Per NEC, can romex wiring be run across the faces of ceiling joists (stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks


  #2   Report Post  
A
 
Posts: n/a
Default wiring across joists

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
link.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks




  #3   Report Post  
A
 
Posts: n/a
Default wiring across joists

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
link.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks




  #4   Report Post  
ChiliJim
 
Posts: n/a
Default wiring across joists

I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks





  #5   Report Post  
ChiliJim
 
Posts: n/a
Default wiring across joists

I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks







  #6   Report Post  
EJ
 
Posts: n/a
Default wiring across joists

"ChiliJim" wrote in message
news
I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden

box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have

to
run between joists and drill through as needed?)

Thanks


My scared book sayeth:

"Exposed Romex cable smaller than 8AWG if three-conductor or smaller than
6AWG if two-conductor running across joists in unfinished basements must
either be run through holes in joists or on running boards (see 334.15(C) in
2002 NEC)."

EJ


  #7   Report Post  
EJ
 
Posts: n/a
Default wiring across joists

"ChiliJim" wrote in message
news
I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a wooden

box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists

(stapled
to the faces) if a suspended ceiling will be installed? (or do I have

to
run between joists and drill through as needed?)

Thanks


My scared book sayeth:

"Exposed Romex cable smaller than 8AWG if three-conductor or smaller than
6AWG if two-conductor running across joists in unfinished basements must
either be run through holes in joists or on running boards (see 334.15(C) in
2002 NEC)."

EJ


  #8   Report Post  
Phisherman
 
Posts: n/a
Default wiring across joists

On Fri, 28 Nov 2003 14:54:19 GMT, "JC" wrote:

Per NEC, can romex wiring be run across the faces of ceiling joists (stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks


Drill a hole through the center of each joist.
  #9   Report Post  
Phisherman
 
Posts: n/a
Default wiring across joists

On Fri, 28 Nov 2003 14:54:19 GMT, "JC" wrote:

Per NEC, can romex wiring be run across the faces of ceiling joists (stapled
to the faces) if a suspended ceiling will be installed? (or do I have to
run between joists and drill through as needed?)

Thanks


Drill a hole through the center of each joist.
  #10   Report Post  
Jimmy
 
Posts: n/a
Default wiring across joists


"EJ" wrote in message
news:OT2yb.248827$mZ5.1854247@attbi_s54...
"ChiliJim" wrote in message
news
I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board

is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a

wooden
box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists
(stapled
to the faces) if a suspended ceiling will be installed? (or do I

have
to
run between joists and drill through as needed?)

Thanks


My scared book sayeth:

"Exposed Romex cable smaller than 8AWG if three-conductor or smaller than
6AWG if two-conductor running across joists in unfinished basements must
either be run through holes in joists or on running boards (see 334.15(C)

in
2002 NEC)."

EJ

When I built new garage I had an issue with this since the wiring I put in

was suppose to be temporary(2 years). I wanted to staple the wires on the
bottom of the ceiling joist. AT first they said I had to drill the joist,
then I got them to let me run it over the top of the ceiling joist. Anyway
when I get through there will be 4" wireway around the perimeter of the shop
with all wiring done from there.




  #11   Report Post  
Jimmy
 
Posts: n/a
Default wiring across joists


"EJ" wrote in message
news:OT2yb.248827$mZ5.1854247@attbi_s54...
"ChiliJim" wrote in message
news
I was once told by the local building inspector that the purpose of
the 1" X 4" board was to prevent you from hanging anything on the
exxposed wires. This was only a requirement if a permanent ceiling
(drywall) was not going to be installed immediately. (This was in a
basement of a new house that I had the builder prewire so that I could
finsish it in the future). He insisted that it was guaranteed that me
(or my wife) would eventually hang something (like a coat hanger) on
the wires for expediency. Seemed pretty anal to me at the time but it
didn't take much effort for the builder to nail up some scrap siding
and the inspector was happy.

After he left the builder (30 yrs. experience) muttered, "that guy was
flipping hamburgers three weeks ago and now he's telling me how to do
construction".

Jim


On Fri, 28 Nov 2003 19:11:09 GMT, "A" wrote:

It totally depends on your local by-law office rules.

Ours allows stapling wires under the joists as long as a 1" X 4" board

is
nailed parallel to the wires to 'protect' them. I have no idea what
protection this gives - I would have thought they would require a

wooden
box
(or metal raceway) type barrier to 'protect' the wires.




"JC" wrote in message
hlink.net...
Per NEC, can romex wiring be run across the faces of ceiling joists
(stapled
to the faces) if a suspended ceiling will be installed? (or do I

have
to
run between joists and drill through as needed?)

Thanks


My scared book sayeth:

"Exposed Romex cable smaller than 8AWG if three-conductor or smaller than
6AWG if two-conductor running across joists in unfinished basements must
either be run through holes in joists or on running boards (see 334.15(C)

in
2002 NEC)."

EJ

When I built new garage I had an issue with this since the wiring I put in

was suppose to be temporary(2 years). I wanted to staple the wires on the
bottom of the ceiling joist. AT first they said I had to drill the joist,
then I got them to let me run it over the top of the ceiling joist. Anyway
when I get through there will be 4" wireway around the perimeter of the shop
with all wiring done from there.


  #12   Report Post  
Tom Horne
 
Posts: n/a
Default wiring across joists

When I built new garage I had an issue with this since the wiring I put in
was suppose to be temporary(2 years). I wanted to staple the wires on the
bottom of the ceiling joist. AT first they said I had to drill the joist,
then I got them to let me run it over the top of the ceiling joist. Anyway
when I get through there will be 4" wireway around the perimeter of the shop
with all wiring done from there.


When you wire a shop, laboratory, or modern office that kind of approach
is the way to go. I have installed perimeter raceway in those
occupancies as well as in museums and historic homes. The raceway is
available in a cross sectional dimension that lends itself to being
installed in place of baseboards so that you can have any outlet at any
point along the wall line. If I should ever have a custom home built I
think I may install it in every room.
--
Tom H

  #13   Report Post  
Tom Horne
 
Posts: n/a
Default wiring across joists

When I built new garage I had an issue with this since the wiring I put in
was suppose to be temporary(2 years). I wanted to staple the wires on the
bottom of the ceiling joist. AT first they said I had to drill the joist,
then I got them to let me run it over the top of the ceiling joist. Anyway
when I get through there will be 4" wireway around the perimeter of the shop
with all wiring done from there.


When you wire a shop, laboratory, or modern office that kind of approach
is the way to go. I have installed perimeter raceway in those
occupancies as well as in museums and historic homes. The raceway is
available in a cross sectional dimension that lends itself to being
installed in place of baseboards so that you can have any outlet at any
point along the wall line. If I should ever have a custom home built I
think I may install it in every room.
--
Tom H

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Loft conversion joists Christian McArdle UK diy 55 July 13th 05 11:10 PM
Crossing ceiling joists with lighting cable Lobster UK diy 4 February 19th 04 09:00 PM
Uneven floor joists....installing new floor covering...2 problems. Dave Bonnell Home Repair 5 October 29th 03 02:58 PM
How long to leave reconstructed piers before fixing joists? RichardS UK diy 2 October 21st 03 09:25 PM
Alternate methods of attaching ceiling joists ? David G UK diy 2 September 8th 03 05:29 PM


All times are GMT +1. The time now is 12:22 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"