject to only
authorized (intelligent) people then no protection is needed. Sorry to be
such a kill joy.

Outlets/lighting are required for equipment only. If you converting his
into an game room or bedroom then you have to follow the those rules.
Basically a outlet within 3 feet of a door and within 12 feet of each other


Please help me here, I'm still learning, so can you tell me where it
states inside 3' of a door?



for all other walls. Your home you get to pick the height. Some local
jurisdictions require an switched light.

GFCI's are only required around water, and outside. Arc fault breakers are
now required for bedrooms.

If this is an unfinished space there are no requirements that I am aware of
for outlets other than for equipment.



thanks,

tom @ www.MedicalJobList.com



  #5   Report Post  
Colbyt
 
Posts: n/a
Default


wrote in message
...
On Wed, 5 Jan 2005 13:32:02 -0700, "SQLit"
wrote:


"William Deans" wrote in message
news:1104952543.3a4494f94d81e6df76883bae38f1fea8@ teranews...
Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor

and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so

I
am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William


All wiring subject to physical damage has to be protected. If you have
children up there then protect the wire. If the area is subject to only
authorized (intelligent) people then no protection is needed. Sorry to

be
such a kill joy.

Outlets/lighting are required for equipment only. If you converting his
into an game room or bedroom then you have to follow the those rules.
Basically a outlet within 3 feet of a door and within 12 feet of each

other

Please help me here, I'm still learning, so can you tell me where it
states inside 3' of a door?



The poster may have been referring to a switch box.

Also I think current code requires wall outlets every 6 foot of wall not the
12 as mentioned. Of course this only applies to living areas. This local
code here and NEC is pretty closely followed here.

Colbyt




  #6   Report Post  
Phisherman
 
Posts: n/a
Default

On Wed, 5 Jan 2005 14:22:25 -0500, "William Deans"
wrote:

Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I am
hoping to get some clarification in this case. I understand that in the end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

Since you have a finished floor and walls, treat it as you would
living space. All wires shall be protected and all outlets and
switches shall have cover plates.

  #7   Report Post  
 
Posts: n/a
Default

On Wed, 5 Jan 2005 21:26:55 -0500, "Colbyt"
wrote:


wrote in message
.. .
On Wed, 5 Jan 2005 13:32:02 -0700, "SQLit"
wrote:


"William Deans" wrote in message
news:1104952543.3a4494f94d81e6df76883bae38f1fea8@ teranews...
Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor

and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so

I
am
hoping to get some clarification in this case. I understand that in the
end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

All wiring subject to physical damage has to be protected. If you have
children up there then protect the wire. If the area is subject to only
authorized (intelligent) people then no protection is needed. Sorry to

be
such a kill joy.

Outlets/lighting are required for equipment only. If you converting his
into an game room or bedroom then you have to follow the those rules.
Basically a outlet within 3 feet of a door and within 12 feet of each

other

Please help me here, I'm still learning, so can you tell me where it
states inside 3' of a door?



The poster may have been referring to a switch box.

Also I think current code requires wall outlets every 6 foot of wall not the
12 as mentioned. Of course this only applies to living areas. This local


I think this is one of those great NEC badly writen codes. It says no
point along the floor line further than 6 feet from a receptacle. So
if you pick a point, and you measure 6 feet one way, receptacle so
code met, and 6 feet other way, receptacle so code met again, but the
receptacles are actuallly seperated by 12 feet.

Just a point, it's not 12 feet either, it's exactly as writen, thats
why I wondered by 3" when the code says withing 6 of a typical door.


code here and NEC is pretty closely followed here.

Colbyt



But thanks for your quick reply, I hope the orginal poster of 3" can
help me understand why.

later,

tom @ www.BookmarkAdmin.com



  #9   Report Post  
William Deans
 
Posts: n/a
Default

Greetings,

What is the proper way to protect the NM wires running perpendicular to the
rafters if I cannot drill holes?

Thanks,
William



"Phisherman" wrote in message
...
On Wed, 5 Jan 2005 14:22:25 -0500, "William Deans"
wrote:

Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

Since you have a finished floor and walls, treat it as you would
living space. All wires shall be protected and all outlets and
switches shall have cover plates.



  #10   Report Post  
 
Posts: n/a
Default

I think this is one of those great NEC badly writen codes. It says no
point along the floor line further than 6 feet from a receptacle. So
if you pick a point, and you measure 6 feet one way, receptacle so
code met, and 6 feet other way, receptacle so code met again, but the
receptacles are actuallly seperated by 12 feet.

Just a point, it's not 12 feet either, it's exactly as writen, thats
why I wondered by 3" when the code says withing 6 of a typical door.


The 6' (12') rule is designed so that normal appliances, (which generally
have a 6' cord) can be placed anywhere along the wall without needing
an extension cord.

The 3' rule sound like what I remember being required for a switchable
light source being within arms reach of the entry, but I'm pretty sure that
that only applies to spaces which are intended to be "occupiable".

I had interpreted the sloping-ceiling rule to be a description of what
floor-space counts toward the minimum dimension requirements:

Thus, (from memory) there has to be a rectangle that's at least 7' in
each horizontal direction, at least 70 square feet in area, over which
the ceiling must be 7'2" or higher, except that a sloping ceiling that's
no more than half the overhead can come down as low as 5', and/or
beams, pipes, or ductwork no closer together than 4' can come down
as low as 6'8"

I don't *THINK* that there's any requirement that the walls actually
come down from that 5' line, it's just that any space under them beyond
that doesn't count towards meeting the room's minimum dimensions.
But I could easily be wrong.

--Goedjn



  #11   Report Post  
Greg
 
Posts: n/a
Default


What is the proper way to protect the NM wires running perpendicular to the
rafters if I cannot drill holes


You run 1x boards next to them, the wire sits in the "valley".

  #12   Report Post  
Phisherman
 
Posts: n/a
Default

You can use conduit or run the wire along exiting ductwork or a board.
The idea is to make it difficult to hook a coat hanger (hook or
anything else) onto the wire. My personal preference is to use metal
conduit.

On Thu, 6 Jan 2005 13:00:39 -0500, "William Deans"
wrote:

Greetings,

What is the proper way to protect the NM wires running perpendicular to the
rafters if I cannot drill holes?

Thanks,
William



"Phisherman" wrote in message
.. .
On Wed, 5 Jan 2005 14:22:25 -0500, "William Deans"
wrote:

Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

Since you have a finished floor and walls, treat it as you would
living space. All wires shall be protected and all outlets and
switches shall have cover plates.



  #13   Report Post  
 
Posts: n/a
Default

On Thu, 6 Jan 2005 13:00:39 -0500, "William Deans"
wrote:

Greetings,

What is the proper way to protect the NM wires running perpendicular to the
rafters if I cannot drill holes?

Thanks,
William


If you can't maintain 1-1/4" between the outside edge of the wood and
the cable, nail guards(1/16" steel) must be installed, is what I
recall.






"Phisherman" wrote in message
.. .
On Wed, 5 Jan 2005 14:22:25 -0500, "William Deans"
wrote:

Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

Since you have a finished floor and walls, treat it as you would
living space. All wires shall be protected and all outlets and
switches shall have cover plates.




later,

tom @ www.ChopURL.com



  #14   Report Post  
William Deans
 
Posts: n/a
Default

Greetings,

If the wire is 12-2 should it be stapled to the 1x or should it be stapled
to the rafter directly beside the 1x (I assume the rafter--but I don't want
to assume incorrectly)? Is a 1x3 (*nominal) sufficient?

Thank you very much for your help,
William

"Greg" wrote in message
...

What is the proper way to protect the NM wires running perpendicular to

the
rafters if I cannot drill holes


You run 1x boards next to them, the wire sits in the "valley".



  #15   Report Post  
Duane Bozarth
 
Posts: n/a
Default

William Deans wrote:

Greetings,

If the wire is 12-2 should it be stapled to the 1x or should it be stapled
to the rafter directly beside the 1x (I assume the rafter--but I don't want
to assume incorrectly)? Is a 1x3 (*nominal) sufficient?



To the rafter beside the 1x...so the Romex is protected...then tack it
to the edge of the 1x between if it wants to sag. 1x3 would be fine...


  #16   Report Post  
 
Posts: n/a
Default

On Thu, 6 Jan 2005 13:00:39 -0500, "William Deans"
wrote:

Greetings,

What is the proper way to protect the NM wires running perpendicular to the
rafters if I cannot drill holes?

Thanks,
William


Sorry about my reply about 'nail guards' mis-read the question, and
since I didn't see anyone post an answer, I'll try this again.

If you goto 2002NEC34.23 (NM in attic spaces) it referrers you to
320.23(AC in attic spaces). Sure you can read it, but for those that
don't have the code book open, it 320.23 says install per 320.23(A)
and 320.23(B). To paraphrase:

320.23(A)- (seems to be your case), Where cable is run accross the
face of rafter withing 7 feet of the floor, or floor joists, in
attics, the cable shall be protected by guard strips. Where in a
space not accessible by permenant stairs, protection shall only be
required 6 feet of the enterances outside edge.


Now, ofcourse this was for information only, get the code book and
apply it to your situation, but it does appear it is ok to do what you
are doing in the attic if you just take a few more steps to it per
code.

Alway have a qualified person do/inspect your work.

hth,



"Phisherman" wrote in message
.. .
On Wed, 5 Jan 2005 14:22:25 -0500, "William Deans"
wrote:

Greetings,

What are the requirements for protecting NM 12 AWG wire in an attic run
along the ceiling? The attic has a walk-up stairwell, finished floor and
walls, but exposed rafters. The rafters start at about 4 feet high.

What are the requirements for outlets? How high? GFCI?

I have looked in the NEC but I do not want to misinterpret anything so I

am
hoping to get some clarification in this case. I understand that in the

end
I must do whatever the local code office wants but first I wanted to
understand what the NEC actually calls for.

Thank you for your time and energy,

William

Since you have a finished floor and walls, treat it as you would
living space. All wires shall be protected and all outlets and
switches shall have cover plates.



tom @ www.ChopURL.com


  #17   Report Post  
Dan Bolt
 
Posts: n/a
Default

On Thu, 06 Jan 2005 13:12:56 -0500, "
wrote:

I think this is one of those great NEC badly writen codes. It says no
point along the floor line further than 6 feet from a receptacle. So
if you pick a point, and you measure 6 feet one way, receptacle so
code met, and 6 feet other way, receptacle so code met again, but the
receptacles are actuallly seperated by 12 feet.

Just a point, it's not 12 feet either, it's exactly as writen, thats
why I wondered by 3" when the code says withing 6 of a typical door.


The 6' (12') rule is designed so that normal appliances, (which generally
have a 6' cord) can be placed anywhere along the wall without needing
an extension cord.

The 3' rule sound like what I remember being required for a switchable
light source being within arms reach of the entry, but I'm pretty sure that
that only applies to spaces which are intended to be "occupiable".

I had interpreted the sloping-ceiling rule to be a description of what
floor-space counts toward the minimum dimension requirements:

Thus, (from memory) there has to be a rectangle that's at least 7' in
each horizontal direction, at least 70 square feet in area, over which
the ceiling must be 7'2" or higher, except that a sloping ceiling that's
no more than half the overhead can come down as low as 5', and/or
beams, pipes, or ductwork no closer together than 4' can come down
as low as 6'8"

I don't *THINK* that there's any requirement that the walls actually
come down from that 5' line, it's just that any space under them beyond
that doesn't count towards meeting the room's minimum dimensions.
But I could easily be wrong.

--Goedjn


You aren't wrong, the space under less than 5' ceiling simply doesn't
count toward room square footage or minimum dimension.

Dan
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Attic mold issue revisited - 105 degree attic temperature today jeff Home Repair 7 March 31st 04 03:24 AM


All times are GMT +1. The time now is 08:52 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"