80 ft of 6 gauge wire conducting 100 AMPS?
What do you think will happen? I think it will burn up the insulation on
the wire. "Dave J" wrote in message ... I have a subpanel that is about 80 feet away from the main panel. It uses 6 gauge copper THHN wires conducting 220V current, in a 3/4" raceway. What will happen if I upgrade the breakers to 100 A and try to use close to 100A of 220V. Thanks, Dave J. |
#2
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
On Mon, 10 Oct 2005 11:33:07 -0400, John Grabowski wrote:
What do you think will happen? I think it will burn up the insulation on the wire. Not likely. Resistance of 6 gauge wire is 0.47 ohms per 1,000 feet. I have 160 feet (going both ways), which makes resistance equal to 160*0.47/1000 = 0.075 ohm. At 100 amps, a 0.047 ohm resistor would produce 7.5 watts of power total, a negligible amount. http://www.bnoack.com/index.html?htt...esistance.html Is my calculation wrong? Dave J "Dave J" wrote in message ... I have a subpanel that is about 80 feet away from the main panel. It uses 6 gauge copper THHN wires conducting 220V current, in a 3/4" raceway. What will happen if I upgrade the breakers to 100 A and try to use close to 100A of 220V. Thanks, Dave J. -- |
#3
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
"Dave J" wrote in message ... On Mon, 10 Oct 2005 11:33:07 -0400, John Grabowski wrote: What do you think will happen? I think it will burn up the insulation on the wire. Not likely. Resistance of 6 gauge wire is 0.47 ohms per 1,000 feet. I have 160 feet (going both ways), which makes resistance equal to 160*0.47/1000 = 0.075 ohm. At 100 amps, a 0.047 ohm resistor would produce 7.5 watts of power total, a negligible amount. http://www.bnoack.com/index.html?htt...ata/wire-resis tance.html Is my calculation wrong? Dave J Power is current SQUARED times resistance... |
#4
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
Dave J wrote:
On Mon, 10 Oct 2005 11:33:07 -0400, John Grabowski wrote: What do you think will happen? I think it will burn up the insulation on the wire. Not likely. Resistance of 6 gauge wire is 0.47 ohms per 1,000 feet. I have 160 feet (going both ways), which makes resistance equal to 160*0.47/1000 = 0.075 ohm. At 100 amps, a 0.047 ohm resistor would produce 7.5 watts of power total, a negligible amount. http://www.bnoack.com/index.html?htt...esistance.html Is my calculation wrong? P=I^2*R Dave J |
#5
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
Dave J wrote:
Not likely. Resistance of 6 gauge wire is 0.47 ohms per 1,000 feet. I have 160 feet (going both ways), which makes resistance equal to 160*0.47/1000 = 0.075 ohm. At 100 amps, a 0.047 ohm resistor would produce 7.5 VOLTS dropped across the wire. 7.5 volts times 100 amps gives 750 watts dissipated in the wire. watts of power total, a negligible amount. -- If John McCain gets the 2008 Republican Presidential nomination, my vote for President will be a write-in for Jiang Zemin. |
#6
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
VOLTS dropped across the wire. 7.5 volts times 100 amps gives 750
watts dissipated in the wire. 750 watts over 80 feet of wire isn't so bad. NEC lists the ampacity of 6 gauge wire as 55 amps or 70 amps depending on environment and raceway. 100 amps is certainly not up to code but probably won't cause an instant fire! Upgrading to a larger wire size may well require a larger raceway, too. Tim. |
#7
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
|
#8
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
"Dave J" wrote in message ... On Mon, 10 Oct 2005 11:33:07 -0400, John Grabowski wrote: What do you think will happen? I think it will burn up the insulation on the wire. Not likely. Resistance of 6 gauge wire is 0.47 ohms per 1,000 feet. I have 160 feet (going both ways), which makes resistance equal to 160*0.47/1000 = 0.075 ohm. At 100 amps, a 0.047 ohm resistor would produce 7.5 watts of power total, a negligible amount. http://www.bnoack.com/index.html?htt...esistance.html Is my calculation wrong? Dave J Yep! Wrong. Two things. My wire tables show 0.39 Ohms per thousand. Also, the formula for power consumed in a resistor is I *squared* times the resistance. Hence, 100 x 100 x 0.39 x 160/1000 = 624 Watts *total*, or 624/80 = 7.8 Watts *per foot* of conduit. "Dave J" wrote in message ... I have a subpanel that is about 80 feet away from the main panel. It uses 6 gauge copper THHN wires conducting 220V current, in a 3/4" raceway. What will happen if I upgrade the breakers to 100 A and try to use close to 100A of 220V. Thanks, Dave J. -- |
#9
|
|||
|
|||
80 ft of 6 gauge wire conducting 100 AMPS?
|
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Whole house surge protector? | Home Repair | |||
Run 12 gauge wire and install 10 20 AMP receptacles | Home Repair | |||
Am I grounded? Electrically speaking. | Home Repair | |||
? Stranded wire OK for grounding electrical boxes? | Home Repair | |||
OT repairing Resistance wire heater in Refrigerator | Metalworking |