Wire gauge needed for amps
I was looking for a site that would tell me which gauge wire to use based on amps and length of wire.
Wanted to run 3 feet for a 15 amp load. Thanks, Andy |
#2
Posted to alt.home.repair
|
|||
|
|||
Wire gauge needed for amps
|
#3
Posted to alt.home.repair
|
|||
|
|||
Wire gauge needed for amps
On 1/2/2018 7:06 PM, Andy wrote:
I was looking for a site that would tell me which gauge wire to use based on amps and length of wire. Wanted to run 3 feet for a 15 amp load. Thanks, Andy If you use thwn-2 copper wire with 90c devices, then you can go as small as 16 ga |
#4
Posted to alt.home.repair
|
|||
|
|||
Wire gauge needed for amps
On Tue, 2 Jan 2018 20:01:19 -0500, Jack Legg Electric
wrote: On 1/2/2018 7:06 PM, Andy wrote: I was looking for a site that would tell me which gauge wire to use based on amps and length of wire. Wanted to run 3 feet for a 15 amp load. Thanks, Andy If you use thwn-2 copper wire with 90c devices, then you can go as small as 16 ga The trick is finding that mythical 90c device. Screw binding terminals are only rated at 60c. (the ones you see on regular switches and receptacles). The "lug" type can be rated 75c but there is not much rated 90c. That still does not deal with voltage drop and that may be what the OP cares about. A lot depends on the voltage you are dealing with. The voltage drop is a function of amperage and wire size but dropping a few volts at 120v is not the same as dropping that same few volts at 12v. That is why we really need to know the percentage of voltage drop, not the absolute VD number. There are plenty of VD calculators online |
#5
Posted to alt.home.repair
|
|||
|
|||
Wire gauge needed for amps
On 1/2/2018 7:27 PM, Ralph Mowery wrote:
In article , says... I was looking for a site that would tell me which gauge wire to use based on amps and length of wire. Wanted to run 3 feet for a 15 amp load. Thanks, Andy For short runs I would just use what is normally the code for house wiring. For 15 amps that would be # 14, 20 amps #12. That is what I'd use too. As for the length, it is ok for the size of you house so would be good for 3 feet. When you get to 100 feet or more voltage drop could be a concern. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
A question of turntables, amps and phono pre-amps. | UK diy | |||
15 amps or 20 amps | Home Repair | |||
Can I stick two 4 gauge and one 6 gauge wire into a 3/4" conduit | Home Repair | |||
80 ft of 6 gauge wire conducting 100 AMPS? | Home Repair | |||
80 ft of 6 gauge wire conducting 100 AMPS? | Home Repair |