Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Who knows about servicing well pressure tanks??

On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregøry Hall

Message-ID:
"My time is correct. Maybe you forget to change your
time to match mine the last time you forged me, punk." --Checkmate


It should be pressurized so that it's a couple pounds lower than
the pressure that the pump starts. You set it with the tank drained.
How you're going to do any of that, especially getting the tank empty
when it's buried, IDK. I've never heard of one being buried before,
that's really dumb.
Typically they are placed outside a building, in a basement, or even
just surrounded by some bushes to hide and protect it, if there is no
other reasonable alternative. If you have to dig it out to get to it,
I'd consider replacing it with an above ground one, if it were me.
Especially if it's a shared one, they don't cost all that much.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 30
Default Who knows about servicing well pressure tanks??

On Sat, 1 Dec 2018 07:05:20 -0800 (PST), trader_4
wrote:

On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregřry Hall

Message-ID:
"My time is correct. Maybe you forget to change your
time to match mine the last time you forged me, punk." --Checkmate


It should be pressurized so that it's a couple pounds lower than
the pressure that the pump starts. You set it with the tank drained.
How you're going to do any of that, especially getting the tank empty
when it's buried, IDK. I've never heard of one being buried before,
that's really dumb.
Typically they are placed outside a building, in a basement, or even
just surrounded by some bushes to hide and protect it, if there is no
other reasonable alternative. If you have to dig it out to get to it,
I'd consider replacing it with an above ground one, if it were me.
Especially if it's a shared one, they don't cost all that much.


I just changed mine a few weeks ago. Everything trader said above is
correct. But, I can't tell which type you have. Older tanks (without
a bladder) lasted forever, but someone had to add air regularly to
keep them working. The air eventually dissolves into the water since
it is in direct contact. The newer tanks with the bladder don't have
that problem, but in my experience don't last very long. Usually less
than 10 years and, in a few cases, only a few years. (Those were then
replaced under warranty because they were guarateed for 7 years -
WellXtrol brand). When the bladder fails, they still work for a while
because, like the old style tanks, it takes a while for the air to
dissolve in the water. Like trader said, I never heard of the
pressure tank being buried. Since I live is a northern climate, I
have only ever seen them in a basement or utility room. Good luck.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Who knows about servicing well pressure tanks??

On Saturday, December 1, 2018 at 10:28:54 AM UTC-5, Pat wrote:
On Sat, 1 Dec 2018 07:05:20 -0800 (PST), trader_4
wrote:

On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq.. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregøry Hall

Message-ID:
"My time is correct. Maybe you forget to change your
time to match mine the last time you forged me, punk." --Checkmate


It should be pressurized so that it's a couple pounds lower than
the pressure that the pump starts. You set it with the tank drained.
How you're going to do any of that, especially getting the tank empty
when it's buried, IDK. I've never heard of one being buried before,
that's really dumb.
Typically they are placed outside a building, in a basement, or even
just surrounded by some bushes to hide and protect it, if there is no
other reasonable alternative. If you have to dig it out to get to it,
I'd consider replacing it with an above ground one, if it were me.
Especially if it's a shared one, they don't cost all that much.


I just changed mine a few weeks ago. Everything trader said above is
correct. But, I can't tell which type you have.


Agree, I assumed it's bladder type since it was done in 2002, but IDK
who in their right mind would bury one of either type, so who knows.




Older tanks (without
a bladder) lasted forever, but someone had to add air regularly to
keep them working. The air eventually dissolves into the water since
it is in direct contact.


Actually they had automatic systems on them to maintain the air level.
If that failed, then they water logged.

The newer tanks with the bladder don't have
that problem, but in my experience don't last very long. Usually less
than 10 years and, in a few cases, only a few years. (Those were then
replaced under warranty because they were guarateed for 7 years -
WellXtrol brand). When the bladder fails, they still work for a while
because, like the old style tanks, it takes a while for the air to
dissolve in the water. Like trader said, I never heard of the
pressure tank being buried. Since I live is a northern climate, I
have only ever seen them in a basement or utility room. Good luck.


Here in NYC area there are a lot of them outside, for irrigation wells.
You drain them for winter. I agree and should have said that the bladder
may have failed. Two ways to figure that out. One is to re-pressurize
it and see if it only lasts a few months. Other would be to remove the
bladder and inspect. I'd go for option two if it's buried and
it's going to be reburied. Just replace the bladder. But like I said,
I'd strongly consider relocating it.



  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,636
Default Who knows about servicing well pressure tanks??

On 12/1/18 9:05 AM, trader_4 wrote:
On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregøry Hall


How does the member know the well pump is cycling too often?

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default Who knows about servicing well pressure tanks??

On Saturday, December 1, 2018 at 10:56:43 AM UTC-5, Dean Hoffman wrote:
On 12/1/18 9:05 AM, trader_4 wrote:
On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregøry Hall


How does the member know the well pump is cycling too often?


"It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on. " ?


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,297
Default Who knows about servicing well pressure tanks??

On 12/1/2018 10:28 AM, Pat wrote:
On Sat, 1 Dec 2018 07:05:20 -0800 (PST), trader_4
wrote:

On Friday, November 30, 2018 at 9:35:09 PM UTC-5, Sir Gregory Hall, Esq. wrote:
I am on a shared well which was dug in 2002 and has
a pump at 48 feet depth and a casing of 60 feet.

Recently, it was noted by a member of the HOA that
the pump may be cycling too often. This is probably
because the pressure tank has NEVER been serviced
since 2002. Googled said well pumps and pressure
tanks may last up to 25 years but the pressure tanks
usually need to be checked for proper air pressure and
capacity so the rubber diaphragm works properly so the
pump doesn't cycle off and on constantly. It would appear
that when about two to three gallons of water is let out
the tap at the well head that the pump cycles on.

According to the plates on the well head the pump is
rated at 15 gpm at 80 psi. That means the pressure tank
is probably about 25 gallons. Not very large. But, it
is buried so it may take a metal detector to locate it but
I suspect it is right next to the well head in line with a
sleeved 4" PVC ball valve that Tees to the water main
that proceeds along the main road.

Has anybody here in these groups any experience with
putting more air into the bladder side of a well pressure
tank?

--

Yours Truly,
Gregøry Hall

Message-ID:
"My time is correct. Maybe you forget to change your
time to match mine the last time you forged me, punk." --Checkmate


It should be pressurized so that it's a couple pounds lower than
the pressure that the pump starts. You set it with the tank drained.
How you're going to do any of that, especially getting the tank empty
when it's buried, IDK. I've never heard of one being buried before,
that's really dumb.
Typically they are placed outside a building, in a basement, or even
just surrounded by some bushes to hide and protect it, if there is no
other reasonable alternative. If you have to dig it out to get to it,
I'd consider replacing it with an above ground one, if it were me.
Especially if it's a shared one, they don't cost all that much.


I just changed mine a few weeks ago. Everything trader said above is
correct. But, I can't tell which type you have. Older tanks (without
a bladder) lasted forever, but someone had to add air regularly to
keep them working. The air eventually dissolves into the water since
it is in direct contact. The newer tanks with the bladder don't have
that problem, but in my experience don't last very long. Usually less
than 10 years and, in a few cases, only a few years. (Those were then
replaced under warranty because they were guarateed for 7 years -
WellXtrol brand). When the bladder fails, they still work for a while
because, like the old style tanks, it takes a while for the air to
dissolve in the water. Like trader said, I never heard of the
pressure tank being buried. Since I live is a northern climate, I
have only ever seen them in a basement or utility room. Good luck.

In over 40 years I've needed 2 new tanks because they started leaking.
The last was over 10 years ago and I recently had the plumber over for a
couple of other jobs and asked him to check the pressure and it was
fine. I had not noticed any more frequent recycling which can be sign
of low pressure in the bladder.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Propane temporarily switching small tanks for big tanks George P Home Repair 21 September 24th 18 05:54 PM
Well, well, well. Apparently even Steve Bannon thinks meeting withthe Russians was.......treason! trader_4 Home Repair 4 January 4th 18 02:15 PM
Well Water and Storage tanks, Any good sites out there? Scott Townsend Home Repair 0 February 20th 06 07:56 PM
Well well well...another pressure tank question N7RX Home Repair 13 October 7th 04 03:01 AM