30amp plug to 20amp device
I want to run a 20amp treadmill on a 30amp outlet. Can I just use an adapter like this and get on with it?
https://www.homedepot.com/p/AC-WORKS...0520/301828753 Thanks, friends. |
#3
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Saturday, February 22, 2020 at 2:07:27 PM UTC-6, Ralph Mowery wrote:
In article , says... want to run a 20amp treadmill on a 30amp outlet. Can I just use an adapter like this and get on with it? https://www.homedepot.com/p/AC-WORKS...0520/301828753 That adapter seems to take the 240 volt outlet and just use one leg of it so you can plug a 120 volt device (usually a small camper or RV ) in to it. If your treadmill runs off 120 volts and uses 30 or less amps , the adapter should work fine. If the treadmill runs off 240 volts, then no. However I doubt they would put what seems to be a 120 volt plug on a 240 volt device. Thanks, Ralph! The treadmill tag states: INPUT 120Voc/60Hz CURRENT 17 A Sounds like I'm in business. |
#4
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On 2/22/2020 2:57 PM, Michael Wilson wrote:
I want to run a 20amp treadmill on a 30amp outlet. Can I just use an adapter like this and get on with it? https://www.homedepot.com/p/AC-WORKS...0520/301828753 Thanks, friends. You didn't say if your 30 amp outlet is providing 120v or 220/240v but most likely, it's 220/240v. I find the description on the web site in your link ambiguous. It's described as an "adapter", not a splitter. I use adapters when I travel abroad so I can use my dual voltage chargers and shaver (with North American 120v plugs) in another country's 220/240v socket. Those adapters don't change the voltage, just match a bunch of round holes to the flat blades on my plugs. Are you sure that the adapter you cite doesn't connect the two hot sides of the 220 outlet to the two flat blade sockets on the female side of the adapter and the neutral from the 220 outlet to the round hole on the female side of the adapter? Chances are that your assumption is correct. But I would plug the adapter into the 30 amp socket and check the voltage across the adapter's two female slots before connecting or turning on something as expensive as a treadmill just to make sure your assumption (that only one side of the 220 source is going to the adapter's female side) is correct. |
#6
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
Thanks for all your help with this! The outlet states: 125/250 V. NEMA 10/30.
|
#7
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On 2/22/2020 4:31 PM, Michael Wilson wrote:
Thanks for all your help with this! The outlet states: 125/250 V. NEMA 10/30. I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). |
#8
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Saturday, February 22, 2020 at 4:11:25 PM UTC-5, Peter wrote:
On 2/22/2020 2:57 PM, Michael Wilson wrote: I want to run a 20amp treadmill on a 30amp outlet. Can I just use an adapter like this and get on with it? https://www.homedepot.com/p/AC-WORKS...0520/301828753 Thanks, friends. You didn't say if your 30 amp outlet is providing 120v or 220/240v but most likely, it's 220/240v. I find the description on the web site in your link ambiguous. It's described as an "adapter", not a splitter. I use adapters when I travel abroad so I can use my dual voltage chargers and shaver (with North American 120v plugs) in another country's 220/240v socket. Those adapters don't change the voltage, just match a bunch of round holes to the flat blades on my plugs. Are you sure that the adapter you cite doesn't connect the two hot sides of the 220 outlet to the two flat blade sockets on the female side of the adapter and the neutral from the 220 outlet to the round hole on the female side of the adapter? Chances are that your assumption is correct. But I would plug the adapter into the 30 amp socket and check the voltage across the adapter's two female slots before connecting or turning on something as expensive as a treadmill just to make sure your assumption (that only one side of the 220 source is going to the adapter's female side) is correct. There is nothing ambiguous about the description. It clearly describes it as a 120 volt 15/20A adapter, that's what the receptacle shown is. There is no 240V anything that looks like that, for obvious reasons. And nothing mysterious there, it's a 4 wire plug on the other side, so using 3 of those connections it can supply 120V. It's specifically for what the OP wants, using a 240V 4 wire receptacle to be able to plug in a 120V load. |
#9
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On 2/23/20 7:24 AM, Peter wrote:
On 2/22/2020 4:31 PM, Michael Wilson wrote: Thanks for all your help with this!* The outlet states: 125/250 V. NEMA 10/30. I'm not questioning the safety rating of the outlet.* I'm questioning whether that outlet is supplying 120 or 220/240 volts.* And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. |
#10
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Sun, 23 Feb 2020 08:24:48 -0500, Peter
wrote: On 2/22/2020 4:31 PM, Michael Wilson wrote: Thanks for all your help with this! The outlet states: 125/250 V. NEMA 10/30. I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. |
#11
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
|
#12
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery
wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. I agree Europe uses different marking standards and it is not even standard across the EU. They are trying but old habits are hard to break and it takes a long time to replace all of the installed equipment. The NEC does recognize the European cord color standards tho. 400.21 (C) Neutral identification ... For jacketed cords furnished with appliances, one conductor having its insulation colored light blue, with the other conductors having their insulation of a readily distinguishable color other than white or gray. |
#13
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote:
On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. I agree Europe uses different marking standards and it is not even standard across the EU. They are trying but old habits are hard to break and it takes a long time to replace all of the installed equipment. The NEC does recognize the European cord color standards tho. 400.21 (C) Neutral identification ... For jacketed cords furnished with appliances, one conductor having its insulation colored light blue, with the other conductors having their insulation of a readily distinguishable color other than white or gray. |
#14
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4
wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. |
#16
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
|
#17
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Monday, February 24, 2020 at 10:51:01 AM UTC-5, wrote:
On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. Silly me, I thought the thread was about the 240V to 120V adapter that the OP posted a link to at HD. |
#18
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 09:35:40 -0800 (PST), trader_4
wrote: On Monday, February 24, 2020 at 10:51:01 AM UTC-5, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. Silly me, I thought the thread was about the 240V to 120V adapter that the OP posted a link to at HD. I was referring to the note you quoted and I assumed you were responding to. |
#19
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote:
One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? |
#20
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Monday, February 24, 2020 at 4:04:37 PM UTC-5, TimR wrote:
On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? It can supply 30A at 120 too. With 240 the 30A goes from one hot to the other. With 120 it goes from one hot to neutral. |
#21
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
|
#22
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 13:04:33 -0800 (PST), TimR
wrote: On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? It is a single phase 120v 30a circuit. The plug itself is not legal unless there is over current protection built in but I guess nobody ever pointed that out. I suppose they could put a 20a fusible link in there but it probably would not be replaceable. |
#23
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
|
#24
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder
wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. The RATING of the adapter does not necessarily mean that is what it is intended for. There seems to be 2 threads going on here. The OP's adapter and a post about some heaters. Ratings of devices is not the same as ratings of utilization equipment. LOTS of extention and power cords use brown and blue with green/yellow stripeed ground since much equipment is builkt for the "world market". North America may well br the only paet of the world that still uses black and white and even here on AC it's black and white - with white being neutral and black live - while on DC black is ground/- and RED is live or +. - The NEC acknowledges the blue neutral in some imported factory assembled cords but all chapter 3 wiring methods define white or gray as grounded conductors (usually but not always a neutral) and bare or green, green/yellow as equipment grounding conductors. |
#26
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 13:04:33 -0800 (PST), TimR
wrote: On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? Full 30 |
#27
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
|
#28
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 19:16:35 -0500, wrote:
On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. No, there is lots of 2 wire+ground #14 cable that is only rated at 300 volts. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. MOST extention or attached power cords ARE 600 volt The RATING of the adapter does not necessarily mean that is what it is intended for. There seems to be 2 threads going on here. The OP's adapter and a post about some heaters. Ratings of devices is not the same as ratings of utilization equipment. LOTS of extention and power cords use brown and blue with green/yellow stripeed ground since much equipment is builkt for the "world market". North America may well br the only paet of the world that still uses black and white and even here on AC it's black and white - with white being neutral and black live - while on DC black is ground/- and RED is live or +. - The NEC acknowledges the blue neutral in some imported factory assembled cords but all chapter 3 wiring methods define white or gray as grounded conductors (usually but not always a neutral) and bare or green, green/yellow as equipment grounding conductors. |
#29
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 21:20:06 -0500, Clare Snyder
wrote: On Mon, 24 Feb 2020 18:33:23 -0500, wrote: On Mon, 24 Feb 2020 13:04:33 -0800 (PST), TimR wrote: On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? It is a single phase 120v 30a circuit. The plug itself is not legal unless there is over current protection built in but I guess nobody ever pointed that out. I suppose they could put a 20a fusible link in there but it probably would not be replaceable. Are you sure?? A 20 amp outlet is also a 15 amp outlet - and WILL be fuded at 20 amps. The fuse is to protect the WIRING - not the device. As long as the adapter is rated to handle 30 amos it is legal and safe. (Legal if it has UL or CSA approval - not legal without even if it had a 15 amp fuse in it) There does not seem to be any NRTL approval stamp but the use of the receptacles is spelled out in 210.21(B)(3) Circuit Rating (Amperes) Receptacle Rating (Amperes) 15.................... Not over 15 20.................. 15 or 20 30..................... 30 40.................. 40 or 50 50...................... 50 You are plugging this into a 30 amp circuit and then coming out with a NEMA 5-20 receptacle. Without supplemental over current protection the utilization equipment you plug in is not adequately protected. For example, that lamp you want to test with will have an 18ga line cord and the maximum short circuit protection on 18ga fixture wire is 20a. (not to be confused with the 7a overcurrent protection) 240.5(B)(2) Fixture Wire. Fixture wire shall be permitted to be tapped to the branch-circuit conductor of a branch circuit in accordance with the following: (1) 20-ampere circuits €” 18 AWG, up to 15 m (50 ft) of run length (2) 20-ampere circuits €” 16 AWG, up to 30 m (100 ft) of run length (3) 20-ampere circuits €” 14 AWG and larger (4) 30-ampere circuits €” 14 AWG and larger (5) 40-ampere circuits €” 12 AWG and larger (6) 50-ampere circuits €” 12 AWG and larger The manufacturer will also tell you what the maximum circuit size you can plug their equipment into but that is generally enforced by the plug. You exceed those instructions at your own peril. |
#30
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 21:23:12 -0500, Clare Snyder
wrote: On Mon, 24 Feb 2020 19:16:35 -0500, wrote: On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. No, there is lots of 2 wire+ground #14 cable that is only rated at 300 volts. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. MOST extention or attached power cords ARE 600 volt Not really, the answer is printed or embossed on the cord. If it has a "J" in it, it is 300v (SJOT, SJT etc your regular "orange cord") That is even true of more expensive cords. ($100) Example of a "heavy Duty" cord https://www.homedepot.com/p/Southwire-100-ft-10-3-SJEOW-Outdoor-Heavy-Duty-T-Prene-Extension-Cord-with-Power-Light-Plug-1789SW0002/203066459 SJEOW cord is about as tough as you get in the consumer market S= hard service J= Junior (300v) E= Thermoplastic Elastomer O= Oil resistant W= Water Resistant. I have never seen any zip cord that was 600v and that even includes the large dryer and range cord. SO cord is 600v but that is the heavy black rubber cord you see at a carnival but you don't see much of that at the Home Depot. |
#31
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 22:59:38 -0500, wrote:
On Mon, 24 Feb 2020 21:20:06 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 18:33:23 -0500, wrote: On Mon, 24 Feb 2020 13:04:33 -0800 (PST), TimR wrote: On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? It is a single phase 120v 30a circuit. The plug itself is not legal unless there is over current protection built in but I guess nobody ever pointed that out. I suppose they could put a 20a fusible link in there but it probably would not be replaceable. Are you sure?? A 20 amp outlet is also a 15 amp outlet - and WILL be fuded at 20 amps. The fuse is to protect the WIRING - not the device. As long as the adapter is rated to handle 30 amos it is legal and safe. (Legal if it has UL or CSA approval - not legal without even if it had a 15 amp fuse in it) There does not seem to be any NRTL approval stamp but the use of the receptacles is spelled out in 210.21(B)(3) Circuit Rating (Amperes) Receptacle Rating (Amperes) 15.................... Not over 15 20.................. 15 or 20 30..................... 30 40.................. 40 or 50 50...................... 50 You are plugging this into a 30 amp circuit and then coming out with a NEMA 5-20 receptacle. Without supplemental over current protection the utilization equipment you plug in is not adequately protected. For example, that lamp you want to test with will have an 18ga line cord and the maximum short circuit protection on 18ga fixture wire is 20a. (not to be confused with the 7a overcurrent protection) 240.5(B)(2) Fixture Wire. Fixture wire shall be permitted to be tapped to the branch-circuit conductor of a branch circuit in accordance with the following: (1) 20-ampere circuits — 18 AWG, up to 15 m (50 ft) of run length (2) 20-ampere circuits — 16 AWG, up to 30 m (100 ft) of run length (3) 20-ampere circuits — 14 AWG and larger (4) 30-ampere circuits — 14 AWG and larger (5) 40-ampere circuits — 12 AWG and larger (6) 50-ampere circuits — 12 AWG and larger The manufacturer will also tell you what the maximum circuit size you can plug their equipment into but that is generally enforced by the plug. You exceed those instructions at your own peril. If he never plans to use it as a 30 amp 240 volt circuit the solution is simple. Replace the 30 amp breaker with a 20 |
#32
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Mon, 24 Feb 2020 23:19:11 -0500, wrote:
On Mon, 24 Feb 2020 21:23:12 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 19:16:35 -0500, wrote: On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. No, there is lots of 2 wire+ground #14 cable that is only rated at 300 volts. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. MOST extention or attached power cords ARE 600 volt Not really, the answer is printed or embossed on the cord. If it has a "J" in it, it is 300v (SJOT, SJT etc your regular "orange cord") That is even true of more expensive cords. ($100) Example of a "heavy Duty" cord https://www.homedepot.com/p/Southwire-100-ft-10-3-SJEOW-Outdoor-Heavy-Duty-T-Prene-Extension-Cord-with-Power-Light-Plug-1789SW0002/203066459 SJEOW cord is about as tough as you get in the consumer market S= hard service J= Junior (300v) E= Thermoplastic Elastomer O= Oil resistant W= Water Resistant. I have never seen any zip cord that was 600v and that even includes the large dryer and range cord. SO cord is 600v but that is the heavy black rubber cord you see at a carnival but you don't see much of that at the Home Depot. 600 volt NM-B 14/2G or 12/2G is the standard cable for residential use in canada. Extention cables without the J are 600 volt. All of my contractor grade cords have no J. SOOW 14AWG and STW 14,, and SOOW 12 Zip cord is NOT an "extention cable" in my books!! It's "Lamp cord" or "speaker wire" There ARE a lot of 300 volt ones out there too, I see - but in the garage or hangar and on job sites we see a lot of 600 volt. |
#33
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Tue, 25 Feb 2020 01:00:20 -0500, Clare Snyder
wrote: On Mon, 24 Feb 2020 23:19:11 -0500, wrote: On Mon, 24 Feb 2020 21:23:12 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 19:16:35 -0500, wrote: On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. No, there is lots of 2 wire+ground #14 cable that is only rated at 300 volts. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. MOST extention or attached power cords ARE 600 volt Not really, the answer is printed or embossed on the cord. If it has a "J" in it, it is 300v (SJOT, SJT etc your regular "orange cord") That is even true of more expensive cords. ($100) Example of a "heavy Duty" cord https://www.homedepot.com/p/Southwire-100-ft-10-3-SJEOW-Outdoor-Heavy-Duty-T-Prene-Extension-Cord-with-Power-Light-Plug-1789SW0002/203066459 SJEOW cord is about as tough as you get in the consumer market S= hard service J= Junior (300v) E= Thermoplastic Elastomer O= Oil resistant W= Water Resistant. I have never seen any zip cord that was 600v and that even includes the large dryer and range cord. SO cord is 600v but that is the heavy black rubber cord you see at a carnival but you don't see much of that at the Home Depot. 600 volt NM-B 14/2G or 12/2G is the standard cable for residential use in canada. "MOST extention or attached power cords ARE 600 volt" Cords are not cables. I already said all chapter 3 conductors are 600v or higher. Extention cables without the J are 600 volt. All of my contractor grade cords have no J. SOOW 14AWG and STW 14,, and SOOW 12 Zip cord is NOT an "extention cable" in my books!! It's "Lamp cord" or "speaker wire" They hook up cooktops and dryers with 10 ga zip cord. https://www.homedepot.com/p/HDX-6-ft...-833/100672782 There ARE a lot of 300 volt ones out there too, I see - but in the garage or hangar and on job sites we see a lot of 600 volt. I don't see a lot of SO cord but I suppose it is out there. |
#34
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Tue, 25 Feb 2020 01:23:46 -0500, wrote:
On Tue, 25 Feb 2020 01:00:20 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 23:19:11 -0500, wrote: On Mon, 24 Feb 2020 21:23:12 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 19:16:35 -0500, wrote: On Mon, 24 Feb 2020 18:35:05 -0500, Clare Snyder wrote: On Mon, 24 Feb 2020 10:50:46 -0500, wrote: On Mon, 24 Feb 2020 05:11:59 -0800 (PST), trader_4 wrote: On Sunday, February 23, 2020 at 2:06:41 PM UTC-5, wrote: On Sun, 23 Feb 2020 10:23:06 -0500, Ralph Mowery wrote: In article , says... I'm not questioning the safety rating of the outlet. I'm questioning whether that outlet is supplying 120 or 220/240 volts. And you can't tell just by examining what it is rated for. The reason that type of outlet is rated for 250v is that it is commonly used to supply power for electric dryers, ovens, ranges, and other high wattage appliances that are engineered to use the 220/240 supply voltage (yes, including use in countries that use 120v for almost all other electrical equipment). That is why NEMA standardizes these plugs. Yes, there are NEMA standards. With all the stuff coming into the US from China and sometimes other countries you never know what they may send into the US. Where I worked we had some big temperature controlled heaters. They ran on 480 volts 3 phase and anywhere from 10 to 200 amps. There was a big building project and another bank of heates were installed. While setting they up we could not get the high end to reach anywhere the 480 volts. Come to find out the equipment was sent in as 380 volt devices. I don't know what country uses that. On another note everything that had the 480 volt disconnects green ment that the breaker was supplying power and red ment it was not. Then the European stuff came in and their idea was red ment the breaker was on and it was dangerous to go in the box and green ment the breaker was off and it was safe. Exectally backwards. I don't remember the colors now,but even the 120 volt replacement cords had blue and brown wires instead of the more normal black and white we use in the US. Ordering low bid stuff from offshore is always a crap shoot but you should verify the voltage ratings are right. It's $20 for a simple adapter and Home Depot is selling it. You are not buying a "simple adapter" from Home Depot to get from 380v to 480 rating. 380v is the European standard 3p wye that gives them the single phase L/N 220v. (also in the other Brit dominated places like NZ and Oz). It will also be rated at 50hz but I doubt a toaster wire heater cares about that. And normal "romex" wiring in Canada and the US is rated for 300volts - - - - or some of it 360 or even 600. Romex (Type NM) is ALL 600v as is virtually all chapter 3 conductors although some are higher. No, there is lots of 2 wire+ground #14 cable that is only rated at 300 volts. The only place you see 300v is in "junior" cords and some fixture wires in Chapter 4. Then there is Chapter 7 low voltage wire. MOST extention or attached power cords ARE 600 volt Not really, the answer is printed or embossed on the cord. If it has a "J" in it, it is 300v (SJOT, SJT etc your regular "orange cord") That is even true of more expensive cords. ($100) Example of a "heavy Duty" cord https://www.homedepot.com/p/Southwire-100-ft-10-3-SJEOW-Outdoor-Heavy-Duty-T-Prene-Extension-Cord-with-Power-Light-Plug-1789SW0002/203066459 SJEOW cord is about as tough as you get in the consumer market S= hard service J= Junior (300v) E= Thermoplastic Elastomer O= Oil resistant W= Water Resistant. I have never seen any zip cord that was 600v and that even includes the large dryer and range cord. SO cord is 600v but that is the heavy black rubber cord you see at a carnival but you don't see much of that at the Home Depot. 600 volt NM-B 14/2G or 12/2G is the standard cable for residential use in canada. "MOST extention or attached power cords ARE 600 volt" Cords are not cables. I already said all chapter 3 conductors are 600v or higher. Extention cables without the J are 600 volt. All of my contractor grade cords have no J. SOOW 14AWG and STW 14,, and SOOW 12 Zip cord is NOT an "extention cable" in my books!! It's "Lamp cord" or "speaker wire" They hook up cooktops and dryers with 10 ga zip cord. https://www.homedepot.com/p/HDX-6-ft...-833/100672782 That's parallel conductor flexible cable but not what I would call "zip cord" It's common on "flat plug" extention cords but has much heavier insulation than "zip cord" which is usuallyconsidered to be 2 wire There ARE a lot of 300 volt ones out there too, I see - but in the garage or hangar and on job sites we see a lot of 600 volt. I don't see a lot of SO cord but I suppose it is out there. We have higher safety standards up here which may be why they are more common here than down there. |
#35
Posted to alt.home.repair
|
|||
|
|||
30amp plug to 20amp device
On Monday, February 24, 2020 at 9:20:09 PM UTC-5, Clare Snyder wrote:
On Mon, 24 Feb 2020 18:33:23 -0500, wrote: On Mon, 24 Feb 2020 13:04:33 -0800 (PST), TimR wrote: On Sunday, February 23, 2020 at 9:36:08 AM UTC-5, Dean Hoffman wrote: One of the pictures shows the male end marked as 125/250 volt with four prongs. The female end is marked as 125 volt with three openings. The connector loses one hot leg in the transition. Not being argumentative, asking because I don't know. Even though I should. That circuit can supply 30 A at 240V on both hot legs. The adapter will use one leg and get 120V. No problem, the treadmill is 120V. But the treadmill uses 17A. Is there still 30A available off just one leg? Or is there half of that, only 15A available? It is a single phase 120v 30a circuit. The plug itself is not legal unless there is over current protection built in but I guess nobody ever pointed that out. I suppose they could put a 20a fusible link in there but it probably would not be replaceable. Are you sure?? A 20 amp outlet is also a 15 amp outlet - and WILL be fuded at 20 amps. The fuse is to protect the WIRING - not the device. But part of the design of the plug, cord, internals of any appliance is that it's going to be plugged into a circuit that was designed for that plug. In this case, using that adapter, Fretwell has a point, you could plug a 15 or 20A appliance into a 30A circuit. If the cord shorts, the designers were expecting it to be fused at no more than 20A. Is it a big deal in the real world that's going to create fires? Probably not. But it doesn't sound code compliant either. As long as the adapter is rated to handle 30 amos it is legal and safe. (Legal if it has UL or CSA approval - not legal without even if it had a 15 amp fuse in it) |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
20amp Circuit How many computers | Home Repair | |||
14 Wire on 20amp Breaker... | Home Repair | |||
15amp breaker on 20amp circuit - ok? | Home Repair | |||
Romex - Connect 12g to 14g on 20amp circuit OK? | Home Ownership | |||
Routing cable from garage to basement for 20amp circuit... | Home Repair |